  #16  
Old 5/7/08, 10:20 PM
bdoles2's Avatar
bdoles2 bdoles2 is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Atlanta, GA
Posts: 3,071
Please Note: bdoles2 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Latent Moisture - Part Two

Quote:
Originally Posted by Ron C. Bibler
Brian what camera did you use for that ir scan ?

Best

Ron
Fluke TiR
Reply With Quote
  #17  
Old 5/7/08, 10:24 PM
bdoles2's Avatar
bdoles2 bdoles2 is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Atlanta, GA
Posts: 3,071
Please Note: bdoles2 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Latent Moisture - Part Two

Quote:
Originally Posted by pogletree
Obviously not... Some do not need even a camera. It's a good practice to obtain a meter for the ones you do not see with the naked eye and IR shows an indication of moisture. Nice image though!!!

Thanks

Paul Ogletree, Instructor/Consultant
NACHI04052691
ASNT Level III Thermal/Infrared
The Snell Group
P.O. Box 6
Montpelier, Vermont 05601-0006 USA
Tel. +1.802.229.9820 Fax +1.802.223.0460
pogletree@thesnellgroup.com
www.thesnellgroup.com
What was unusual was how the visible mold was not as evident on the lower wainscot section of the wall. I'm assuming that growth is not as rapid on "gloss" paint, the top half is a flat paint which shows the most growth. The source was a flooded basement, about 10" or so.
Reply With Quote
  #18  
Old 5/7/08, 10:54 PM
John McKenna's Avatar
John McKenna John McKenna is offline
InterNACHI Member
 
Join Date: Jun 2006
Location: Crockett, Tx
Posts: 12,252
Default Re: Latent Moisture - Part Two

All my inspection come with IR.

When someone says "will you do an inspection without the IR
scan, so I can save money?"...

I reply...

"is it alright if there is hidden moisture in the house and I do not
report it?"

They always say "NO"... and I say "now you know why I will
not do an inspection without my IR camera".

It's a no brainer.

I just found 4 hidden moisture areas in a house today.
Don't leave home without your IR camera.



John McKenna, CMI (TREC #4565)
Executive Director - Master Inspector Certification Board
25 Yrs Constr Exp - 13 Yrs Home Inspector Exp
American Home Inspection - East Texas.


Last edited by jmckenna1; 5/7/08 at 11:06 PM..
Reply With Quote
  #19  
Old 5/8/08, 1:22 AM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,686
Default Re: Latent Moisture - Part Two

I find myself in the middle of the road on this one.

What the infrared camera can do is not known by the general public, as of yet. Asking someone if they want to spend another $125 over the cost of a normal home inspection for something they don't understand is not very productive.

I think that increasing your overall pricing in use by are on every inspection pays for itself in numerous ways.

Increased income per job.
You are going to find something in many cases.
The examples of what this technology can find gets around rapidly.
In a very short period of time I have begun receiving specific infrared inspection calls from people with problems that they know about.
The camera doesn't do any good in the case.
You don't learn how to use the camera when it's in the case.
You can't gather a library of reference photos for future use when you're depending on paid inspections only.

This week I did an inspection with infrared at an inflated price. I found a new construction home with no insulation on the second-floor. The builder hired me after repairs were made. They were still issues. The client rehired me again before closing. $1500 on an inspection where the client declined IR as an add-on. My inflated initial price covered use of the camera and produced two more inspections on the same house.

One other point, if you don't use it and get experience (even if it's for free) where are you going to get your experience from? This week I was also confronted in a new construction situation questioning the validity of the infrared camera to determine the lack of insulation in a home where there was no physical access to the attic. Due to the lack of accessibility there was no way for me to do follow-up investigations or use other equipment to verify the infrared findings. I was bombarded from six different corporate personnel, insulation company owners and HVAC contractors. I stood my ground. Eventually they knocked a hole in the ceiling and climbed into the attic space "he's right there is no insulation up here!".

This also covers the point concerning adequate education in the use of this equipment. We are not going to be received with open arms in the building community. If you make an ***** out of yourself one time, your credibility is shot forever.
Reply With Quote
  #20  
Old 5/8/08, 8:00 AM
pogletree pogletree is offline
InterNACHI Member
 
Join Date: May 2004
Location: Cocoa, FL
Posts: 6
Default Re: Latent Moisture - Part Two

Quote:
Originally Posted by bdoles2
What was unusual was how the visible mold was not as evident on the lower wainscot section of the wall. I'm assuming that growth is not as rapid on "gloss" paint, the top half is a flat paint which shows the most growth. The source was a flooded basement, about 10" or so.
You're on the right track about the paint Brian. Gloss paint is "sealed" and the flat paint has "open pores" that can trap moisture for extended periods of time. We all know mold grows with moisture...

Thanks

Paul Ogletree, Instructor/Consultant
NACHI04052691
ASNT Level III Thermal/Infrared
The Snell Group
P.O. Box 6
Montpelier, Vermont 05601-0006 USA
Tel. +1.802.229.9820 Fax +1.802.223.0460
pogletree@thesnellgroup.com
www.thesnellgroup.com
Reply With Quote
  #21  
Old 5/8/08, 8:58 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 3,875
Default Re: Latent Moisture - Part Two

Quote:
Originally Posted by dandersen
I find myself in the middle of the road on this one.

What the infrared camera can do is not known by the general public, as of yet. Asking someone if they want to spend another $125 over the cost of a normal home inspection for something they don't understand is not very productive.

I think that increasing your overall pricing in use by are on every inspection pays for itself in numerous ways.

Increased income per job.
You are going to find something in many cases.
The examples of what this technology can find gets around rapidly.
In a very short period of time I have begun receiving specific infrared inspection calls from people with problems that they know about.
The camera doesn't do any good in the case.
You don't learn how to use the camera when it's in the case.
You can't gather a library of reference photos for future use when you're depending on paid inspections only.

This week I did an inspection with infrared at an inflated price. I found a new construction home with no insulation on the second-floor. The builder hired me after repairs were made. They were still issues. The client rehired me again before closing. $1500 on an inspection where the client declined IR as an add-on. My inflated initial price covered use of the camera and produced two more inspections on the same house.

One other point, if you don't use it and get experience (even if it's for free) where are you going to get your experience from? This week I was also confronted in a new construction situation questioning the validity of the infrared camera to determine the lack of insulation in a home where there was no physical access to the attic. Due to the lack of accessibility there was no way for me to do follow-up investigations or use other equipment to verify the infrared findings. I was bombarded from six different corporate personnel, insulation company owners and HVAC contractors. I stood my ground. Eventually they knocked a hole in the ceiling and climbed into the attic space "he's right there is no insulation up here!".

This also covers the point concerning adequate education in the use of this equipment. We are not going to be received with open arms in the building community. If you make an ***** out of yourself one time, your credibility is shot forever.
David you are so correct the infrared camera spreads like wild fire I will be traveling 4 hours this Saturday to do a one year warranty scan. Received a call yesterday to do an inspection on a FSBO with basement water problems all of the Realtors in this town have stayed away from this home and did not want to list it because of the water problems.



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #22  
Old 5/8/08, 9:12 AM
jrivera's Avatar
jrivera jrivera is offline
Active Poster
 
Join Date: Jun 2004
Location: Shirley, NY
Posts: 1,340
Please Note: jrivera is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Latent Moisture - Part Two

Quote:
Originally Posted by dandersen
This also covers the point concerning adequate education in the use of this equipment. We are not going to be received with open arms in the building community. If you make an ***** out of yourself one time, your credibility is shot forever.

Amen to that
Reply With Quote
  #23  
Old 5/13/08, 3:04 AM
Ron C. Bibler Ron C. Bibler is offline
Active Poster
 
Join Date: Mar 2008
Location: Healdsburg Ca
Posts: 105
Please Note: Ron C. Bibler is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Latent Moisture - Part Two

Been using IR on all my inspection and not providing any information to the buyers or agents unless they pay for the service. I shot this in a condo. A common wall 2x4 second story interior. The adjacent unit is the same set up open living room. No adjacent sun light. No plumbing in the areas adjacent to this scan. No plumbing/vent pipes from the lower units. The wall had 2 outlets and 1 cable outlet.
Q. has anyone had any hot wires in walls that looks like this ?
or around the base boards?

room temp 68F.
lower center area on the wall 72F.
streak up the wall 71F.

Best

Ron
Attached Thumbnails
latent-moisture-part-two-hpim4797.jpg   latent-moisture-part-two-ir_0023.jpg  

Last edited by Ron C. Bibler; 5/13/08 at 3:25 AM..
Reply With Quote
  #24  
Old 5/13/08, 8:37 AM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,686
Default Re: Latent Moisture - Part Two

Yes, but this does not look like that to me.

If a wire touches or almost touches the sheetrock you will get a definitive line. If it on the correct location of the stud, the stud bay will be warmer throughout.

The geometric pattern looks more like air movement to me.
Reply With Quote
  #25  
Old 5/13/08, 9:51 AM
kweiss's Avatar
kweiss kweiss is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Rowlett, TX
Posts: 1,060
Default Re: Latent Moisture - Part Two

I agree with David. Appears to be some sort of air infiltration. Was it warmer outside?




Kevin Weiss

Professional Inspector
Level I Infrared
www.AbsoluteInspections.net
www.homeinspectorsplanotx.com
www.homeinspectorsmckinney.com
Absolute Inspections, LLC
972-463-0887
Reply With Quote
  #26  
Old 5/13/08, 10:54 AM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,686
Default Re: Latent Moisture - Part Two

He posted that this is a second story so there is definitely a potential heat source below.
It appears that the image scale adjustment has been pushed to the limits so we are not talking about a whole lot of heat here.

I would change the palate to rainbow to see the direction of heat flow. Electrical wiring may show rather consistent across a wider source whereas air flow will graduate proportionately away from the source/point of entry.
Reply With Quote
  #27  
Old 5/13/08, 11:15 AM
Ron C. Bibler Ron C. Bibler is offline
Active Poster
 
Join Date: Mar 2008
Location: Healdsburg Ca
Posts: 105
Please Note: Ron C. Bibler is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Latent Moisture - Part Two

David i reset the palette to rain for your rivew.

david i think you are correct. it look like a heat source from the lower unit. may have a small void or a nott in the wall plate...

have another look.

Thanks

Ron
Attached Thumbnails
latent-moisture-part-two-ir_0015-nachi.jpg  
Reply With Quote
  #28  
Old 5/14/08, 9:59 AM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,686
Default Re: Latent Moisture - Part Two

Large difference! No?

Now you can see the deficient insulation in the stud bay behind the Scale!

Another Tip: If you adjust the scale (move hi/lo towards each other) you can get all of the colors of the palette in the scan.

Last edited by dandersen; 12/9/09 at 1:24 PM..
Reply With Quote
  #29  
Old 5/15/08, 12:15 AM
pogletree pogletree is offline
InterNACHI Member
 
Join Date: May 2004
Location: Cocoa, FL
Posts: 6
Default Re: Latent Moisture - Part Two

Ron,

Conductive heat flow travels from warm to cool (your room being the cooler).
The only way to accurately figure out your image is to see whats on the other side or try looking at the first floor unit if possible. If this is not possible, you may want to scan the area at different times during the day.

Three degrees isn't a huge concern if your camera is set accurately (ie. correct emissivity value set in camera, and a calibration has been performed recently). If this hasn't been done, you should be careful stating temperatures to clients. Here is an easy way to check your calibration of your camera in the field.
Ambient conditions of 67-75 F
Reference subject (Human face) should be calm
Set emissivity to .98
View subject’s face directly from approximately 3’
Use area- max (preferred) or spot feature
Measure temperature of tear duct area.
Radiometric reading s/b ~92-96 F

Manually adjusting your range and span is a good practice using auto can sometimes "mask" thermal variances. Changing palettes can be misleading, you can actually make things appear that really is not there.

I hope this helps you and maybe even some other readers.

Thanks.
Paul Ogletree, Instructor/Consultant
NACHI04052691
ASNT Level III Thermal/Infrared #125356
The Snell Group
P.O. Box 6
Montpelier, Vermont 05601-0006 USA
Tel. +1.802.229.9820 Fax +1.802.223.0460
pogletree@thesnellgroup.com
www.thesnellgroup.com
Reply With Quote
  #30  
Old 5/15/08, 10:01 AM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,686
Default Re: Latent Moisture - Part Two

This "calibration" test leaves a lot to be desired in my opinion!

Ambient conditions; (+/-) 10 degrees

Radiometric reading results; (+/-) 4 degrees

No reference to rh

"Approximately 3’ "; SSR compliant for a tear duct?

"should be calm"; how do we determine this? Ever study polygraph examinations! You can tell if someone is lying with IR by looking into their face!

I don't think anyone here has a camera you can adjust the Range on. At any rate, the "Auto" setting does not change "Range" of the camera, it changes "Level & Span".

Quote:
Changing palettes can be misleading, you can actually make things appear that really is not there.
Can you post an example of this?
Are you saying the palette is "making stuff up"?

I have always used melting ice to conduct a calibration check on my mid- temperature testing devices.

My camera manufacturer recommends the following testing procedure:
First, the calibration check should never be relied upon.
A field calibration check only addresses one temperature.
You must have a constant set up and procedure to do this properly.
Make sure nothing important changes between tests.
The target should be a metal container that produces high conductivity.
Make a high emissivity spot on the target large enough for the SSR/distance ratio.
The use of "melting ice" and water should be used to produce the desired test temperature (ice cubes are colder than 32°F, therefore the metal container).
An alternate is boiling water (at a rolling boil).

Most importantly, the conditions of this calibration test can be duplicated (which is an important scientific/legal requirement).

The materials required are more likely available at the home inspection site (metal cup, electricians tape, ice, water, known elevation). It is highly unlikely you will find a calm buyer, seller, real estate agent or home inspector at the home inspection site!

Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Preventing Moisture related Problems mcyr Ancillary Inspection Services & Additional Topics 1 12/19/07 9:30 AM
Moisture in slabs mcyr Structural Inspections 7 8/20/07 8:33 PM
bbbb mcyr Structural Inspections 1 8/19/07 11:26 PM
Moisture control for slab on grade in protecting floor finishes mcyr General Inspection Discussion 2 8/13/07 8:53 PM


All times are GMT -4. The time now is 11:23 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts