Default Sean F 101

Sean just for you here are some electrical scan from today's inspect. I very seldom do a residential electrical panel that has a electrical cook stove and or cook top that does not mirror these images take note they are in focus most important of all you can not change the focus in the software. FORD is the word.

Take note of the main L1 L2 feeds to the 150 amp breaker some what of a temp difference due to different amp on the two wires one had about 80 amps the other had 115 amps. Different story on the cook stove breaker, same amps on both sides of the double pole breaker but near 10 degrees difference between the two legs. I will report that as a loose connection

BTW this home was vacant and I still loaded that panel
Attached Thumbnails
sean-f-101-3702-willow-lake-lane-enid-8-26-11-082.jpg   sean-f-101-3702-willow-lake-lane-enid-8-26-11-084.jpg   sean-f-101-3702-willow-lake-lane-enid-8-26-11-089.jpg   sean-f-101-3702-willow-lake-lane-enid-8-26-11-042.jpg  



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
Need a home inspection in Missouri? Check out InterNACHI's listing of Missouri certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 8/26/11, 6:35 PM
Sean Fogarty's Avatar
Sean Fogarty Sean Fogarty is offline
InterNACHI Member
 
Join Date: Sep 2009
Location: Somewhere in Knoxville TN flipping breakers
Posts: 2,267
Default Re: Sean F 101

Thanks Charley!




Infraspection Institute Level 1 Certified Infrared Thermographer

Fogarty Inspection Services Group of Knoxville TN

Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.

865-256-5397

www.homeinspectorknoxville.com

www.moldandradon.com

www.thermal-inspection.net

www.commercial-building-inspector.net
Reply With Quote
  #3  
Old 8/26/11, 7:52 PM
Wayne B. Wilson's Avatar
Wayne B. Wilson Wayne B. Wilson is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Powell, Tn
Posts: 8,234
Default Re: Sean F 101

Please note AMP Meter lolol and focus



Wayne Wilson
East TN Home Inspections LLC
Knoxville, Oak Ridge, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.
865-256-1490

http://site.myhomeinspection.net

Reply With Quote
  #4  
Old 8/26/11, 8:23 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Sean F 101

Quote:
Originally Posted by wwilson3 View Post
Please note AMP Meter lolol and focus
A little bird told me you was going to buy him a meter any truth to that story



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #5  
Old 8/26/11, 8:53 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,927
Default Re: Sean F 101



One note of caution when comparing two conductors on the same heavily loaded circuit breaker; when the breakers are stacked horizontally, the heat from the lower conductor/phase moves upward from convection/conduction and the combined heat at the upper conductor will become warmer than the lower.
You will notice in Charley's scan (which I modified) there is a V pattern above the lower phase, widening as it approaches the upper phase. The temperature gradients of purple are wider above the hot breaker then they are below the hot breaker. This is the visible effect of convection.

You'll also notice heat moving across to the next breaker above where there is a slight blue pattern on that breaker which is 5° warmer than other parts of that breaker.

Extremely hot wires also radiate a considerable amount and you will notice a pattern change on adjacent wires and components from this radiating effect.

You can see a slightly lighter purple color on the conductors above the hot breaker on the bottom of the wires. In this case it is a combination of both radiation and convection. In some instances the same pattern will be noted at great distances across the panel, beyond the distance which convection will cause this affect. This would be almost total radiation affect.

We must always consider conditions which may push the anomaly over the top into the "repair immediately" zone when actually it may not have gotten there yet.

This becomes even of greater concern when you own a higher end camera as the camera is sensitive enough to pick up these increases and record them.
There's a high probability you would not even see any of this with an I5.
Attached Thumbnails
sean-f-101-3702-20willow-20lake-20lane-20enid-208-26-11-20089.jpg  



"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein

David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #6  
Old 8/26/11, 10:13 PM
Wayne B. Wilson's Avatar
Wayne B. Wilson Wayne B. Wilson is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Powell, Tn
Posts: 8,234
Default Re: Sean F 101

Quote:
Originally Posted by cbottger View Post
A little bird told me you was going to buy him a meter any truth to that story
Yeah i heard that too, funny i think i have a amp probe older than him lolol



Wayne Wilson
East TN Home Inspections LLC
Knoxville, Oak Ridge, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.
865-256-1490

http://site.myhomeinspection.net

Reply With Quote
  #7  
Old 8/26/11, 10:44 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Sean F 101

Quote:
Originally Posted by dandersen View Post


One note of caution when comparing two conductors on the same heavily loaded circuit breaker; when the breakers are stacked horizontally, the heat from the lower conductor/phase moves upward from convection/conduction and the combined heat at the upper conductor will become warmer than the lower.
You will notice in Charley's scan (which I modified) there is a V pattern above the lower phase, widening as it approaches the upper phase. The temperature gradients of purple are wider above the hot breaker then they are below the hot breaker. This is the visible effect of convection.

You'll also notice heat moving across to the next breaker above where there is a slight blue pattern on that breaker which is 5° warmer than other parts of that breaker.

Extremely hot wires also radiate a considerable amount and you will notice a pattern change on adjacent wires and components from this radiating effect.

You can see a slightly lighter purple color on the conductors above the hot breaker on the bottom of the wires. In this case it is a combination of both radiation and convection. In some instances the same pattern will be noted at great distances across the panel, beyond the distance which convection will cause this affect. This would be almost total radiation affect.

We must always consider conditions which may push the anomaly over the top into the "repair immediately" zone when actually it may not have gotten there yet.

This becomes even of greater concern when you own a higher end camera as the camera is sensitive enough to pick up these increases and record them.
There's a high probability you would not even see any of this with an I5.
Dave what you did not know and I did not tell was how much time did the breaker have the amount of load that it had which was less than 10 minutes when one uses a oven it is usually more than 10 minutes and the breaker would have exceeded the indicated temp had I extended the test which I deemed not necessary so in this particular case time was of more importance than the actual temp



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #8  
Old 8/26/11, 10:46 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Sean F 101

Quote:
Originally Posted by wwilson3 View Post
Yeah i heard that too, funny i think i have a amp probe older than him lolol
Xmas is coming soon buy him a gift



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #9  
Old 8/27/11, 12:35 AM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,927
Default Re: Sean F 101

I never judge a scan just by it's temp (or without any of the other items of information that should be considered).

I found this scan to be a great example of thermal movement and it's effect on the other elements in the panel.

If this was evident in a short time, it was in a very aggressive transition.

Sorry about messing with your scan, but when you mess with these things some interesting stuff always comes to light. Just though I would share what I saw that many never look at. All those colors and funny lines tell a story.



"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein

David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #10  
Old 8/27/11, 7:51 AM
Sean Fogarty's Avatar
Sean Fogarty Sean Fogarty is offline
InterNACHI Member
 
Join Date: Sep 2009
Location: Somewhere in Knoxville TN flipping breakers
Posts: 2,267
Default Re: Sean F 101

Thanks David!

Wayne, you know you wanna buy me an amp meter..




Infraspection Institute Level 1 Certified Infrared Thermographer

Fogarty Inspection Services Group of Knoxville TN

Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.

865-256-5397

www.homeinspectorknoxville.com

www.moldandradon.com

www.thermal-inspection.net

www.commercial-building-inspector.net
Reply With Quote
  #11  
Old 8/27/11, 7:52 AM
Wayne B. Wilson's Avatar
Wayne B. Wilson Wayne B. Wilson is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Powell, Tn
Posts: 8,234
Default Re: Sean F 101

Maybe Santa lol



Wayne Wilson
East TN Home Inspections LLC
Knoxville, Oak Ridge, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.
865-256-1490

http://site.myhomeinspection.net

Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
A certification that means something sfogarty General Inspection Discussion 48 12/4/10 10:25 PM
Real-estate agent and home inspector face off rcooke Canadian Inspectors 5 9/22/10 9:46 PM