Default Not convinced

Had this bathroom today with a large amount of tile everywhere walls,floors. I alway use the IR camera around shower stalls just for the heck of it knowing the reflective value of tile is not going to be very accurate. Today I actually observed a cold spot on the floor just out side of the stall and moved around at different angles and the spot stayed the same. I even tried two different palettes with the same results. So I am thinking perhaps a leak perhaps a reflection. No guessing here luck on my side, Raised floor and when I entered the crawl space low and behold the shower stall pan was leaking.

Still not convinced If I was seeing a reflection or actually had water between the sub-flooring and the tile on the floor. All I can say for sure is the drain pan was leaking



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging

Last edited by cbottger; 5/13/08 at 10:08 PM..
Reply With Quote
  #2  
Old 3/4/08, 7:49 PM
mashburn's Avatar
mashburn mashburn is offline
InterNACHI Member
 
Join Date: May 2006
Location: Pittsburgh, PA
Posts: 286
Default Re: Not convinced

Nice find Charley.



Ashburn Inspections
724-516-1665
Reply With Quote
  #3  
Old 3/4/08, 8:53 PM
John McKenna's Avatar
John McKenna John McKenna is offline
InterNACHI Member
 
Join Date: Jun 2006
Location: Crockett, Tx
Posts: 12,303
Default Re: Not convinced

Good catch.



John McKenna, CMI (TREC #4565)
Executive Director - Master Inspector Certification Board
25 Yrs Constr Exp - 13 Yrs Home Inspector Exp
American Home Inspection - East Texas.

Reply With Quote
  #4  
Old 3/7/08, 7:47 AM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: TEXAS
Posts: 3,932
Default Re: Not convinced

Charley,

Proof the inspector's 5 senses are his/her best tools...how'd it taste?



ADAIR INSPECTION
972-487-5634

Commercial-Residential-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

2008 US Member of the Year

life is the random lottery of events followed by numerous narrow escapes accept the good
Reply With Quote
  #5  
Old 3/7/08, 8:41 AM
asargisian asargisian is offline
InterNACHI Member
 
Join Date: Nov 2007
Location: Columbia, MO
Posts: 313
Default Re: Not convinced

Good Job on finding the problem Charley
Reply With Quote
  #6  
Old 3/10/08, 8:01 AM
Rick K. Kie's Avatar
Rick K. Kie Rick K. Kie is offline
InterNACHI Member
 
Join Date: Jan 2008
Location: Endwell, NY
Posts: 385
Default Re: Not convinced

The Neo-Angle shower pans are noted for having leaks in the doors, the doors actually fill with water and leak. or when the door is opened after the shower it will leak. furthermore while taking a shower the threshold will leak, spilling water on the floor in the area your IR camera is detecting. My two cents is be carefully in your wording is the pan leaking or the caulking bad and water intrusion is noted or could the door be leaking. The pan and drain may be perfectly fine.
I love the cameras



Rick Kie
Reply With Quote
  #7  
Old 3/10/08, 9:29 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Not convinced

Quote:
Originally Posted by rkie
The Neo-Angle shower pans are noted for having leaks in the doors, the doors actually fill with water and leak. or when the door is opened after the shower it will leak. furthermore while taking a shower the threshold will leak, spilling water on the floor in the area your IR camera is detecting. My two cents is be carefully in your wording is the pan leaking or the caulking bad and water intrusion is noted or could the door be leaking. The pan and drain may be perfectly fine.
I love the cameras
See Pic above no door, shower curtain is used. I am always very careful where I direct the shower head no water splash allowed



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #8  
Old 3/11/08, 6:56 AM
Rick K. Kie's Avatar
Rick K. Kie Rick K. Kie is offline
InterNACHI Member
 
Join Date: Jan 2008
Location: Endwell, NY
Posts: 385
Default Re: Not convinced

I should have looked at the picture before i spoke. I assumed it was a fiberglass pan.



Rick Kie
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT -4. The time now is 6:12 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts