  #16  
Old 1/28/12, 11:48 AM
Eric C. Van De Ven's Avatar
Eric C. Van De Ven Eric C. Van De Ven is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: South Florida
Posts: 2,323
Default Re: Citizens re-inspect

Quote:
Originally Posted by aalm View Post
What do I tell my client? It will cost him $440 a year. Permit complete in the city of Delray Beach.


Cedar Shake roof installed in 2007...I found plenty of shiners at least 2in of nail measured and 5/8 sheathing....The citizens inspector says its a 6d nail?? WTF????
Is there plywood here with battens on top?
Reply With Quote
Need a home inspection in Missouri? Check out InterNACHI's listing of Missouri certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #17  
Old 1/28/12, 11:50 AM
Preston L. Halstead Preston L. Halstead is offline
InterNACHI Member
 
Join Date: Apr 2009
Location: West Palm Beaach, FL
Posts: 696
Default Re: Citizens re-inspect

Typically in a re roof of the kind the batten boards would be new- and only have 1 nail per board. also I know someone in delray beach that had to fight to have ther wood shake roof installed this way as it did not meet current codes. According to the building department.

Regardless the form specifically states which box to check in this situation. You can spin it however you like unfortunately the wording is already there



Preston L. Halstead
VP FL Home & Insurance Inspectors Chapter
Elite Property Inspection & Management
LICENSED GENERAL CONTRACTOR CGC1515203
LICENSED BUILDING INSPECTOR BN6262
LICENSED HOME INSPECTOR HI549



HOME INSPECTION ~ WIND MITIGATION INSPECTION
Serving Boca Raton, Boynton Beach, Delray Beach, Juno Beach, Jupiter, Lake Park, Lake Worth, Lantana, North Palm Beach, Palm Beach, Palm Beach Gardens, Royal Palm Beach, Wellington, West Palm Beach.
Reply With Quote
  #18  
Old 1/28/12, 11:53 AM
Jay C. Murray's Avatar
Jay C. Murray Jay C. Murray is offline
InterNACHI Member
 
Join Date: Jun 2009
Location: Port Saint Lucie, Fl
Posts: 784
Default Re: Citizens re-inspect

Reinspection just screwed a client.

We all know, that marking UNKNOWN equates to a serious loss of credits. However, reinspection firms love this selection. They use it to point out a descreptancy between the original inspection and the reinspection as validation for their business scheme.

Here's the client's situation: -Batten deck was sheeted over with plywood and nailed 6 x 6 with 8d or greater nails, (Ashpalt Shingles with permit in 2006 re roof).

Reinspector marked UNKNOWN.

Their reasoning is:

'since the reinspector is not a professional engineer, that don't know what the psf rating would be.'

Jusitfying their conduct with an insinuation that the psf rating could actually be higher than the 182psf.

Either way, the client loses credits for a permited feature that was performed to current Florida Building Code and passed inspection. That is criminal.



Your Home Inspection & Wind Mitigation Provider
Jay C. Murray
Florida Home & Insurance Inspector Chapter Board Member
Licensed General Contractor & Home Inspector
Serving Port St. Lucie, Ft. Pierce, Stuart, Palm City, Jensen Beach,
The Palm Beaches, & The Treasure Coast

Last edited by jmurray4; 1/28/12 at 12:08 PM..
Reply With Quote
  #19  
Old 1/28/12, 12:06 PM
Eric C. Van De Ven's Avatar
Eric C. Van De Ven Eric C. Van De Ven is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: South Florida
Posts: 2,323
Default Re: Citizens re-inspect

Quote:
Originally Posted by phalstead View Post
Typically in a re roof of the kind the batten boards would be new- and only have 1 nail per board. also I know someone in delray beach that had to fight to have ther wood shake roof installed this way as it did not meet current codes. According to the building department.

Regardless the form specifically states which box to check in this situation. You can spin it however you like unfortunately the wording is already there
Weren't we talking about "intent of the form" at the meeting?

It is quite apparent to me, the "intent" and that is what I would go by.

As an aside, I notice there is no check-box for a shake roof. An oversight or on purpose?


What band of monkeys uses one nail for anything? Way way back, we used two nails minimum for this decking.

Now, I do have a question which may be the cause of the confusion.

In all of the ceder shake roofs I have seen down here and the ones I have installed, where battens were used, the battens were 1 x 4 x 8 wood. The felt was woven in between the battens and then, the shakes were installed on top of the battens. The battens were 4 inches apart.

I know of some installations that have decking and then 1 x 1 battens on top of the decking and then the shakes are attached to that. There are also some types of cement tile roofs that are done that way.

What are we talking about in this case.

Last edited by evandeven; 1/28/12 at 12:16 PM..
Reply With Quote
  #20  
Old 1/28/12, 1:28 PM
Carl Pennick's Avatar
Carl Pennick Carl Pennick is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lighthouse Point, FL
Posts: 931
Default Re: Citizens re-inspect

Quote:
Originally Posted by jmurray4 View Post
Reinspection just screwed a client.

We all know, that marking UNKNOWN equates to a serious loss of credits. However, reinspection firms love this selection. They use it to point out a descreptancy between the original inspection and the reinspection as validation for their business scheme.

Here's the client's situation: -Batten deck was sheeted over with plywood and nailed 6 x 6 with 8d or greater nails, (Ashpalt Shingles with permit in 2006 re roof).

Reinspector marked UNKNOWN.

Their reasoning is:

'since the reinspector is not a professional engineer, that don't know what the psf rating would be.'

Jusitfying their conduct with an insinuation that the psf rating could actually be higher than the 182psf.

Either way, the client loses credits for a permited feature that was performed to current Florida Building Code and passed inspection. That is criminal.
The home owner should dispute this



www.wisemovehomeinspection.com
Carl Pennick
Lighthouse Point, FL
954-946 2737
407-928 8489

Florida Licensed Home Inspector #65
NACHI #04072098
ICC #5294144
Certified Master Inspector
Reply With Quote
  #21  
Old 1/28/12, 1:52 PM
Eric C. Van De Ven's Avatar
Eric C. Van De Ven Eric C. Van De Ven is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: South Florida
Posts: 2,323
Default Re: Citizens re-inspect

Quote:
Originally Posted by jmurray4 View Post
Reinspection just screwed a client.

We all know, that marking UNKNOWN equates to a serious loss of credits. However, reinspection firms love this selection. They use it to point out a descreptancy between the original inspection and the reinspection as validation for their business scheme.

Here's the client's situation: -Batten deck was sheeted over with plywood and nailed 6 x 6 with 8d or greater nails, (Ashpalt Shingles with permit in 2006 re roof).

Reinspector marked UNKNOWN.

Their reasoning is:

'since the reinspector is not a professional engineer, that don't know what the psf rating would be.'

Jusitfying their conduct with an insinuation that the psf rating could actually be higher than the 182psf.

Either way, the client loses credits for a permited feature that was performed to current Florida Building Code and passed inspection. That is criminal.
I would contact the roofer and see what he used.
As there is roof decking:

Quote:
C. Plywood/OSB roof sheathing with a minimum thickness of 7/16”inch attached to the roof truss/rafter (spaced a maximum of
24”inches o.c.) by 8d common nails spaced a maximum of 6” inches in the field.
-OR- Dimensional lumber/Tongue & Groove
decking with a minimum of 2 nails per board (or 1 nail per board if each board is equal to or less than 6 inches in width).
-OR- Any
system of screws, nails, adhesives, other deck fastening system or truss/rafter spacing that is shown to have an equivalent or greater
resistance than 8d common nails spaced a maximum of 6 inches in the field or has a mean uplift resistance of at least 182 psf.
Reply With Quote
  #22  
Old 1/28/12, 2:31 PM
Eric C. Van De Ven's Avatar
Eric C. Van De Ven Eric C. Van De Ven is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: South Florida
Posts: 2,323
Default Re: Citizens re-inspect

Quote:
Originally Posted by aalm View Post
What do I tell my client? It will cost him $440 a year. Permit complete in the city of Delray Beach.


Cedar Shake roof installed in 2007...I found plenty of shiners at least 2in of nail measured and 5/8 sheathing....The citizens inspector says its a 6d nail?? WTF????
If battens only roof 1
If decking, roof 2.

I suspect at some point, there will have to be a letter like the one we had to use for tile roofs.

To whom it may concern,
In order to shaft those with wood shake roofs, the OIR has conveniently left a selection for them off of the "type of roof covering" section. Instead, they have co-mingled roof types with roof decking attachment, which have nothing to do with each other.

The inspector is forced to check box A no matter what type of underlying decking is present.

The roof in question conforms to the building code at the time of construction.
Attached Files
File Type: pdf roof1.pdf (96.4 KB, 21 views)
File Type: pdf roof2.pdf (106.0 KB, 21 views)
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Citizens board approves legislative package jshishilla Florida Inspectors 4 12/17/11 1:14 PM
Citizens insurance prepares to drop or reduce coverage, raise premiums wsiegel Florida Inspectors 1 12/1/11 6:19 AM
Four Point Inspection Question jmiller1 Florida Inspectors 98 4/22/11 10:11 PM
Citizens property insurance premiums rise with rebuilding costs wsiegel Florida Inspectors 0 4/21/11 2:13 PM
Citizens Insurance hands out another no-bid contract jburkeson1 Florida Inspectors 12 5/27/10 8:53 PM


All times are GMT -4. The time now is 11:39 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts