I found this on my afternoon inspection today. As per my normal routine, I fired up the furnace at the end of the inspection. But, I noticed this scorch mark during my visual inspection of the furnace. The furnace fired up and was running for about 5 minutes before I snapped this image (back side of gas fired forced air furnace).

Funny thing is the the Agent broke out the sellers disclosure and it had a reciept from a HVAC technician that clearly indicated that the furnace was functional and safe to operate. How could the Tech have missed the big scorth mark in the back of the furnace is beyond me.

Anyways, any ideas as to possible cause? Cracked heat exchanger, maybe? For you HVAC Gurus out there

Thanks,

Kevin
Attached Thumbnails
scorch-mark-furnace-scorchmark_furnace.jpg  



Kevin A. Richardson, BA
Level III Certified Infrared Thermographer, #7493
BPI Certified Building Performance Analyst
Maryland Licensed Home Inspector, #29727
INACHI Certified Home Inspector, #04091175

301-942-4610
www.richnspect.com
(Residential Inspections)
www.infrared-diagnostics.com
(Commercial Infrared Services)
www.thehomegreenteam.com
(Home Energy Performance Audits)

Last edited by krichardson; 7/25/08 at 7:58 PM..
Reply With Quote
  #2  
Old 7/25/08, 7:52 PM
Mark Nahrgang's Avatar
Mark Nahrgang Mark Nahrgang is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Saint Peters, MO
Posts: 3,946
Default Re: Scorch Mark on Furnace

Would a cracked heat exchanger cause that?
Reply With Quote
  #3  
Old 7/25/08, 8:00 PM
Kevin A. Richardson Kevin A. Richardson is offline
InterNACHI Member
 
Join Date: Sep 2004
Posts: 1,145
Default Re: Scorch Mark on Furnace

Quote:
Originally Posted by mnahrgang
Would a cracked heat exchanger cause that?
We must be on the same wavelength

I edited my original post to include "Cracked heat exchanger, maybe?" while you were posting your answer.

Let's see what anyone else come up with.

Kevin



Kevin A. Richardson, BA
Level III Certified Infrared Thermographer, #7493
BPI Certified Building Performance Analyst
Maryland Licensed Home Inspector, #29727
INACHI Certified Home Inspector, #04091175

301-942-4610
www.richnspect.com
(Residential Inspections)
www.infrared-diagnostics.com
(Commercial Infrared Services)
www.thehomegreenteam.com
(Home Energy Performance Audits)
Reply With Quote
  #4  
Old 7/25/08, 8:06 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: Scorch Mark on Furnace

Quote:
Originally Posted by krichardson
We must be on the same wavelength

I edited my original post to include "Cracked heat exchanger, maybe?" while you were posting your answer.

Let's see what anyone else come up with.

Kevin
What type of furnace is it? A picture would help.



"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector

Reply With Quote
  #5  
Old 7/25/08, 8:12 PM
Kevin A. Richardson Kevin A. Richardson is offline
InterNACHI Member
 
Join Date: Sep 2004
Posts: 1,145
Default Re: Scorch Mark on Furnace

Quote:
Originally Posted by mlarson
What type of furnace is it? A picture would help.
Gas fired forced air furnace (Lennox).

Kevin
Attached Thumbnails
scorch-mark-furnace-cimg0609.jpg  



Kevin A. Richardson, BA
Level III Certified Infrared Thermographer, #7493
BPI Certified Building Performance Analyst
Maryland Licensed Home Inspector, #29727
INACHI Certified Home Inspector, #04091175

301-942-4610
www.richnspect.com
(Residential Inspections)
www.infrared-diagnostics.com
(Commercial Infrared Services)
www.thehomegreenteam.com
(Home Energy Performance Audits)
Reply With Quote
  #6  
Old 7/25/08, 8:19 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: Scorch Mark on Furnace

The bottom of the heat exchanger is just behind that scorch mark on the back.

It looks like and old furnace.
I wonder how the HVAC "tech" "tested" the unit.



"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector

Reply With Quote
  #7  
Old 7/25/08, 8:39 PM
James F. McKee's Avatar
James F. McKee James F. McKee is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Amherst, Oh
Posts: 4,403
Default Re: Scorch Mark on Furnace

I was just thinking that sure looks like an old unit...I'd call for a evaluation by hvac specialist....jim



Classic Home inspections

Jim Mckee
Amherst, Ohio

www.amhersthomeinspector.com
Reply With Quote
  #8  
Old 7/25/08, 8:55 PM
Rick Maday's Avatar
Rick Maday Rick Maday is offline
InterNACHI Member
 
Join Date: Jan 2008
Location: Itasca, IL
Posts: 4,591
Default Re: Scorch Mark on Furnace

Quote:
Originally Posted by jmckee
I was just thinking that sure looks like an old unit...I'd call for a evaluation by hvac specialist....jim


Quote:
Originally Posted by krichardson
Funny thing is the the Agent broke out the sellers disclosure and it had a reciept from a HVAC technician that clearly indicated that the furnace was functional and safe to operate. How could the Tech have missed the big scorth mark in the back of the furnace is beyond me.



Owl Home Inspections
Rick Maday
Itasca, IL


Home Inspector Serving all Chicago Suburbs

Schaumburg Home Inspector
Naperville Home Inspector
Lake County Home Inspector
Reply With Quote
  #9  
Old 7/25/08, 9:01 PM
James F. McKee's Avatar
James F. McKee James F. McKee is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Amherst, Oh
Posts: 4,403
Default Re: Scorch Mark on Furnace

Quote:
Originally Posted by rmaday



I can read Rick....i'm just saying what i would put in my report....maybe that first guy was not all seeing.....I sure would not just say ok to that unit....jim



Classic Home inspections

Jim Mckee
Amherst, Ohio

www.amhersthomeinspector.com
Reply With Quote
  #10  
Old 7/25/08, 9:51 PM
cbottger's Avatar
cbottger cbottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 2,738
Default Re: Scorch Mark on Furnace

You know guys as one gets older other things do not appear as old either. Has anyone ever really observed an old furnace I will show you one from today.

Kevin you may not have a cracked exchanger just yet but the proballity is very high. The unit could also be staying on to long for various reasons and the high limit switch not working. You have a problem there should be no heat marks on the outer shell of the furnace cabinet. I think you can wear a feather in your cap on this one. HVAC techs do not walk on water they can miss things also I see their work all of the time.
Attached Thumbnails
scorch-mark-furnace-1004-riveria-pc-7-25-08-040.jpg   scorch-mark-furnace-1004-riveria-pc-7-25-08-045.jpg  



Freedom Express Inspections LLC
CMOR Thermography Certified Level 11 #2097
freedomexpressinspections.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
Professional Home Inspector State License # 130
Reporting system by Home Inspector Pro

Serving the State of Okla.
Reply With Quote
  #11  
Old 7/25/08, 10:11 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 3,697
Default Re: Scorch Mark on Furnace

Looks broke to me!

You should be able to look in the burner compartment and see this type heat exchanger.

Was the elevation about the same as the burners?

The heat exchanger could have been worked on in it's past life and is touching the back of the cabinet.

I would put my $$$ on the cracked HE.

Time to get out the bore scope!



David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Certified Level II Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620

Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #12  
Old 7/25/08, 10:32 PM
Kevin A. Richardson Kevin A. Richardson is offline
InterNACHI Member
 
Join Date: Sep 2004
Posts: 1,145
Default Re: Scorch Mark on Furnace

Quote:
Originally Posted by dandersen
Looks broke to me!

You should be able to look in the burner compartment and see this type heat exchanger.

Was the elevation about the same as the burners?

The heat exchanger could have been worked on in it's past life and is touching the back of the cabinet.

I would put my $$$ on the cracked HE.

Time to get out the bore scope!
Well, it looks like I'm going to be called out on this one. Got a call from the agent a little while ago. They want me and I quote "my camera" to return to the property on Monday. The sellers want to have the HVAC tech that conducted the inspection on site.

I'm up for the challange!!

Thanks for the replies.

Kevin



Kevin A. Richardson, BA
Level III Certified Infrared Thermographer, #7493
BPI Certified Building Performance Analyst
Maryland Licensed Home Inspector, #29727
INACHI Certified Home Inspector, #04091175

301-942-4610
www.richnspect.com
(Residential Inspections)
www.infrared-diagnostics.com
(Commercial Infrared Services)
www.thehomegreenteam.com
(Home Energy Performance Audits)
Reply With Quote
  #13  
Old 7/26/08, 12:59 AM
Rick Maday's Avatar
Rick Maday Rick Maday is offline
InterNACHI Member
 
Join Date: Jan 2008
Location: Itasca, IL
Posts: 4,591
Default Re: Scorch Mark on Furnace

Quote:
Originally Posted by jmckee
I can read Rick....i'm just saying what i would put in my report....maybe that first guy was not all seeing.....I sure would not just say ok to that unit....jim
Jim,

Sorry if I implied that - no offense meant.
This is quite clearly something that needs a tech (who knows what's going on).

Ironic that they want the original guy back out there.



Owl Home Inspections
Rick Maday
Itasca, IL


Home Inspector Serving all Chicago Suburbs

Schaumburg Home Inspector
Naperville Home Inspector
Lake County Home Inspector
Reply With Quote
  #14  
Old 7/31/08, 10:37 PM
Peter W. Bennett Peter W. Bennett is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Little Silver, NJ
Posts: 373
Default Re: Scorch Mark on Furnace

Love the photos. Which FLIR cam were you using?
Reply With Quote
  #15  
Old 8/1/08, 12:13 AM
Peter C. Russell's Avatar
Peter C. Russell Peter C. Russell is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Rollinsford, NH
Posts: 2,824
Default Re: Scorch Mark on Furnace

Quote:
Originally Posted by pbennett1
Love the photos. Which FLIR cam were you using?
Also, what's the resolution? Nice picture.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
980 Questions/Answers to the NHIE....Free! jbushart Legislation, Licensing & Legal Issues 50 4/20/08 2:26 AM
Furnace Problem Comments Welcome rfrost HVAC 24 10/21/07 7:26 PM
Sweating decision:Settle for lower SEER to use existing furnace? Fel Randolph HVAC 2 6/6/07 3:56 PM
Condemned Furnaces Spark Safety Issues Gary Reecher HVAC 7 3/8/07 9:17 PM
Misuse of Title rwand1 Canadian Inspectors 20 10/14/06 9:19 AM


All times are GMT -4. The time now is 7:16 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts