Default Lets get it on

Ok guys flat roof ice standing 10:00 AM clear no wind why is this temp reading 7 degrees on the ice E-setting 70



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging

Last edited by cbottger; 5/13/08 at 11:11 PM..
Reply With Quote
  #2  
Old 12/19/07, 6:30 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,684
Default Re: Lets get it on

Quote:
Originally Posted by cbottger
Ok guys flat roof ice standing 10:00 AM clear no wind why is this temp reading 7 degrees on the ice E-setting 70
Reflection from the sun.
Reply With Quote
  #3  
Old 12/19/07, 6:40 PM
ldapkus ldapkus is offline
Active Poster
 
Join Date: Mar 2006
Posts: 5,719
Please Note: ldapkus is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Lets get it on

Colder areas are shaded from the sun.
Reply With Quote
  #4  
Old 12/19/07, 6:51 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,686
Default Re: Lets get it on

Reflection of the sky.

All reflective surfaces will read the surrounding temps (at some point on them depending on their shape) rather than their temp.

Example: Watch out for breaker panel terminal lugs, they look hot because of your body heat.
Reply With Quote
  #5  
Old 12/19/07, 7:11 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,684
Default Re: Lets get it on

Quote:
Originally Posted by dandersen
Example: Watch out for breaker panel terminal lugs, they look hot because of your body heat.
Yup, and most will look hotter than others but you must actually go by the actual temperature of the area in question. If you see a thermal image of a breaker reading a temperature of 110 degrees, it may not be a problem verses seeing a breaker hot spot at 210 degrees.
Reply With Quote
  #6  
Old 12/19/07, 7:11 PM
Kevin A. Richardson Kevin A. Richardson is offline
InterNACHI Member
 
Join Date: Sep 2004
Posts: 1,334
Default Re: Lets get it on

Your e-setting for this application is too low.

Kevin



Kevin A. Richardson
Level III Infraspection Institute Certified Infrared ThermographerŪ, #7493
Infraspection Institute Thermography Instructor
BPI Certified Building Performance Analyst
RESNET Level II Home Energy Survey Professional
Maryland Licensed Home Inspector, #29727
InterNACHI Certified Professional Inspector, #04091175


301-942-4610
www.richnspect.com
www.infrared-diagnostics.com
www.thehomegreenteam.com
Reply With Quote
  #7  
Old 12/19/07, 7:12 PM
ldapkus ldapkus is offline
Active Poster
 
Join Date: Mar 2006
Posts: 5,719
Please Note: ldapkus is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Lets get it on

Quote:
Originally Posted by dandersen
Reflection of the sky.

All reflective surfaces will read the surrounding temps (at some point on them depending on their shape) rather than their temp.

Example: Watch out for breaker panel terminal lugs, they look hot because of your body heat.
New shiny conduit looks hot too. It fooled me the other day when I was showing a builder my cam.
Reply With Quote
  #8  
Old 12/19/07, 7:19 PM
Mario A. Kyriacou, CHI's Avatar
Mario A. Kyriacou, CHI Mario A. Kyriacou, CHI is offline
ESOP Committee Member
 
Join Date: Jun 2006
Location: Toronto, Ontario, Canada
Posts: 5,856
Default Re: Lets get it on

[quote=dandersen]Reflection of the sky.

All reflective surfaces will read the surrounding temps (at some point on them depending on their shape) rather than their temp.




Dave

Exactly!! That's why roof (inspections)scans should be conducted in the evening.





'Imagination is more important than knowledge' (sometimes)
Mario Kyriacou CHI CMI-NACHI Canadian Member of the Year 2007

www.360degreeshomeinspections.com
Tel.# 416-722-6132
e-mail torontohomeinspector@yahoo.com
Reply With Quote
  #9  
Old 12/19/07, 7:28 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,686
Default Re: Lets get it on

Attic door, colder in the attic than in the house.
Where is the hot spot coming from?


My reflection.

Last edited by dandersen; 12/9/09 at 1:24 PM..
Reply With Quote
  #10  
Old 12/19/07, 7:30 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,686
Default Re: Lets get it on

Quote:
Exactly!! That's why roof (inspections)scans should be conducted in the evening.
Why is that?
The sky is the same temp, day or night (if it is clear and low humidity)?
Reply With Quote
  #11  
Old 12/19/07, 8:06 PM
Mario A. Kyriacou, CHI's Avatar
Mario A. Kyriacou, CHI Mario A. Kyriacou, CHI is offline
ESOP Committee Member
 
Join Date: Jun 2006
Location: Toronto, Ontario, Canada
Posts: 5,856
Default Re: Lets get it on

Quote:
Originally Posted by dandersen
Why is that?
The sky is the same temp, day or night (if it is clear and low humidity)?
You tell me Dave. If you are conducting a roof moisture survey why would you do it in the daylight.
Would it not be better to do it after sunset? This will eliminate reflections,shadows and allow you to detect roof moisture. But you already know this stuff you are Level 3!!





'Imagination is more important than knowledge' (sometimes)
Mario Kyriacou CHI CMI-NACHI Canadian Member of the Year 2007

www.360degreeshomeinspections.com
Tel.# 416-722-6132
e-mail torontohomeinspector@yahoo.com
Reply With Quote
  #12  
Old 12/19/07, 8:19 PM
William Warner's Avatar
William Warner William Warner is offline
InterNACHI Member
 
Join Date: May 2003
Location: Dayton, OH
Posts: 3,236
Default Re: Lets get it on

Quote:
Originally Posted by mkyriacou
You tell me Dave. If you are conducting a roof moisture survey why would you do it in the daylight.
Would it not be better to do it after sunset? This will eliminate reflections,shadows and allow you to detect roof moisture. But you already know this stuff you are Level 3!!
The thermal window is open the widest in the early morning or late afternoon/early evening. It is typically at its most narrow margin at high noon. As water has a high thermal capacitance, the chance to observe moisture on a flat roof is at its greatest potential in the mornings and evenings especially with a less sensitive camera.




Submit your AWARDS NOMINATIONS here

Visit the InterNACHI Awards web portal here

Blessed are the blissfully ignorant... for they shall be easily led...
Reply With Quote
  #13  
Old 12/19/07, 8:23 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,686
Default Re: Lets get it on

Quote:
You tell me Dave.
I am seriously asking you.

There are many good reasons to do roof scans at night. As you posted.

My question is why in this case would the ice show up differently at night?
Reply With Quote
  #14  
Old 12/19/07, 8:33 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,686
Default Re: Lets get it on

Thank you Mr. Warner.

I was taught a method of determining the maximum Delta T by monitoring the temperature of the roof and the temperature of water in a container. In the morning you'll receive the greatest temperature difference as the roof begins to warm more rapidly than the water. At some point around midday, it is likely that the water temperature will match that of the roof temperature. Later in the evening the roof will cool more rapidly than the water. At some time late at night, just like at high noon the temperature of the roof and the water will equalize.
Reply With Quote
  #15  
Old 12/19/07, 8:35 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 3,875
Default Re: Lets get it on

Guys this was not a test I was surprised my self when the low temp showed up I was not actually scanning the roof was the wrong time of day especially with the water frozen. And yes my instructor did say the night time after radiation cooling takes place never scan a roof in the heat of the day. you are looking for evaporation of the water beneath the roof covering; water holds the heat longer and will show up.

Yes I did have the wrong E setting I just happen to have the camera in my hand when I went on the roof as I had been called to check an interior wall which I will post later I just wanted to view the roof before I went inside. Just forgot to change the E-setting for the roof. The outside ambient was in the low 30's when I snapped that IR pic. But that still does not explain 7 degrees as nothing in the area was that cold. When I am just playing with the camera I will often change the E-setting just to see the variances in the temps.

As for the breaker temp being discussed my instructor stated the allen set screw hole will create a reflection or cause the actual temp to be off and has to be adjusted for. There is a specific name for this and I can not recall the name without going back to my books. I was not jacking with any one don't have a clue why the temp in the pic was so low. I am open for serious discussion.



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT -4. The time now is 3:29 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts