  #1  
Old 2/7/09, 1:20 AM
cbottger's Avatar
cbottger cbottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 2,738
Default A little on the warm side

A total electrical home had a 200 amp external breaker below the meter base being fed from the pole with 1-0 Al wire. When I loaded up the amps with the water heater the dryer, the kitchen cooks stove and the heat pump this is what I got
Attached Thumbnails
little-warm-side-ir_1274.jpg  



Freedom Express Inspections LLC
CMOR Thermography Certified Level 11 #2097
freedomexpressinspections.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
Professional Home Inspector State License # 130
Reporting system by Home Inspector Pro

Serving the State of Okla.
Reply With Quote
  #2  
Old 2/7/09, 3:14 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 3,701
Default Re: A little on the warm side

Thats just your reflection; You hot head!



David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Certified Level II Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620

Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #3  
Old 2/10/09, 11:26 AM
OJ Utter OJ Utter is offline
New User
 
Join Date: Jan 2009
Location: Nebraska
Posts: 70
Send a message via Skype™ to OJ Utter
Please Note: OJ Utter is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: A little on the warm side

Charley- Were you able to move the camera around and determine the source of the heating? This looks like a potentially much more serious of a problem then even what it shows. We don't have the source of the heating (the loose part). I would consider this an indirect temperature measurement. I would personally advise the customer to make sure that they fix that ASAP and don't sit on it.

If you don't mind, I would really like to look at that image more in it original format so I can tweak it some. You can send it to me via http://utterprecision.com/upload.

Godspeed!
OJ Utter
Level 3 itc Thermographer
Reply With Quote
  #4  
Old 2/10/09, 10:42 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 3,701
Default Re: A little on the warm side

OJ, please post what you find if he sends it to you. I see some things I am curious about as well.



David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Certified Level II Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620

Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #5  
Old 2/10/09, 11:09 PM
cbottger's Avatar
cbottger cbottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 2,738
Default Re: A little on the warm side

Quote:
Originally Posted by OJ Utter View Post
Charley- Were you able to move the camera around and determine the source of the heating? This looks like a potentially much more serious of a problem then even what it shows. We don't have the source of the heating (the loose part). I would consider this an indirect temperature measurement. I would personally advise the customer to make sure that they fix that ASAP and don't sit on it.

If you don't mind, I would really like to look at that image more in it original format so I can tweak it some. You can send it to me via http://utterprecision.com/upload.

Godspeed!
OJ Utter
Level 3 itc Thermographer
Hi OJ I just caught your post I am in the middle of writing todays inspection report I will send the Pic tomorrow. Yes I do not sit on those types of images I personally called the service provider and they were sending an electrician out immediately as this was on their side of the service. The home was not occupied. I jacked the amps up when I located this and yes I did check from different angles same results. This was taken approximately 10:30 AM on the west exterior wall outside ambient was in the low to mid 60's. Camera was BX-320. My dertermination was loose connection and improper wire size.



Freedom Express Inspections LLC
CMOR Thermography Certified Level 11 #2097
freedomexpressinspections.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
Professional Home Inspector State License # 130
Reporting system by Home Inspector Pro

Serving the State of Okla.
Reply With Quote
  #6  
Old 2/11/09, 7:47 PM
cbottger's Avatar
cbottger cbottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 2,738
Default Re: A little on the warm side

OJ
I uploaded the image through your site have fun Pretty neat site you have I see your company is a full PM company I presume you are in Lincoln.

You know I am available as a sub contractor for IR and I do travel if you get overloaded give me a call



Freedom Express Inspections LLC
CMOR Thermography Certified Level 11 #2097
freedomexpressinspections.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
Professional Home Inspector State License # 130
Reporting system by Home Inspector Pro

Serving the State of Okla.
Reply With Quote
  #7  
Old 2/11/09, 11:57 PM
OJ Utter OJ Utter is offline
New User
 
Join Date: Jan 2009
Location: Nebraska
Posts: 70
Send a message via Skype™ to OJ Utter
Please Note: OJ Utter is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: A little on the warm side

Here all is what I found on this. Great job Charely. Especially on the call out for the electrician on this. Here is the pdf with my tweeking. Freedom Express Report

You did the very best that you can do with the equipment you have. I would strongly suggest recommending to your customer that you be allowed to perform a follow up on this to insure that is has been completely resolved. I've had industrial issues that hang around for years because the company didn't have a technology like infrared to follow up there repairs and they just never dug deep enough to completely solve the issue even when the original recommendation that was given was what they wound up finding out to be the problem. One time that almost cost a maintenance technician his life. And there is no dollar amount to replace that.

Godspeed!
OJ Utter
Level 3 itc Thermographer
Reply With Quote
  #8  
Old 2/12/09, 4:06 PM
cbottger's Avatar
cbottger cbottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 2,738
Default Re: A little on the warm side

Quote:
Originally Posted by OJ Utter View Post
Here all is what I found on this. Great job Charely. Especially on the call out for the electrician on this. Here is the pdf with my tweeking. Freedom Express Report

You did the very best that you can do with the equipment you have. I would strongly suggest recommending to your customer that you be allowed to perform a follow up on this to insure that is has been completely resolved. I've had industrial issues that hang around for years because the company didn't have a technology like infrared to follow up there repairs and they just never dug deep enough to completely solve the issue even when the original recommendation that was given was what they wound up finding out to be the problem. One time that almost cost a maintenance technician his life. And there is no dollar amount to replace that.

Godspeed!
OJ Utter
Level 3 itc Thermographer

OJ I know my hearing is going but did not question my eye sight was not able to find the link on your page to the PDF a little guidance please BTW is your video working on your site was not able to get it to play perhaps I don't have the correct video player installed on my end.



Freedom Express Inspections LLC
CMOR Thermography Certified Level 11 #2097
freedomexpressinspections.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
Professional Home Inspector State License # 130
Reporting system by Home Inspector Pro

Serving the State of Okla.
Reply With Quote
  #9  
Old 2/13/09, 12:03 AM
OJ Utter OJ Utter is offline
New User
 
Join Date: Jan 2009
Location: Nebraska
Posts: 70
Send a message via Skype™ to OJ Utter
Please Note: OJ Utter is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: A little on the warm side

Sorry Charley! Hate when I do that. http://www.utterprecision.com/docs/f...domExpress.pdf

Also I need to fix the link for that video. Just haven't quite gotten there yet. You can see it here for now. http://www.youtube.com/watch?v=8scQ5vLUGqE

Some of you all might like this one too: http://www.youtube.com/watch?v=N-BERTdQ_SU

OJ Utter
Level 3 itc Thermographer
www.utterprecision.com
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical 6 9/15/08 8:57 AM
980 Questions/Answers to the NHIE....Free! jbushart Legislation, Licensing & Legal Issues 50 4/20/08 2:26 AM
What's this video worth? jtedesco1 Education 5 4/18/08 10:24 AM
Keep on the Sunny Side... Always on the Sunny Side, Keep on the Sunny Side of Life jburkeson1 Misc. Discussion 0 8/22/07 10:33 AM


All times are GMT -4. The time now is 9:44 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts