Does anyone know of good articles stating why hoods must be ducted outside. I know sop says so and I truly understand why but sometimes an article written by a third party puts the point across to a client or RE agent better.
|
| Need a home inspection in District Of Columbia? Check out InterNACHI's listing of District Of Columbia certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#2
|
|||
|
|||
|
(c) Range exhaust vent. The inspector shall
report as Deficient: (2) a vent pipe that does not terminate outside the structure, if the unit is not of a recirculating type or configuration; SOP states that only if vented, needs to be to the outside. Some jurisdictions require hoods to be vented, but most cities allow recirculating as well. Fort Worth Home Inspector Dallas Home Inspector |
|
#3
|
||||
|
||||
|
IBC 2006
SECTION M1503 RANGE HOODS M1503.1 General. Range hoods shall discharge to the outdoors through a single-wall duct. The duct serving the hood shall have a smooth interior surface, shall be air tight and shall be equipped with a backdraft damper. Ducts serving range hoods shall not terminate in an attic or crawl space or areas inside the building. Exception: Where installed in accordance with the manufacturer’s installation instructions, and where mechanical or natural ventilation is otherwise provided, listed and labeled ductless range hoods shall not be required to discharge to the outdoors. Christopher Currins Certified, Licensed Proudly serving the St.Louis Metro St. Charles, St. Peters, Maryland Heights, O'Fallon, Florrisant, MO Home Inspector BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Microwave/range hood distance to range top | 35capes3 | AskNACHI.org Inspection Questions Forum | 10 | 4/17/10 5:52 PM |
| Micro / Range Hood on a wall switch | sgilligan1 | Electrical Inspections | 9 | 7/14/08 11:57 PM |
| Range hood | Ian Gills | Electrical Inspections | 3 | 2/2/07 8:14 AM |
| Range exhaust hood question | mmorgan | Interior Inspections | 24 | 4/20/06 9:50 PM |