And I am not afraid of anything. Keep finding these breakers on kitchen ranges/cooktops
Attached Thumbnails
scares-me-ir_1644.jpg   scares-me-ir_1645.jpg  



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
Find an InterNACHI certified New York Home Inspector (and anywhere else in North America)
  #2  
Old 3/27/09, 1:42 AM
Keith Runquist, CMI Keith Runquist, CMI is offline
InterNACHI Member
 
Join Date: Dec 2008
Location: Rapid City, SD
Posts: 605
Send a message via AIM to krunquist
Default Re: Scares me

Is that a 40 amp stove breaker? The wire does not look large enough.
Reply With Quote
  #3  
Old 3/27/09, 3:33 AM
jhicks jhicks is offline
InterNACHI Member
 
Join Date: Mar 2009
Posts: 15
Default Re: Scares me

I am new to infrared, as I have just recently received my Flir B60. I have been playing with it and found that an image like the one you show, tells you very little without knowing how much current is flowing through the circuit. I looked at my panel, saw the same thing and upon checking it with a clamp on amp meter found that there was only 8 amps flowing through a #12 wire and the 20 amp breaker. Far less than 80% of the breaker value. As this circuit was hotter than the rest, I got this disturbing thermal image. Correct me if I am missing something, but imaging a distribution panel without checking current flow is a waste of time. To simply look and tell the realtor and the client that they better have an electrician check it out is doing a diservice. The people involved are going to be a liitle upset if they have to schedule an electrician to come out and tell them everything is OK. I am aware that checking current is outside the scope of our inspections, but then again, so is thermal imaging.
Reply With Quote
  #4  
Old 3/27/09, 6:39 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: Scares me

Quote:
Originally Posted by cbottger View Post
And I am not afraid of anything. Keep finding these breakers on kitchen ranges/cooktops

Charley,

Do you have the digital image of that breaker area?
Reply With Quote
  #5  
Old 3/27/09, 7:21 AM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,927
Default Re: Scares me

That is a very good observation James.

There is all kinds of insufficient information here. However, a differential in temperature across the two legs is an indicator, as the load should be balanced for this appliance circuit.

Also, any temperature in this range is enough of a consideration if the ambient temperature in the panel is this low. As this is a dedicated appliance circuit, we can often assume that the circuit is operating at capacity for this appliance, regardless of amperage (that is if the appliance is completely turned on during testing).

We must assume that the emissivity was correctly set (but unless Charlie is playing his "Watz-This" games, you can be assured it's correct).

I don't understand your post information fully. More information needed there also.
You're absolutely correct if you say that a "slightly" overheated breaker can be "significant" even at low temperatures.

It is very refreshing to see someone new to NACHI as well as the infrared field making these observations. There is far too much opinion here that qualitative thermal analysis is sufficient!

You will probably be put in the doghouse for suggesting such absurd comments like taking amperage readings during thermal analysis of electrical service equipment, but hang in there!



"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein

David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #6  
Old 3/27/09, 7:57 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Scares me

Quote:
Originally Posted by dvalley View Post
Charley,

Do you have the digital image of that breaker area?
Have fun I have a early morning inspect trying to beat the snow storm will get back with this later
Attached Thumbnails
scares-me-100_0776.jpg  



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #7  
Old 3/28/09, 11:10 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Scares me

James when you come to know me a little better I think you will realize that I don't make silly mistakes like you mentioned. As David A. stated it is refreshing to see someone use their head for something more than a hat rack. Your statements make a lot of good sense.

The pic's I illustrated were of a 4 burner cook top breaker no oven. I shot several images of this panel and documented the rise of temp over a time frame of approximately 15 to 20 minutes with the elements in the high range full amp load. This home had a 1968 FP 100 amp panel original as built but the home had undergone add on's was approximately 2500 SQ feet and no electrical updates. My client has the intentions to convert the electrical cook top and oven over to gas and my recommendation in the report was to update the main panel by a licensed electrican to accomondiate the size of the home.



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #8  
Old 3/29/09, 12:59 AM
John McKenna's Avatar
John McKenna John McKenna is offline
InterNACHI Member
 
Join Date: Jun 2006
Location: Crockett, Tx
Posts: 12,303
Default Re: Scares me

Quote:
Originally Posted by dandersen View Post
There is far too much opinion here that qualitative thermal analysis is sufficient!
Since there is so MUCH, please show me ONE person who has suggested
that qualitative analysis alone, on the electrical system, is sufficient. I have
never seen anyone on this forum post such an idea.



John McKenna, CMI (TREC #4565)
Executive Director - Master Inspector Certification Board
25 Yrs Constr Exp - 13 Yrs Home Inspector Exp
American Home Inspection - East Texas.

Reply With Quote
  #9  
Old 3/29/09, 1:21 AM
jhicks jhicks is offline
InterNACHI Member
 
Join Date: Mar 2009
Posts: 15
Default Re: Scares me

Hello John, I took your course and found it very informative. Thank You. So qualitative analysis alone is not enough, I certainly agree, but how do most inspectors handle a hot spot (and wire) in a panel? Surely they dont recommend an electrician just because the one circuit is warmer than the others. As I said before, it may be well within the capacity of the breaker and the connected wire. It may simply have more of a load than the others. Charley, I was not referring to you, I was speaking in general. If I find a FP (Federal Pacific?) panel, I recommend replacement anyway. I guess I did not read your original post well as I thought we werer looking at two seperate 110V breakers.
Reply With Quote
  #10  
Old 3/29/09, 8:46 AM
David Sorge's Avatar
David Sorge David Sorge is offline
InterNACHI Member
 
Join Date: Oct 2008
Location: Jacksonville Fl
Posts: 342
Default Re: Scares me

Quote:
Originally Posted by jmckenna1 View Post
Since there is so MUCH, please show me ONE person who has suggested
that qualitative analysis alone, on the electrical system, is sufficient. I have
never seen anyone on this forum post such an idea.
The biggest problem here is people pretending to be electricians and writing up problems that don't exist. (not you Charlie)



David Sorge (USN Retired)
FL License HI142
Infrared Certified Thermographer
Inspect-It 1st of Northeast Florida
Serving Jacksonville and surrounding communities
904-484-4847
dsorge@inspectit1st.com
http://www.dsorgeinspects.com

http://www.linkedin.com/profile?view...US&trk=tab_pro

We see RED...InfraRED



When we see RED...
You see $GREEN$


Ask us how?

Last edited by dsorge; 3/29/09 at 9:32 AM..
Reply With Quote
  #11  
Old 3/29/09, 8:48 AM
David Sorge's Avatar
David Sorge David Sorge is offline
InterNACHI Member
 
Join Date: Oct 2008
Location: Jacksonville Fl
Posts: 342
Default Re: Scares me

Quote:
Originally Posted by cbottger View Post
Have fun I have a early morning inspect trying to beat the snow storm will get back with this later
Would that be a Federal Pacific Stab-Lok panel I see?



David Sorge (USN Retired)
FL License HI142
Infrared Certified Thermographer
Inspect-It 1st of Northeast Florida
Serving Jacksonville and surrounding communities
904-484-4847
dsorge@inspectit1st.com
http://www.dsorgeinspects.com

http://www.linkedin.com/profile?view...US&trk=tab_pro

We see RED...InfraRED



When we see RED...
You see $GREEN$


Ask us how?
Reply With Quote
  #12  
Old 3/29/09, 9:58 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Scares me

Quote:
Originally Posted by dsorge View Post
The biggest problem here is people pretending to be electricians and writing up problems that don't exist. (not you Charlie)
David S would you expand on your statement a little and yes that panel was a FP stab-loc I have a ton of them here.



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #13  
Old 3/29/09, 10:11 AM
David Sorge's Avatar
David Sorge David Sorge is offline
InterNACHI Member
 
Join Date: Oct 2008
Location: Jacksonville Fl
Posts: 342
Default Re: Scares me

Quote:
Originally Posted by cbottger View Post
David S would you expand on your statement a little and yes that panel was a FP stab-loc I have a ton of them here.
Actually my statement was jab at someone that likes to make thinly veiled inuendos every time the topic of IR comes up. (again...not you)

Being a stab-lok says it all and so does the thermograph. The focused heat pattern clearly indicates poor contact which is common to stab-loks. Those panels heat-cycle more than modern units due to poor contact of the breaker at the bus, and inevitably are prone to loosening of connectors. You need not investigate further. Its the reason that I always recommend immediate upgrade of these units. This would be a problem whether the circuit had 3 or 30 amps running through it.



David Sorge (USN Retired)
FL License HI142
Infrared Certified Thermographer
Inspect-It 1st of Northeast Florida
Serving Jacksonville and surrounding communities
904-484-4847
dsorge@inspectit1st.com
http://www.dsorgeinspects.com

http://www.linkedin.com/profile?view...US&trk=tab_pro

We see RED...InfraRED



When we see RED...
You see $GREEN$


Ask us how?
Reply With Quote
Find an InterNACHI certified New York Home Inspector (and anywhere else in North America)
  #14  
Old 3/29/09, 12:37 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,927
Default Re: Scares me

Quote:
The focused heat pattern clearly indicates poor contact which is common to stab-loks. Those panels heat-cycle more than modern units due to poor contact of the breaker at the bus
You can't even see the part of the breaker where it connects to the buss!
How do you know this?

Quote:
The biggest problem here is people pretending to be electricians and writing up problems that don't exist. (not you Charlie)
No, I'm not pretending to be an electrician here!
By the way, it doesn't take an electrician to call this. It takes a trained thermographer.

Quote:
This would be a problem whether the circuit had 3 or 30 amps running through it.
And I assumed you determined this the same way you conjured up this...
Quote:
Being a stab-lok says it all



"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein

David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #15  
Old 3/29/09, 1:21 PM
David Sorge's Avatar
David Sorge David Sorge is offline
InterNACHI Member
 
Join Date: Oct 2008
Location: Jacksonville Fl
Posts: 342
Default Re: Scares me

Quote:
Originally Posted by dandersen View Post
You can't even see the part of the breaker where it connects to the buss!
How do you know this?


No, I'm not pretending to be an electrician here!
By the way, it doesn't take an electrician to call this. It takes a trained thermographer.


And I assumed you determined this the same way you conjured up this...
Do some research on Stab-Lok panels and you'll know it too

Umm...er...concentrated heat at a contact lug comes from resistence. Resistence that shouldn't be present at the breaker lug. Resistance that comes from poor contact. Concentrated heat that radiated outwards through conduction from the source.

The basic theory behind the heat/resistence relationship was around long before I "conjured" it up.



David Sorge (USN Retired)
FL License HI142
Infrared Certified Thermographer
Inspect-It 1st of Northeast Florida
Serving Jacksonville and surrounding communities
904-484-4847
dsorge@inspectit1st.com
http://www.dsorgeinspects.com

http://www.linkedin.com/profile?view...US&trk=tab_pro

We see RED...InfraRED



When we see RED...
You see $GREEN$


Ask us how?
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT -4. The time now is 6:27 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts