Default Chinese Drywall

I inspected a home today that was built in the 2004/2005 time frame. The AC evaporator coil had typical rust/corrosion; however the thin copper tubing on the evaporator coil had the black corrosion associated with tainted drywall. (see attachment). I have either seen all or none and that is the main reason for posting.

Ground wires on 5 sample outlets through out the home and metal parts, i.e. faucets, spigots, door hardware etc had no visible corrosion.

Unfortunately the refrigerator was brand new and the coils were clean.

Ceiling drywall markings over two livable areas of the home were National Gypsum which is not a Chinese drywall manufacture.

According to the latest guidance from the CPSC (March 2011), for homes built or renovated in the 2001-2009 time frame the Threshold Inspection is positive if there is Blackening of copper electrical
wiring and/or air conditioning evaporator coil and Mean ground wire corrosion
rating >2


Based on the CPSC guidance, this home meets the requirements for suspect tainted drywall and therefore meets the prerequisite for Step 2, "Corroborating Evidence"

Would you agree?
Attached Thumbnails
chinese-drywall-100_7795.jpg  



Richard Ross
Accurate Home Inspections of America, LLC
Cape Coral, FL 33914
239-271-8499 Office
239-271-8499 Mobile
407-358-5376 FAX
Reply With Quote
Need a home inspection in Kentucky? Check out InterNACHI's listing of Kentucky certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 2/10/12, 5:45 PM
Humberto Carvajal's Avatar
Humberto Carvajal Humberto Carvajal is offline
InterNACHI Member
 
Join Date: May 2005
Location: Homestead, FL
Posts: 819
Default Re: Chinese Drywall

Hello Richard. First, those capillary tubes sure show a lot of
"patina" customarily associated with copper. There are areas that do appear to be blackening but, it's very small and may be caused by something else and not necessarily tainted drywall. Also, I do believe that you'd be very lucky to find tainted drywall on the ceilings as from the information I remember at a meeting I attended last year, the drywall used on the walls and not the size used in ceilings have been found to be contaminated. I may be wrong and maybe someone will chime in and correct me. Neighborhood information is also helpful in determining. Are there other homes within the community known to be contaminated? Just a few things to think about. I would be very careful to draw any positive conclusions based on the little evidence you have provided here in this picture. That's just me though. Thanks for posting and hopefully some others will contribute as well.

Bert





Humberto Carvajal Jr.
Florida State Property Inspections, LLC
Florida Home Inspector License# HI884
LEEDŽ Accredited Professional
Member USGBC South Florida Chapter

Reply With Quote
  #3  
Old 2/10/12, 6:04 PM
Richard M. Ross's Avatar
Richard M. Ross Richard M. Ross is offline
InterNACHI Member
 
Join Date: Mar 2007
Location: Cape Coral, FL
Posts: 190
Send a message via Yahoo to rross2 Send a message via Skype™ to rross2
Default Re: Chinese Drywall

Thanks for the response Humberto. I believe you maybe thinking of the 5/8" sheet rock used in garage ceilings which has not been associated with Chinese Drywall.



Richard Ross
Accurate Home Inspections of America, LLC
Cape Coral, FL 33914
239-271-8499 Office
239-271-8499 Mobile
407-358-5376 FAX
Reply With Quote
  #4  
Old 2/10/12, 6:08 PM
Humberto Carvajal's Avatar
Humberto Carvajal Humberto Carvajal is offline
InterNACHI Member
 
Join Date: May 2005
Location: Homestead, FL
Posts: 819
Default Re: Chinese Drywall

You may be right. For some reason I thought I heard someone say they hadn't found it in 1/2" only in 3/8" drywall? maybe I was mistaken.

Bert





Humberto Carvajal Jr.
Florida State Property Inspections, LLC
Florida Home Inspector License# HI884
LEEDŽ Accredited Professional
Member USGBC South Florida Chapter

Reply With Quote
  #5  
Old 2/10/12, 6:50 PM
Eric C. Van De Ven's Avatar
Eric C. Van De Ven Eric C. Van De Ven is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: South Florida
Posts: 2,323
Default Re: Chinese Drywall

The coils have some patina but I don't think that is an issue.
Here are a set of 16 year old coils.
Attached Thumbnails
chinese-drywall-reyes-95-large-.jpg (Large).jpg
Views:	96
Size:	80.3 KB
ID:	52495  
Reply With Quote
  #6  
Old 2/10/12, 7:32 PM
Gary Young Gary Young is offline
InterNACHI Member
 
Join Date: Nov 2011
Posts: 28
Default Re: Chinese Drywall

I agree with Bert. That's a pretty big statement to go on the pic youv'e shown.
Reply With Quote
  #7  
Old 2/11/12, 12:51 PM
Brian C. Hoagland Brian C. Hoagland is offline
InterNACHI Member
 
Join Date: Dec 2006
Location: Cocoa, FL
Posts: 3,410
Default Re: Chinese Drywall

Quote:
Originally Posted by rross2 View Post
Thanks for the response Humberto. I believe you maybe thinking of the 5/8" sheet rock used in garage ceilings which has not been associated with Chinese Drywall.
The 1/2" inch drywall imported from China was not rated for use on cielings on 24" centers. On 24" centers it must be a 1/2" made for that application or 5/8" drywall. That is why looking for it on cielings is a waste of time. Side walls adjacent to vaulted areas in the attic might help though.

Any idea how old that evap coil is? Don't forget that high sulpur content water can off gas chemicals that can cause this too. Is there a well pump in the garage?

Err on the side of caution and be carefull how you word the report.
Reply With Quote
  #8  
Old 2/11/12, 1:52 PM
John Shishilla's Avatar
John Shishilla John Shishilla is offline
InterNACHI Member
 
Join Date: Jul 2008
Location: Melbourne, FL
Posts: 3,051
Default Re: Chinese Drywall

I some experience with this. I was threatened and a complaint filed on me by a person I did NOT do an inspection for. She relied on my report and then thought the home had contaminated drywall. My report specifically stated no visible contaminated drywall was visible at the time of the inspection.

She threatened, filed complaints on all of my licenses. DBPR sent out an investigator, found no evidence of contaminated drywall and dropped the complaints. They asked that I respond to her, even though she was not my client and I had never even talked with her.

We had Joe Ferry send her a letter and she went away(hopefully to get mental help). You can not be too careful.




John Shishilla
State of Florida Licensed Home Inspector #21
Residential Contractor
Accredited Claims Adjuster (ACA)
Mold Assessor MRSA 1544
President of Fl Home & Insurance Inspectors Chptr
VP of Nachi Managment


Serving all of Baytree, Melbourne, Palm Bay, Cocoa, Rockledge, Viera, Satellite Beach, Indian Harbor Beach, Indialantic and surrounding areas.

Honor Construction Inspection Service
www.honorconstruction.com
"Because details matter"

321-327-2950

Reply With Quote
  #9  
Old 2/11/12, 2:33 PM
Brian C. Hoagland Brian C. Hoagland is offline
InterNACHI Member
 
Join Date: Dec 2006
Location: Cocoa, FL
Posts: 3,410
Default Re: Chinese Drywall

John did your client (not the crazy lady) specifically ask you to., pay you for an inspection for contaminated drywall leading to that statement regarding it that you put in the report? I am asking because I generally disclaim this stuff.
Reply With Quote
  #10  
Old 2/11/12, 3:27 PM
John Shishilla's Avatar
John Shishilla John Shishilla is offline
InterNACHI Member
 
Join Date: Jul 2008
Location: Melbourne, FL
Posts: 3,051
Default Re: Chinese Drywall

Quote:
Originally Posted by bhoagland View Post
John did your client (not the crazy lady) specifically ask you to., pay you for an inspection for contaminated drywall leading to that statement regarding it that you put in the report? I am asking because I generally disclaim this stuff.
Yes it was a drywall inspection, the house was thought to have it before I went in. I did not know but the listing said, "Chinese Drywall."

After my report the new listing said, "No Chinese Drywall."

When the Realtor realized she may be sued, she called me and asked me to defend her. I told her that I would not, but stood behind my report. No visible contaminated drywall.

They had a well with high sulfur content.




John Shishilla
State of Florida Licensed Home Inspector #21
Residential Contractor
Accredited Claims Adjuster (ACA)
Mold Assessor MRSA 1544
President of Fl Home & Insurance Inspectors Chptr
VP of Nachi Managment


Serving all of Baytree, Melbourne, Palm Bay, Cocoa, Rockledge, Viera, Satellite Beach, Indian Harbor Beach, Indialantic and surrounding areas.

Honor Construction Inspection Service
www.honorconstruction.com
"Because details matter"

321-327-2950

Reply With Quote
  #11  
Old 2/11/12, 3:53 PM
Brian C. Hoagland Brian C. Hoagland is offline
InterNACHI Member
 
Join Date: Dec 2006
Location: Cocoa, FL
Posts: 3,410
Default Re: Chinese Drywall

I thought as much. This is a catch 22 situation for us, while the photo provided did not exhibit what most of us would consider a classic case scenario, once we start down the path of considering it a possibility we owe it to ourselves to point it out. The costs to repair are so high and the stigma of missing it are buisiness killers.

On the other hand, labelling a property as having it without proof could be equally as bad. With consequences including liability to the current owner.

Report writing regarding this issue is critically important to protect the interests of all concerned.
Reply With Quote
  #12  
Old 2/11/12, 4:37 PM
Jay C. Murray's Avatar
Jay C. Murray Jay C. Murray is offline
InterNACHI Member
 
Join Date: Jun 2009
Location: Port Saint Lucie, Fl
Posts: 784
Default Re: Chinese Drywall

Quote:
Originally Posted by jshishilla View Post
I some experience with this. I was threatened and a complaint filed on me by a person I did NOT do an inspection for. She relied on my report and then thought the home had contaminated drywall. My report specifically stated no visible contaminated drywall was visible at the time of the inspection.

She threatened, filed complaints on all of my licenses. DBPR sent out an investigator, found no evidence of contaminated drywall and dropped the complaints. They asked that I respond to her, even though she was not my client and I had never even talked with her.

We had Joe Ferry send her a letter and she went away(hopefully to get mental help). You can not be too careful.
People suck!



Your Home Inspection & Wind Mitigation Provider
Jay C. Murray
Florida Home & Insurance Inspector Chapter Board Member
Licensed General Contractor & Home Inspector
Serving Port St. Lucie, Ft. Pierce, Stuart, Palm City, Jensen Beach,
The Palm Beaches, & The Treasure Coast
Reply With Quote
  #13  
Old 2/12/12, 11:36 AM
Bruce Meyer Bruce Meyer is offline
InterNACHI Member
 
Join Date: Sep 2009
Posts: 2
Default Re: Chinese Drywall

The 5/8" ceiling drywall, made in the USA may be contaminated, so it is NOT a waste of time to check it. I have found this on many occassions.
Also, you need to check more than 5 outlets. If you have reason to believe there is contaminated drywall, i.e. black coils, you should check one on each wall (minimum) until you find black ground wire. I have found it in one room on one wall.
You cannot only rely on black copper coils, especially if it is not conclusive.

Bruce Meyer
Florida Home Inspections
Ft. Myers, Fl. area
Reply With Quote
Need a home inspection in Kentucky? Check out InterNACHI's listing of Kentucky certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 2/12/12, 1:12 PM
John Shishilla's Avatar
John Shishilla John Shishilla is offline
InterNACHI Member
 
Join Date: Jul 2008
Location: Melbourne, FL
Posts: 3,051
Default Re: Chinese Drywall

Quote:
Originally Posted by bmeyer3 View Post
The 5/8" ceiling drywall, made in the USA may be contaminated, so it is NOT a waste of time to check it. I have found this on many occassions.
Also, you need to check more than 5 outlets. If you have reason to believe there is contaminated drywall, i.e. black coils, you should check one on each wall (minimum) until you find black ground wire. I have found it in one room on one wall.
You cannot only rely on black copper coils, especially if it is not conclusive.

Bruce Meyer
Florida Home Inspections
Ft. Myers, Fl. area
That is the problem, nothing is conclusive. You can only state with testing that there is elevated levels of contaminates. You can advise your client to do further testing. Some american drywall is thought to be problematic also, possibly from recycled drywall.

I find many inspectors call it out and they are wrong. The best step is identifying the drywall. I do like when I am asked to do the inspection and the drywall is labeled made in china. I does make life easy.




John Shishilla
State of Florida Licensed Home Inspector #21
Residential Contractor
Accredited Claims Adjuster (ACA)
Mold Assessor MRSA 1544
President of Fl Home & Insurance Inspectors Chptr
VP of Nachi Managment


Serving all of Baytree, Melbourne, Palm Bay, Cocoa, Rockledge, Viera, Satellite Beach, Indian Harbor Beach, Indialantic and surrounding areas.

Honor Construction Inspection Service
www.honorconstruction.com
"Because details matter"

321-327-2950

Reply With Quote
  #15  
Old 2/12/12, 2:31 PM
Brian C. Hoagland Brian C. Hoagland is offline
InterNACHI Member
 
Join Date: Dec 2006
Location: Cocoa, FL
Posts: 3,410
Default Re: Chinese Drywall

Quote:
Originally Posted by bmeyer3 View Post
The 5/8" ceiling drywall, made in the USA may be contaminated, so it is NOT a waste of time to check it. I have found this on many occassions.
Also, you need to check more than 5 outlets. If you have reason to believe there is contaminated drywall, i.e. black coils, you should check one on each wall (minimum) until you find black ground wire. I have found it in one room on one wall.
You cannot only rely on black copper coils, especially if it is not conclusive.

Bruce Meyer
Florida Home Inspections
Ft. Myers, Fl. area
Well yeah, you can test it but you are not going to know by looking at it, I was referring to simply inspecting for the chinese stuff if it is on the cieling on 24" centers than it should be replaced anyway.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
News from the CPS and HUD on Chinese Drywall rhensel General Inspection Discussion 2 9/17/11 6:25 PM
Chinese Drywall Advisors - Your guide to the Chinese Drywall Problem Clark Kilby General Inspection Discussion 2 7/27/10 3:48 AM
CPSC info on Chinese Drywall jfunderburk Interior Inspections 1 5/29/10 6:17 AM