Yesterday's townhome warranty inspection. 55 degrees and cloudy outside and 73 degrees inside, furnace running.

See the two IR pics of the ceiling to the attic. Note the clearly defined slightly colder areas. There were several of these in the main living area. Not going to report anything about these, but I am curious as to what is causing them.

Initially, due to the small temperature difference, I though maybe these areas would be under the attic decking for the HVAC access. That there might be missing or improperly installed batt type insulation under the decking. When I got into the attic, I found that there is no decking in these areas. The access was poor but I could see that there was blown certainteed type fiberglass insulation above this room. The insulation install was typical and adequate. Being blown in type insulation, there was variance in the level through out. No clearly define rectangle with less insulation were visible from the attic.

So what is causing the colder rectangles. Not something I normally see and I am curious.
Attached Thumbnails
whats-happening-here-ir003604.jpg   whats-happening-here-ir003605.jpg  




Kevin Weiss

Professional Inspector
Level I Infrared
www.AbsoluteInspections.net
www.homeinspectorsplanotx.com
www.homeinspectorsmckinney.com
Absolute Inspections, LLC
972-463-0887
Reply With Quote
Need a home inspection in Maryland? Check out InterNACHI's listing of Maryland certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 3/17/10, 2:32 PM
John E. Mullarkey John E. Mullarkey is offline
InterNACHI Member
 
Join Date: Oct 2009
Location: Sarasota, Fl
Posts: 349
Default Re: What's happening here?

My guess would be that the isulation was somehow compressed. Is this an older house that had the insulation upgraded? new insulation shot over existing typical batts that might have been compressed?

Just a thought
Reply With Quote
  #3  
Old 3/17/10, 2:36 PM
Wayne B. Wilson's Avatar
Wayne B. Wilson Wayne B. Wilson is online now
InterNACHI Member
 
Join Date: Aug 2008
Location: Powell, Tn
Posts: 8,236
Default Re: What's happening here?

With that little of difference , I wonder if it is compression , Or is it a different type of insulation . Any pictures from the attic?
Was the main duct in that area?



Wayne Wilson
East TN Home Inspections LLC
Knoxville, Oak Ridge, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.
865-256-1490

http://site.myhomeinspection.net

Reply With Quote
  #4  
Old 3/17/10, 3:55 PM
Jason Kaylor Jason Kaylor is offline
InterNACHI Member
 
Join Date: Feb 2009
Location: Tempe, AZ
Posts: 970
Send a message via Yahoo to jkaylor
Default Re: What's happening here?

yeah I agree, it is compressed or a different type of insulation. It could also have been compromised in some fashion, but because of the exact shape I doubt that is the case.

Jason Kaylor – JJ
AC Tool Supply
VP of Specialty Products
Level II SNT-TC-1A
Infraspection Institute #8031
877/207-1244
AC Tool Supply
Energy Auditor Talk

Last edited by jkaylor; 3/17/10 at 4:00 PM..
Reply With Quote
  #5  
Old 3/17/10, 4:17 PM
ldapkus ldapkus is offline
Active Poster
 
Join Date: Mar 2006
Posts: 5,717
Please Note: ldapkus is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What's happening here?

Convection Colder air moving behind the vapor barrier. See it quite a bit.
Attached Thumbnails
whats-happening-here-brown-ir-008-640x480-.jpg  

Last edited by ldapkus; 3/17/10 at 4:25 PM..
Reply With Quote
  #6  
Old 3/17/10, 4:33 PM
kweiss's Avatar
kweiss kweiss is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Rowlett, TX
Posts: 1,060
Default Re: What's happening here?

One year old construction. Blown in fiberglass insulation. Did not take any pictures of the attic because they would not show anything. Typical new installation for around here, variable surface levels between 10 - 12 inches as is typical for that type blown in.

Compression?

NO signs of compression or disturbance at all in the insulation. Certainly nothing in a recognizable shape as indicated in the IR pic. While the area was not easily accessible, I could see the area above the pictured anomaly reasonably well.

Vapor Barrier?

I do not typically see a vapor barrier under the blown in insulation around here. Notice these areas were not along an outside wall, they were in the middle areas of the room.

Possible something laying on the sheetrock in that channel between the ceiling joists? Could not get close enough to dig in it.




Kevin Weiss

Professional Inspector
Level I Infrared
www.AbsoluteInspections.net
www.homeinspectorsplanotx.com
www.homeinspectorsmckinney.com
Absolute Inspections, LLC
972-463-0887
Reply With Quote
  #7  
Old 3/17/10, 5:41 PM
Wayne B. Wilson's Avatar
Wayne B. Wilson Wayne B. Wilson is online now
InterNACHI Member
 
Join Date: Aug 2008
Location: Powell, Tn
Posts: 8,236
Default Re: What's happening here?

OK
here is a thought i wonder if something was left and insulated over. Like bags from the insulation.



Wayne Wilson
East TN Home Inspections LLC
Knoxville, Oak Ridge, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.
865-256-1490

http://site.myhomeinspection.net

Reply With Quote
  #8  
Old 3/17/10, 7:14 PM
Jeffrey Moore Jeffrey Moore is offline
InterNACHI Member
 
Join Date: Feb 2008
Location: Mesa, AZ
Posts: 282
Default Re: What's happening here?

What was the temp in attic? If the attic was warmer than outside air the ceiling Delta is not as great as a wall. This could account for the smaller temp diff between the areas.



Jeff Moore
www.quantumhomeinspections.com
Flir (ITC) Level II Thermographer
Mesa, AZ
Reply With Quote
  #9  
Old 3/17/10, 11:23 PM
measter measter is offline
Active Poster
 
Join Date: Oct 2009
Location: Independence, KS
Posts: 162
Please Note: measter is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What's happening here?

Quote:
Originally Posted by kweiss View Post
Possible something laying on the sheetrock in that channel between the ceiling joists? Could not get close enough to dig in it.
Yes. That what I would guess. Looks like an air gap due to it being pretty consistent across the rafter spaces.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Why is this happening in america "home of the free"? gluck Miscellaneous Discussion for Inspectors 14 3/18/10 11:21 AM
What's happening here? dvalley Thermal Imaging, Infrared Cameras & Energy Audits 56 3/5/08 8:09 PM
Find out about what's happening for new electrical rules in the NEC jtedesco1 Electrical Inspections 0 6/16/06 12:57 PM


All times are GMT -4. The time now is 9:34 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts