Default Secondary Water Resistance

Wind Mitigation Form
8. Secondary Water Resistance

I am 99% certain that 2 layers of 15# felt doesn't meet this requirement, but thought I would post this just to make sure.

Do you agree?




Lee Curtis - Home Inspector
Revealing the Secrets of Your Home!
CGC1519195 - HI3222 - InterNACHI #11011001
Lee@CurtisHomeInspections.com
www.CurtisHomeInspections.com

www.CurtisHomeDesign.com
Reply With Quote
Need a home inspection in North Dakota? Check out InterNACHI's listing of North Dakota certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 5/11/11, 7:54 PM
John Shishilla, CMI's Avatar
John Shishilla, CMI John Shishilla, CMI is offline
InterNACHI Member
 
Join Date: Jul 2008
Location: Melbourne, FL
Posts: 5,191
Default Re: Secondary Water Resistance

I concur

"Self adhering polymer modified bitumen roofing underlayment applied directly to the sheathing or foam adhesive SWR barrier (not foamed on insulation) applied as a secondary means to protect the dwelling from water intrusion."



Visit the InterNACHI Awards page

John Shishilla
State of Fl Home Inspector #21
Certified Residential Contractor CRC1330745
Accredited Claims Adjuster (ACA)
Mold Assessor MRSA 1544
Pres of Fl Home & Insurance Inspectors Chptr
VP of Nachi Managment


Serving all of Melbourne, Palm Bay, Cocoa, Rockledge, Viera, Satellite Beach, Indian Harbor Beach, Indialantic and surrounding areas.

Honor Construction Inspection Service
www.honorconstruction.com

321-327-2950

Reply With Quote
  #3  
Old 5/11/11, 8:33 PM
Ken Ruppert Ken Ruppert is online now
InterNACHI Member
 
Join Date: Aug 2008
Location: Merritt Island, FL
Posts: 94
Default Re: Secondary Water Resistance

Yes. It's not peel and stick, so it's not swr.




Ken Ruppert
NACHI # 08081129
Florida Lic # HI162

www.happyhomeinspection.com
Reply With Quote
  #4  
Old 5/11/11, 8:52 PM
Dennis P. Quigley's Avatar
Dennis P. Quigley Dennis P. Quigley is offline
InterNACHI Member
 
Join Date: May 2010
Location: Vero Beach, Florida
Posts: 941
Default Re: Secondary Water Resistance

you are correct that it does not meet the requirements - Nor does a hot mop under tile
Reply With Quote
  #5  
Old 5/12/11, 4:18 PM
Michael J. Meeker, CMI's Avatar
Michael J. Meeker, CMI Michael J. Meeker, CMI is offline
InterNACHI Member
 
Join Date: Dec 2009
Location: South East Florida
Posts: 11,895
Default Re: Secondary Water Resistance

Nor does peel and stick on top of tintagged felt or just on the seams of the wood.

Only what is said on the form.





Wind Mitigation Specialist
FLORIDA LICENSED GENERAL CONTRACTOR
Call 954-922-0584 or E-Mail Me For The Best Wind Mitigation Inspection in Florida at a Great Price

www.homeinspection.meekerindustries.com
mike@meekerindustries.com
http://www.meekerindustries.com

I WILL FIGHT FOR YOUR RIGHTS SO YOU WILL NOT LOSE THEM.

Last edited by mmeeker; 5/12/11 at 5:17 PM..
Reply With Quote
  #6  
Old 5/12/11, 7:00 PM
John Shishilla, CMI's Avatar
John Shishilla, CMI John Shishilla, CMI is offline
InterNACHI Member
 
Join Date: Jul 2008
Location: Melbourne, FL
Posts: 5,191
Default Re: Secondary Water Resistance

Where does it say that seam sealed does not qualify?



Visit the InterNACHI Awards page

John Shishilla
State of Fl Home Inspector #21
Certified Residential Contractor CRC1330745
Accredited Claims Adjuster (ACA)
Mold Assessor MRSA 1544
Pres of Fl Home & Insurance Inspectors Chptr
VP of Nachi Managment


Serving all of Melbourne, Palm Bay, Cocoa, Rockledge, Viera, Satellite Beach, Indian Harbor Beach, Indialantic and surrounding areas.

Honor Construction Inspection Service
www.honorconstruction.com

321-327-2950

Reply With Quote
  #7  
Old 5/12/11, 7:09 PM
Michael J. Meeker, CMI's Avatar
Michael J. Meeker, CMI Michael J. Meeker, CMI is offline
InterNACHI Member
 
Join Date: Dec 2009
Location: South East Florida
Posts: 11,895
Default Re: Secondary Water Resistance

The plywood would not be covered then. Nowhere does it say on the form that covering the seams only is sufficient as far as I know. Wood is not waterproof.
I have been wrong before and I have yet to pay to hear anyone else's opinion on the matter. Have you seen it say somewhere that is acceptable. With the foam underneath it is like super gluing the deck to the trusses. It would not seem right that taping the seams would result in the same discount.





Wind Mitigation Specialist
FLORIDA LICENSED GENERAL CONTRACTOR
Call 954-922-0584 or E-Mail Me For The Best Wind Mitigation Inspection in Florida at a Great Price

www.homeinspection.meekerindustries.com
mike@meekerindustries.com
http://www.meekerindustries.com

I WILL FIGHT FOR YOUR RIGHTS SO YOU WILL NOT LOSE THEM.

Last edited by mmeeker; 5/12/11 at 7:24 PM..
Reply With Quote
  #8  
Old 5/12/11, 8:12 PM
Lawrence W. Losciale's Avatar
Lawrence W. Losciale Lawrence W. Losciale is offline
InterNACHI Member
 
Join Date: May 2010
Location: Inverness, Florida
Posts: 648
Default Re: Secondary Water Resistance

I believe John is right. I've taken two differant courses that pointed out that seam sealing is acceptable. Also the foaming is meant more to seal the seams than for hold down. I see glue and adhiesive caulk for uplift resistance around here.
Reply With Quote
  #9  
Old 5/12/11, 9:03 PM
Michael J. Meeker, CMI's Avatar
Michael J. Meeker, CMI Michael J. Meeker, CMI is offline
InterNACHI Member
 
Join Date: Dec 2009
Location: South East Florida
Posts: 11,895
Default Re: Secondary Water Resistance

If anyone has answers please post them.





Wind Mitigation Specialist
FLORIDA LICENSED GENERAL CONTRACTOR
Call 954-922-0584 or E-Mail Me For The Best Wind Mitigation Inspection in Florida at a Great Price

www.homeinspection.meekerindustries.com
mike@meekerindustries.com
http://www.meekerindustries.com

I WILL FIGHT FOR YOUR RIGHTS SO YOU WILL NOT LOSE THEM.
Reply With Quote
  #10  
Old 5/12/11, 9:25 PM
John Shishilla, CMI's Avatar
John Shishilla, CMI John Shishilla, CMI is offline
InterNACHI Member
 
Join Date: Jul 2008
Location: Melbourne, FL
Posts: 5,191
Default Re: Secondary Water Resistance

Quote:
Originally Posted by mmeeker View Post
If anyone has answers please post them.

The three manuals I have say it is good. Some even use concrete(ie, condo) as SWR. The five classes I took all said the same, modified bitumen peel and stick tape(4") is good. I even built a home with it on the decking.



Visit the InterNACHI Awards page

John Shishilla
State of Fl Home Inspector #21
Certified Residential Contractor CRC1330745
Accredited Claims Adjuster (ACA)
Mold Assessor MRSA 1544
Pres of Fl Home & Insurance Inspectors Chptr
VP of Nachi Managment


Serving all of Melbourne, Palm Bay, Cocoa, Rockledge, Viera, Satellite Beach, Indian Harbor Beach, Indialantic and surrounding areas.

Honor Construction Inspection Service
www.honorconstruction.com

321-327-2950

Reply With Quote
  #11  
Old 5/12/11, 9:36 PM
Michael J. Meeker, CMI's Avatar
Michael J. Meeker, CMI Michael J. Meeker, CMI is offline
InterNACHI Member
 
Join Date: Dec 2009
Location: South East Florida
Posts: 11,895
Default Re: Secondary Water Resistance

Good enough for me. Thanks for sharing.





Wind Mitigation Specialist
FLORIDA LICENSED GENERAL CONTRACTOR
Call 954-922-0584 or E-Mail Me For The Best Wind Mitigation Inspection in Florida at a Great Price

www.homeinspection.meekerindustries.com
mike@meekerindustries.com
http://www.meekerindustries.com

I WILL FIGHT FOR YOUR RIGHTS SO YOU WILL NOT LOSE THEM.
Reply With Quote
  #12  
Old 5/12/11, 9:40 PM
Humberto Carvajal's Avatar
Humberto Carvajal Humberto Carvajal is offline
InterNACHI Member
 
Join Date: May 2005
Location: Homestead, FL
Posts: 2,166
Default Re: Secondary Water Resistance

John, am I correct in saying that this SWR does NOT apply to Townhomes and condominiums since they are excluded from the definition of site built single family residences? Also low sloped or built up roofs are excluded from these mitigation requirements?





Humberto Carvajal Jr.
Florida State Property Inspections, LLC
Florida Home Inspector License# HI884
LEED® Accredited Professional
Member USGBC South Florida Chapter

Reply With Quote
  #13  
Old 5/12/11, 9:57 PM
Dennis J. Bonner's Avatar
Dennis J. Bonner Dennis J. Bonner is offline
InterNACHI Member
 
Join Date: Mar 2009
Location: Deerfield Beach, Florida
Posts: 1,183
Default Re: Secondary Water Resistance

peel and stick on seems applied directly to deck(thats key), or, foamseal.. end of discussion



Florida Insurance Inspections
Serving Dade, Broward, and Palm Beach Counties since 2001.
Dennis J. Bonner, G.C
CGC-1514215, HI-256

Dade: (305)759-4587
Palm Beach: (561) 471-8911
Broward: (954) 566-2822

http://www.floridainsuranceinspections.com

Florida State Certified General Contractor
Certified Master Inspector
Reply With Quote
Need a home inspection in North Dakota? Check out InterNACHI's listing of North Dakota certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 5/12/11, 10:02 PM
John Shishilla, CMI's Avatar
John Shishilla, CMI John Shishilla, CMI is offline
InterNACHI Member
 
Join Date: Jul 2008
Location: Melbourne, FL
Posts: 5,191
Default Re: Secondary Water Resistance

Quote:
Originally Posted by hcarvajal View Post
John, am I correct in saying that this SWR does NOT apply to Townhomes and condominiums since they are excluded from the definition of site built single family residences? Also low sloped or built up roofs are excluded from these mitigation requirements?

I write 1802s on townhomes and condos all the time. I agree that a low slope roof with modified bit would just be two layers of roofing, not secondary. One could argue the same with at tile roof. The underlayment is a primary. I have not seen these written anywhere that I can remember.



Visit the InterNACHI Awards page

John Shishilla
State of Fl Home Inspector #21
Certified Residential Contractor CRC1330745
Accredited Claims Adjuster (ACA)
Mold Assessor MRSA 1544
Pres of Fl Home & Insurance Inspectors Chptr
VP of Nachi Managment


Serving all of Melbourne, Palm Bay, Cocoa, Rockledge, Viera, Satellite Beach, Indian Harbor Beach, Indialantic and surrounding areas.

Honor Construction Inspection Service
www.honorconstruction.com

321-327-2950

Reply With Quote
  #15  
Old 5/12/11, 10:07 PM
Humberto Carvajal's Avatar
Humberto Carvajal Humberto Carvajal is offline
InterNACHI Member
 
Join Date: May 2005
Location: Homestead, FL
Posts: 2,166
Default Re: Secondary Water Resistance

Oh, I believe, cement and clay tile roofs are also exempt from the requirement.





Humberto Carvajal Jr.
Florida State Property Inspections, LLC
Florida Home Inspector License# HI884
LEED® Accredited Professional
Member USGBC South Florida Chapter

Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
What's this video worth? jtedesco1 Inspection Education & Training 5 4/18/08 10:24 AM
New Washington Legislation Submitted gdomagala Legislation, Licensing, Ethics & Legal Issues for Inspectors 294 2/10/08 2:20 AM
Need Help On Chimney Liners Nick Scibetta Exterior Inspections 13 1/11/06 10:53 PM

All times are GMT -4. The time now is 10:56 AM.
no new posts