Default IR Pics of Natural Gas Furnace & 30 Amp Breaker

These IR pictures were taken today from a 19 year old gas furnace and 30 amp breaker (notice the temperature of the top of furnace and breaker). The house also had extensive termite damage, polybutylene plumbing, mold inside the garage, and required a new roof and HVAC system. Ouch!
Attached Thumbnails
ir-pics-natural-gas-furnace-and-30-amp-breaker-ir_1110.jpg   ir-pics-natural-gas-furnace-and-30-amp-breaker-ir_1101.jpg  
Reply With Quote
  #2  
Old 11/4/08, 6:28 PM
Darren Spencer Darren Spencer is offline
InterNACHI Member
 
Join Date: Nov 2007
Location: Bellevue, WA
Posts: 549
Default Re: IR Pics of Natural Gas Furnace & 30 Amp Breaker

what temperature is too hot for a 30 amp breaker?
Reply With Quote
  #3  
Old 11/4/08, 6:46 PM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: IR Pics of Natural Gas Furnace & 30 Amp Breaker

Quote:
Originally Posted by dspencer1 View Post
what temperature is too hot for a 30 amp breaker?
From the Square D website:


"Square D circuit breakers can be applied in ambient temperatures within the
range of -10°C to 60°C (14°F to 140°F). This document provides guidelines
to follow when adjusting for ambient conditions."

So if it may be used in 140F ambient, it would be expected that it may operate at a higher temp but be derated above some chosen temp. What is hot to us may not be "hot" to a breaker that was designed to operate in hot conditions.

Check with the manufacturers instructions and limitations.
Reply With Quote
  #4  
Old 11/4/08, 10:25 PM
Dan Bowers, CMI Dan Bowers, CMI is offline
InterNACHI Member
 
Join Date: Oct 2003
Location: Shawnee Mission, KS
Posts: 3,893
Default Re: IR Pics of Natural Gas Furnace & 30 Amp Breaker

What Camera you using (model, etc).
Reply With Quote
  #5  
Old 11/5/08, 10:16 PM
Kenneth (Kip) R. McCullough, Jr. Kenneth (Kip) R. McCullough, Jr. is offline
InterNACHI Member
 
Join Date: Mar 2007
Location: Smyrna, GA
Posts: 35
Default Re: IR Pics of Natural Gas Furnace & 30 Amp Breaker

Quote:
Originally Posted by dbowers View Post
What Camera you using (model, etc).
Hey Dan,

I have the Flir B Cam SD.Very long battery life.
Reply With Quote
  #6  
Old 11/5/08, 11:47 PM
Darren Spencer Darren Spencer is offline
InterNACHI Member
 
Join Date: Nov 2007
Location: Bellevue, WA
Posts: 549
Default Re: IR Pics of Natural Gas Furnace & 30 Amp Breaker

exactly, the breaker can operate at 140 so what is the Ouch ? Seems everyone gets these cameras and reports anything that is red as a flagged area.
Reply With Quote
  #7  
Old 11/6/08, 12:03 AM
Stephen W. Stanczyk's Avatar
Stephen W. Stanczyk Stephen W. Stanczyk is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Kapowsin, WA
Posts: 4,965
Send a message via AIM to sstanczyk
Default Re: IR Pics of Natural Gas Furnace & 30 Amp Breaker

Just because the breaker is manufactured to operate within the given temperature range doesn't mean there isn't a problem. Looking at the other breakers with a greatly different temperature range makes one wonder why this double pole breaker is running at such a different temperature.

My first thought was it was a split bus with this breaker feeding the lower section, but the conductors don't look large enough and don't take the path of the normal feeds. My second guess is either the water heater or an electric baseboard/wall heater. Both suck up the juice, especially when we first start testing.

So Kip...... what was the breaker operating?




Stephen Stanczyk
Washington State Licensed Home Inspector # 221
President, Washington Association of Property Inspectors (WAPI)
(253) 241-0602 calls answered until 10pm


Pierce County -Thurston County - King County - Snohomish County
Reply With Quote
  #8  
Old 11/6/08, 12:40 AM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,927
Default Re: IR Pics of Natural Gas Furnace & 30 Amp Breaker

1st; a gas furnace runs on 120vac.

You are showing a 240VAC. Wrong label?

2nd the furnace your showing may likely get that hot during operation.
I can't tell by any photo (IR is the worst), buy you appear to have a non-induced natural draft furnace with an air break inside the furnace where it is hot.

Do you have any other information for us?



"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein

David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #9  
Old 11/6/08, 11:41 AM
Kenneth (Kip) R. McCullough, Jr. Kenneth (Kip) R. McCullough, Jr. is offline
InterNACHI Member
 
Join Date: Mar 2007
Location: Smyrna, GA
Posts: 35
Default Re: IR Pics of Natural Gas Furnace & 30 Amp Breaker

Quote:
Originally Posted by dspencer1 View Post
exactly, the breaker can operate at 140 so what is the Ouch ? Seems everyone gets these cameras and reports anything that is red as a flagged area.
The temperature differential between the breaker shown in the IR picture and the temperature of the other breakers was 60 degrees, which presents a potential fire hazard. I would consider a potential fire hazard as a red flag. The “ouch” comes from the price tag to repair the problems with the house as listed in my original post.
Reply With Quote
  #10  
Old 11/6/08, 12:31 PM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: IR Pics of Natural Gas Furnace & 30 Amp Breaker

Quote:
Originally Posted by kmccullough View Post
The temperature differential between the breaker shown in the IR picture and the temperature of the other breakers was 60 degrees, which presents a potential fire hazard. I would consider a potential fire hazard as a red flag. The “ouch” comes from the price tag to repair the problems with the house as listed in my original post.
Were all other breakers loaded to the same level/% as the "hot" one?
Did you use a clamp-on meter to obtain/compare amps?

Do we have a standard to guide us and any test /safe level #'s against which we can compare what we can find in the field.

Did you consult the breaker manufacturer's literature or contact them to see if they considered the temps a problem?

Last edited by Brian A. MacNeish; 11/7/08 at 11:12 AM..
Reply With Quote
  #11  
Old 11/6/08, 3:46 PM
Jim Seffrin Jim Seffrin is offline
InterNACHI Member
 
Join Date: Feb 2008
Location: Burlington, NJ
Posts: 85
Default Re: IR Pics of Natural Gas Furnace & 30 Amp Breaker

Dear All:

The Standard for Infrared Inspection of Electrical Systems & Rotating Equipment provides detailed inspection procedures and reporting requirements as well as operating temperature limits for in-service electrical devices. It also provides an IEEE formula that allows one to calculate the maximum allowable temperature for any operating electrical component.

While it is possible for some untrained infrared imager operators to 'cry wolf' without any justification, I believe that is not the case here.

Referring to the thermal image and allowing that the measured temperatures are reasonably accurate, the body of the circuit breaker is at or above 140°F or 60°C. The line side connections of the breaker connections appear to be operating higher still.

According to the above-referenced Standard, the maximum allowable temperature for a molded case breaker is 60°C at 100% load. For breakers operating at lighter loads, this number would be lower. Although load readings were not provided, it is unlikely that the subject breaker was carrying 30 amps.

Were this my inspection, I would have reported this breaker as an exception. Based upon experience with similar items, I would expect that the observed thermal pattern was due to either:
  • an internal defect such as a loose or deteriorated contact or
  • a loose or deteriorated line side connection
Should you be interested in obtaining a copy of the Standard for Infrared Inspection of Electrical Systems & Rotating Equipment, copies are available from the Standards section of the Infraspection online store.

Please feel free to give me a call directly if you need further info.



Jim Seffrin, Director

Infraspection Institute

425 Ellis Street
Burlington, NJ 08016
609-239-4788

SuccessIRies.com
IRINFO.ORG
IRINFOConference.com
Reply With Quote
  #12  
Old 11/6/08, 4:01 PM
Mario A. Kyriacou, CHI's Avatar
Mario A. Kyriacou, CHI Mario A. Kyriacou, CHI is offline
ESOP Committee Member
 
Join Date: Jun 2006
Location: Toronto, Ontario, Canada
Posts: 5,851
Default Re: IR Pics of Natural Gas Furnace & 30 Amp Breaker

Thanks Jim!





'Imagination is more important than knowledge' (sometimes)
Mario Kyriacou CHI CMI-NACHI Canadian Member of the Year 2007

www.360degreeshomeinspections.com
Tel.# 416-722-6132
e-mail torontohomeinspector@yahoo.com
Reply With Quote
  #13  
Old 11/6/08, 4:14 PM
Dale Duffy's Avatar
Dale Duffy Dale Duffy is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Scottsdale, AZ
Posts: 8,261
Default Re: IR Pics of Natural Gas Furnace & 30 Amp Breaker

I have used my IR Thermometer on breakers and all of them were 140+ because it was 115 degrees outside where the service panel was located.

Breakers operating under a load were 160+ with no apparent problems in a new service panel positioned directly in our hot Arizona sun.
Reply With Quote
  #14  
Old 11/6/08, 4:23 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: IR Pics of Natural Gas Furnace & 30 Amp Breaker

Quote:
Originally Posted by dduffy View Post
I have used my IR Thermometer on breakers and all of them were 140+ because it was 115 degrees outside where the service panel was located.

Breakers operating under a load were 160+ with no apparent problems in a new service panel positioned directly in our hot Arizona sun.
Yeppers Dale.
Reply With Quote
  #15  
Old 11/6/08, 5:15 PM
kweiss's Avatar
kweiss kweiss is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Rowlett, TX
Posts: 1,060
Default Re: IR Pics of Natural Gas Furnace & 30 Amp Breaker

Actually, I think you prove the point, Dale.

It is not as much about the temperature by itself as it is about one particular breaker being significantly hotter than the rest, given similar conditions and loads. I see pretty hot panels in garages in our summers too, AFCI in these can be 20 - 30 degree warmer when they group them.

I would have probably noted this breaker to, based on the limite dinformation here. If I see one breaker that much hotter than the other in the panel. (I used to use my IR thermometer too, before my camera.)




Kevin Weiss

Professional Inspector
Level I Infrared
www.AbsoluteInspections.net
www.homeinspectorsplanotx.com
www.homeinspectorsmckinney.com
Absolute Inspections, LLC
972-463-0887
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
AFCI Questions and Answers - Mike Holt pabernathy Electrical Inspections 7 4/16/12 9:51 PM
Bootlegged Breaker? Pics sglick Electrical Inspections 3 9/19/08 10:04 AM
980 Questions/Answers to the NHIE....Free! jbushart Legislation, Licensing & Legal Issues for Inspectors 50 4/20/08 1:26 AM
question on wireing furnace, legal or not Bill Hathaway Electrical Inspections 26 1/19/07 10:36 PM
PICs of furnace lab for Commercial Inspection Training Center. gromicko Miscellaneous Discussion for Inspectors 5 8/20/06 9:41 AM


All times are GMT -4. The time now is 8:19 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts