Default temp of transformer

What do you guys think of this low voltage transformer temperature found in the attic sitting on the vapour barrier, gyproc. Are they suppose to run this warm?
Attached Thumbnails
temp-transformer-ir_0117.jpg   temp-transformer-ir_0118.jpg  
Reply With Quote
  #2  
Old 11/24/08, 6:38 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,927
Default Re: temp of transformer

Yes.

There are IR programs for training concerning "standards".

I would highly recommend that if you only attended a "Basic" IR course that you continue ( and cough up the bucks) with education and experience in IR.

99% of camera owners do not know what they are looking at.

Just don't subscribe to that group.



"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein

David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission

Last edited by dandersen; 11/24/08 at 6:42 PM..
Reply With Quote
  #3  
Old 11/24/08, 6:51 PM
ldapkus ldapkus is offline
Active Poster
 
Join Date: Mar 2006
Posts: 5,717
Please Note: ldapkus is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: temp of transformer

Mark is certified
Reply With Quote
  #4  
Old 11/24/08, 8:32 PM
Kevin A. Richardson Kevin A. Richardson is offline
InterNACHI Member
 
Join Date: Sep 2004
Posts: 1,334
Default Re: temp of transformer

Quote:
Originally Posted by dandersen View Post
Yes.

There are IR programs for training concerning "standards".

I would highly recommend that if you only attended a "Basic" IR course that you continue ( and cough up the bucks) with education and experience in IR.

99% of camera owners do not know what they are looking at.

Just don't subscribe to that group.
David,

Why don't you chill out! Mark asked for help not unsolicited advice from a know it all!

Frankly I'm getting tired of your posts lately. If you don't want to help Mark then don't bother posting.

For the record, I would venture to say that many Level I, II and III Thermographers may not know the answer to his question, which I believe is a very good one.

Keep 'em coming, Mark.

Kevin



Kevin A. Richardson
Level III Infraspection Institute Certified Infrared ThermographerŪ, #7493
Infraspection Institute Thermography Instructor
BPI Certified Building Performance Analyst
RESNET Level II Home Energy Survey Professional
Maryland Licensed Home Inspector, #29727
InterNACHI Certified Professional Inspector, #04091175


301-942-4610
www.richnspect.com
www.infrared-diagnostics.com
www.thehomegreenteam.com
Reply With Quote
  #5  
Old 11/24/08, 8:44 PM
ldapkus ldapkus is offline
Active Poster
 
Join Date: Mar 2006
Posts: 5,717
Please Note: ldapkus is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: temp of transformer

Thanks Kevin,
We're not all Mr. Know-It-Alls.
Reply With Quote
  #6  
Old 11/24/08, 8:46 PM
Kevin A. Richardson Kevin A. Richardson is offline
InterNACHI Member
 
Join Date: Sep 2004
Posts: 1,334
Default Re: temp of transformer

Quote:
Originally Posted by ldapkus View Post
Thanks Kevin,
We're not all Mr. Know-It-Alls.
I know.......previous post was kinda harsh

I'm tired and it's been a long day......

Kevin



Kevin A. Richardson
Level III Infraspection Institute Certified Infrared ThermographerŪ, #7493
Infraspection Institute Thermography Instructor
BPI Certified Building Performance Analyst
RESNET Level II Home Energy Survey Professional
Maryland Licensed Home Inspector, #29727
InterNACHI Certified Professional Inspector, #04091175


301-942-4610
www.richnspect.com
www.infrared-diagnostics.com
www.thehomegreenteam.com
Reply With Quote
  #7  
Old 11/24/08, 10:14 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,927
Default Re: temp of transformer

I'm also tired and had a long day.
Just go to bed Kevin!

If I am not mistaken Kevin, you promote the IR programs and standards I am referring to. Are you going to just hang around here with your level III training and answer these types of questions, hoping someone will find it some how in your words of knowledge? Just don't be right too much, you'll become a know-it-all.

I don't know it all. I simply state "known facts". If some of you want to make up crap as you go along that's just fine.

If you don't know the facts, there are places to get them.
If you think NACHI is a place to get it all for free, call Ben and he'll make a video.

Know it all,?
I don't make this stuff up.
I guess I need to screw up more and be part of the good ole boy club...

The fact of the matter is that many hvac and ir threads seem to end with my name.
No on seems to research anything and prove me wrong, so I just keep on, keeping on.
If you have proof, post it. What power do I have to keep you from disclosing the truth? I am always looking for something new to learn. Teach me something for a change.

I have posted time and time again, if you don't know what your pointing your IR camera at, point it elsewhere. There are those of you out there that have a $5k imager, spent $$ on training (of sorts) and you haven't yet pointed it at your cell phone charger and realized that transformers make a lot of heat?
In this case, just what building material has a flash point below 112 degrees F?
They say there are no stupid questions, some say stupid people ask questions, I say some questions are asked by lazy people.

In my opinion, if I were to pay someone $300 to check my house I think they should know what moisture looks like, what air infiltration looks like, what a hot electrical service is and is not. These things have specific signatures. Basic Level I.

GFIC's, transformers, smoke detectors, motors, heating and a/c equipment generate heat due to the work they do. There ARE standards. Get them, learn them, then go do your job. If you don't, you make all of those above us in this field look like fools and bring discredit upon the industry. Which is not an asset to anyone.

There are standards, and few of you are getting it.
Your not even paying attention to John M's HI course. If you don't invest in the training it means very little. Free advise here obviously means very little to many who blindly oppose. John told me that many take his two day course and never turn in the field assignment. Evidence to my point.

Contact jim@infraspection.com and others that have years on us and get with the program.

Ya'll tired of my posts, well that can be remedied. I'm tired of your posts and we can call it even.

Mark, I apologize to you. This is not about you or your question. This is about complacency of those that should know better. You should have been taught the answer to your question. That is by beef.

I also apologize to the others; my trying to interpret the facts, trying to make a wild-*****-guess on minimal information, for getting frustrated when other know-it-alls (by interpretation) call overheated breakers, hundreds of times over the accepted standard as being "NORMAL".

Yup,
Quote:
.......previous post was kinda harsh
I'm not one to kiss your ***** and make you feel good. I just want you to do the right thing by your customer and maybe keep your sorry butt out of court.

I'll take my book of "know-it-all" and be gone.
Bye.



"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein

David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #8  
Old 11/24/08, 10:21 PM
mnicholet's Avatar
mnicholet mnicholet is offline
Active Poster
 
Join Date: Mar 2008
Location: Vancouver Island, BC
Posts: 543
Please Note: mnicholet is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: temp of transformer

Quote:
Originally Posted by dandersen View Post
Yes.

There are IR programs for training concerning "standards".

I would highly recommend that if you only attended a "Basic" IR course that you continue ( and cough up the bucks) with education and experience in IR.

99% of camera owners do not know what they are looking at.

Just don't subscribe to that group.
I appreciate your concern, I believe education is a valuable asset and yes I am Infrared-Certified. Although, I can never learn enough. What is your opinion of the heat from this transformer. It was located in a garage and the median temperature in my location this time of year is around 5 C or 41 F.

I guess, next time I could write the manufacturer information down and give them a call...

I just wanted some discussion on it
Reply With Quote
  #9  
Old 11/24/08, 10:25 PM
mnicholet's Avatar
mnicholet mnicholet is offline
Active Poster
 
Join Date: Mar 2008
Location: Vancouver Island, BC
Posts: 543
Please Note: mnicholet is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: temp of transformer

Quote:
Originally Posted by dandersen View Post
I'm also tired and had a long day.
Just go to bed Kevin!

If I am not mistaken Kevin, you promote the IR programs and standards I am referring to. Are you going to just hang around here with your level III training and answer these types of questions, hoping someone will find it some how in your words of knowledge? Just don't be right too much, you'll become a know-it-all.

I don't know it all. I simply state "known facts". If some of you want to make up crap as you go along that's just fine.

If you don't know the facts, there are places to get them.
If you think NACHI is a place to get it all for free, call Ben and he'll make a video.

Know it all,?
I don't make this stuff up.
I guess I need to screw up more and be part of the good ole boy club...

The fact of the matter is that many hvac and ir threads seem to end with my name.
No on seems to research anything and prove me wrong, so I just keep on, keeping on.
If you have proof, post it. What power do I have to keep you from disclosing the truth? I am always looking for something new to learn. Teach me something for a change.

I have posted time and time again, if you don't know what your pointing your IR camera at, point it elsewhere. There are those of you out there that have a $5k imager, spent $$ on training (of sorts) and you haven't yet pointed it at your cell phone charger and realized that transformers make a lot of heat?
In this case, just what building material has a flash point below 112 degrees F?
They say there are no stupid questions, some say stupid people ask questions, I say some questions are asked by lazy people.

In my opinion, if I were to pay someone $300 to check my house I think they should know what moisture looks like, what air infiltration looks like, what a hot electrical service is and is not. These things have specific signatures. Basic Level I.

GFIC's, transformers, smoke detectors, motors, heating and a/c equipment generate heat due to the work they do. There ARE standards. Get them, learn them, then go do your job. If you don't, you make all of those above us in this field look like fools and bring discredit upon the industry. Which is not an asset to anyone.

There are standards, and few of you are getting it.
Your not even paying attention to John M's HI course. If you don't invest in the training it means very little. Free advise here obviously means very little to many who blindly oppose. John told me that many take his two day course and never turn in the field assignment. Evidence to my point.

Contact jim@infraspection.com and others that have years on us and get with the program.

Ya'll tired of my posts, well that can be remedied. I'm tired of your posts and we can call it even.

Mark, I apologize to you. This is not about you or your question. This is about complacency of those that should know better. You should have been taught the answer to your question. That is by beef.

I also apologize to the others; my trying to interpret the facts, trying to make a wild-*****-guess on minimal information, for getting frustrated when other know-it-alls (by interpretation) call overheated breakers, hundreds of times over the accepted standard as being "NORMAL".

Yup, I'm not one to kiss your ***** and make you feel good. I just want you to do the right thing by your customer and maybe keep your sorry butt out of court.

I'll take my book of "know-it-all" and be gone.
Bye.
Ok, point taken, thanks.
Reply With Quote
  #10  
Old 11/24/08, 10:40 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: temp of transformer

Kevin I can understand David's furstration (for a lack of a better word) some of us have absolutely spent thousands of dollars on the best training available (our choice) and when someone that comes on line with $150.00 worth of training wanting answers to yes a very simple question that an apprentice electrican could answer. The question did not really have anything to do with thermal imaging that just simply was the tool being used to determine temp and it was apparent to me that Mark does not really understand how the camera detects temp he was capturing a temp of an electrical device that was shiney in nature with the E-value set on 95 thus when the actually the true temp would have been approximately 106 to 108 if taken in a conventional manner. I don't understand why you would say that a level 1 2 or 3 might not be able two answer that question is beyond me. My point is one should know something about what one is taking images of, know what the standards are.

Yes David can be a little rough at times but if one has thick skin will probally survive to be the better HI for it. Why don't we all just get along.



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #11  
Old 11/24/08, 11:51 PM
Kevin A. Richardson Kevin A. Richardson is offline
InterNACHI Member
 
Join Date: Sep 2004
Posts: 1,334
Default Re: temp of transformer

Quote:
If I am not mistaken Kevin, you promote the IR programs and standards I am referring to. Are you going to just hang around here with your level III training and answer these types of questions, hoping someone will find it some how in your words of knowledge? Just don't be right too much, you'll become a know-it-all.
This is a very "Jerk" statement. Of course I promote proper training and the adherence to a set of standards. If I have time I will most certainly answer questions or try to be helpful. As a matter of fact, I spent a lot of time doing just that. There are many behind the scenes of the MB who have asked questions relating to Thermography. I certainly do not claim to know it all just because I have a Level III. There is a big difference in being helpful and talking down to someone. Mark simply asked a question! Regardless of weather or not you thought it was stupid or not, he didn't deserve to be lectured by you.

Quote:
The fact of the matter is that many hvac and ir threads seem to end with my name.
No on seems to research anything and prove me wrong, so I just keep on, keeping on.
If you have proof, post it. What power do I have to keep you from disclosing the truth? I am always looking for something new to learn. Teach me something for a change.
Your over bloated ego has gotten the best of you. I don't need to teach you a damn thing. By the way you talk here, you would probably just argue and claim you are always right.

Quote:
There ARE standards. Get them, learn them, then go do your job. If you don't, you make all of those above us in this field look like fools and bring discredit upon the industry. Which is not an asset to anyone.
Agreed. Inspectors should go get the standards relating to IR work. However, the later part of your statement is just more self-centered nonsense. Keep your own house in order and stopping spreading fear. Who are "those above us," anyways?

Listen, I have always stressed the importance of getting the proper training for whatever it is your going to be doing. But, beating people into the ground here just for asking a question is not really productive. If you don't have the time or don't want to answer the question, then don't post.

David, it seems to me that you are somehow taking his question personal. Mark's lack of knowledge does not affect you one bit. Nor, does it reflect negatively upon you or the industry as a whole. To think otherwise is naive.

Kevin



Kevin A. Richardson
Level III Infraspection Institute Certified Infrared ThermographerŪ, #7493
Infraspection Institute Thermography Instructor
BPI Certified Building Performance Analyst
RESNET Level II Home Energy Survey Professional
Maryland Licensed Home Inspector, #29727
InterNACHI Certified Professional Inspector, #04091175


301-942-4610
www.richnspect.com
www.infrared-diagnostics.com
www.thehomegreenteam.com

Last edited by krichardson; 11/25/08 at 12:03 AM..
Reply With Quote
  #12  
Old 11/24/08, 11:57 PM
Kevin A. Richardson Kevin A. Richardson is offline
InterNACHI Member
 
Join Date: Sep 2004
Posts: 1,334
Default Re: temp of transformer

Quote:
Originally Posted by cbottger View Post
Kevin I can understand David's furstration (for a lack of a better word) some of us have absolutely spent thousands of dollars on the best training available (our choice) and when someone that comes on line with $150.00 worth of training wanting answers to yes a very simple question that an apprentice electrican could answer. The question did not really have anything to do with thermal imaging that just simply was the tool being used to determine temp and it was apparent to me that Mark does not really understand how the camera detects temp he was capturing a temp of an electrical device that was shiney in nature with the E-value set on 95 thus when the actually the true temp would have been approximately 106 to 108 if taken in a conventional manner. I don't understand why you would say that a level 1 2 or 3 might not be able two answer that question is beyond me. My point is one should know something about what one is taking images of, know what the standards are.

Yes David can be a little rough at times but if one has thick skin will probally survive to be the better HI for it. Why don't we all just get along.
You'll be suprised to what other people know or don't know!! Last I checked people get along by being nice and helpful to one another. Not just preaching or talking down to one another.

I wonder if Mark or any other Inspector will post an example or question here again? This section of the message board was developed for us to have discussions relating to Thermography and to share ideas and questions. I just think it is counter productive to just talk down to someone for just posting a simple question.

enough said.....

Kevin

Kevin



Kevin A. Richardson
Level III Infraspection Institute Certified Infrared ThermographerŪ, #7493
Infraspection Institute Thermography Instructor
BPI Certified Building Performance Analyst
RESNET Level II Home Energy Survey Professional
Maryland Licensed Home Inspector, #29727
InterNACHI Certified Professional Inspector, #04091175


301-942-4610
www.richnspect.com
www.infrared-diagnostics.com
www.thehomegreenteam.com
Reply With Quote
  #13  
Old 11/25/08, 12:49 AM
Jeff Moore Jeff Moore is offline
New User
 
Join Date: Aug 2008
Posts: 29
Please Note: Jeff Moore is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: temp of transformer

Wow, what a pleasant discussion.

One cannot tell from the IR image whether the surface is shiny
or if it is a black plastic. Therefore, to assume that his emissivity
setting is improper is reaching just a little. To make that assumtion
we would need to see a digital image of same area. To many people who take IR training the most difficult area is in electrical componets and what is an abnormal temperature for a given usage. If you search the web and read different literature it is easy to become confused with what is correct and what is not.

Mark came to this board asking for some information. He was trashed.
A simple " Do some reading in your text books" along with " Nope, not a problem" would have been sufficient.

I also am an advocate for education. IR is a tool that can be very beneficial when applied properly. It also can take you places you don't want to be. (court)

IMHO

Jeff
ITC/FLIR Level 1
IR for Weatherization
Reply With Quote
  #14  
Old 11/25/08, 8:16 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: temp of transformer

Quote:
Originally Posted by krichardson View Post
You'll be suprised to what other people know or don't know!! Last I checked people get along by being nice and helpful to one another. Not just preaching or talking down to one another.

I wonder if Mark or any other Inspector will post an example or question here again? This section of the message board was developed for us to have discussions relating to Thermography and to share ideas and questions. I just think it is counter productive to just talk down to someone for just posting a simple question.

enough said.....

Kevin

Kevin

No Kevin surprised is one thing I am not as to what people know or don't know generally speaking it becomes obvious very quickly. I was not trying to take sides both you and David should have taken that discussion to private E-mails Two wrongs doesn't make a right



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #15  
Old 11/25/08, 9:12 AM
Dale Duffy's Avatar
Dale Duffy Dale Duffy is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Scottsdale, AZ
Posts: 8,261
Default Re: temp of transformer

Quote:
Originally Posted by dandersen View Post
I'm also tired and had a long day.
Just go to bed Kevin!

If I am not mistaken Kevin, you promote the IR programs and standards I am referring to. Are you going to just hang around here with your level III training and answer these types of questions, hoping someone will find it some how in your words of knowledge? Just don't be right too much, you'll become a know-it-all.

I don't know it all. I simply state "known facts". If some of you want to make up crap as you go along that's just fine.

If you don't know the facts, there are places to get them.
If you think NACHI is a place to get it all for free, call Ben and he'll make a video.

Know it all,?
I don't make this stuff up.
I guess I need to screw up more and be part of the good ole boy club...

The fact of the matter is that many hvac and ir threads seem to end with my name.
No on seems to research anything and prove me wrong, so I just keep on, keeping on.
If you have proof, post it. What power do I have to keep you from disclosing the truth? I am always looking for something new to learn. Teach me something for a change.

I have posted time and time again, if you don't know what your pointing your IR camera at, point it elsewhere. There are those of you out there that have a $5k imager, spent $$ on training (of sorts) and you haven't yet pointed it at your cell phone charger and realized that transformers make a lot of heat?
In this case, just what building material has a flash point below 112 degrees F?
They say there are no stupid questions, some say stupid people ask questions, I say some questions are asked by lazy people.

In my opinion, if I were to pay someone $300 to check my house I think they should know what moisture looks like, what air infiltration looks like, what a hot electrical service is and is not. These things have specific signatures. Basic Level I.

GFIC's, transformers, smoke detectors, motors, heating and a/c equipment generate heat due to the work they do. There ARE standards. Get them, learn them, then go do your job. If you don't, you make all of those above us in this field look like fools and bring discredit upon the industry. Which is not an asset to anyone.

There are standards, and few of you are getting it.
Your not even paying attention to John M's HI course. If you don't invest in the training it means very little. Free advise here obviously means very little to many who blindly oppose. John told me that many take his two day course and never turn in the field assignment. Evidence to my point.

Contact jim@infraspection.com and others that have years on us and get with the program.

Ya'll tired of my posts, well that can be remedied. I'm tired of your posts and we can call it even.

Mark, I apologize to you. This is not about you or your question. This is about complacency of those that should know better. You should have been taught the answer to your question. That is by beef.

I also apologize to the others; my trying to interpret the facts, trying to make a wild-*****-guess on minimal information, for getting frustrated when other know-it-alls (by interpretation) call overheated breakers, hundreds of times over the accepted standard as being "NORMAL".

Yup, I'm not one to kiss your ***** and make you feel good. I just want you to do the right thing by your customer and maybe keep your sorry butt out of court.

I'll take my book of "know-it-all" and be gone.
Bye.
Nice post David , I do not have an IR Cam but I bite my tongue at "some" of the questions asked from lack of proper training.

In my opinion, if someone does not know exactly what they are doing with any aspect of the inspection business, they should be learning what they are weak in before accepting money for such an inspection.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
Transformer humming noise mnicholet Electrical Inspections 13 11/25/08 4:05 PM
What's this video worth? jtedesco1 Inspection Education & Training 5 4/18/08 9:24 AM
Temp differential dlee2 Inspecting HVAC Systems 4 8/22/06 11:01 AM


All times are GMT -4. The time now is 6:31 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts