And I am not afraid of anything. Keep finding these breakers on kitchen ranges/cooktops
Freedom Express Inspections LLC CMOR Thermography Certified Level III #8486 freedomexpressinspections.com www.oklahomathermalinfraredimaging.com freedomexpress495@att.net NACHI Member Okla. State DEQ Environmental Phase One Certified Master HVAC Mechanic (Retired) Certified Universal Freon by 40CFR 82 Sub-part F State License # 130 Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging |
| Find an InterNACHI certified New York Home Inspector (and anywhere else in North America) |
|
#2
|
|||
|
|||
|
Is that a 40 amp stove breaker? The wire does not look large enough.
|
|
#3
|
|||
|
|||
|
I am new to infrared, as I have just recently received my Flir B60. I have been playing with it and found that an image like the one you show, tells you very little without knowing how much current is flowing through the circuit. I looked at my panel, saw the same thing and upon checking it with a clamp on amp meter found that there was only 8 amps flowing through a #12 wire and the 20 amp breaker. Far less than 80% of the breaker value. As this circuit was hotter than the rest, I got this disturbing thermal image. Correct me if I am missing something, but imaging a distribution panel without checking current flow is a waste of time. To simply look and tell the realtor and the client that they better have an electrician check it out is doing a diservice. The people involved are going to be a liitle upset if they have to schedule an electrician to come out and tell them everything is OK. I am aware that checking current is outside the scope of our inspections, but then again, so is thermal imaging.
|
|
#4
|
||||
|
||||
|
Quote:
Charley, Do you have the digital image of that breaker area? |
|
#5
|
||||
|
||||
|
That is a very good observation James.
There is all kinds of insufficient information here. However, a differential in temperature across the two legs is an indicator, as the load should be balanced for this appliance circuit. Also, any temperature in this range is enough of a consideration if the ambient temperature in the panel is this low. As this is a dedicated appliance circuit, we can often assume that the circuit is operating at capacity for this appliance, regardless of amperage (that is if the appliance is completely turned on during testing). We must assume that the emissivity was correctly set (but unless Charlie is playing his "Watz-This" games, you can be assured it's correct). I don't understand your post information fully. More information needed there also. You're absolutely correct if you say that a "slightly" overheated breaker can be "significant" even at low temperatures. It is very refreshing to see someone new to NACHI as well as the infrared field making these observations. There is far too much opinion here that qualitative thermal analysis is sufficient! You will probably be put in the doghouse for suggesting such absurd comments like taking amperage readings during thermal analysis of electrical service equipment, but hang in there! "Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein Clarksville - Nashville Home Inspector Lic#40 http://www.midtninspections.com ITC Level III Thermographer Cert#1958 Building Science Thermographer Cert#33784 http://www.thermalimagingscan.com HVAC Certification EPA Cert#2046620 Link to my Website at: http://www.midtninspections.com/link-submission |
|
#6
|
||||
|
||||
|
Have fun I have a early morning inspect trying to beat the snow storm will get back with this later
Freedom Express Inspections LLC CMOR Thermography Certified Level III #8486 freedomexpressinspections.com www.oklahomathermalinfraredimaging.com freedomexpress495@att.net NACHI Member Okla. State DEQ Environmental Phase One Certified Master HVAC Mechanic (Retired) Certified Universal Freon by 40CFR 82 Sub-part F State License # 130 Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging |
|
#7
|
||||
|
||||
|
James when you come to know me a little better I think you will realize that I don't make silly mistakes like you mentioned. As David A. stated it is refreshing to see someone use their head for something more than a hat rack. Your statements make a lot of good sense.
The pic's I illustrated were of a 4 burner cook top breaker no oven. I shot several images of this panel and documented the rise of temp over a time frame of approximately 15 to 20 minutes with the elements in the high range full amp load. This home had a 1968 FP 100 amp panel original as built but the home had undergone add on's was approximately 2500 SQ feet and no electrical updates. My client has the intentions to convert the electrical cook top and oven over to gas and my recommendation in the report was to update the main panel by a licensed electrican to accomondiate the size of the home. Freedom Express Inspections LLC CMOR Thermography Certified Level III #8486 freedomexpressinspections.com www.oklahomathermalinfraredimaging.com freedomexpress495@att.net NACHI Member Okla. State DEQ Environmental Phase One Certified Master HVAC Mechanic (Retired) Certified Universal Freon by 40CFR 82 Sub-part F State License # 130 Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging |
|
#8
|
||||
|
||||
|
Quote:
that qualitative analysis alone, on the electrical system, is sufficient. I have never seen anyone on this forum post such an idea. John McKenna, CMI (TREC #4565)
Executive Director - Master Inspector Certification Board 25 Yrs Constr Exp - 13 Yrs Home Inspector Exp American Home Inspection - East Texas. |
|
#9
|
|||
|
|||
|
Hello John, I took your course and found it very informative. Thank You. So qualitative analysis alone is not enough, I certainly agree, but how do most inspectors handle a hot spot (and wire) in a panel? Surely they dont recommend an electrician just because the one circuit is warmer than the others. As I said before, it may be well within the capacity of the breaker and the connected wire. It may simply have more of a load than the others. Charley, I was not referring to you, I was speaking in general. If I find a FP (Federal Pacific?) panel, I recommend replacement anyway. I guess I did not read your original post well as I thought we werer looking at two seperate 110V breakers.
|
|
#10
|
||||
|
||||
|
Quote:
David Sorge (USN Retired) FL License HI142 Infrared Certified Thermographer Inspect-It 1st of Northeast Florida Serving Jacksonville and surrounding communities 904-484-4847 dsorge@inspectit1st.com http://www.dsorgeinspects.com http://www.linkedin.com/profile?view...US&trk=tab_pro We see RED...InfraRED When we see RED... You see $GREEN$ Ask us how? Last edited by dsorge; 3/29/09 at 9:32 AM.. |
|
#11
|
||||
|
||||
|
Would that be a Federal Pacific Stab-Lok panel I see?
David Sorge (USN Retired) FL License HI142 Infrared Certified Thermographer Inspect-It 1st of Northeast Florida Serving Jacksonville and surrounding communities 904-484-4847 dsorge@inspectit1st.com http://www.dsorgeinspects.com http://www.linkedin.com/profile?view...US&trk=tab_pro We see RED...InfraRED When we see RED... You see $GREEN$ Ask us how? |
|
#12
|
||||
|
||||
|
David S would you expand on your statement a little and yes that panel was a FP stab-loc I have a ton of them here.
Freedom Express Inspections LLC CMOR Thermography Certified Level III #8486 freedomexpressinspections.com www.oklahomathermalinfraredimaging.com freedomexpress495@att.net NACHI Member Okla. State DEQ Environmental Phase One Certified Master HVAC Mechanic (Retired) Certified Universal Freon by 40CFR 82 Sub-part F State License # 130 Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging |
|
#13
|
||||
|
||||
|
Quote:
Being a stab-lok says it all and so does the thermograph. The focused heat pattern clearly indicates poor contact which is common to stab-loks. Those panels heat-cycle more than modern units due to poor contact of the breaker at the bus, and inevitably are prone to loosening of connectors. You need not investigate further. Its the reason that I always recommend immediate upgrade of these units. This would be a problem whether the circuit had 3 or 30 amps running through it. David Sorge (USN Retired) FL License HI142 Infrared Certified Thermographer Inspect-It 1st of Northeast Florida Serving Jacksonville and surrounding communities 904-484-4847 dsorge@inspectit1st.com http://www.dsorgeinspects.com http://www.linkedin.com/profile?view...US&trk=tab_pro We see RED...InfraRED When we see RED... You see $GREEN$ Ask us how? |
| Find an InterNACHI certified New York Home Inspector (and anywhere else in North America) |
|
#14
|
||||
|
||||
|
Quote:
How do you know this? Quote:
By the way, it doesn't take an electrician to call this. It takes a trained thermographer. Quote:
Quote:
"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein Clarksville - Nashville Home Inspector Lic#40 http://www.midtninspections.com ITC Level III Thermographer Cert#1958 Building Science Thermographer Cert#33784 http://www.thermalimagingscan.com HVAC Certification EPA Cert#2046620 Link to my Website at: http://www.midtninspections.com/link-submission |
|
#15
|
||||
|
||||
|
Quote:
Umm...er...concentrated heat at a contact lug comes from resistence. Resistence that shouldn't be present at the breaker lug. Resistance that comes from poor contact. Concentrated heat that radiated outwards through conduction from the source. The basic theory behind the heat/resistence relationship was around long before I "conjured" it up. David Sorge (USN Retired) FL License HI142 Infrared Certified Thermographer Inspect-It 1st of Northeast Florida Serving Jacksonville and surrounding communities 904-484-4847 dsorge@inspectit1st.com http://www.dsorgeinspects.com http://www.linkedin.com/profile?view...US&trk=tab_pro We see RED...InfraRED When we see RED... You see $GREEN$ Ask us how? |
![]() |