Default Re: Roof sheathing moisture-Don't just add vents

He was guessing from a picture. Are you surprised?

I have examined this pattern, the article and the picture before jumping to conclusions.
I do not agree with James about the author's info. What I was most disturbed about was the Picture and the lack of ventilation as he says was there on the inspection.
I am also disturbed at the lack of proper pattern for infiltration into the attic and location of the mold.
The rafters give the biggest clue of all!



THE RIGHT TRAK
CIAQP, IAC2
Certified Master Inspector
kwoodinspections@hotmail.com
www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ
www.linkedin.com/in/kevinwoodiaq
OOVOO account kwoodinspections
Cell: 705-971-2096
Ph : 705-946-2676
Reply With Quote
Need a home inspection in Arizona? Check out InterNACHI's listing of Arizona certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #62  
Old 12/21/11, 12:32 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,092
Default Re: Roof sheathing moisture-Don't just add vents

The writer of the article clearly states
Quote:
I recommended that the homeowners confirm the air-leakage diagnosis with some performance testing and likely air-sealing resolution.
Do you disagree with his prescription?

The original HI screwed up by suggesting the need for additional ventilation not the writer of the article who was working with pictures only.



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
  #63  
Old 12/21/11, 12:32 PM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Southwest Missouri
Posts: 20,958
Default Re: Roof sheathing moisture-Don't just add vents

Quote:
Originally Posted by jbraun View Post
air sealing
What does the amount of insulation have to do with "air sealing"?



James H. Bushart

Professional Building Analyst, BPI
Missouri, Kansas and Arkansas
314-803-2167

Reply With Quote
  #64  
Old 12/21/11, 12:38 PM
James E. Braun, CMI's Avatar
James E. Braun, CMI James E. Braun, CMI is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Jefferson City, MO
Posts: 6,945
Default Re: Roof sheathing moisture-Don't just add vents

It is just a part. The more insulation, the less leakage can occur.



Braun Inspection Consultants
Serving Jefferson City, Columbia, Sedalia, Fulton and Lake of the Ozarks
Reply With Quote
  #65  
Old 12/21/11, 12:39 PM
Peter C. Russell's Avatar
Peter C. Russell Peter C. Russell is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Alton Bay NH
Posts: 3,998
Default Re: Roof sheathing moisture-Don't just add vents

Quote:
Originally Posted by jbraun View Post
It is just a part. The more insulation, the less leakage can occur.

WOW, are you kidding me????



Russell Inspection Services
New Hampshire state license # 57
Level I Thermographer, ITC
Certified Building Science Thermographer, ITC
Certified Building Analyst, BPI
Certified Commercial Inspector, ITA
Certified Septic Evaluator, GSDI #148

www.newenglandthermalimaging.com
www.russellinspectionservices.com
www.nhsepticinspection.com
Reply With Quote
  #66  
Old 12/21/11, 12:40 PM
James E. Braun, CMI's Avatar
James E. Braun, CMI James E. Braun, CMI is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Jefferson City, MO
Posts: 6,945
Default Re: Roof sheathing moisture-Don't just add vents

Quote:
Originally Posted by mlarson View Post
The writer of the article clearly statesDo you disagree with his prescription?

The original HI screwed up by suggesting the need for additional ventilation not the writer of the article who was working with pictures only.
It has no open soffit vents in the picture. It needs better venting.



Braun Inspection Consultants
Serving Jefferson City, Columbia, Sedalia, Fulton and Lake of the Ozarks
Reply With Quote
  #67  
Old 12/21/11, 12:41 PM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Southwest Missouri
Posts: 20,958
Default Re: Roof sheathing moisture-Don't just add vents

Quote:
Originally Posted by jbraun View Post
it is just a part. The more insulation, the less leakage can occur.
LOL.



James H. Bushart

Professional Building Analyst, BPI
Missouri, Kansas and Arkansas
314-803-2167

Reply With Quote
  #68  
Old 12/21/11, 12:42 PM
Robert Ernst Robert Ernst is online now
InterNACHI Member
 
Join Date: Sep 2010
Location: Sparks,NV
Posts: 655
Default Re: Roof sheathing moisture-Don't just add vents

The guys diagnosis of the photo was confirmed by an on site inspection and diagnostic testing. The person that did the testing was BPI Certified and used equipment to do the testing. So why not accept the science behind it and use it to further yourself in this field. You will serve your clients better and not make the mistake the inspector did in this instance. We are generalist and are to refer to the professionals. I agree not all professionals know what they are talking about but this time I think the guy in right on.



Nevada Inspector of Structures #1730
Nevada Energy Auditor #30
www.homecsi.com
Reply With Quote
  #69  
Old 12/21/11, 12:44 PM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Southwest Missouri
Posts: 20,958
Default Re: Roof sheathing moisture-Don't just add vents

Quote:
Originally Posted by rernst1 View Post
The guys diagnosis of the photo was confirmed by an on site inspection and diagnostic testing. The person that did the testing was BPI Certified and used equipment to do the testing. So why not accept the science behind it and use it to further yourself in this field. You will serve your clients better and not make the mistake the inspector did in this instance. We are generalist and are to refer to the professionals. I agree not all professionals know what they are talking about but this time I think the guy in right on.
At least one of those who are opposing the information presented in the article also think that adding more insulation will address air leakage issues. I think that says it all, don't you?



James H. Bushart

Professional Building Analyst, BPI
Missouri, Kansas and Arkansas
314-803-2167

Reply With Quote
  #70  
Old 12/21/11, 12:46 PM
Peter C. Russell's Avatar
Peter C. Russell Peter C. Russell is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Alton Bay NH
Posts: 3,998
Default Re: Roof sheathing moisture-Don't just add vents

Quote:
Originally Posted by jbushart View Post
At least one of those who are opposing the information presented in the article also think that adding more insulation will address air leakage issues. I think that says it all, don't you?
Yes, both seem to have a total misunderstanding of air movement, ventilation and insulation.



Russell Inspection Services
New Hampshire state license # 57
Level I Thermographer, ITC
Certified Building Science Thermographer, ITC
Certified Building Analyst, BPI
Certified Commercial Inspector, ITA
Certified Septic Evaluator, GSDI #148

www.newenglandthermalimaging.com
www.russellinspectionservices.com
www.nhsepticinspection.com
Reply With Quote
  #71  
Old 12/21/11, 12:48 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,092
Default Re: Roof sheathing moisture-Don't just add vents

Quote:
Originally Posted by prussell View Post
Yes, both seem to have a total misunderstanding of air movement, ventilation and insulation.
And they are CMIs

Go figure



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
  #72  
Old 12/21/11, 12:49 PM
James E. Braun, CMI's Avatar
James E. Braun, CMI James E. Braun, CMI is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Jefferson City, MO
Posts: 6,945
Default Re: Roof sheathing moisture-Don't just add vents

Quote:
Originally Posted by prussell View Post
WOW, are you kidding me????
http://www.finehomebuilding.com/how-...px?ac=ts&ra=fp



Braun Inspection Consultants
Serving Jefferson City, Columbia, Sedalia, Fulton and Lake of the Ozarks
Reply With Quote
  #73  
Old 12/21/11, 12:51 PM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Southwest Missouri
Posts: 20,958
Default Re: Roof sheathing moisture-Don't just add vents

Quote:
Originally Posted by prussell View Post
Yes, both seem to have a total misunderstanding of air movement, ventilation and insulation.
I agree.

The first mistake that the home inspector made was to recommend a remedy at all. He should stick to the SOP and point out the material defect and recommend that someone with the proper skills address the issue.

He would have then provided a valuable service and would not be called out in error as he was in this article.

Otherwise, filtering/cleaning the air as it leaks from a building with "more insulation" is the kind of advice a home owner can expect.



James H. Bushart

Professional Building Analyst, BPI
Missouri, Kansas and Arkansas
314-803-2167

Reply With Quote
Need a home inspection in Arizona? Check out InterNACHI's listing of Arizona certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #74  
Old 12/21/11, 12:52 PM
Peter C. Russell's Avatar
Peter C. Russell Peter C. Russell is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Alton Bay NH
Posts: 3,998
Default Re: Roof sheathing moisture-Don't just add vents

James Braun, I can tell you from experience that all the cellulose insulation in the world will not seal the attic.



Russell Inspection Services
New Hampshire state license # 57
Level I Thermographer, ITC
Certified Building Science Thermographer, ITC
Certified Building Analyst, BPI
Certified Commercial Inspector, ITA
Certified Septic Evaluator, GSDI #148

www.newenglandthermalimaging.com
www.russellinspectionservices.com
www.nhsepticinspection.com
Reply With Quote
  #75  
Old 12/21/11, 12:52 PM
KEVIN WOOD's Avatar
KEVIN WOOD KEVIN WOOD is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 3,112
Default Re: Roof sheathing moisture-Don't just add vents

James is not pointing out that adding more insulation will solve the problem. Tests have shown that you can add as much insulation as you want and air will go through with no vapor barrier. It will slow down to some degree. I have even seen tests between different types of insulation without vapor control but that is a whole new topic.



THE RIGHT TRAK
CIAQP, IAC2
Certified Master Inspector
kwoodinspections@hotmail.com
www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ
www.linkedin.com/in/kevinwoodiaq
OOVOO account kwoodinspections
Cell: 705-971-2096
Ph : 705-946-2676
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Roof sheathing impressions ins roof apeden Roofing Inspections 5 11/30/10 12:55 AM
Closing Gable Vent Kevin Patteri General Inspection Discussion 26 11/8/10 10:30 AM
Shooting to begin on comprehensive new roofing courses kshepard Inspection Education & Training 4 11/7/09 2:59 PM
Interesting Roof Vents cevans Exterior Inspections 1 6/19/09 2:03 AM
IAC2 In new residential construction mcyr IAC2 Indoor Air Forum 0 10/9/07 6:45 PM