Default IR & Load centers

Here are two set of identical pic's that I was playing around with. The breaker closeup has different temps and the overall panel has different temps. What would bother a person about these images. I did indeed change the E setting in the software to show the difference.
Attached Thumbnails
ir-and-load-centers-dfdf.jpg   ir-and-load-centers-ir_0893.jpg   ir-and-load-centers-ir_0894.jpg   ir-and-load-centers-dfdf-1-.jpg.jpg
Views:	59
Size:	100.6 KB
ID:	25543  



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #2  
Old 12/5/08, 7:47 PM
bkelly1's Avatar
bkelly1 bkelly1 is offline
Active Poster
 
Join Date: Jan 2004
Location: Rives, TN
Posts: 1,738
Please Note: bkelly1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: IR & Load centers

Did you measure the amps on phase b? Just curious.
Reply With Quote
  #3  
Old 12/5/08, 7:54 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: IR & Load centers

Quote:
Originally Posted by bkelly1 View Post
Did you measure the amps on phase b? Just curious.
No I did not



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #4  
Old 12/5/08, 9:52 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: IR & Load centers

I might add I did call out the breaker in my report it is a 220 volt breaker feeding a kitchen range would you consider the temp as excessive



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #5  
Old 12/5/08, 10:20 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,927
Default Re: IR & Load centers

I would say a 20 rise leg to leg and 50 above ambient is worth investigating.



"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein

David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #6  
Old 12/5/08, 11:53 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: IR & Load centers

Quote:
Originally Posted by dandersen View Post
I would say a 20 rise leg to leg and 50 above ambient is worth investigating.
Your right and that was the point of my post 120 degree's does not necessarily mean a problem but being a 220 volt circuit the load should have been more balanced and that was what caught my attention BTW the electrican did find a loose connection at the wall outlet to the kitchen stove. Gotta luv these cameras. This particular problem would have not been detected with out it as the wire at the breaker had no indication of excessive heat but would have at some point in the future. In my past life this would have been called preventive maintenance.



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #7  
Old 12/6/08, 8:58 AM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,927
Default Re: IR & Load centers

The Naysayers didn't bit for this one. Maybe they read Jim Seffrin's "standards" document he posted!?



"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein

David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #8  
Old 12/6/08, 10:51 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: IR & Load centers

Quote:
Originally Posted by dandersen View Post
The Naysayers didn't bit for this one. Maybe they read Jim Seffrin's "standards" document he posted!?

Me thinks they are getting wise to me I have been known to run a trap line



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #9  
Old 12/6/08, 8:33 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: IR & Load centers

Wouldn't an IR thermometer have told you the same thing?
Reply With Quote
  #10  
Old 12/6/08, 9:34 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,927
Default Re: IR & Load centers

Yes, to a point.
They do not have the emissivity adjustment for the accuracy you are able to get with the Camera. Some just give you a setting for "dull" or "shiny" settings.

As you can see with Charlies scans, incorrect E setting gives incorrect temp readings and delta T.

I have used IR Thermo's for many, many years. If you pay very close attention and have a good memory, you can pick up on things but you will never establish the patterns we use to identify what type of anomaly we are scanning.



"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein

David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #11  
Old 12/6/08, 10:28 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: IR & Load centers

Quote:
Originally Posted by dandersen View Post
Yes, to a point.
They do not have the emissivity adjustment for the accuracy you are able to get with the Camera. Some just give you a setting for "dull" or "shiny" settings.

As you can see with Charlies scans, incorrect E setting gives incorrect temp readings and delta T.

I have used IR Thermo's for many, many years. If you pay very close attention and have a good memory, you can pick up on things but you will never establish the patterns we use to identify what type of anomaly we are scanning.

Ahhh, I see, so which pictures depict the incorrect settings again?
Reply With Quote
  #12  
Old 12/7/08, 1:38 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: IR & Load centers

Quote:
Originally Posted by bkelly2 View Post
Ahhh, I see, so which pictures depict the incorrect settings again?
Bk the E valve was adjusted within the software just to give an example of how the E setting can effect the temp. If you would notice I have a close up of a breaker and a distance image of a panel the distance to the target will also effect the temp. In this example the higher the E valve the lower the temp reading and the lower the E valve the higher the temp indicating one needs to know the E valve of the target if the temp is the main concern as in electrical.

The same as David I used a Thermal gun for years no comparision takes to long for one. Second to hard to place the image of that little dot from the infrared gun in a report Third have never had a electrican question my ability with the camera they seem to understand a picture. Fourth gets me more business when a client has viewed one of my reports. That in its self was worth the price of the camera. I don't understand why you and Duffy both are not doing electrical scans Duffy keeps saying not enough rain in AZ to warrant a camera surely you have electrical or are you guys still burning kerosene



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #13  
Old 12/7/08, 5:48 AM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: IR & Load centers

Well then, just adjust your E setting so you "change the temperature" to a safe level and leave the temperature set there.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Where do I put the Aquarium? mcyr Structural Inspections 3 11/6/07 3:05 PM


All times are GMT -4. The time now is 8:17 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts