Default Range hood ducting

Does anyone know of good articles stating why hoods must be ducted outside. I know sop says so and I truly understand why but sometimes an article written by a third party puts the point across to a client or RE agent better.
Reply With Quote
Need a home inspection in District Of Columbia? Check out InterNACHI's listing of District Of Columbia certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 3/12/11, 11:08 AM
Tom Leahy Tom Leahy is offline
InterNACHI Member
 
Join Date: Dec 2009
Location: Arlington, Texas
Posts: 358
Default Re: Range hood ducting

(c) Range exhaust vent. The inspector shall
report as Deficient:
(2) a vent pipe that does not terminate
outside the structure, if the unit is not of a recirculating
type or configuration;

SOP states that only if vented, needs to be to the outside. Some jurisdictions require hoods to be vented, but most cities allow recirculating as well.



Fort Worth Home Inspector
Dallas Home Inspector
Reply With Quote
  #3  
Old 3/12/11, 1:51 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,631
Default Re: Range hood ducting

IBC 2006

SECTION M1503 RANGE HOODS

M1503.1 General.

Range hoods shall discharge to the outdoors through a single-wall duct. The duct serving the hood shall have a smooth interior surface, shall be air tight and shall be equipped with a backdraft damper. Ducts serving range hoods shall not terminate in an attic or crawl space or areas inside the building.

Exception: Where installed in accordance with the manufacturer’s installation instructions, and where mechanical or natural ventilation is otherwise provided, listed and labeled ductless range hoods shall not be required to discharge to the outdoors.



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Microwave/range hood distance to range top 35capes3 AskNACHI.org Inspection Questions Forum 10 4/17/10 5:52 PM
Micro / Range Hood on a wall switch sgilligan1 Electrical Inspections 9 7/14/08 11:57 PM
Range hood Ian Gills Electrical Inspections 3 2/2/07 8:14 AM
Range exhaust hood question mmorgan Interior Inspections 24 4/20/06 9:50 PM


All times are GMT -4. The time now is 10:16 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts