Default How are you advising home owners on room temps

How are you advising home owners on room temps... See the images attached. I find this in homes with Concrete slab floors with Central heat from the ceilings. The lower half of the room indicated temps in the 60F. and the upper half is 70F. plus.

Ceiling fans, Better Ceiling Diffusers, Or ?

Thanks for your views...

Best

Ron
Attached Thumbnails
you-advising-home-owners-room-temps-ir_0086.jpg   you-advising-home-owners-room-temps-ir_0087.jpg  
Reply With Quote
Find an InterNACHI certified Rhode Island Home Inspector (and anywhere else in North America)
  #2  
Old 4/30/09, 12:24 AM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Cassville, MO
Posts: 13,636
Default Re: How are you advising home owners on room temps

IRC (R303.8 ) says, basically that the dwelling unit shall be provided with heating facilities capable of maintaining a minimum room temp of 68 degrees (F) at a point three feet above the floor and two feet from exterior walls in all habitable rooms. The installation of one or more portable space heaters shall not be used to achieve compliance with this section. When these temps cannot be maintained, the room is not considered habitable.

I don't think that this can be determined with an infrared camera.
Reply With Quote
  #3  
Old 4/30/09, 12:45 AM
Rick Maday's Avatar
Rick Maday Rick Maday is offline
InterNACHI Member
 
Join Date: Jan 2008
Location: Itasca, IL
Posts: 4,591
Default Re: How are you advising home owners on room temps

Wild ***** Guess (question) here - were there bushes around the exterior where the lower temps were?



Owl Home Inspections
Rick Maday
Itasca, IL


Home Inspector Serving all Chicago Suburbs

Schaumburg Home Inspector
Naperville Home Inspector
Lake County Home Inspector
Reply With Quote
  #4  
Old 4/30/09, 1:10 AM
Ron Bibler Ron Bibler is offline
InterNACHI Member
 
Join Date: Nov 2008
Location: Healdsburg Ca
Posts: 385
Default Re: How are you advising home owners on room temps

Quote:
Originally Posted by rmaday View Post
Wild ***** Guess (question) here - were there bushes around the exterior where the lower temps were?
No... Open exterior wall at about 11:00 AM.

Best

Ron
Reply With Quote
  #5  
Old 4/30/09, 1:12 AM
Ron Bibler Ron Bibler is offline
InterNACHI Member
 
Join Date: Nov 2008
Location: Healdsburg Ca
Posts: 385
Default Re: How are you advising home owners on room temps

Nice to see you can find the code... But you miss the point!

Best

Ron
Reply With Quote
  #6  
Old 4/30/09, 1:32 AM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Cassville, MO
Posts: 13,636
Default Re: How are you advising home owners on room temps

Is not the top half of a room....regardless of where the vents are placed....always warmer? Seems like "Mr. Wizard" taught us something in the '50s about how warm air rises....

Knowing that...and knowing that relevant temps are inside the wall space (and not the temp of the walls themselves) what is the point of the IR photos and question. You're right....I missed it.
Reply With Quote
  #7  
Old 4/30/09, 2:12 AM
John McKenna's Avatar
John McKenna John McKenna is offline
InterNACHI Member
 
Join Date: Jun 2006
Location: Crockett, Tx
Posts: 7,398
Default Re: How are you advising home owners on room temps

Quote:
Originally Posted by rbibler View Post
How are you advising home owners on room temps... See the images attached. I find this in homes with Concrete slab floors with Central heat from the ceilings. The lower half of the room indicated temps in the 60F. and the upper half is 70F. plus.

Ceiling fans, Better Ceiling Diffusers, Or ?

Thanks for your views...

Best

Ron
I would advise the Client that the floors may cause them
to feel cold (common to naked slabs), even though
the heater is running. If they understand why the feel
uncomfortable, then they are less likely to call you back
to complain.

In houses with high ceilings and lots of naked slab or cold
tile, I will advise my clients of this "possibility" in order to
head off any complaints before they arise.

I also advise them that we cannot verify if every room in
the house will "feel comfortable" to them during all the
seasons of the year (this is beyond the scope of our
inspection).

Even if this house meets the "code" it may still cause
some people to feel uncomfortable at times... IMHO

This type of problem is a common issue that is also
overlooked during an energy audit. A cold slab is hard
for some people to get used to, especially as they get
older. They may not be aware of it until after they
get moved in.

When you recommend covering the floors with carpet
and padding, they whine. What can you do?

I think they will start installing more embedded heating
systems in slabs in the future.... IMHO.

Last edited by jmckenna1; 4/30/09 at 2:22 AM..
Reply With Quote
  #8  
Old 4/30/09, 12:24 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 3,697
Default Re: How are you advising home owners on room temps

This is significant air stratification and is likely the result of improper duct design, not just because there is a slab.

If you do not remove the unconditioned air from the floor it cannot be treated at the equipment. Hot and cold fluids do not mix well, so blowing warm air into a cold room is not effective.

Air conditioning/heating systems are" suckers" not "blowers" as everyone precives.
The supply and return registers are probably both in the ceiling. (?)

This causes the conditioned air to short cycle back into the return register without affecting the air at the floor. This condition can get so bad that the furnace may shut off on high temperature sensors.

This is also an efficiency loss as the extremely high temperature difference at the ceiling and upper walls cause faster heat transfer to the outdoors.

This design will work fine in the air-conditioning mode because the cold air falls to the floor from the supply registers and the hot air is being removed from the ceiling where it rises to.

It should also be noted that you cannot design an air duct system to function efficiently in both the heating and cooling modes.

Adding a second return air register at the floor level and switching which register is being utilized between heating and cooling will correct the situation. If you have to pick one location over the other, supply at the ceiling and return at the floor is your best option.

Have fun with this one! You'll have nothing but arguments from the HVAC and general contractor.

Wrong is wrong, no matter how often you do it, it still remains wrong.



David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Certified Level II Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620

Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #9  
Old 4/30/09, 12:54 PM
Ron Bibler Ron Bibler is offline
InterNACHI Member
 
Join Date: Nov 2008
Location: Healdsburg Ca
Posts: 385
Default Re: How are you advising home owners on room temps

Thanks David thats some very good info...

Best

Ron
Reply With Quote
  #10  
Old 4/30/09, 7:36 PM
Kevin R. Weiss Kevin R. Weiss is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Rowlett, TX
Posts: 842
Default Re: How are you advising home owners on room temps

Ron,

Just a question/observation - not meant as criticism. Had you run the heat significantly in a cold house immediately before taking the images?

I have found, personally that if I go into a home and run the heat for an extended period, particularly if the temperature when I arrived was low, and raise the indoor temperature too much to quickly - that I tend to see this pattern. I always attributed it to the normal heat rising and ceiling supplies and returns. As I do not see it when I only raise the temps by a degree or so or if the natural delta to outside is already very good.

Poor system design is almost a given around here and we have mostly slabs. And as David said, the systems are designed more with cooling in mind.



Kevin Weiss

Professional Inspector
Infrared Imaging Specialist
www.AbsoluteInspections.net
Absolute Inspections, LLC
972-463-0887
Reply With Quote
  #11  
Old 4/30/09, 7:58 PM
Jason Kaylor Jason Kaylor is offline
InterNACHI Member
 
Join Date: Feb 2009
Posts: 290
Default Re: How are you advising home owners on room temps

I kind of had the same thoughts that Kevin has. I noticed two hot spots in the images that look like the registers. Both are very near the walls.

Jason Kaylor – JJ
VP of Specialty Products
877/207-1244
AC Tool Supply
Fluke Thermal Imagers
Testo Infrared Cameras
HotShot Hi-Rez Infrared Cameras

Fluke TiR1 Resources
FLIR B60 Resources
Retrotec Duct & Blower Door
Makita Power Tools
Reply With Quote
  #12  
Old 4/30/09, 11:29 PM
John McKenna's Avatar
John McKenna John McKenna is offline
InterNACHI Member
 
Join Date: Jun 2006
Location: Crockett, Tx
Posts: 7,398
Default Re: How are you advising home owners on room temps

Quote:
Originally Posted by dandersen View Post
It should also be noted that you cannot design an air duct system to function efficiently in both the heating and cooling modes.
Sometimes this is true. You backed up what I said...
Thanks.
Reply With Quote
  #13  
Old 5/1/09, 12:28 AM
Dan Bowers, CMI Dan Bowers, CMI is offline
InterNACHI Member
 
Join Date: Oct 2003
Location: Shawnee Mission, KS
Posts: 1,756
Default Re: How are you advising home owners on room temps

Ron -

Is the duct system typical apt style (eonomy) with supply and returns both high up
Reply With Quote
Find an InterNACHI certified Rhode Island Home Inspector (and anywhere else in North America)
  #14  
Old 5/1/09, 2:03 AM
Ron Bibler Ron Bibler is offline
InterNACHI Member
 
Join Date: Nov 2008
Location: Healdsburg Ca
Posts: 385
Default Re: How are you advising home owners on room temps

Quote:
Originally Posted by dbowers View Post
Ron -

Is the duct system typical apt style (eonomy) with supply and returns both high up

Yes. this was an cheap low price home. with the returns up in the ceiling of the hallway. about 25 Feet away from the walls in view.



Please see the walls of this home. This was a high end home 5,000 SQ. The room in view is a slab floor with a 12' ceiling with a bedroom above.
open exterior walls at about 10:00 AM East & north view. the heat was on for some time on this home. I think inspection was about 5 months back. but it had the same condition. low temps to the flooring with heat gathering at the ceiling. The returns were up high along with the registers.

My camera is a FLIR B2 160X120

Thanks for your views...

Best

Ron
Attached Thumbnails
you-advising-home-owners-room-temps-ir_0352.jpg   you-advising-home-owners-room-temps-ir_0343.jpg  
Reply With Quote
  #15  
Old 5/1/09, 2:09 AM
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 11,730
Default Re: How are you advising home owners on room temps

A couple of $30 ceiling fans would fix the whole thing



"Never ever threaten anyone in Camoflage"
Tim Wilson

"Not everyone follows the same path"
Governor Sanford, musings on the Appalachian Trail
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Hiring a Home Inspector mkyriacou Canadian Inspectors 7 4/24/09 5:26 PM
Orange County Home Inspections whandley California Inspectors 1 1/25/09 10:34 PM
Coeur d'Alene, ID Home Inspectors rspriggs Misc. Discussion 12 1/8/09 6:16 PM
Buckeye Home Inspections Service Area sboyd2 Misc. Discussion 3 9/4/06 8:21 PM
PIC of State Rep and sponsor of new NACHI H.I. Bill in NH. gromicko Misc. Discussion 53 8/30/06 6:58 PM


All times are GMT -4. The time now is 12:30 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts