Default Window leak or lack of insulation?

Same parameters as last post:

Temp inside: 72-74, humidity inside: 39%, temp outside: low 50s








Reply With Quote
Need a home inspection in Louisiana? Check out InterNACHI's listing of Louisiana certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 11/23/11, 10:17 PM
Chad Norlen, CPI's Avatar
Chad Norlen, CPI Chad Norlen, CPI is offline
InterNACHI Member
 
Join Date: Nov 2011
Location: American Falls, ID
Posts: 233
Default Re: Window leak or lack of insulation?

I take an uneducated stab at it. Cold air falling from a window leak would also chill the base board. It appears the baseboard is insulating against some of the infiltration.



Chad Norlen
SEI Inspections
InterNACHI Member

Certified Professional Inspector
HVAC Journeyman - State of Idaho
EPA Certified Universal Technician
Reply With Quote
  #3  
Old 11/23/11, 11:21 PM
rswartz rswartz is offline
New User
 
Join Date: Dec 2009
Location: WV
Posts: 9
Please Note: rswartz is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Window leak or lack of insulation?

Looks to me like there is rim joist leakage at the baseboard. Several window jacks make up the vertical lines under the first window. A leaky receptacle is the culprit under the large window.
Reply With Quote
  #4  
Old 11/24/11, 3:20 AM
Carl A. Brown's Avatar
Carl A. Brown Carl A. Brown is offline
InterNACHI Member
 
Join Date: Jan 2006
Location: Kansas City, ks
Posts: 10,763
Default Re: Window leak or lack of insulation?

Most windows are improperly installed due to the lack of backer rod and sealant around the window on the exterior.



"I create controversy whether they like it or not"



Reply With Quote
  #5  
Old 11/24/11, 9:19 PM
Mark CDavis Mark CDavis is offline
New User
 
Join Date: Nov 2011
Posts: 14
Please Note: Mark CDavis is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Window leak or lack of insulation?

Plan is to remove the whitewood (ick) trim around all the window banks that have Southern exposure (1000' elevation too) and replace with Hardie with 3/8" gaps, backer rod, and Sonolastic 150. Reflash as well.

Still trying to figure out if this window is actually leaking or not...Will remove the wood trim soon. I keep doing that for other window banks and keep finding missing sections of drywall where there was a previous repair...scary.

Moisture meter readings -- both EM and invasive -- are quite good all over...EM shows 3-5 on the drywall, 6-8 on the wood trim, and sometimes 10 around the nail heads . No evidence from the meters of leakage.

Meters are Delmhorst and Wagner.

-mark
Reply With Quote
  #6  
Old 11/24/11, 10:37 PM
Carl A. Brown's Avatar
Carl A. Brown Carl A. Brown is offline
InterNACHI Member
 
Join Date: Jan 2006
Location: Kansas City, ks
Posts: 10,763
Default Re: Window leak or lack of insulation?

How do you flash under the sill and out over the cladding?



"I create controversy whether they like it or not"



Reply With Quote
  #7  
Old 11/25/11, 1:38 AM
Dan Bowers, CMI Dan Bowers, CMI is offline
InterNACHI Member
 
Join Date: Oct 2003
Location: Shawnee Mission, KS
Posts: 3,893
Default Re: Window leak or lack of insulation?

Kinda curious ... You see the cooler area at the studs in the wall and at the baseboard - rim - floor as always. Where exactly was the water leak.
Reply With Quote
  #8  
Old 11/25/11, 4:59 AM
Peter C. Russell's Avatar
Peter C. Russell Peter C. Russell is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Alton Bay NH
Posts: 3,998
Default Re: Window leak or lack of insulation?

Quote:
Originally Posted by Mark CDavis View Post
Plan is to remove the whitewood (ick) trim around all the window banks that have Southern exposure (1000' elevation too) and replace with Hardie with 3/8" gaps, backer rod, and Sonolastic 150. Reflash as well.

Still trying to figure out if this window is actually leaking or not...Will remove the wood trim soon. I keep doing that for other window banks and keep finding missing sections of drywall where there was a previous repair...scary.

Moisture meter readings -- both EM and invasive -- are quite good all over...EM shows 3-5 on the drywall, 6-8 on the wood trim, and sometimes 10 around the nail heads . No evidence from the meters of leakage.

Meters are Delmhorst and Wagner.

-mark
Mark, a few suggestions.

If the moisture meeter is reading only 3-5 and 6-8 are you sure you have a water intrusion problem?

Is 3/8 hardiplank trim a good solution? What is the profile of the siding. I cant tell from your picture but it looks like vinyl with cedar shakes on top. If so I would make sure that the window trim extends past the siding detail, in the case of vinyl and shakes I would use 5/4 stock and by the looks of the window wall I would go with a low maintenance material such as PVC. Flashing should be used not only on top of the window casing/header but on top of the window itself. Also, eliminate the caulking. Caulking is no substitute for flashing. If you caulk these windows they will only be destined to fail again. Finally, the trim detail needs to change on the center window. Both ends of the header casing look like a good entry point. I would increase the elevation of the trim so it's a solid piece all the way across the lower windows. The detail that I see in your picture is very difficult to flash and the corners where the lower trim meets the header is a good place for water to enter.

Before I did all the above, and the fact of the low moisture readings would guide me in this direction first, I would remove the interior drywall under the window and check for air infiltration. A simple solution, if this area is dry inside the wall cavity, is to buy a large container of two part spray foam and not only air seal the cavities but insulate them as well. Once this is completed re-scan the windows to see if you were successful.

My comments are based on very limited info. that you have provide but I have worked on many window walls myself. If you want to talk feel free to give me a call, I would be more than happy to talk.



Russell Inspection Services
New Hampshire state license # 57
Level I Thermographer, ITC
Certified Building Science Thermographer, ITC
Certified Building Analyst, BPI
Certified Commercial Inspector, ITA
Certified Septic Evaluator, GSDI #148

www.newenglandthermalimaging.com
www.russellinspectionservices.com
www.nhsepticinspection.com
Reply With Quote
  #9  
Old 11/25/11, 8:40 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,848
Default Re: Window leak or lack of insulation?

Good info, Peter...



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #10  
Old 11/25/11, 8:50 PM
Carl A. Brown's Avatar
Carl A. Brown Carl A. Brown is offline
InterNACHI Member
 
Join Date: Jan 2006
Location: Kansas City, ks
Posts: 10,763
Default Re: Window leak or lack of insulation?

Windows with trim around them need three pieces of flashing. imo

The head of the window out and bent over the edge of the vertical trim on the window.
The same at the trim above the head of the window.
Under the sill behind the trim under the window and out over the cladding!
Caulk and backer rod on the sides and between the window and the trim under the sill.

Kinda like these.

http://www.badstucco.com/properflash/properflash.html

Any water that is in can get out over the cladding.



"I create controversy whether they like it or not"



Reply With Quote
  #11  
Old 11/25/11, 8:51 PM
Carl A. Brown's Avatar
Carl A. Brown Carl A. Brown is offline
InterNACHI Member
 
Join Date: Jan 2006
Location: Kansas City, ks
Posts: 10,763
Default Re: Window leak or lack of insulation?

A lot of the ones around here have no flashing and no moisture barrier under the trim.

http://www.badstucco.com/repair2.html



"I create controversy whether they like it or not"



Reply With Quote
  #12  
Old 11/25/11, 9:08 PM
Carl A. Brown's Avatar
Carl A. Brown Carl A. Brown is offline
InterNACHI Member
 
Join Date: Jan 2006
Location: Kansas City, ks
Posts: 10,763
Default Re: Window leak or lack of insulation?

The flashing that is under the sill and out over the cladding needs end damns on it.



"I create controversy whether they like it or not"



Reply With Quote
  #13  
Old 11/25/11, 9:33 PM
Carl A. Brown's Avatar
Carl A. Brown Carl A. Brown is offline
InterNACHI Member
 
Join Date: Jan 2006
Location: Kansas City, ks
Posts: 10,763
Default Re: Window leak or lack of insulation?

Never 45 the trim around openings, might end up looking like this.
Attached Thumbnails
window-leak-lack-insulation-bad-window-trim-2.jpg   window-leak-lack-insulation-bad-window-trim-1.jpg  



"I create controversy whether they like it or not"



Reply With Quote
Need a home inspection in Louisiana? Check out InterNACHI's listing of Louisiana certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 11/26/11, 1:06 AM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,927
Default Re: Window leak or lack of insulation?

Can someone tell (or show) me how to tell the difference between an air and moisture anomaly with Thermal Imaging without using a moisture meter?

It seems that we have as much trouble with the moisture meters as the thermal cameras.



"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein

David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #15  
Old 11/26/11, 8:17 AM
Wayne B. Wilson's Avatar
Wayne B. Wilson Wayne B. Wilson is online now
InterNACHI Member
 
Join Date: Aug 2008
Location: Powell, Tn
Posts: 8,236
Default Re: Window leak or lack of insulation?

I would think this a air filtration nothing more. I see a outlet, Most likely Insulation has been displaced by the sparky. Wire feed from underside?



Wayne Wilson
East TN Home Inspections LLC
Knoxville, Oak Ridge, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.
865-256-1490

http://site.myhomeinspection.net

Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Building Science- research from respected sources Brian A. MacNeish Ancillary Inspection Services & Additional Topics 17 7/12/11 6:31 AM
Need help flashing top of replacement window on brick wall !!! Bill Featherstone Exterior Inspections 5 6/26/10 10:25 PM
Renovating Your Basement for Livability mkyriacou Canadian Inspectors 0 10/22/09 11:45 AM
WH blanket badair Plumbing Inspections 5 7/2/06 7:10 AM


All times are GMT -4. The time now is 9:34 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts