Default Improper insulation causes roof sheathing damage.

Its always good to actualy see the results of poor work. This home was only a few years old and the plumbing vent was inside the small attic space.
I noted unusual wavyness on the roof, but it was too steep to walk. SO instead I pulled down a little insulation.
No air gap for ventilation because they installed it wrong, and the whole area was covered in mold. The osb was also starting to delam. Suprising enough it was not damp, but must have been at times. My foot might have gone thru if I could have walked on the roof.
I guess it goes to show you what can happen to cathedral ceilings if they can't breath.
Attached Thumbnails
improper-insulation-causes-roof-sheathing-damage-1.jpg   improper-insulation-causes-roof-sheathing-damage-2.jpg  




Infraspection Institute Level 1 Certified Infrared Thermographer

Fogarty Inspection Services Group of Knoxville TN

Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.

865-256-5397

www.homeinspectorknoxville.com

www.moldandradon.com

www.thermal-inspection.net

www.commercial-building-inspector.net
Reply With Quote
Need a home inspection in Missouri? Check out InterNACHI's listing of Missouri certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 8/23/10, 11:20 PM
Tom Leahy Tom Leahy is offline
InterNACHI Member
 
Join Date: Dec 2009
Location: Arlington, Texas
Posts: 358
Default Re: Improper insulation causes roof sheathing damage.

Sean, just to make sure I understand what happened here, no vent baffle was installed between insulation and roof deck, blocking the soffit vent. Plumbing vent terminating in attic and put it all together and you get this mess.

Looks like you went beyond SOP and pulled the insulation down to get the visual you needed.

Good pics, Thanks



Fort Worth Home Inspector
Dallas Home Inspector
Reply With Quote
  #3  
Old 8/24/10, 7:39 AM
Sean Fogarty's Avatar
Sean Fogarty Sean Fogarty is offline
InterNACHI Member
 
Join Date: Sep 2009
Location: Somewhere in Knoxville TN flipping breakers
Posts: 2,267
Default Re: Improper insulation causes roof sheathing damage.

You are correct. If the whole roof is this bad I just saved the buyer thousands of dollars by going beyond the sop.
THe houses on either side of me had the same noticable roof wavyness.
All rental cabins.




Infraspection Institute Level 1 Certified Infrared Thermographer

Fogarty Inspection Services Group of Knoxville TN

Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.

865-256-5397

www.homeinspectorknoxville.com

www.moldandradon.com

www.thermal-inspection.net

www.commercial-building-inspector.net
Reply With Quote
  #4  
Old 8/24/10, 7:50 AM
Wayne B. Wilson's Avatar
Wayne B. Wilson Wayne B. Wilson is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Powell, Tn
Posts: 8,226
Default Re: Improper insulation causes roof sheathing damage.

Good find, just another example of fine unsupervised workmanship. No building inspector in that area till a couple of years ago.



Wayne Wilson
East TN Home Inspections LLC
Knoxville, Oak Ridge, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.
865-256-1490

http://site.myhomeinspection.net

Reply With Quote
  #5  
Old 8/25/10, 7:12 AM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Improper insulation causes roof sheathing damage.

Quote:
Originally Posted by sfogarty View Post
Its always good to actualy see the results of poor work. This home was only a few years old and the plumbing vent was inside the small attic space.
I noted unusual wavyness on the roof, but it was too steep to walk. SO instead I pulled down a little insulation.
No air gap for ventilation because they installed it wrong, and the whole area was covered in mold. The osb was also starting to delam. Suprising enough it was not damp, but must have been at times. My foot might have gone thru if I could have walked on the roof.
I guess it goes to show you what can happen to cathedral ceilings if they can't breath.

Correct the 2 much larger flaws in your pictures, the continuous moisture source of the open vent and the cathredral ceiling insulation with NO ATTEMPT AT AN AIR BARRIER, and the moisture problems on the sheahing will disappear. Adding ventilation to this setup after correcting the vent situation will increase energy costs!!
Reply With Quote
  #6  
Old 9/11/10, 9:38 PM
ROBERT V. YOUNG's Avatar
ROBERT V. YOUNG ROBERT V. YOUNG is online now
InterNACHI Member
 
Join Date: Mar 2010
Location: Montreal.
Posts: 5,022
Default Re: Improper insulation causes roof sheathing damage.

They make baffle vents for that very purpose.They work great.I see more and more of what you are showing me and home owners screening at high energy bills.They do not realize there roof is degrading.Once the problem is solved it a much lower energy cost and a dryer environment.
No gabble end vents?
Reply With Quote
  #7  
Old 9/11/10, 10:13 PM
Sean Fogarty's Avatar
Sean Fogarty Sean Fogarty is offline
InterNACHI Member
 
Join Date: Sep 2009
Location: Somewhere in Knoxville TN flipping breakers
Posts: 2,267
Default Re: Improper insulation causes roof sheathing damage.

No gable vents. No room with the style of ceiling




Infraspection Institute Level 1 Certified Infrared Thermographer

Fogarty Inspection Services Group of Knoxville TN

Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.

865-256-5397

www.homeinspectorknoxville.com

www.moldandradon.com

www.thermal-inspection.net

www.commercial-building-inspector.net
Reply With Quote
  #8  
Old 9/12/10, 5:02 AM
ROBERT V. YOUNG's Avatar
ROBERT V. YOUNG ROBERT V. YOUNG is online now
InterNACHI Member
 
Join Date: Mar 2010
Location: Montreal.
Posts: 5,022
Default Re: Improper insulation causes roof sheathing damage.

Sorry Sean.I understand Sorry I did not read you where in small attic space I just surmised by the pics it was gambrel. . I assumed,Man I walked into that one.Any vents at all to release the moisture?
Reply With Quote
  #9  
Old 9/15/10, 4:12 PM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 3,417
Send a message via ICQ to kshepard
Default Re: Improper insulation causes roof sheathing damage.

Quote:
Originally Posted by sfogarty View Post
Its always good to actualy see the results of poor work. This home was only a few years old and the plumbing vent was inside the small attic space.
I noted unusual wavyness on the roof, but it was too steep to walk. SO instead I pulled down a little insulation.
No air gap for ventilation because they installed it wrong, and the whole area was covered in mold. The osb was also starting to delam. Suprising enough it was not damp, but must have been at times. My foot might have gone thru if I could have walked on the roof.
I guess it goes to show you what can happen to cathedral ceilings if they can't breath.
1. A plumbing vent should terminate at the exterior to prevent sewer gas from entering the living space, not because it's a big source of moisture.

2. That's an attic space, not a cathedral ceiling. The insulation should be installed in the floor, not between the rafters and the attic space vented to help keep the roof cooler.. Basically, with no attic venting and insulation installed between rafters, the attic is part of the conditioned space and should have a minimum of 3.5 air changes per hour, just like the rest of the living space, to prevent moisture levels from becoming too high.

3. In cathedral ceilings, the air space created by the baffles is to cool the roof and help prevent premature failure of the roof-covering material, especially comp shingles, due to excessively high temperatures. Moisture is a separate issue.

4. Heat wouldn't make OSB delaminate, but moisture would. The source of moisture should be found and corrected.




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
InterNACHI Director of International Development
Director of Green Building

EXPERT WITNESS SERVICE
Conventional and Log homes

(303) 717-8940
Reply With Quote
  #10  
Old 9/15/10, 5:27 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,342
Send a message via Yahoo to jfunderburk
Default Re: Improper insulation causes roof sheathing damage.

Quote:
Originally Posted by kshepard View Post
2. That's an attic space, not a cathedral ceiling. The insulation should be installed in the floor, not between the rafters and the attic space vented to help keep the roof cooler.. Basically, with no attic venting and insulation installed between rafters, the attic is part of the conditioned space and should have a minimum of 3.5 air changes per hour, just like the rest of the living space, to prevent moisture levels from becoming too high.
I agree. The insulation on the sheathing is improper. They've created an "unventilated attic". The IRC addresses unventilated attics and this one is definitely wrong. The insulation on the roof sheathing is supposed to be closed cell foam and there should be no insulation on the ceiling, if that's what they were trying to do. FUBAR.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #11  
Old 9/15/10, 5:47 PM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 3,417
Send a message via ICQ to kshepard
Default Re: Improper insulation causes roof sheathing damage.

I'm leery of the closed cell foam on the underside of the roof sheathing.
If the roof leaks, how will the occupant know? The leakage won't be able to get past the foam and will be absorbed by the roof sheathing, which will decay quickly if it can't dry to the inside and dries only slowly to the outside.
Also, heat will dissipate more slowly, since the roof can't dump heat to the attic. This may cause comp shingles and underlayment to fail prematurely.




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
InterNACHI Director of International Development
Director of Green Building

EXPERT WITNESS SERVICE
Conventional and Log homes

(303) 717-8940
Reply With Quote
  #12  
Old 9/15/10, 10:53 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,342
Send a message via Yahoo to jfunderburk
Default Re: Improper insulation causes roof sheathing damage.

Quote:
Originally Posted by kshepard View Post
I'm leery of the closed cell foam on the underside of the roof sheathing.
If the roof leaks, how will the occupant know? The leakage won't be able to get past the foam and will be absorbed by the roof sheathing, which will decay quickly if it can't dry to the inside and dries only slowly to the outside.
Also, heat will dissipate more slowly, since the roof can't dump heat to the attic. This may cause comp shingles and underlayment to fail prematurely.
I'm with you 100%, but that's what it says.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #13  
Old 9/15/10, 11:02 PM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 3,417
Send a message via ICQ to kshepard
Default Re: Improper insulation causes roof sheathing damage.

Yep, certain factions of the green building movement have been promoting it. Great ideas aren't always great ideas.




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
InterNACHI Director of International Development
Director of Green Building

EXPERT WITNESS SERVICE
Conventional and Log homes

(303) 717-8940
Reply With Quote
Need a home inspection in Missouri? Check out InterNACHI's listing of Missouri certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 9/17/10, 5:52 AM
ROBERT V. YOUNG's Avatar
ROBERT V. YOUNG ROBERT V. YOUNG is online now
InterNACHI Member
 
Join Date: Mar 2010
Location: Montreal.
Posts: 5,022
Default Re: Improper insulation causes roof sheathing damage.

Thank you Ken. I was totally confused by the pic,s. They are not explaining as to what is being described to how the roof would look as a cathedral ceiling.I should have pointed this out to hm in the first place.
Thank you for your observations.
You are right in all your observations and conclusions.



montrealbuildinginspectionservice.com
montreal-home-inspection-services.com
home-inspections-montreal.com
homeinspectionsservicesmontreal.com
ROBERT YOUNG'S MONTREAL HOME INSPECTION SERVICE INC.
Certified Inspecteur Professionnel Certifié en Bâtiment membre de InterNACHI ACHI , Chapters - OntarioAchi et du M.I.C.Q (CPI) - (CHI)
OFFICE (514) 489-1887 MOBILE (514) 441-3732 TOLL FREE 1- 855-819-1816
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Newer roof with wet sheathing jbraun General Inspection Discussion 9 3/6/10 7:53 AM
Insulating Your House from CMHC mkyriacou Canadian Inspectors 10 2/14/10 3:50 PM
Cracked shingles pwigle Exterior Inspections 54 4/23/09 11:52 PM
Isomere insulation and roof ventilation hvanderbeek General Inspection Discussion 5 3/10/06 2:36 PM
Massachusetts Board of Registration of Home Inspectors jtedesco1 Legislation, Licensing & Legal Issues for Inspectors 0 2/14/06 3:38 AM


All times are GMT -4. The time now is 11:34 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts