Default New form required for all homes closing after Feb 1

I just came back from a CLIB approved wind mit class and was told that all homes closing after Feb 1 have t be written on the new form. That is going to create havoc for all of us who are still using the old form on houses not closing this month.
Reply With Quote
Need a home inspection in New Jersey? Check out InterNACHI's listing of New Jersey certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 1/21/12, 6:05 PM
Eric C. Van De Ven's Avatar
Eric C. Van De Ven Eric C. Van De Ven is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: South Florida
Posts: 2,323
Default Re: New form required for all homes closing after Feb 1

Quote:
Originally Posted by wsiegel View Post
I just came back from a CLIB approved wind mit class and was told that all homes closing after Feb 1 have t be written on the new form. That is going to create havoc for all of us who are still using the old form on houses not closing this month.
Do them on the new form at the same time Bill, then just send them out.

Or if anything is different, label it under the pictures, take for instance a strap with two nails on one side and one on the other which is a clip on the old for, will become a single wrap on the new one.

Same ting goes for the old clips that now require three nails.
Reply With Quote
  #3  
Old 1/21/12, 9:26 PM
Preston L. Halstead Preston L. Halstead is offline
InterNACHI Member
 
Join Date: Apr 2009
Location: West Palm Beaach, FL
Posts: 696
Default Re: New form required for all homes closing after Feb 1

What class did you take?



Preston L. Halstead
VP FL Home & Insurance Inspectors Chapter
Elite Property Inspection & Management
LICENSED GENERAL CONTRACTOR CGC1515203
LICENSED BUILDING INSPECTOR BN6262
LICENSED HOME INSPECTOR HI549



HOME INSPECTION ~ WIND MITIGATION INSPECTION
Serving Boca Raton, Boynton Beach, Delray Beach, Juno Beach, Jupiter, Lake Park, Lake Worth, Lantana, North Palm Beach, Palm Beach, Palm Beach Gardens, Royal Palm Beach, Wellington, West Palm Beach.
Reply With Quote
  #4  
Old 1/22/12, 12:11 PM
Brian C. Hoagland Brian C. Hoagland is offline
InterNACHI Member
 
Join Date: Dec 2006
Location: Cocoa, FL
Posts: 3,410
Default Re: New form required for all homes closing after Feb 1

Everything I have inspected this month has two wind mits in my computer, but that won't solve the problem of the agents and underwriters rejecting the new forms if they don't know about them yet. That won't happen though because they are so knowledgable and on the ball though... right?
Reply With Quote
  #5  
Old 1/22/12, 1:45 PM
Jay C. Murray's Avatar
Jay C. Murray Jay C. Murray is offline
InterNACHI Member
 
Join Date: Jun 2009
Location: Port Saint Lucie, Fl
Posts: 784
Default Re: New form required for all homes closing after Feb 1

Starting last week we began using the new form unless the present form was specifically requested (for whatever reason).

New pricing is in effect as well....30% increase.

Still a deal when you figure that the Hip roof rating alone amy force you to measure the entire roof perimeter.

By the way, here's a free one for all.

The present form requires:
"Hip roof with no other roof shapes greater than 10% of the total building perimeter."


The NEW form requires:

"Hip roof with no other roof shapes greater than 10% of the total roof system perimeter." Yes, that's overhangs and rise / slope.


That's right, be prepared to measure the whole damn thing. Break out the tape measure....The floor plan from the property apraisers office will NOT work! Building perimeter is NOT roof system perimeter.



Your Home Inspection & Wind Mitigation Provider
Jay C. Murray
Florida Home & Insurance Inspector Chapter Board Member
Licensed General Contractor & Home Inspector
Serving Port St. Lucie, Ft. Pierce, Stuart, Palm City, Jensen Beach,
The Palm Beaches, & The Treasure Coast

Last edited by jmurray4; 1/22/12 at 1:52 PM..
Reply With Quote
  #6  
Old 1/22/12, 4:05 PM
Michael J. Meeker's Avatar
Michael J. Meeker Michael J. Meeker is online now
InterNACHI Member
 
Join Date: Dec 2009
Location: South East Florida
Posts: 5,712
Default Re: New form required for all homes closing after Feb 1

Quote:
Originally Posted by jmurray4 View Post
Starting last week we began using the new form unless the present form was specifically requested (for whatever reason).

New pricing is in effect as well....30% increase.

Still a deal when you figure that the Hip roof rating alone amy force you to measure the entire roof perimeter.

By the way, here's a free one for all.

The present form requires:
"Hip roof with no other roof shapes greater than 10% of the total building perimeter."


The NEW form requires:

"Hip roof with no other roof shapes greater than 10% of the total roof system perimeter." Yes, that's overhangs and rise / slope.


That's right, be prepared to measure the whole damn thing. Break out the tape measure....The floor plan from the property apraisers office will NOT work! Building perimeter is NOT roof system perimeter.

How is that to be accomplished accurately on complex multi level roof systems?


Bill,

You never mentioned how the class was? Who was the instructor and what did you think.

How did he come to the conclusions he did with no experience submitting the new forms to insurance folks yet.

No one can tell me they know what they will or will not want. It is going to be a real mess.



Florida Licensed General Contractor
Florida Licensed Home Inspector #299
Wind Mitigation Specialist
Call 954-922-0584 or E-Mail Me For The Best Wind Mitigation Inspection in Florida at a Great Price
Reply With Quote
  #7  
Old 1/25/12, 4:53 PM
Gary Young Gary Young is offline
InterNACHI Member
 
Join Date: Nov 2011
Posts: 28
Default Re: New form required for all homes closing after Feb 1

My understanding of this is you measure the perimeter of the roof that is not hip and divide it by the perimeter of the hip. If its greater than 10% the roof is not hip. No slope involved.
Reply With Quote
  #8  
Old 1/25/12, 5:04 PM
Eric C. Van De Ven's Avatar
Eric C. Van De Ven Eric C. Van De Ven is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: South Florida
Posts: 2,323
Default Re: New form required for all homes closing after Feb 1

Quote:
Originally Posted by gyoung1 View Post
My understanding of this is you measure the perimeter of the roof that is not hip and divide it by the perimeter of the hip. If its greater than 10% the roof is not hip. No slope involved.
If I remember correctly, it is the perimeter of the roof divided by the length of the non hip feature.
I am pretty sure it is going to be covered in the new course.

Perimeter: 45+30+45+30= 150
Length of non-hip feature: 12
150/12= 8% non-hip=Hip roof.
The wind mit form I have does that calculation for you.

Another one would be:
213/22=10.33% non-hip=Non hip roof.
Attached Files
File Type: pdf Percent.pdf (82.4 KB, 66 views)
File Type: pdf percent2.pdf (82.4 KB, 53 views)

Last edited by evandeven; 1/25/12 at 5:07 PM..
Reply With Quote
  #9  
Old 1/25/12, 5:34 PM
Michael C. Wagner Michael C. Wagner is offline
InterNACHI Member
 
Join Date: Nov 2009
Location: Lake Worth, FL
Posts: 103
Default Re: New form required for all homes closing after Feb 1

Quote:
Originally Posted by jmurray4 View Post
Starting last week we began using the new form unless the present form was specifically requested (for whatever reason).

New pricing is in effect as well....30% increase.

Still a deal when you figure that the Hip roof rating alone amy force you to measure the entire roof perimeter.

By the way, here's a free one for all.

The present form requires:
"Hip roof with no other roof shapes greater than 10% of the total building perimeter."


The NEW form requires:

"Hip roof with no other roof shapes greater than 10% of the total roof system perimeter." Yes, that's overhangs and rise / slope.


That's right, be prepared to measure the whole damn thing. Break out the tape measure....The floor plan from the property apraisers office will NOT work! Building perimeter is NOT roof system perimeter.
How about using the floor plan as a starting point? You can measure the roof overhangs (from the exterior wall to the fascia) and make the proper additions to the measurements on the floor plan. If the non-hip portion is close to 10% you might want to use a more accurate method. But when the non-hip portion is 20%, 30%, or more I would think using the floor plan as a starting point would be fine.
Reply With Quote
  #10  
Old 1/25/12, 9:52 PM
Jay C. Murray's Avatar
Jay C. Murray Jay C. Murray is offline
InterNACHI Member
 
Join Date: Jun 2009
Location: Port Saint Lucie, Fl
Posts: 784
Default Re: New form required for all homes closing after Feb 1

Quote:
Originally Posted by mwagner View Post
How about using the floor plan as a starting point? You can measure the roof overhangs (from the exterior wall to the fascia) and make the proper additions to the measurements on the floor plan. If the non-hip portion is close to 10% you might want to use a more accurate method. But when the non-hip portion is 20%, 30%, or more I would think using the floor plan as a starting point would be fine.
That will work in many cases to give validity to the Hip rating. However, be prepared to measure the roof in a close situation.



Your Home Inspection & Wind Mitigation Provider
Jay C. Murray
Florida Home & Insurance Inspector Chapter Board Member
Licensed General Contractor & Home Inspector
Serving Port St. Lucie, Ft. Pierce, Stuart, Palm City, Jensen Beach,
The Palm Beaches, & The Treasure Coast
Reply With Quote
  #11  
Old 1/26/12, 5:36 PM
Brian C. Hoagland Brian C. Hoagland is offline
InterNACHI Member
 
Join Date: Dec 2006
Location: Cocoa, FL
Posts: 3,410
Default Re: New form required for all homes closing after Feb 1

Quote:
Originally Posted by jmurray4 View Post
Starting last week we began using the new form unless the present form was specifically requested (for whatever reason).

New pricing is in effect as well....30% increase.

Still a deal when you figure that the Hip roof rating alone amy force you to measure the entire roof perimeter.

By the way, here's a free one for all.

The present form requires:
"Hip roof with no other roof shapes greater than 10% of the total building perimeter."


The NEW form requires:

"Hip roof with no other roof shapes greater than 10% of the total roof system perimeter." Yes, that's overhangs and rise / slope.


That's right, be prepared to measure the whole damn thing. Break out the tape measure....The floor plan from the property apraisers office will NOT work! Building perimeter is NOT roof system perimeter.
Jay, I don't think I understand the reference to overhangs generally the overhang for the soffit area adds to the perimeter, making the 10% a lesser value as related to the hip/ other calculation. Please clearify your viewpoint. Do you believe we should be measuring the leading edge of the roof at the fascia accounting for the linear footage of the pitched portion of the roof in the area of a gable? That is not clear to me from any training I have recieved in the past . However I can interpret the form that way. I don't want to, I don't think it was intended to be so, but I can see it.

Last edited by bhoagland; 1/26/12 at 5:42 PM..
Reply With Quote
  #12  
Old 1/26/12, 7:06 PM
Manny NIEBLAS Manny NIEBLAS is offline
InterNACHI Member
 
Join Date: Mar 2011
Location: Miami Lakes, Florida
Posts: 97
Default Re: New form required for all homes closing after Feb 1

Quote:
Originally Posted by evandeven View Post
If I remember correctly, it is the perimeter of the roof divided by the length of the non hip feature.
I am pretty sure it is going to be covered in the new course.

Perimeter: 45+30+45+30= 150
Length of non-hip feature: 12
150/12= 8% non-hip=Hip roof.
The wind mit form I have does that calculation for you.

Another one would be:
213/22=10.33% non-hip=Non hip roof.
That was a good idea make the form calculate % I added it to my forms



Manny Nieblas
A Full Service Inspection Company
Florida Licensed Home Inspector HI-165
C.M.I. Certified Master Inspector
Direct: 305.606.6797
Wind Mitigations, 4 Points, Roof Certifications
&
Home Inspection
Reply With Quote
  #13  
Old 1/26/12, 7:08 PM
Humberto Carvajal's Avatar
Humberto Carvajal Humberto Carvajal is offline
InterNACHI Member
 
Join Date: May 2005
Location: Homestead, FL
Posts: 819
Default Re: New form required for all homes closing after Feb 1

Manny was that difficult to do?





Humberto Carvajal Jr.
Florida State Property Inspections, LLC
Florida Home Inspector License# HI884
LEEDŽ Accredited Professional
Member USGBC South Florida Chapter

Reply With Quote
Need a home inspection in New Jersey? Check out InterNACHI's listing of New Jersey certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 1/26/12, 8:15 PM
Eric C. Van De Ven's Avatar
Eric C. Van De Ven Eric C. Van De Ven is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: South Florida
Posts: 2,323
Default Re: New form required for all homes closing after Feb 1

Quote:
Originally Posted by hcarvajal View Post
Manny was that difficult to do?
No, depending on which form designer you are using.
Adobe Professional uses java script, and you can find that almost anywhere.
Livecycle uses a different script, Formcalc, which is even easier.
Reply With Quote
  #15  
Old 1/26/12, 8:56 PM
Manny NIEBLAS Manny NIEBLAS is offline
InterNACHI Member
 
Join Date: Mar 2011
Location: Miami Lakes, Florida
Posts: 97
Default Re: New form required for all homes closing after Feb 1

Hey Bert just like Eric said I will call you tomorrow.



Manny Nieblas
A Full Service Inspection Company
Florida Licensed Home Inspector HI-165
C.M.I. Certified Master Inspector
Direct: 305.606.6797
Wind Mitigations, 4 Points, Roof Certifications
&
Home Inspection
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Cap and Trade: A License Required for your Home fcarrio Legislation, Licensing & Legal Issues for Inspectors 349 10/21/11 6:56 PM
Learn the Differences: Site-Built, Modular, Manufactured/Mobile Homes jsieg General Inspection Discussion 10 12/22/07 11:20 PM
PIC of State Rep and sponsor of new NACHI H.I. Bill in NH. gromicko Miscellaneous Discussion for Inspectors 53 8/30/06 5:58 PM
Common Defects List by Age of House trausch Inspection Education & Training 10 6/12/06 4:52 AM