Default Re: Blower Door

Quote:
Originally Posted by krichardson View Post
Not accurate!!

You can use a blower door to "pressurize" the building and then use an Infrared Camera to detect air exfiltration on the exterior envelope. This survey is usually conducted a night or two hours post sunset.

Remember that due to the principles of "stack effect", air infiltrates in the lower plane of a building, while air exfiltrates in the upper plane of a building.

However, I've never really found the need to use a blower door, and I've conducted hundreds of energy audits using ITI. When I first started doing them with infrared, I would conduct them during normal business hours (daytime), but I have since changed that and conduct all of my energy audits at night. That way I can detect both air infiltration/exfiltration by conducting interior/exterior scans. Plus, in my area (wash DC) you get a way better temperature differential at night.

Kevin
The best place to reduce air leakage is at the interior wall surfaces of the outside walls, therefore, the best way of finding air leaks is with depressurization of the building on cold days. The quickest way to find the air leakage would be with IR while the building is depressurized.

When you see air leakage on the outside of a building, you may not find the exact location of the air leakage at the inside wall surface, that's where you want to seal it. It's similar to finding a roof leak sometimes...... where the water shows up on the ceiling may be many feet away from the actual roof leak!!
Reply With Quote
  #47  
Old 11/15/08, 11:37 AM
Kevin A. Richardson Kevin A. Richardson is offline
InterNACHI Member
 
Join Date: Sep 2004
Posts: 1,334
Default Re: Blower Door

Quote:
Originally Posted by Brian A. MacNeish View Post
The best place to reduce air leakage is at the interior wall surfaces of the outside walls, therefore, the best way of finding air leaks is with depressurization of the building on cold days. The quickest way to find the air leakage would be with IR while the building is depressurized.

When you see air leakage on the outside of a building, you may not find the exact location of the air leakage at the inside wall surface, that's where you want to seal it. It's similar to finding a roof leak sometimes...... where the water shows up on the ceiling may be many feet away from the actual roof leak!!
Agreed! The best and probably the easiest way to detect air leakage is from within the building. That is not to say that it cannot be done from the exterior. An exterior IR scan is a lot more difficult and has a lot of factors that can produce errors or misleading conclusions. Just because it's not consider "easy" does not mean it should not be done.

Proper training and experience is critical for conducting exterior energy loss scans using infrared (with or without the blower door).


Kevin
Attached Thumbnails
blower-door-ir_0178.jpg   blower-door-ir_0180.jpg  



Kevin A. Richardson
Level III Infraspection Institute Certified Infrared ThermographerŪ, #7493
Infraspection Institute Thermography Instructor
BPI Certified Building Performance Analyst
RESNET Level II Home Energy Survey Professional
Maryland Licensed Home Inspector, #29727
InterNACHI Certified Professional Inspector, #04091175


301-942-4610
www.richnspect.com
www.infrared-diagnostics.com
www.thehomegreenteam.com
Reply With Quote
  #48  
Old 11/15/08, 6:45 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,686
Default Re: Blower Door

Quote:
the best way of finding air leaks is with depressurization
Oh yea of little training...................



"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein

David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #49  
Old 11/16/08, 8:53 AM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Blower Door

Quote:
Originally Posted by dandersen View Post
Oh yea of little training...................
Care to expound on your theories......or deeper knowledge??

Last edited by Brian A. MacNeish; 11/16/08 at 9:17 PM..
Reply With Quote
  #50  
Old 11/16/08, 9:40 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,684
Default Re: Blower Door

I've received requests for blower door IR scans and I simply tell the callers that blower door scanning simply magnifies anomalies that my camera can detect anyways. I still book the IR scan.

I would like to purchase blower door equipment, but the problem I'm having now is finding someone to train me on how to properly set it up and read the instrumentation. I've contacted locals here but they refuse to return my calls because they're afraid I'm going to cut into their side of the business.

If someone can show me how to properly utilize the blower door system, I'm interested in getting together.
Reply With Quote
  #51  
Old 11/16/08, 12:40 PM
Rodney Misener's Avatar
Rodney Misener Rodney Misener is offline
InterNACHI Member
 
Join Date: Jul 2008
Location: Pictou County, Nova Scotia
Posts: 468
Default Re: Blower Door

Quote:
Originally Posted by dvalley View Post
I've received requests for blower door IR scans and I simply tell the callers that blower door scanning simply magnifies anomalies that my camera can detect anyways. I still book the IR scan.

I would like to purchase blower door equipment, but the problem I'm having now is finding someone to train me on how to properly set it up and read the instrumentation. I've contacted locals here but they refuse to return my calls because they're afraid I'm going to cut into their side of the business.

If someone can show me how to properly utilize the blower door system, I'm interested in getting together.
David,

If you purchase a Minneapolis Blower door system it comes with in depth instructions on how to set-up and operate.



Rodney Misener, CMI
Trinity Inspection Services
Pictou County, Nova Scotia
http://www.trinityinspectionservices.com

Certified Home Inspector
Certified Level 1 Thermographer
Certified Energy Advisor
WETT Certified Inspector
IAC2 Radon/Mold Certified
Infrared Certified
Reply With Quote
  #52  
Old 11/16/08, 2:58 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,684
Default Re: Blower Door

Quote:
Originally Posted by rmisener View Post
David,

If you purchase a Minneapolis Blower door system it comes with in depth instructions on how to set-up and operate.
Great. I like the fact that the directions come with the product, but I would like to obtain hands-on training, in order for me to know exactly what I'm doing when performing these BD tests for the first couple of times.

I don't think anyone (new at BD testing) would feel comfortable performing a blower door test for the first time and reading the directions while setting it up. The clients would love to see the professional they hired reading the directions, ayyy?

That's why I prefer to participate in a hands-on training.

If anyone (with a BD) wants to volunteer their time, I'd have no problem flying out to you.
Reply With Quote
  #53  
Old 11/17/08, 8:53 AM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Blower Door

Quote:
Originally Posted by dvalley View Post
Great. I like the fact that the directions come with the product, but I would like to obtain hands-on training, in order for me to know exactly what I'm doing when performing these BD tests for the first couple of times.

I don't think anyone (new at BD testing) would feel comfortable performing a blower door test for the first time and reading the directions while setting it up. The clients would love to see the professional they hired reading the directions, ayyy?

That's why I prefer to participate in a hands-on training.

If anyone (with a BD) wants to volunteer their time, I'd have no problem flying out to you.
David:

Why not fly out to the Energy Conservatory or Retrotec and pick up your door. They'll probably be more than willing to instruct you!

Energy Conservatory

www.energyconservatory.com

2801 21st Ave S # 160
Minneapolis, MN
55407
(612) 827-1117

http://www.retrotec.com/

PS: There is an additional use for a blower door that no one has mentioned yet: Enclosure Integrity Testing to NFPA 2001. Being in a highly populated area, there may be a way to work into that market. I did a couple of tests before I got out of the private contractor market in 1990. Both were for an electrical utility: One was on a 25 megawatt electrical generation backup station (using a modified 747 jet turbine) and the other was for the central communications facility at head office.

http://www.energyconservatory.com/ap...lications6.htm

http://www.retrotec.com/fire_testing/

Current president of Retrotec, Colin Genge, wrote the original 2001 standard and should still be one of the best sources of info on the topic. Met him when bought my door in 1981. He's very approachable and willing to talk.

Last edited by Brian A. MacNeish; 11/17/08 at 10:37 AM..
Reply With Quote
  #54  
Old 11/17/08, 11:07 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,684
Default Re: Blower Door

Quote:
Originally Posted by Brian A. MacNeish View Post
David:

Why not fly out to the Energy Conservatory or Retrotec and pick up your door. They'll probably be more than willing to instruct you!

Energy Conservatory
I'm looking into training (on the instrumentation) as we speak.

Thanks.
Reply With Quote
  #55  
Old 11/26/08, 2:22 PM
David C. Macy's Avatar
David C. Macy David C. Macy is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: NE. OH
Posts: 2,555
Default Re: Blower Door

Quote:
Originally Posted by dvalley View Post
I'm looking into training (on the instrumentation) as we speak.

Thanks.
I have spoken to several professionals that provide energy inspections and use blower doors in my area.

The normal fee is $350. One company is offering an energy inspection for $149.

I am having them come do my home. I figure for $150 I can watch an expert and ask him a lot of questions and also see where I am losing energy. (I know were my heat losses are I just want to see how the camera and blower door work)

I want to see the blower door and thermal camera they use.
Reply With Quote
  #56  
Old 11/26/08, 5:33 PM
Scott Gilligan,  CMI's Avatar
Scott Gilligan, CMI Scott Gilligan,  CMI is offline
InterNACHI Member
 
Join Date: May 2007
Location: Philadelphia, PA
Posts: 1,824
Send a message via AIM to sgilligan1 Send a message via MSN to sgilligan1 Send a message via Yahoo to sgilligan1
Default Re: Blower Door

Quote:
Originally Posted by dvalley View Post
I'm looking into training (on the instrumentation) as we speak.

Thanks.
Look into the Duct Blaster unit. You can use it for duct leak detections and also use it as a blower door fan. I have been looking into the equipment myself too.
Reply With Quote
  #57  
Old 11/26/08, 8:38 PM
Rodney Misener's Avatar
Rodney Misener Rodney Misener is offline
InterNACHI Member
 
Join Date: Jul 2008
Location: Pictou County, Nova Scotia
Posts: 468
Default Re: Blower Door

Quote:
Originally Posted by sgilligan1 View Post
Look into the Duct Blaster unit. You can use it for duct leak detections and also use it as a blower door fan. I have been looking into the equipment myself too.
Scott,

I don't think you can use the duct blaster system as a blower door. It is a much smaller fan and a different setup. It wouldn't come with a door frame.



Rodney Misener, CMI
Trinity Inspection Services
Pictou County, Nova Scotia
http://www.trinityinspectionservices.com

Certified Home Inspector
Certified Level 1 Thermographer
Certified Energy Advisor
WETT Certified Inspector
IAC2 Radon/Mold Certified
Infrared Certified
Reply With Quote
  #58  
Old 11/26/08, 11:12 PM
Scott Gilligan,  CMI's Avatar
Scott Gilligan, CMI Scott Gilligan,  CMI is offline
InterNACHI Member
 
Join Date: May 2007
Location: Philadelphia, PA
Posts: 1,824
Send a message via AIM to sgilligan1 Send a message via MSN to sgilligan1 Send a message via Yahoo to sgilligan1
Default Re: Blower Door

Quote:
Originally Posted by rmisener View Post
Scott,

I don't think you can use the duct blaster system as a blower door. It is a much smaller fan and a different setup. It wouldn't come with a door frame.
According to the website and product literature you can use it as a blower door fan. It won't handle huge houses, but for the average home it says it will do just fine. There is a door frame for it that you can buy separately that fits the fan.
Reply With Quote
  #59  
Old 11/27/08, 7:27 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,684
Default Re: Blower Door

Quote:
Originally Posted by dmacy View Post
I have spoken to several professionals that provide energy inspections and use blower doors in my area.

The normal fee is $350. One company is offering an energy inspection for $149.

I am having them come do my home. I figure for $150 I can watch an expert and ask him a lot of questions and also see where I am losing energy. (I know were my heat losses are I just want to see how the camera and blower door work)

I want to see the blower door and thermal camera they use.
Good point, Dave. I may do the same if I must.
Reply With Quote
  #60  
Old 11/27/08, 7:42 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,684
Default Re: Blower Door

Quote:
Originally Posted by sgilligan1 View Post
According to the website and product literature you can use it as a blower door fan. It won't handle huge houses, but for the average home it says it will do just fine. There is a door frame for it that you can buy separately that fits the fan.

Scott,

If I were performing whole house blower door IR inspections, I personally wouldn't take the chance of utilizing a small HVAC fan (for a blower door) that only operates at a lousy 1,500 CFM of free air, when I can obtain 6,300 CFM of free air with the heavy duty fan that is intended to be utilized for a typical blower door.

I would imagine that a smaller fan would not allow you to obtain you proper readings on the instrumentation in a larger home. What happens when you get a request for a blower door on a 3,000 sq. ft. home? Are you going to tell your prospect that your fan is undersized for the job?

IMO, it's not worth the savings....
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Newbie here with a slab "standards" question Robert Young, #3 Structural Inspections 17 4/10/07 11:48 AM
Bad Door and Water on the Floor jnicholson Exterior Inspections 7 10/4/06 10:45 PM


All times are GMT -4. The time now is 7:49 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts