#31
|
||||
|
||||
|
I'm curious too. My answer 184.6.
Professional Inspector Level I Infrared www.AbsoluteInspections.net www.homeinspectorsplanotx.com www.homeinspectorsmckinney.com Absolute Inspections, LLC 972-463-0887 |
|
#32
|
||||
|
||||
|
Hey, at 65% load and 120 F, it is, already, a problem.
Will Decker, CMI ILL License # 450.0002240 Board Certified Master Inspector Decker Home Services, LLC Chicago and Northern Suburban Home Inspections Office: (847) 676-8393 Cell: (847) 609-2345 Home: (847) 673-2702 wjd@DeckerHomeServices.com www.DeckerHomeServices.com Learn, Educate, Serve and have fun doing it! |
|
#33
|
|||
|
|||
|
That may be true but it doesn't answer the question.
Hey Kevin, how'd you come up with 184.6. Mine I just added the missing 35% to the 120 degrees. InterNachi Awards Portal: http://co.nachi.org/inachiawards/ ____________________________________________ "An Education, not just an Inspection" Larry Kage, CMI Lake Ann (Traverse City), Michigan 49650 231 929 3525 Professional Inspector serving the Traverse City, Michigan area and beyond.
|
|
#34
|
||||
|
||||
|
Algebra. Which is probably oversimplified but was my best guess.
Professional Inspector Level I Infrared www.AbsoluteInspections.net www.homeinspectorsplanotx.com www.homeinspectorsmckinney.com Absolute Inspections, LLC 972-463-0887 |
|
#35
|
||||
|
||||
|
Yes John, I understand what you're saying. If it's hot, it's hot. But what about if it's not. What about the cases where the breaker is not all that hot and you decide not to include it in your inspection report or refer it for further evaluation.
Then something happens and the house catches fire and people get hurt. You made this decision on the information you collected. But how many people do not collect all the information, and make these decisions on incomplete information? How many times have you seen electrical issues called out and no one took a load reading because "that is outside the scope of home inspection". Well, so is thermal imaging. This thread is about liability. I agree with everyone. If you say it increases reliability, depending on its use it may. I personally started using thermal imaging to reduce my liability, and it does. I am also not saying that you have to perform "quantum physics". But when you make an assessment you must be able to back up your decisions with facts and point and shoot thermodynamics does not take this into consideration. It's not murder investigation? No but it may be negligent homicide! Kevin, you state that you simply report conditions that you find and show pictures and recommended further investigation. The same argument holds true for your statement. The report conditions, but how you determine the conditions? You show the pictures, therefore you have just handed out your liability. Again, what is the criteria to report or not to report? I hate to drop this and run but I have to do a two day IR trip to East Tennessee. Hopefully we can pick this up later. "Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein Clarksville - Nashville Home Inspector Lic#40 http://www.midtninspections.com ITC Level III Thermographer Cert#1958 Building Science Thermographer Cert#33784 http://www.thermalimagingscan.com HVAC Certification EPA Cert#2046620 Link to my Website at: http://www.midtninspections.com/link-submission |
|
#36
|
||||
|
||||
|
Quote:
John McKenna, CMI (TREC #4565)
Executive Director - Master Inspector Certification Board 25 Yrs Constr Exp - 13 Yrs Home Inspector Exp American Home Inspection - East Texas. Last edited by jmckenna1; 2/25/09 at 9:06 AM.. |
|
#37
|
||||
|
||||
|
Please Note:
Kevin Luce is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
Even though the question you asked is important to know, I looked at that situation as I would seeing only one furnace that is 40,000 BTU in a 3,000 sq. ft. house running all the time while the house is only getting up to 65 degrees while it is only 20 degrees outside. Here is the answer to your question. Corrected temperature at full load = 120 X (1.538 raised to the 1.8 power) = 260 |
|
#38
|
||||
|
||||
|
Please Note:
Kevin Luce is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
This is the formula used. Cor. ΔT = M ΔT X ( NFL )n ML Cor. ΔT = the corrected temperature difference which will be apparent when the equipment is back operating at normal full load. M ΔT = The temperature difference measured with the infrared camera using the proper emissivity and back ground settings at the time of inspection. NFL = The normal full load in amps at which the equipment usually operates. Note: This is not the rated load for the equipment. ML = The measured load in amps at the time of the inspection. Values for the exponential n When the problem is right at the surface of the component n=1.6 When the problem is close to the surface, good heat conductivity n=1.8 When the problem is far from the surface, poor heat conductivity n=2.0 Last edited by Kevin Luce; 2/25/09 at 6:32 PM.. Reason: Note: ML is suppose to be under NFL |
|
#39
|
|||
|
|||
|
Quote:
I appreciate the lesson. InterNachi Awards Portal: http://co.nachi.org/inachiawards/ ____________________________________________ "An Education, not just an Inspection" Larry Kage, CMI Lake Ann (Traverse City), Michigan 49650 231 929 3525 Professional Inspector serving the Traverse City, Michigan area and beyond.
|
|
#40
|
|||
|
|||
|
Please Note:
InspectorDana is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#41
|
||||
|
||||
|
No...they're Thermo-phobics.
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| How about it illinois | cbottger | Thermal Imaging, Infrared Cameras & Energy Audits | 13 | 8/19/11 6:07 PM |
| Look out John M here I come | cbottger | Thermal Imaging, Infrared Cameras & Energy Audits | 14 | 12/28/08 11:01 AM |
| Texas Needs a Boot | cbottger | Thermal Imaging, Infrared Cameras & Energy Audits | 1 | 12/26/08 1:52 PM |
| Ohio I know we can do it | cbottger | Thermal Imaging, Infrared Cameras & Energy Audits | 0 | 12/26/08 12:31 AM |