Default Ridge Cap Shingles over Ridge Vent

I have come across a few roofs where the roofer laid ridge cap shingles continuously over the ridge vent without stopping. The shingles went up and over the end of the ridge vent , across and down the other end. I am looking for some technical literature approving this method. I found the attached photo on the internet showing this issue.
Attached Thumbnails
ridge-cap-shingles-over-ridge-vent-gu60-01_lg.jpg  





Randy Mayo, P.E.

573-201-8162

www.rlmengineers.com
Reply With Quote
Need a home inspection in Arkansas? Check out InterNACHI's listing of Arkansas certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 12/28/12, 11:54 AM
kwood kwood is offline
Banned
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 11,816
Please Note: kwood is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Ridge Cap Shingles over Ridge Vent

Randy I don't think you will!
Reply With Quote
  #3  
Old 12/28/12, 11:56 AM
Juan C. Jimenez Juan C. Jimenez is offline
InterNACHI Member
 
Join Date: Jan 2012
Location: central va
Posts: 6,209
Default Re: Ridge Cap Shingles over Ridge Vent

I see it all the time. Its a non issue for me.

http://www.airvent.com/pdf/installat...dRVInstSht.pdf



Juan Jimenez
A House on a Rock Home Inspections LLC
God. Family. Home.
804-269-4321
Richmond Home Inspector
Chesterfield Home Inspector
Petersburg Home Inspector
Richmond Radon Testing


Reply With Quote
  #4  
Old 12/28/12, 12:24 PM
Marcel R. Cyr, CMI's Avatar
Marcel R. Cyr, CMI Marcel R. Cyr, CMI is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 25,242
Default Re: Ridge Cap Shingles over Ridge Vent

Used and installed like the picture many times Randy.

http://www.airvent.com/homeowner/pro...ngleVent.shtml
Reply With Quote
  #5  
Old 12/28/12, 2:00 PM
Eric C. Van De Ven's Avatar
Eric C. Van De Ven Eric C. Van De Ven is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: The Treasure Coast
Posts: 5,941
Default Re: Ridge Cap Shingles over Ridge Vent

You can do it that way. I didn't when I did mine, as I ran the ridge vent all the way across the roof and to the end. I just didn't cut the decking at the ends or at the valley connection. They make a piece that fits in the end to seal it.



Reply With Quote
  #6  
Old 12/28/12, 2:14 PM
kwood kwood is offline
Banned
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 11,816
Please Note: kwood is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Ridge Cap Shingles over Ridge Vent

Point being that Randy is saying is you will not find it as a standard way of doing it.
You must follow the exact instructions in order to have a warranty.
The Instructions clearly show how it is to be installed and requires an end cap like Eric is pointing out.
Small print under warranty of 5 years
ridge vent has been installed in strict accordance with Air Vent's written installation instructions

Last edited by kwood; 12/28/12 at 2:18 PM..
Reply With Quote
  #7  
Old 12/28/12, 2:29 PM
Randy Mayo, P.E.'s Avatar
Randy Mayo, P.E. Randy Mayo, P.E. is offline
InterNACHI Member
 
Join Date: May 2006
Location: Rolla, MO
Posts: 723
Default Re: Ridge Cap Shingles over Ridge Vent

Here is a video link showing the ridge cap shingles going up over and down over the ends of the ridge vent. https://www.youtube.com/watch?v=LRljTkjF5n4





Randy Mayo, P.E.

573-201-8162

www.rlmengineers.com
Reply With Quote
  #8  
Old 12/28/12, 2:30 PM
Eric C. Van De Ven's Avatar
Eric C. Van De Ven Eric C. Van De Ven is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: The Treasure Coast
Posts: 5,941
Default Re: Ridge Cap Shingles over Ridge Vent

Quote:
Originally Posted by kwood View Post
Point being that Randy is saying is you will not find it as a standard way of doing it.
You must follow the exact instructions in order to have a warranty.
The Instructions clearly show how it is to be installed and requires an end cap like Eric is pointing out.
Small print under warranty of 5 years
ridge vent has been installed in strict accordance with Air Vent's written installation instructions
It may be a local requirement to prevent the ends from coming up, although I didn't see that anywhere on my instructions.

http://www.airvent.com/pdf/literatur...intakevent.pdf

http://www.airvent.com/homeowner/pro...dgeVents.shtml



Reply With Quote
  #9  
Old 12/28/12, 2:35 PM
Eric C. Van De Ven's Avatar
Eric C. Van De Ven Eric C. Van De Ven is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: The Treasure Coast
Posts: 5,941
Default Re: Ridge Cap Shingles over Ridge Vent

Quote:
Originally Posted by rmayo View Post
Here is a video link showing the ridge cap shingles going up over and down over the ends of the ridge vent. https://www.youtube.com/watch?v=LRljTkjF5n4
That is a pretty poorly installed roof! I saw at least ten popped nails in the field.

Here is a better video. At the end, they show the capped off edge.

https://www.youtube.com/watch?featur...OfC5o4zeM&NR=1



Reply With Quote
  #10  
Old 12/28/12, 2:51 PM
kwood kwood is offline
Banned
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 11,816
Please Note: kwood is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Ridge Cap Shingles over Ridge Vent

I have seen poped nails also and I will dig up a picture of what we see here. This ridge cap goes all the way to the edge and has an end cap.
I only mention to put silicon on the exposed nails but we don't have the wind secure requirement here.
Attached Thumbnails
ridge-cap-shingles-over-ridge-vent-479-river-rd-sept-6-2012-122.jpg  

Last edited by kwood; 12/28/12 at 2:57 PM..
Reply With Quote
  #11  
Old 12/28/12, 3:17 PM
Marcel R. Cyr, CMI's Avatar
Marcel R. Cyr, CMI Marcel R. Cyr, CMI is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 25,242
Default Re: Ridge Cap Shingles over Ridge Vent

There are various types of ridge vents all with there own instructions for installation.
The one in the picture in the first post is using this.

No end caps used with this type and running it to the end of the gable end is a preference of the installer.
In the case of the picture, they stopped short and still works. It now becomes an esthetic thing.
Other types, you run to the gable or stop short of and install a cap by the manufacturer.
I have installed both ways.
Reply With Quote
  #12  
Old 12/28/12, 3:25 PM
kwood kwood is offline
Banned
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 11,816
Please Note: kwood is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Ridge Cap Shingles over Ridge Vent

If it is that type Marcel than I would agree! I can't tell from the picture.
Reply With Quote
  #13  
Old 12/28/12, 5:26 PM
Eric C. Van De Ven's Avatar
Eric C. Van De Ven Eric C. Van De Ven is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: The Treasure Coast
Posts: 5,941
Default Re: Ridge Cap Shingles over Ridge Vent

Quote:
Originally Posted by mcyr View Post
There are various types of ridge vents all with there own instructions for installation.
[COLOR=#0000ff]The one in the picture in the first post is using this.
No end caps used with this type and running it to the end of the gable end is a preference of the installer.
In the case of the picture, they stopped short and still works. It now becomes an esthetic thing.
Other types, you run to the gable or stop short of and install a cap by the manufacturer.
I have installed both ways.
Is that the type that uses no plastic cap, just the mesh? If so, it is inferior to the ones that use the plastic supported piece, then the mesh inside.
I inspected a home recently and one of the complaints from the tenants, was the fact that during the summer, the cold water was hot for some time and the a/c never worked. When I got into the attic, there were all the plumbing pipes. The insulation was also run all the way up to the end of the attic, blocking every single soffit vent. Then, the ridge vent was installed like the one in the picture and of the type you show in your picture.

In some areas, they actually shingled over the cut-out in the roof.

The overheating of the attic, probably had something to do with the last two pictures, which might have something to do with the a/c issue.

I moved the insulation out of the way to allow the air to at least flow into the attic. I recommended that the ridge vent be replaced and installed properly, there was only about 10 feet of vent that might be functioning, and to replace the duct work. This home had both quiet flex and owl-flex duct work, and I suspect, at one time, polybutylene plumbing that had been replaced.

This inspection was done on a cool day in the morning and the attic temperature was already at 100 degrees.
Attached Thumbnails
ridge-cap-shingles-over-ridge-vent-rahbani2-23-large-.jpg (Large).jpg
Views:	449
Size:	54.9 KB
ID:	61241   ridge-cap-shingles-over-ridge-vent-rahbani2-17-large-.jpg (Large).jpg
Views:	892
Size:	42.7 KB
ID:	61242   ridge-cap-shingles-over-ridge-vent-rahbani2-20-large-.jpg (Large).jpg
Views:	622
Size:	56.5 KB
ID:	61243   ridge-cap-shingles-over-ridge-vent-rahbani2-11-large-.jpg (Large).jpg
Views:	643
Size:	50.6 KB
ID:	61244   ridge-cap-shingles-over-ridge-vent-rahbani2-12-large-.jpg (Large).jpg
Views:	469
Size:	45.8 KB
ID:	61245  




Reply With Quote
Need a home inspection in Arkansas? Check out InterNACHI's listing of Arkansas certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 12/28/12, 5:33 PM
Marcel R. Cyr, CMI's Avatar
Marcel R. Cyr, CMI Marcel R. Cyr, CMI is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 25,242
Default Re: Ridge Cap Shingles over Ridge Vent

Yes, not the preferred type.
But the type seen in the picture.
What I posted was one of the very first to come out. Now there are too many to mention here.
Reply With Quote
  #15  
Old 12/28/12, 5:50 PM
kwood kwood is offline
Banned
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 11,816
Please Note: kwood is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Ridge Cap Shingles over Ridge Vent

How can you tell Marcel! I looked at it 3 times and seen that it is too high on the end for that type however I am willing to change if you can explain different.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
asphalt shingles remain 'best bang for your buck' rcooke Canadian Inspectors 0 9/2/11 12:15 PM
ridge cap shingles kdolin Roofing Inspections 22 11/4/10 4:35 PM
Shooting to begin on comprehensive new roofing courses kshepard Inspection Education & Training 4 11/7/09 2:59 PM

All times are GMT -4. The time now is 5:57 PM.
no new posts