Default Water intrusion case study.

Client, today, asked to find the source of water intrusion into a 3 unit condo (duplex up, duplex down with middle unit on one floor.

Split faced block, but the roof was sloped and there is usually little problems with split faced block with sloped roofs. But the front had a peaked front wall (brick veneer over block).

I could tell, just from the efflorescence and drip pattern.

1) Front view of the building. Please note that the 3rd level (above grade) had a small (4' wide) balcony above the 2nd level.
2) Peaked front face with a small flat parapet near the chimney chase. Note the efflorescence / drip pattern.
3) Interior regular picture at the interface of the sloped parapet coping to the flat coping.
4) IR image of #3.

Hope this helps;
Attached Thumbnails
water-intrusion-case-study-pa230300.jpg   water-intrusion-case-study-pa230305.jpg   water-intrusion-case-study-dc_0712.jpg   water-intrusion-case-study-ir_0711.jpg  



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
Need a home inspection in Indiana? Check out InterNACHI's listing of Indiana certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 10/23/11, 11:11 PM
William J. Decker's Avatar
William J. Decker William J. Decker is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 7,785
Default Re: Water intrusion case study.

Secondarily. The front ceiling at the 2nd level displayed signs of water intrusion. Since the balcony for the 3rd level was above it, naturally the owners thought that the balcony roofing was the problem.

But it was not.

The space between the 2nd floor ceiling and the balcony had "Building Envelope Confusion" and condensation problems where it interfaced with the floor / ceiling space above the 2nd floor.

Check out the pictures.
Attached Thumbnails
water-intrusion-case-study-dc_0704.jpg   water-intrusion-case-study-ir_0703.jpg   water-intrusion-case-study-dc_0706.jpg   water-intrusion-case-study-ir_0705.jpg  



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
  #3  
Old 10/25/11, 2:04 PM
John McKenna's Avatar
John McKenna John McKenna is offline
InterNACHI Member
 
Join Date: Jun 2006
Location: Crockett, Tx
Posts: 12,303
Default Re: Water intrusion case study.

Nice catch Will



John McKenna, CMI (TREC #4565)
Executive Director - Master Inspector Certification Board
25 Yrs Constr Exp - 13 Yrs Home Inspector Exp
American Home Inspection - East Texas.

Reply With Quote
  #4  
Old 10/25/11, 4:41 PM
Linas Dapkus's Avatar
Linas Dapkus Linas Dapkus is offline
InterNACHI Member
 
Join Date: Feb 2011
Location: Home
Posts: 2,187
Default Re: Water intrusion case study.

Typical Chicago Polish contractor construction. Keeps us busy during the rainy periods.
Reply With Quote
  #5  
Old 10/25/11, 4:46 PM
William J. Decker's Avatar
William J. Decker William J. Decker is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 7,785
Default Re: Water intrusion case study.

Actually an Irish masonry contractor. Many masons are hesitent to do through wall flashing on a sloped parapet, believing that the stone will fall off. Evidently, they don't teach pinning in Irish masonry schools.
It also seems like they don't teach building science in Architecture school either.

Hope this helps;



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
  #6  
Old 10/25/11, 11:25 PM
Joseph Hagarty,  CMI's Avatar
Joseph Hagarty, CMI Joseph Hagarty,  CMI is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Parkesburg, PA
Posts: 5,636
Default Re: Water intrusion case study.

Quote:
Originally Posted by wdecker View Post

Actually an Irish masonry contractor.

Irish masonry schools.

It also seems like they don't teach building science in Architecture school either.
Irish Masonry School
Which one are you suggesting?



Joseph P. Hagarty
joseph.hagarty@comcast.net
Main Line Inspections, Inc.
Phone: 610-399-3675
Email: MainLineHI@comcast.net

http://pa.nachi.org/mainlinepa/about.html
http://www.householdinspector.com

National President / NACHI (2003-2004)
NACHI Education Committee Member
Reply With Quote
  #7  
Old 10/26/11, 7:03 AM
Linas Dapkus's Avatar
Linas Dapkus Linas Dapkus is offline
InterNACHI Member
 
Join Date: Feb 2011
Location: Home
Posts: 2,187
Default Re: Water intrusion case study.

Quote:
Originally Posted by jhagarty View Post
Irish Masonry School
Which one are you suggesting?
The nearest liquor store.
Reply With Quote
  #8  
Old 10/26/11, 7:24 AM
William J. Decker's Avatar
William J. Decker William J. Decker is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 7,785
Default Re: Water intrusion case study.

Now Linus, play nice.



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
  #9  
Old 10/26/11, 8:05 AM
Linas Dapkus's Avatar
Linas Dapkus Linas Dapkus is offline
InterNACHI Member
 
Join Date: Feb 2011
Location: Home
Posts: 2,187
Default Re: Water intrusion case study.

Quote:
Originally Posted by wdecker View Post
Now Linus, play nice.
Oops sorry Will, I meant to say "Pub".
Reply With Quote
  #10  
Old 10/26/11, 10:16 AM
William J. Decker's Avatar
William J. Decker William J. Decker is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 7,785
Default Re: Water intrusion case study.

Quote:
Originally Posted by ldapkus1 View Post
Oops sorry Will, I meant to say "Pub".
That's better.



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
  #11  
Old 10/26/11, 10:31 AM
William J. Decker's Avatar
William J. Decker William J. Decker is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 7,785
Default Re: Water intrusion case study.

To clarify my earlier post, with regards to "Irish Masonry School", this is what I meant.

In this area, there appears to be 4 different "schools" of masonry thought, i.e., I see things done in one of four different ways. I even see some masonry buildings that have two or more of these schools displayed (changed masonry contractors during the build).

Please note that the people who work according to these techniques are not, necessarily, members of these ethnic groups. Probably the result of who trained them and/or where they were trained (if they were actually, formally trained).

1) Italian - Good quality work, great for repairs on the older masonry buildings. Use fairly large aggigate sand for the mortar, but the motrar is not over sanded. Square of concave pointing. Great flashing detail.
2) Irish - Also good with regards to the mortar mix, but smaller aggrigate sand. Tend more towards pre-mixed mortar. Mostly good flashing and lintel / brick spaces left open. OK for flashing, but will not flash under parapet wall coping for sloped coping.
3) Polish - Good speed. Do not butter the ends of the brick before placing but have a "helper" follow behind them and point the head joints (check by placing screwdriver in the head joint and pressing. The joint usually collapses). Tend to grout the lintel / brick space and cover or cut the lintel flashing. Usually do not use end dams on lintel flashing. Don't flash under coping stones. Add more sand to pre-mixed mortars.
4) Similar to the polich school, except they caulk the lintel / brick area instead of mortaring it. They usually pull out the weep wicks before they caulk. Do not flash under copings, but always install weep wicks instead.

At least that has been my experience in the Chicago area.

Hope this helps;



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
  #12  
Old 11/11/11, 11:33 PM
Peter W. Bennett Peter W. Bennett is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Little Silver, NJ
Posts: 546
Default Re: Water intrusion case study.

Will,
Could you get to the roof?
Would like to see a photo.
Reply With Quote
  #13  
Old 11/11/11, 11:40 PM
Joseph Hagarty,  CMI's Avatar
Joseph Hagarty, CMI Joseph Hagarty,  CMI is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Parkesburg, PA
Posts: 5,636
Default Re: Water intrusion case study.

the masonry facade is improperly installed
with lack of weeps and drainage

the problem is visibly evident...
the cam only confirms...

Without a Cam, would you report the exterior facade as deficient?
Hmmmm???



Joseph P. Hagarty
joseph.hagarty@comcast.net
Main Line Inspections, Inc.
Phone: 610-399-3675
Email: MainLineHI@comcast.net

http://pa.nachi.org/mainlinepa/about.html
http://www.householdinspector.com

National President / NACHI (2003-2004)
NACHI Education Committee Member

Last edited by jhagarty; 11/11/11 at 11:44 PM..
Reply With Quote
Need a home inspection in Indiana? Check out InterNACHI's listing of Indiana certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 11/12/11, 7:51 AM
Linas Dapkus's Avatar
Linas Dapkus Linas Dapkus is offline
InterNACHI Member
 
Join Date: Feb 2011
Location: Home
Posts: 2,187
Default Re: Water intrusion case study.

Quote:
Originally Posted by jhagarty View Post
the masonry facade is improperly installed
with lack of weeps and drainage

the problem is visibly evident...
the cam only confirms...

Without a Cam, would you report the exterior facade as deficient?
Hmmmm???
Visual inspection confirms it's evidently poor masonry construction, the cam confirms with colorful images, the moisture meter verifies it got inside. That's why some choose to do more with a thermal camera than just wave it around at a home inspection. Look at all the imagers for sale on this message board. Go figure!!! Hope this helps.
Reply With Quote
  #15  
Old 11/12/11, 12:24 PM
Joseph Hagarty,  CMI's Avatar
Joseph Hagarty, CMI Joseph Hagarty,  CMI is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Parkesburg, PA
Posts: 5,636
Default Re: Water intrusion case study.

I am amazed and appalled at the stereotypes professed within this thread as if they are somehow factual...



Joseph P. Hagarty
joseph.hagarty@comcast.net
Main Line Inspections, Inc.
Phone: 610-399-3675
Email: MainLineHI@comcast.net

http://pa.nachi.org/mainlinepa/about.html
http://www.householdinspector.com

National President / NACHI (2003-2004)
NACHI Education Committee Member

Last edited by jhagarty; 11/12/11 at 5:27 PM..
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Water Pressure Problem dcossar Plumbing Inspections 19 11/21/09 8:47 PM
980 Questions/Answers to the NHIE....Free! jbushart Legislation, Licensing & Legal Issues for Inspectors 50 4/20/08 1:26 AM
Common Defects List by Age of House trausch Inspection Education & Training 10 6/12/06 4:52 AM