InterNACHI


Go Back   InterNACHI Message Board > Specific Inspection Topics > Green Building Inspections

Notices

Green Building Inspections Contains discussions about green buildings and specific concerns when inspecting them.

Reply
 
LinkBack Thread Tools
  #31  
Old 11/7/08, 10:32 PM
Brian A. MacNeish Brian A. MacNeish is offline
Active Poster
 
Join Date: Apr 2007
Posts: 2,382
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Blower Door

Quote:
Originally Posted by rmisener View Post
Joe,

Do you have any links or articles on this? I'd be interested to read on it. I haven't heard this come up yet.
IMHO, some scare tactics being "thought" up by someone not understanding the process!! I should be sued by now if I was making people sick with blower door testing since I began doing it in 1981. Never had a complaint about dust and mould entering the house from the walls.

The highest pressure differential created across a wall in a blower door test is 60 pascals. 60 pascals is velocity pressure of a 22.3 mile per hour wind!!!

Our houses experience winds that are much higher than 22.4 mph many times a year. So if people are afraid of the pressures created in a blower door test---60 pascals........ they should really be afraid of the pressures created when the wind blows 50 miles an hour---261 pascals. That should should be enough air velocity to really clean the walls out until the same time next year!!!
Reply With Quote
  #32  
Old 11/8/08, 9:45 AM
Joe Farsetta's Avatar
Joe Farsetta Joe Farsetta is offline
ESOP Committee Member
 
Join Date: Oct 2002
Location: Pearl River, NY
Posts: 3,207
Default Re: Blower Door

Brian,

I have heard from a number of reliable sources that blower door tests have either been eliminated from the list of approved procedures or soon will be. The announcement will come from the EPA, with support from the CDC.

As I understand it, the blower door significantly de-pressurizes the dwelling, and allows any number of conditions to occurr regarding Indoor Air Quality.

It has been documented that such tests actually suck in contaminents from a variety of sources, including wall cavities. Depending on what exists in these cavities (including dust, mold spores, dander, mice hair, feces, etc), these contaminents quickly permeate throughout the dwelling, landing on furniture, people, pets, food, etc.

And this is why the EPA now believes that the upside to using this technology is outweighed by the negative effects it results in.

It's not a scare tactic on my part by any stretch of the imagination. De-pressurization is a genuine issue. For instance,studies have confirmed that high efficiency furnaces and boilers, absent of having sources of exterior combustion air, can depressurize a structure enough to cause the premature failure of thermopane window and door seals. If this moderate source of suction can cause these sort of problems, just imagine what a huge source of depressurization can cause.
Reply With Quote
  #33  
Old 11/8/08, 10:45 AM
Rodney Misener's Avatar
Rodney Misener Rodney Misener is offline
InterNACHI Member
 
Join Date: Jul 2008
Location: Pictou County, Nova Scotia
Posts: 336
Default Re: Blower Door

Joe,

Can you provide any documentation to support?



Rodney Misener
Trinity Inspection Services Ltd.
Pictou County, Nova Scotia
http://www.trinitymaintenance.com

Certified Home Inspector
Certified Level 1 Thermographer
Certified Energy Advisor
WETT Certified Inspector
IAC2 Radon/Mold Certified
Infrared Certified
Reply With Quote
  #34  
Old 11/8/08, 2:12 PM
Brian A. MacNeish Brian A. MacNeish is offline
Active Poster
 
Join Date: Apr 2007
Posts: 2,382
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Blower Door

[quote=jfarsetta;436074]Brian,

I have heard from a number of reliable sources that blower door tests have either been eliminated from the list of approved procedures or soon will be. The announcement will come from the EPA, with support from the CDC.

As I understand it, the blower door significantly de-pressurizes the dwelling, (re-read my previous post....regular winds create much stronger presssure differentials across walls....do we do away the winds also?) and allows any number of conditions to occurr regarding Indoor Air Quality.

It has been documented that such tests actually suck in contaminents from a variety of sources, including wall cavities. Depending on what exists in these cavities (including dust, mold spores, dander, mice hair, feces, etc), these contaminents quickly permeate throughout the dwelling, landing on furniture, people, pets, food, etc.

And this is why the EPA now believes that the upside to using this technology is outweighed by the negative effects it results in.

It's not a scare tactic on my part by any stretch of the imagination. De-pressurization is a genuine issue. For instance,studies have confirmed that high efficiency furnaces and boilers, absent of having sources of exterior combustion air, can depressurize a structure enough to cause the premature failure of thermopane window and door seals. If this moderate source of suction can cause these sort of problems, just imagine what a huge source of depressurization can cause.[/quote]

Joe:
I'm sorry to say that you're just hearing stories from the street with no actual factual basis. Stuff from the street has a way of being not that good a source of info......check your sources. Remember in the mid 80's with AIDS being only a gay male disease until some guy got it from his girlfriend!! I have seen some very well respected contractors not have a clue about this stuff but spout "facts" like they knew it inside out.

I have worked with airtight housing since 1977 and have not heard anything like this. I believe you're as least a bit familiar wth Canada's R2000 system with which I worked for 9+ years. During that period, two of my clients were named Canada's R2000 "Builder of the Year". I was a site advisor/inspector/certifying air leakage tester/"troubleshooter" for the local New Brunswick as well as doing follow-up research after the homes were lived in to ensure unforseen problems were not occurring.

Joe Lstiburek was involved in the forerunner program to and the early R2000 program and helped set the standards for the system. He's been a main partner of the "Building America" program and sat of the board of directors of the Energy-Efficient Buildings Association and was co-chair of the American Lung Association's "Health House" technical committee. To date, I have not heard anything from his organization to this effect......and they have been leaders in this field for years!!!

Check your sources!!!

BPI has had a recommendation of no blower testing for houses known to contain ACM's such asbestos containing loose fill vermiculite insulation.

Last edited by Brian A. MacNeish; 11/8/08 at 2:31 PM..
Reply With Quote
  #35  
Old 11/11/08, 1:18 AM
Nick Gromicko's Avatar
Nick Gromicko Nick Gromicko is offline
InterNACHI Member
 
Join Date: Aug 2002
Location: Valley Forge, PA
Posts: 19,594
Default Re: Blower Door

The biggest causes of depressurization in a home are (in order):

1. Stack effect (especially in the winter).
2. Venturi effect (wind passing across open windows and other openings).


Not flues or appliances.



Nick Gromicko, CMI
Founder
World's biggest, best inspection association
"Planet InterNACHI... resistance is futile"
Reply With Quote
  #36  
Old 11/11/08, 6:31 PM
James E. Braun, CMI James E. Braun, CMI is online now
InterNACHI Member
 
Join Date: Jan 2005
Location: Jefferson City, MO
Posts: 2,786
Default Re: Blower Door

Why not just presuurize the home instead? Blower doors can run both ways.
Reply With Quote
  #37  
Old 11/11/08, 11:29 PM
Yuri Olhovsky's Avatar
Yuri Olhovsky Yuri Olhovsky is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Richmond Hill, ON
Posts: 335
Default Re: Blower Door

Jim, how are you going to find air leaks by pressurizing the house?



Yuri Olhovsky CMI, CEA, PHPI
National Certificate Holder NCA00372
Richmond Hill, ON Canada
NACHI ID 04070207
Reply With Quote
  #38  
Old 11/12/08, 11:11 AM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 3,700
Default Re: Blower Door

With the blower door, that is what it does. Measures air flow.



David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Certified Level II Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620

Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #39  
Old 11/12/08, 11:16 AM
Yuri Olhovsky's Avatar
Yuri Olhovsky Yuri Olhovsky is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Richmond Hill, ON
Posts: 335
Default Re: Blower Door

Yes, the blower door measures pressure differential or air flow. I'm asking about finding particular places that loose heat by air leakage. You can only find them when the house is de-pressurized, not pressurized.



Yuri Olhovsky CMI, CEA, PHPI
National Certificate Holder NCA00372
Richmond Hill, ON Canada
NACHI ID 04070207
Reply With Quote
  #40  
Old 11/12/08, 3:15 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 3,700
Default Re: Blower Door

Why can't chemical smoke pass out of the building envelope when pressurized?

Instead of blowing away from an opening, it will get sucked in.

I am in favor of sucking over blowing, but it can be done.
It may have to be done at a higher pressure (60 vs 20 pascal), but it can be done.



David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Certified Level II Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620

Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #41  
Old 11/12/08, 4:55 PM
James E. Braun, CMI James E. Braun, CMI is online now
InterNACHI Member
 
Join Date: Jan 2005
Location: Jefferson City, MO
Posts: 2,786
Default Re: Blower Door

I have seen it done with a smoke pen. It is pretty freaky to see smoke draw out of house.
Reply With Quote
  #42  
Old 11/12/08, 6:03 PM
Yuri Olhovsky's Avatar
Yuri Olhovsky Yuri Olhovsky is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Richmond Hill, ON
Posts: 335
Default Re: Blower Door

Well, gentlemen, the smoke pencil is a chemical, and I don't use chemicals. The back of my hand works equally well but only during the de-pressurization test.



Yuri Olhovsky CMI, CEA, PHPI
National Certificate Holder NCA00372
Richmond Hill, ON Canada
NACHI ID 04070207
Reply With Quote
  #43  
Old 11/12/08, 6:49 PM
Justo Mickey Rivera's Avatar
Justo Mickey Rivera Justo Mickey Rivera is offline
InterNACHI Member
 
Join Date: Jun 2004
Location: Shirley, NY
Posts: 1,311
Default Re: Blower Door

Quote:
Originally Posted by yolhovsky View Post
the smoke pencil is a chemical, and I don't use chemicals.
How much smoke do you use? Not trying to be funny. But in the big scheme of things........it can't be any worse than when I pass gas. If I had to compare the two, I think people would rather have the smoke than my gas.

You could use one of those theatrical foggers also.

Or as a last resort I could stand on one side of the wall and pass my gas and you on the other to sniff it out. LOL . Sorry I couldn't resist that one.

Mic



Physical strength can never permanently withstand the impact of spiritual force.
FRANKLIN D. ROOSEVELT 32nd U.S. President

Last edited by jrivera; 11/12/08 at 10:11 PM..
Reply With Quote
  #44  
Old 11/12/08, 8:26 PM
Rodney Misener's Avatar
Rodney Misener Rodney Misener is offline
InterNACHI Member
 
Join Date: Jul 2008
Location: Pictou County, Nova Scotia
Posts: 336
Default Re: Blower Door

There is about as much smoke from a smoke pencil as there from a cigarette. Pressurization works fine, depressurization is a bit easier thats all. Its not like the h/o is in contact with the smoke, the air pushes/pulls it outside the home in a matter of seconds.



Rodney Misener
Trinity Inspection Services Ltd.
Pictou County, Nova Scotia
http://www.trinitymaintenance.com

Certified Home Inspector
Certified Level 1 Thermographer
Certified Energy Advisor
WETT Certified Inspector
IAC2 Radon/Mold Certified
Infrared Certified
Reply With Quote
  #45  
Old 11/15/08, 9:04 AM
Kevin A. Richardson Kevin A. Richardson is offline
InterNACHI Member
 
Join Date: Sep 2004
Posts: 1,145
Default Re: Blower Door

Quote:
Originally Posted by yolhovsky View Post
Yes, the blower door measures pressure differential or air flow. I'm asking about finding particular places that loose heat by air leakage. You can only find them when the house is de-pressurized, not pressurized.
Not accurate!!

You can use a blower door to "pressurize" the building and then use an Infrared Camera to detect air exfiltration on the exterior envelope. This survey is usually conducted a night or two hours post sunset.

Remember that due to the principles of "stack effect", air infiltrates in the lower plane of a building, while air exfiltrates in the upper plane of a building.

However, I've never really found the need to use a blower door, and I've conducted hundreds of energy audits using ITI. When I first started doing them with infrared, I would conduct them during normal business hours (daytime), but I have since changed that and conduct all of my energy audits at night. That way I can detect both air infiltration/exfiltration by conducting interior/exterior scans. Plus, in my area (wash DC) you get a way better temperature differential at night.

Kevin
Attached Thumbnails
blower-door-1313.jpg   blower-door-1314.jpg  



Kevin A. Richardson, BA
Level III Certified Infrared Thermographer, #7493
BPI Certified Building Performance Analyst
Maryland Licensed Home Inspector, #29727
INACHI Certified Home Inspector, #04091175

301-942-4610
www.richnspect.com
(Residential Inspections)
www.infrared-diagnostics.com
(Commercial Infrared Services)
www.thehomegreenteam.com
(Home Energy Performance Audits)
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Newbie here with a slab "standards" question Robert Young, #3 Structural 17 4/10/07 11:48 AM
Bad Door and Water on the Floor jnicholson Exterior 7 10/4/06 10:45 PM


All times are GMT -4. The time now is 9:07 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts