Default My worst enemy

Is most usually Me, I have been thinking which is probably dangerous for me of a way to speed up and create a faster blower door than simply using in house exhaust fans such as dryers kitchen exhaust and bathroom exhausts.

My question is has anyone ever seen a high cfm fan mounted on a board or plastic that would fit into a standard door frame or window frame considered as portable that one person might carry to the job site to move large volumes of air quickly. I am in the process of pushing energy audits due to the high prices of fuel and or energy and have been thinking about fabricating such a device to move air but thought there might be one on the market already. Anyone have any knowledge of this.



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #2  
Old 3/26/08, 10:30 AM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,927
Default Re: My worst enemy

Charlie,

I use one of those window fans that fit in like a window a/c unit. You can "suck" or "blow".

I'm sure you have a manometer or a magnehelic laying around.
Reply With Quote
  #3  
Old 3/26/08, 10:44 AM
Doug Edwards's Avatar
Doug Edwards Doug Edwards is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Florida panhandle
Posts: 4,850
Default Re: My worst enemy

Why couldn't you use a condenser fan motor assembly off an old outside unit. You would need to replace the motor with one that runs off 115 volts but that should not be a problem. I took the top of an old outside unit to build an attic gable vent fan once. Made the box out of duct board and code tape, mounted it in the gable vent (large round vent). I left the 230 volt motor in, it only pulls 1 amp. Put it on an inline thermostat. It would would dang near blow you hat off if you walked under the gable. It dropped the temp in that attic significantly and my cooling bill dropped along with it. I can go into the attic and work if necessary without too much discomfort whereas before I could not stay but maybe 5 mins. Point is, you can probably find everything you need right now. It already comes with a cage to cover the blades, plus it does not weight that much. I humped it up into the attic by my lonesome and mounted it.
Reply With Quote
  #4  
Old 3/26/08, 5:25 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,848
Default Re: My worst enemy

Quote:
Originally Posted by cbottger
Is most usually Me, I have been thinking which is probably dangerous for me of a way to speed up and create a faster blower door than simply using in house exhaust fans such as dryers kitchen exhaust and bathroom exhausts.

My question is has anyone ever seen a high cfm fan mounted on a board or plastic that would fit into a standard door frame or window frame considered as portable that one person might carry to the job site to move large volumes of air quickly. I am in the process of pushing energy audits due to the high prices of fuel and or energy and have been thinking about fabricating such a device to move air but thought there might be one on the market already. Anyone have any knowledge of this.
Please let me know what you find Charley. I'm interested in that, too, but I've been so busy that time is short.



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #5  
Old 3/26/08, 7:14 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,918
Default Re: My worst enemy

Make the board from coroplast.
A corrugated PVC.
4x8 sheet sells for 8 bucks.
Reply With Quote
  #6  
Old 3/26/08, 7:26 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: My worst enemy

Quote:
Originally Posted by lkage
Please let me know what you find Charley. I'm interested in that, too, but I've been so busy that time is short.
I googled blower door and found some for sale $2K to much for me I will build one. I have an old squirrel cage blower from a furnace that moves a ton of air I may look into Bob the builders Sheet of plastic for a base and cut it down to fit the door. Time is also my problem
</IMG>



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #7  
Old 3/26/08, 7:52 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,848
Default Re: My worst enemy

Quote:
Originally Posted by cbottger
I googled blower door and found some for sale $2K to much for me I will build one. I have an old squirrel cage blower from a furnace that moves a ton of air I may look into Bob the builders Sheet of plastic for a base and cut it down to fit the door. Time is also my problem
</IMG>
I'll let you know if I come up with any better ideas.



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #8  
Old 3/26/08, 9:35 PM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: My worst enemy

Quote:
Originally Posted by cbottger
I googled blower door and found some for sale $2K to much for me I will build one. I have an old squirrel cage blower from a furnace that moves a ton of air I may look into Bob the builders Sheet of plastic for a base and cut it down to fit the door. Time is also my problem
</IMG>
If its a Minneapolis door, the $2K may be worth it for its compactness and ease of set up.

Last edited by Brian A. MacNeish; 3/26/08 at 10:31 PM..
Reply With Quote
  #9  
Old 3/26/08, 9:52 PM
William J. Decker's Avatar
William J. Decker William J. Decker is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 7,785
Default Re: My worst enemy

If you are doing quanitative inspections, a professional door is a must. You don't just want to create negative pressure, but a certain LEVEL of negative pressure.

I have a door, but I have found it is rarely needed for residential use.

Hope this helps;



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
  #10  
Old 3/26/08, 10:30 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: My worst enemy

Quote:
Originally Posted by wdecker
If you are doing quanitative inspections, a professional door is a must. You don't just want to create negative pressure, but a certain LEVEL of negative pressure.

I have a door, but I have found it is rarely needed for residential use.

Hope this helps;
I have ready excess to the gages and was considering a 3 speed motor and set it up with switches to manipulate volume of air. To me if one is charging good money for energy audits you should be as professional as possible. Just operating dryers and exhaust fans one has no way to actually determine the level of negative pressure just a guess and a whim.



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #11  
Old 3/26/08, 10:47 PM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: My worst enemy

Quote:
Originally Posted by cbottger
I have ready excess to the gages and was considering a 3 speed motor and set it up with switches to manipulate volume of air. To me if one is charging good money for energy audits you should be as professional as possible. Just operating dryers and exhaust fans one has no way to actually determine the level of negative pressure just a guess and a whim.
Without a calibrated blower door and program, you can't give the client any idea about how his house compares against some standard or norm. What are the Air Changes per Hour (ACH @ 50 pa) or the Equivalent Leakage Area (ELA) or the Normalized Leakage Area (NLA), etc.? You've got nothing to gauge the amount of air leakage against to tell the client whether a professional airsealing program (at many $$$) will be a good investment. If you're using an energy audit program (as a class "A" auditor should), then you'll need some air leakage data to complete the house picture.....other than than it becomes a "garbage in/garbage out" situation

After about 1 year in the airsealing business in the early 1980's, I was actually telling some homeowners after a blower door test that it wasn't worth them hiring my services to reduce air leakage....the payback wasn't there. That sure gets around in a small town!!

Last edited by Brian A. MacNeish; 3/27/08 at 5:27 AM..
Reply With Quote
  #12  
Old 3/26/08, 11:23 PM
Chuck Lambert Chuck Lambert is offline
Unmoderated Guest
 
Join Date: Jan 2008
Location: Southern California
Posts: 228
Please Note: Chuck Lambert is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: My worst enemy

I would not even attempt to build or run a blower door without the proper training. Please if any of you build one and are in Southern California please call me when you do you first house with a fireplace!!!

Chuck
Reply With Quote
  #13  
Old 3/27/08, 2:40 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,927
Default Re: My worst enemy

Quote:
I have ready excess to the gages and was considering a 3 speed motor and set it up with switches to manipulate volume of air.
Charlie,
Use a single speed motor and get a router speed controller so you can adjust your pressures more accurately.

If you're going to use a squirrel cage blower, it (the motor) does not have to go into a door or window opening. Leave the blower assembly in the house and connect it with flex duct to a supply air duct boot mounted on an adjustable panel to fit a window opening. You can easily install your magnehelic connections to get your airflow volume if necessary.

Those of you that are damning Charlie for making a blower door, he's talking about using it to enhance qualitative thermal inspections not to determine quantitative leakage of the house.

Reply With Quote
  #14  
Old 3/27/08, 2:54 PM
John McKenna's Avatar
John McKenna John McKenna is offline
InterNACHI Member
 
Join Date: Jun 2006
Location: Crockett, Tx
Posts: 12,303
Default Re: My worst enemy

As this thread illustrates, there are a lot of ideas that can be throw on the table
as to how to do an energy audit and what methods can be used to get there.

All the post I have read have some merit.

Now if you find out what the client expects vs what you supply, that is the key.

If you are not going to market you energy audit as an exact science, then
perhaps Will's comments are a practicle middle ground to consider.

Also what does the client want.? Most really want to know where to spend
the bucks that give the most bang in return.

Brians comments come from what he experienced. Please tell us more.

BTW... this post is not bashing anyone.



John McKenna, CMI (TREC #4565)
Executive Director - Master Inspector Certification Board
25 Yrs Constr Exp - 13 Yrs Home Inspector Exp
American Home Inspection - East Texas.

Reply With Quote
  #15  
Old 3/27/08, 3:10 PM
Richard L. Bennett Richard L. Bennett is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Frostproof, Fl
Posts: 2,304
Default Re: My worst enemy

Router speed controller will not work on a motor unless it is a "universial" motor.

Easy way to tell is it will have brushes

Most blower motors are not of the universial type

rlb
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Official: Housing Slump To Be Worst In Lifetime jburkeson1 Miscellaneous Discussion for Inspectors 0 1/11/08 6:11 PM
Gloom & Doom Economist Says Worst Is Yet to Come jburkeson1 Miscellaneous Discussion for Inspectors 0 10/22/07 8:52 PM
Worst furnace install ever cbottger Inspecting HVAC Systems 3 1/6/07 6:42 PM
Best and Worst Christmas Presants cpennick Miscellaneous Discussion for Inspectors 15 12/10/06 10:24 PM


All times are GMT -4. The time now is 6:20 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts