Default Roof Deck Seams Visible - What's Wrong?

Saw this yesterday (11/17) on the home I was inspecting, and several other homes around it. Brand new construction. I've seen this sort of thing before, but not this visible nor widespread. The decking is 7/16" OSB with rafters 24" OC. Location is central Texas. My guess is that it rained while the decking was exposed, and the edges all swelled up. OSB swells when it gets wet, but does not subsequently shrink back after it dries. Some of these ridges are 3/4" proud of the surface. Will this prematurely wear the shingles? What is your take on this, and what should be done?
Attached Thumbnails
roof-deck-seams-visible-whats-wrong-2009-11-17-6399-r-n-1293-012.jpg   roof-deck-seams-visible-whats-wrong-2009-11-17-6399-r-n-1293-013.jpg   roof-deck-seams-visible-whats-wrong-2009-11-17-6399-r-n-1293-014.jpg  
Reply With Quote
Find an InterNACHI certified Virginia Home Inspector (and anywhere else in North America)
  #2  
Old 11/18/09, 8:10 AM
psullivan psullivan is offline
InterNACHI Member
 
Join Date: Feb 2004
Location: Round Rock, TX
Posts: 6
Default Re: Roof Deck Seams Visible - What's Wrong?

Oh yeah ... I forgot to mention that H-Clips were properly installed.
Reply With Quote
  #3  
Old 11/18/09, 9:28 AM
Jeffrey Moore Jeffrey Moore is offline
InterNACHI Member
 
Join Date: Feb 2008
Location: Mesa, AZ
Posts: 255
Default Re: Roof Deck Seams Visible - What's Wrong?

How was the attic ventilation and was the decking "bouncy" ?



Jeff Moore
www.quantumhomeinspections.com
Flir (ITC) Level 1 Thermographer
Mesa, AZ
Reply With Quote
  #4  
Old 11/18/09, 9:31 AM
psullivan psullivan is offline
InterNACHI Member
 
Join Date: Feb 2004
Location: Round Rock, TX
Posts: 6
Default Re: Roof Deck Seams Visible - What's Wrong?

Attic ventilation was fine (plenty of soffit & static vents). Deck was solid. This is a brand new home.
Reply With Quote
  #5  
Old 11/18/09, 12:25 PM
mnahrgang's Avatar
mnahrgang mnahrgang is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Springfield, OH
Posts: 5,799
Default Re: Roof Deck Seams Visible - What's Wrong?

I wouldn't buy it like that. I think you are likely correct that the shingles will wear. Also it looks like crap cosmetically. I'd write it up basically saying what you said and let the buyers make their own decisions. Bad move on the roofers part to leave exposed sheathing in a rain storm...



Mark Nahrgang
www.DaytonSpringfieldHomeInspector.com
www.HeyMark.info

Home Inspections for Springfield, Dayton, and surrounding OH areas.
Reply With Quote
  #6  
Old 11/18/09, 1:22 PM
Doug Edwards,  CMI's Avatar
Doug Edwards, CMI Doug Edwards,  CMI is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Florida panhandle
Posts: 4,760
Default Re: Roof Deck Seams Visible - What's Wrong?

Do you have any photos of the swollen edges from inside the attic. A 3/4 inch deflection is pretty significant. I would be surprised if the shingle manufacture's warranty would honor this if in the event the roof fails as it was installed improperly over degraded surface decking material. Also note that the swollen edges over the trusses are the nailing points which when the edges are already damaged (swollen from the water exposure) further weakens the integrity of the roofing structure. Water damaged OSB just comes apart / crumbles when anyone tries to used fasteners on it. Roofer (and the builder) ought to have their heads examined for going ahead and roofing over degraded decking. Just asking for a lawsuit.



"War is an ugly thing, but not the ugliest of things; the decayed and degraded state of moral and patriotic feeling which thinks nothing is worth a war, is worse. A man who has nothing which he cares more about than he does about his personal safety is a miserable creature who has no chance at being free, unless made and kept so by the exertions of better men than himself."

- John Stuart Mill







Reply With Quote
  #7  
Old 11/18/09, 2:17 PM
George P. Wells, CMI's Avatar
George P. Wells, CMI George P. Wells, CMI is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Michigan
Posts: 544
Send a message via Skype™ to gwells
Default Re: Roof Deck Seams Visible - What's Wrong?

Quote:
Originally Posted by mnahrgang View Post
I wouldn't buy it like that. I think you are likely correct that the shingles will wear. Also it looks like crap cosmetically. I'd write it up basically saying what you said and let the buyers make their own decisions. Bad move on the roofers part to leave exposed sheathing in a rain storm...
I see this all the time. It is one of my pet peeves. Builders around here (SE MI & NW OH) refuse to cover roofs during construction. They tell homebuyers that this is "normal". I tell my customers that it may be normal for the builder but it still isn't right!

The problems are not only with roof decks. I see a lot of damaged sub-floors too. This is one of the reasons why home inspection is still a growing industry.



Licensed Electrical Contractor
Master Electrician
BS Electrical Engineering
Certified Master Inspector

B
estInspectors.Net

License Prep and Continuing Education
Home and Commercial Building Inspection - Electrical
Plumbing - HVAC- Hydronics - Refrigeration - Fire Alarm
Fire and Explosion Investigation - Commercial Sign
Installation - Real Estate (Agent and Broker) - Appraisal

Inspection Report Software for
Windows - iOS - Mac - Android - Linux



est. 1992
Reply With Quote
  #8  
Old 11/18/09, 3:34 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,684
Default Re: Roof Deck Seams Visible - What's Wrong?

Those are definitely swollen edges on that OSB.

The builder should be forced to re-do their work.
Reply With Quote
  #9  
Old 11/18/09, 4:17 PM
George Russell George Russell is offline
New User
 
Join Date: Nov 2008
Location: Austin,Texas
Posts: 6
Please Note: George Russell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Roof Deck Seams Visible - What's Wrong?

Was those pics taken in the morning? If so go back in the afternoon....betcha can't see them then
G
Reply With Quote
  #10  
Old 11/18/09, 4:43 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 18,918
Default Re: Roof Deck Seams Visible - What's Wrong?

If this is new construction, it should point blank not be acceptable for sale until corrected.
No one should have to live with an obvious defect as such.
If the builder gets pinched on this one, next time he will protect the godarn thing properly. Makes all builders look bad.
Reply With Quote
  #11  
Old 11/19/09, 1:09 AM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 3,407
Send a message via ICQ to kshepard
Default Re: Roof Deck Seams Visible - What's Wrong?

Quote:
Originally Posted by psullivan View Post
Saw this yesterday (11/17) on the home I was inspecting, and several other homes around it. Brand new construction. I've seen this sort of thing before, but not this visible nor widespread. The decking is 7/16" OSB with rafters 24" OC. Location is central Texas. My guess is that it rained while the decking was exposed, and the edges all swelled up. OSB swells when it gets wet, but does not subsequently shrink back after it dries. Some of these ridges are 3/4" proud of the surface. Will this prematurely wear the shingles? What is your take on this, and what should be done?
That's caused by a significant amount of moisture being absorbed by the sheathing after the shingles were installed. Shingles have buckled at the panel edges as sheathing panels expanded.
It's not really the roofer's fault but the fault of the general contractor or whoever did the scheduling. OSB reacts pretty quickly once it gets rained on. I guess it's possible that the roofer got up there on recently-rained-on sheathing that hadn't yet expanded, but I think it's more likely that the moisture was absorbed from the underside.
This has popped up in researching the roofing course and this photo a great example. In what I've read, they talked about moisture being absorbed for the underside. They never said... but they implied that sheathing panels reacted fairly quickly to being rained on. If it was rain on exposed panels which were then roofed over, it would have to be residual moisture on the surface of the sheathing that got locked in by the roofing materials that would cause enough swelling to buckle shingles 3/4", which is a lot of buckling and reflects a lot of sheathing expansion. That's my 2 cents.

The source... man, it's so dry here in CO that we seldom see this. Maybe closing the home up as drywall mud is drying, especially if the home has recessed lighting left on. That can create quite a bit of stack effect that pull moist air up into the attic. It could be made worse if there'd been recent rain and the air was humid and also if the sheathing was wet when the roofer climbed up there. It can be a combination of things.




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
InterNACHI Director of International Development
Director of Green Building

EXPERT WITNESS SERVICE
Conventional and Log homes

(303) 717-8940

Last edited by kshepard; 11/19/09 at 1:30 AM..
Reply With Quote
  #12  
Old 11/19/09, 1:12 AM
mnahrgang's Avatar
mnahrgang mnahrgang is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Springfield, OH
Posts: 5,799
Default Re: Roof Deck Seams Visible - What's Wrong?

Quote:
Originally Posted by kshepard View Post
That's caused by a significant amount of moisture being absorbed by the sheathing after the shingles were installed. Shingles have buckled at the panel edges.
Kenton...Honest question here....

What makes you say with such conviction, that the moisture was absorbed after the shingles were installed? And if so, what could introduce that much moisture to them?

I'm only asking, because the other explanations presented so far, seem more plausible to me on the surface. I'd like to know what you know on this.



Mark Nahrgang
www.DaytonSpringfieldHomeInspector.com
www.HeyMark.info

Home Inspections for Springfield, Dayton, and surrounding OH areas.
Reply With Quote
  #13  
Old 11/19/09, 1:27 AM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 3,407
Send a message via ICQ to kshepard
Default Re: Roof Deck Seams Visible - What's Wrong?

Quote:
Originally Posted by mnahrgang View Post
Kenton...Honest question here....

What makes you say with such conviction, that the moisture was absorbed after the shingles were installed? And if so, what could introduce that much moisture to them?

I'm only asking, because the other explanations presented so far, seem more plausible to me on the surface. I'd like to know what you know on this.
I added to my post below, Mark.




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
InterNACHI Director of International Development
Director of Green Building

EXPERT WITNESS SERVICE
Conventional and Log homes

(303) 717-8940
Reply With Quote
Find an InterNACHI certified Virginia Home Inspector (and anywhere else in North America)
  #14  
Old 11/19/09, 1:28 AM
mnahrgang's Avatar
mnahrgang mnahrgang is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Springfield, OH
Posts: 5,799
Default Re: Roof Deck Seams Visible - What's Wrong?

Quote:
Originally Posted by kshepard View Post
I added to my post below, Mark.
Thanks...

So it got rained on, shingled, then expanded/buckled...



Mark Nahrgang
www.DaytonSpringfieldHomeInspector.com
www.HeyMark.info

Home Inspections for Springfield, Dayton, and surrounding OH areas.
Reply With Quote
  #15  
Old 11/19/09, 1:28 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 7,708
Send a message via Yahoo to jfunderburk
Default Re: Roof Deck Seams Visible - What's Wrong?

May want to point out that it will come back to haunt the buyer when they decide to sell it.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Building Science- research from respected sources Brian A. MacNeish Ancillary Inspection Services & Additional Topics 17 7/12/11 7:31 AM
Roof deck question wdecker Exterior Inspections 3 11/17/08 11:17 PM
Deck Failures rcooke Miscellaneous Discussion for Inspectors 29 10/25/07 6:47 PM