Here are some images that have been thermally tuned from a inspect today that I find on a regular biases.

The main panel was a 100 amp installed 1971 never been updated the home was vacant with only the built in appliances and lighting circuits available for use. The home had been added on to had two A/C units with gas furnaces a 5 ton and a 3-1/2 ton, dishwasher, electric oven and 4 cooktop burners, two electrical bathroom heaters and if you would note the pic,s I exceeded 100 amps on this panel with nothing connected to the 110 outlets very easy to load a panel up on a vacant home.

The 220 breaker with the unbalanced and excessive temp was a 50 amp double pole for the cook stove I have built a good business around items like this.

The next time I find one of these messes I still own my B-cam 120X120 resolution I will take a image with it and compare to my 320X240
Attached Thumbnails
more-than-point-and-shoot-2800-e-prospect-pc-9-25-10-065.jpg   more-than-point-and-shoot-2800-e-prospect-pc-9-25-10-068.jpg   more-than-point-and-shoot-ir_0437.jpg   more-than-point-and-shoot-ir_0438.jpg   more-than-point-and-shoot-ir_0440.jpg  




Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
Need a home inspection in Tennessee? Check out InterNACHI's listing of Tennessee certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 9/26/10, 3:38 AM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,918
Default Re: More than point and shoot

Quote:
Originally Posted by cbottger View Post
Here are some images that have been thermally tuned from a inspect today that I find on a regular biases.

The main panel was a 100 amp installed 1971 never been updated the home was vacant with only the built in appliances and lighting circuits available for use. The home had been added on to had two A/C units with gas furnaces a 5 ton and a 3-1/2 ton, dishwasher, electric oven and 4 cooktop burners, two electrical bathroom heaters and if you would note the pic,s I exceeded 100 amps on this panel with nothing connected to the 110 outlets very easy to load a panel up on a vacant home.

The 220 breaker with the unbalanced and excessive temp was a 50 amp double pole for the cook stove I have built a good business around items like this.

The next time I find one of these messes I still own my B-cam 120X120 resolution I will take a image with it and compare to my 320X240
Whats the correction?
Reply With Quote
  #3  
Old 9/26/10, 9:22 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: More than point and shoot

Quote:
Originally Posted by belliott View Post
Whats the correction?
Recommended updating the Main panel as determined by a licensed qualified electrician. Not allowed to exceed 80% of its rated capacity



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #4  
Old 9/26/10, 10:00 AM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,927
Default Re: More than point and shoot

Bob, This re-print is for your comment you made on the other thread about Will Decker not needing a better camera:





Charley, This is not electrical, it is moisture (which is even harder to deal with as you know). I searched for these two scans that were in the same type conditions (4 degree split). I no longer have my BCAM so I can not do side-by-side comparison any more.

I have made these comparisons in the past and posted here when I did have both cameras but obviously the "PROOF" that everyone asks for, fell on deaf eyes!

So don't waste too much time away from the more important issues of your business.



"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein

David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #5  
Old 9/26/10, 10:51 AM
John McKenna's Avatar
John McKenna John McKenna is offline
InterNACHI Member
 
Join Date: Jun 2006
Location: Crockett, Tx
Posts: 12,303
Default Re: More than point and shoot

FLIR-ITC teaches that a BCAM can be used for a home inspection in a building.
RESNET teaches that a BCAM meets their minimum standard for performing
an energy audit. I have seen no proof otherwise and I have used a BCAM for
several years without one complaint or missed issue... but then again, I know
what I am doing.



John McKenna, CMI (TREC #4565)
Executive Director - Master Inspector Certification Board
25 Yrs Constr Exp - 13 Yrs Home Inspector Exp
American Home Inspection - East Texas.


Last edited by jmckenna1; 9/26/10 at 10:56 AM..
Reply With Quote
  #6  
Old 9/26/10, 11:03 AM
Russell J. Hensel's Avatar
Russell J. Hensel Russell J. Hensel is online now
InterNACHI Member
 
Join Date: Jul 2008
Location: Fort Myers, FL
Posts: 5,576
Default Re: More than point and shoot

Great info and thanks for sharing..



Comprehensive Building Consultants
Naples Home Inspection, Naples Mold Inspection, Naples Radon Inspection, Bonita Springs Home Inspection, Bonita Springs Mold Inspection, Bonita Springs Radon Inspection.



Donate here:

or send checks to the
Fl Home and Insurance Inspector Chapter
1103 W Hibiscus Blvd Ste 311
Melbourne, Fl 32901
Reply With Quote
  #7  
Old 9/26/10, 11:32 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: More than point and shoot

Quote:
Originally Posted by jmckenna1 View Post
FLIR-ITC teaches that a BCAM can be used for a home inspection in a building.
RESNET teaches that a BCAM meets their minimum standard for performing
an energy audit. I have seen no proof otherwise and I have used a BCAM for
several years without one complaint or missed issue... but then again, I know
what I am doing.
Yes John we all know what the minimum standard is but minimum does not always cut the mustard. Sometimes it is what is perceived by the public take one of your 120X120 image of a residential electrical panel and place it side by side of one of mine and show them to a client that knows absolutely nothing about IR and see who they pick for the job.

As for you knowing what you are doing that has yet to be determined why don't you post one of your real life panel images that have been thermally tuned and lets compare apples to apples



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #8  
Old 9/26/10, 11:40 AM
John McKenna's Avatar
John McKenna John McKenna is offline
InterNACHI Member
 
Join Date: Jun 2006
Location: Crockett, Tx
Posts: 12,303
Default Re: More than point and shoot

Quote:
Originally Posted by cbottger View Post
Yes John we all know what the minimum standard is but minimum does not always cut the mustard. Sometimes it is what is perceived by the public take one of your 120X120 image of a residential electrical panel and place it side by side of one of mine and show them to a client that knows absolutely nothing about IR and see who they pick for the job.

As for you knowing what you are doing that has yet to be determined why don't you post one of your real life panel images that have been thermally tuned and lets compare apples to apples
I have posted many IR images over the years. My job as
an inspector is to observe and report.

A higher resolution camera will always produce a nicer
picture. But that does not keep me from reporting
defects in my home inspections with a BCAM level camera.

I have seen many a person buy a better camera and
then turn around like a little kid and tell everyone that
all inspectors must have better pictures in their reports
now. When you ask why, they just say because mine
look nicer. That seems a little vain.

If I buy a better camera than you, just to produce a
prettier picture of the same thing, does that mean
you can no longer do your job?

I have never had a client comment that my IR images
did not look nice enough compared to someone else.

If you are asking me to compare the number of clients
I get and the size of my pay check compared to yours....
I decline.

Try to grow up.



John McKenna, CMI (TREC #4565)
Executive Director - Master Inspector Certification Board
25 Yrs Constr Exp - 13 Yrs Home Inspector Exp
American Home Inspection - East Texas.


Last edited by jmckenna1; 9/26/10 at 11:59 AM..
Reply With Quote
  #9  
Old 9/26/10, 12:33 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: More than point and shoot

Quote:
Originally Posted by jmckenna1 View Post
I have posted many IR images over the years. My job as
an inspector is to observe and report.

A higher resolution camera will always produce a nicer
picture. But that does not keep me from reporting
defects in my home inspections with a BCAM level camera.

I have seen many a person buy a better camera and
then turn around like a little kid and tell everyone that
all inspectors must have better pictures in their reports
now. When you ask why, they just say because mine
look nicer. That seems a little vain.

If I buy a better camera than you, just to produce a
prettier picture of the same thing, does that mean
you can no longer do your job?

I have never had a client comment that my IR images
did not look nice enough compared to someone else.

If you are asking me to compare the number of clients
I get and the size of my pay check compared to yours....
I decline.

Try to grow up.
Well that is a first I got you to decline on something mission accomplished



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #10  
Old 9/26/10, 12:52 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: More than point and shoot

Another sad story from an inspection last week the home had and old FP panel that had been updated before my inspection by a licensed unqualified electrican he replaced the one panel with two panels a main and a sub the home had been added onto in the past but the panel had never been updated.

When it was inspected by a electrican he recommended a update and the relo company that owned the home agreed and the pic's is what he installed not accounting for the addition on to the home and adding the second A/C, he stayed with a 100 amp main instead of increasing the size.

As indicated in the PIC,s I exceeded the 80% load on the main with just inhouse appliances the home was vacant. My recommendation was to update the main by a licensed qualified electrician and I stress the word qualified my clients have hired me to do a re-inspect this next week before close of escrow it will be very interesting to see how they straightened up this abortion.
Attached Thumbnails
more-than-point-and-shoot-3624-mistletoe-pc-9-17-10-054.jpg   more-than-point-and-shoot-3624-mistletoe-pc-9-17-10-059.jpg   more-than-point-and-shoot-3624-mistletoe-pc-9-17-10-068.jpg   more-than-point-and-shoot-ir_0403.jpg  



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #11  
Old 9/26/10, 5:18 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,927
Default Re: More than point and shoot

John, it's too bad you feel so inferior and feel everyone is trying to surpass you!

We are SHARING REALITY. We don't want your job!

Can't you look at my scans and see that you can not in fact everything there!?
Are you so closed minded that you think you never missed something?!

I tell my clients on every job that I likely missed something!

I'm not saying it's all or nothing when it comes to cameras. But for you to damn us because we made a business of this and can afford better equipment because of it, that's just very little of you!

We are not better, just further down the road. Your stuck at the Stop Sign!



"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein

David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #12  
Old 9/26/10, 5:32 PM
John McKenna's Avatar
John McKenna John McKenna is offline
InterNACHI Member
 
Join Date: Jun 2006
Location: Crockett, Tx
Posts: 12,303
Default Re: More than point and shoot

Quote:
Originally Posted by dandersen View Post
John, it's too bad you feel so inferior and feel everyone is trying to surpass you!

We are SHARING REALITY. We don't want your job!

I am trying to help people hear the truth.



Can't you look at my scans and see that you can not in fact everything there!?
Are you so closed minded that you think you never missed something?

I see nothing that proves a BCAM will not work for a home
inspection. Nothing.


I tell my clients on every job that I likely missed something!

I tell them too. But I have never had a complaint or anyone
telling me I missed something with my IR camera.


I'm not saying it's all or nothing when it comes to cameras. But for you to damn us because we made a business of this and can afford better equipment because of it, that's just very little of you! '

I am just saying that you should not condemn those who
cannot afford an expensive camera. That's all. If they,
do it with a BCAM until they can afford more then that is
OK and it will work fine for a home inspection.


We are not better, just further down the road. Your stuck at the Stop Sign!

Just because I correct you, does not mean that is a stop
sign to me.

Next...



John McKenna, CMI (TREC #4565)
Executive Director - Master Inspector Certification Board
25 Yrs Constr Exp - 13 Yrs Home Inspector Exp
American Home Inspection - East Texas.

Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
4 Point Insp Contract jwilhelm1 Florida Inspectors 20 9/4/10 5:47 PM
NACHI Four Point Form gbell Miscellaneous Discussion for Inspectors 16 4/1/08 7:14 PM
Today MICB adopts new 1,000 point system for Certified Master Inspector CMI. gromicko Miscellaneous Discussion for Inspectors 39 7/9/06 11:37 AM


All times are GMT -4. The time now is 6:19 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts