Default low slope roof

What do you think the slope of this lower roof is?

The builder says its within the range where 2 layers of 15 lb felt can be used under the shingles.
Attached Thumbnails
low-slope-roof-007.jpg  



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
License NC2449 and SC1597
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
Need a home inspection in Maine? Check out InterNACHI's listing of Maine certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 9/22/11, 4:25 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,092
Default Re: low slope roof

Quote:
Originally Posted by bking View Post
What do you think the slope of this lower roof is?

The builder says its within the range where 2 layers of 15 lb felt can be used under the shingles.
My Android roof pitch app says Too Low

It may be OK

See this mfg. recommendation for installation on low pitch roofs.

http://www.iko.com/misc/CasmaPdf/16-LowSlopedRoofs.PDF

Quote:
The underlay can be improved in one of two ways; two plies of asphalt saturated felt, or
one ply of self-adhering modified asphalt membrane may be used. Should water from
wind-driven heavy rains sneak past the shingles, the underlay can now provide a
secondary water shedding layer......................................

Despite using quality materials and following all of these application recommendations, a
low slope roof is a severe exposure condition for asphalt roofing shingles. In Canadian
latitudes and climates, shingles on low slope roofs typically age more rapidly than
steeper roofs, and rarely last longer than fifteen years



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
  #3  
Old 9/22/11, 4:31 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,927
Default Re: low slope roof

Make sure they dump the upper gutter on the lower roof (like they do around here) and see what happens!

Wonderful job security!



"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein

David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #4  
Old 9/22/11, 4:36 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,631
Default Re: low slope roof

Quote:
What do you think the slope of this lower roof is?
From here less than 4/12
Quote:
The builder says its within the range where 2 layers of 15 lb felt can be used under the shingles.
What does manufacturer of shingles he's using say?



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #5  
Old 9/22/11, 4:37 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,631
Default Re: low slope roof

In order to achieve fire-resistant ratings (Class A or C), an underlayment must be used regardless of the type of shingle being installed.

A minimum of 2 layers of felt or 60lbs of base (2 layers of 30lb) is required for roofs with slopes less than 4/12. In such cases, the application must meet the requirements for low slope roofs.

Alternatives for 2 layers would be 1 layer ice and water shield.



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #6  
Old 9/22/11, 7:28 PM
bdoles2's Avatar
bdoles2 bdoles2 is offline
Active Poster
 
Join Date: Aug 2006
Location: Atlanta, GA
Posts: 3,071
Please Note: bdoles2 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: low slope roof

In most cases it's not only the additional felt, but it's also in the modification of the shingle exposure. Reducing the shingle exposure can result in a so-called "triple coverage".

I've done this on several projects and have never had an issue. Many manufacturers explain this process in their training manuals.

But again, I'm in the land of not having to deal with "ice dams".
Reply With Quote
  #7  
Old 9/22/11, 9:27 PM
ROBERT V. YOUNG's Avatar
ROBERT V. YOUNG ROBERT V. YOUNG is offline
InterNACHI Member
 
Join Date: Mar 2010
Location: Montreal.
Posts: 5,050
Default Re: low slope roof

2006 IRC code
R905.2.2 Slope
Asphalt shingles shall be used only on roof slopes of 2 units vertical in 12
units horizontal (2:12) or greater. For roof slopes from 2 units vertical in 12
units horizontal (2:12) up to 4 units vertical in 12 units horizontal (4:12), double
underlayment application is required in accordance with Section R905.2.7
Look up 2009. May have changed.
International Residential Code (IRC) 2006 | Section R905
http://www.lsuagcenter.com/NR/rdonly...odeHIGHRES.pdf



montrealbuildinginspectionservice.com
montreal-home-inspection-services.com
home-inspections-montreal.com
homeinspectionsservicesmontreal.com
ROBERT YOUNG'S MONTREAL HOME INSPECTION SERVICE INC.
Certified Inspecteur Professionnel Certifié en Bâtiment membre de InterNACHI ACHI , Chapters - OntarioAchi et du M.I.C.Q (CPI) - (CHI)
OFFICE (514) 489-1887 MOBILE (514) 441-3732 TOLL FREE 1- 855-819-1816
Reply With Quote
  #8  
Old 10/15/11, 2:10 AM
Nick Gromicko's Avatar
Nick Gromicko Nick Gromicko is offline
InterNACHI Member
 
Join Date: Aug 2002
Location: Valley Forge, PA
Posts: 30,614
Default Re: low slope roof

The simplest solution would be to install a standing-seam metal roof over it. Many (not all) metal roofs are fine at a 1:12 pitch pitch or even less. Snap-Loc 24 can be installed at a nearly-level 1/4:12 pitch!



Nick Gromicko, Certified Master Inspector

Find a Home Inspector
"Just as iron sharpens iron, one man sharpens another." Proverbs 27:17

Last edited by gromicko; 10/15/11 at 2:31 AM..
Reply With Quote
  #9  
Old 10/15/11, 2:16 AM
Joseph Hagarty,  CMI's Avatar
Joseph Hagarty, CMI Joseph Hagarty,  CMI is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Parkesburg, PA
Posts: 5,636
Default Re: low slope roof

Less than 3 in 12
Low slope materials required...
If he can convince a Municipal Building Inspector to accept
(Which it appears to be)
what is the question?
?



Joseph P. Hagarty
joseph.hagarty@comcast.net
Main Line Inspections, Inc.
Phone: 610-399-3675
Email: MainLineHI@comcast.net

http://pa.nachi.org/mainlinepa/about.html
http://www.householdinspector.com

National President / NACHI (2003-2004)
NACHI Education Committee Member
Reply With Quote
  #10  
Old 10/15/11, 2:20 AM
Nick Gromicko's Avatar
Nick Gromicko Nick Gromicko is offline
InterNACHI Member
 
Join Date: Aug 2002
Location: Valley Forge, PA
Posts: 30,614
Default Re: low slope roof

Another issue: It appears the builder ran out of StraightFlash (the correct product to flash the top and sides of the windows when using a house wrap)...and switched to mere Tyvek seam tape to flash 3 of the windows. This is incorrect.

Optimally the sills would be done with FlexWrap, but a roll is really expensive (I bought a roll today)... so don't ever expect to find it on a spec home.



Nick Gromicko, Certified Master Inspector

Find a Home Inspector
"Just as iron sharpens iron, one man sharpens another." Proverbs 27:17

Last edited by gromicko; 10/15/11 at 3:13 AM..
Reply With Quote
  #11  
Old 4/12/12, 3:53 AM
John Mathew John Mathew is offline
New User
 
Join Date: Apr 2012
Posts: 1
Please Note: John Mathew is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: low slope roof

You can check with Tradition Roofing & Exteriors. Who are in roofing & exteriors for more than 15 years providing quality work and excellent customer service.
Reply With Quote
  #12  
Old 4/12/12, 2:32 PM
Jeffery L. Haynes Jeffery L. Haynes is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Concord, NC
Posts: 3,495
Default Re: low slope roof

Bruce,

If this is NC then check the NCRC and go from there because that is all the builder has to conform too....that and the manufacturer which will ultimately state to adhere to local and state codes.
Reply With Quote
  #13  
Old 4/12/12, 4:36 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: low slope roof

Hard to say for sure. I'd put it in the report, make the buyer aware of the requirements and put the burden on the builder to prove it is greater than 2 in 12.







“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
Need a home inspection in Maine? Check out InterNACHI's listing of Maine certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 4/12/12, 6:08 PM
ROBERT V. YOUNG's Avatar
ROBERT V. YOUNG ROBERT V. YOUNG is offline
InterNACHI Member
 
Join Date: Mar 2010
Location: Montreal.
Posts: 5,050
Default Re: low slope roof

Quote:
Originally Posted by gromicko View Post
Another issue: It appears the builder ran out of StraightFlash (the correct product to flash the top and sides of the windows when using a house wrap)...and switched to mere Tyvek seam tape to flash 3 of the windows. This is incorrect.

Optimally the sills would be done with FlexWrap, but a roll is really expensive (I bought a roll today)... so don't ever expect to find it on a spec home.

Nice observation oh great one.



montrealbuildinginspectionservice.com
montreal-home-inspection-services.com
home-inspections-montreal.com
homeinspectionsservicesmontreal.com
ROBERT YOUNG'S MONTREAL HOME INSPECTION SERVICE INC.
Certified Inspecteur Professionnel Certifié en Bâtiment membre de InterNACHI ACHI , Chapters - OntarioAchi et du M.I.C.Q (CPI) - (CHI)
OFFICE (514) 489-1887 MOBILE (514) 441-3732 TOLL FREE 1- 855-819-1816
Reply With Quote
  #15  
Old 4/12/12, 6:35 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,207
Default Re: low slope roof

I basically reported this during a predrywall inspection as irregardless of actual measured slope or code, this will leak over time if proper low slope methods are not installed. The buyer and I convinced the builder to do what I rcommended and they did!

Sometimes the code angle will hurt your client since the builder can refuse to do something if it actually meets code. Many roofs like this will meet code and leak.
I guess I just have the right way of communicating because I get lots of things done for my clients.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
License NC2449 and SC1597
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Built Up Roof Narrative jscaparo Roofing Inspections 20 7/2/11 1:18 PM
Retro Roof Area and Slope Calculator edeandres Florida Inspectors 0 6/12/11 3:20 PM
Please post questions about anything having to do with roofing kshepard Exterior Inspections 165 6/17/09 11:47 AM
Roof deck question wdecker Exterior Inspections 3 11/17/08 10:17 PM
Chimney flashing photo's needed: brick and stone done correctly kshepard Exterior Inspections 6 10/13/07 8:10 AM


All times are GMT -4. The time now is 8:46 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts