#1
|
||||
|
||||
|
Question on how you would report on the following? See Poll
1966 Ranch with a basement. Roof 3D architectural shingles. 5 years old 1 layer. Venting is soffit/ridge and gable ends. No moisture stains at roof decking, insulation is a fiberglass loose fill 12-15 inches with baffles. Performing Home Inspections in Cleveland, Strongsville, Brecksville, Broadview Heights, North Royalton, Parma and surrounding areas. |
| Need a home inspection in New Mexico? Check out InterNACHI's listing of New Mexico certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#2
|
||||
|
||||
|
No question about the poll on this one ah David!
THE RIGHT TRAK CIAQP, IAC2 Certified Master Inspector kwoodinspections@hotmail.com www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ www.linkedin.com/in/kevinwoodiaq OOVOO account kwoodinspections Cell: 705-971-2096 Ph : 705-946-2676 |
|
#3
|
|||
|
|||
|
It looks like the trim and soffit is covered in alum and vinyl. Most likely at a later date and was not orginal to the house. I would mention this and that you cannot see the condition of the orginal trim/soffit.
|
|
#4
|
||||
|
||||
|
After lifting the attic hatch, I pop my head up into the attic with NO lights so that I can get an idea if there is adequate intake ventilation at the soffits. If there is no evidence of under ventilation then I simply report:
"No significant deficiencies observed at the time of inspection." The SOP does not require a description of the ventilation methods and I do not include this information in my reports. I take lots of photos and include the following: Limitations and exclusions of a visual insulation & ventilation inspection: "Where continuously vented soffit is installed over pre-existing soffit, the presence of adequate ventilation behind was not determined." Rick Strand, CPI CAHPI Associate Strand Home Inspections Inc. Calgary, Alberta, Canada Serving Calgary, Okotoks, Airdrie, Chestermere and Cochrane Alberta
|
|
#5
|
||||
|
||||
|
I would rather see gable end vents than soffits.
Not a big fan of soffit vents. Russell Inspection Services New Hampshire state license # 57 Level I Thermographer, ITC Certified Building Science Thermographer, ITC Certified Building Analyst, BPI Certified Commercial Inspector, ITA Certified Septic Evaluator, GSDI #148 www.newenglandthermalimaging.com www.russellinspectionservices.com www.nhsepticinspection.com |
|
#6
|
||||
|
||||
|
Quote:
And although we prefer not to have gable vents with soffit vents, having both does not make it wrong. More information is required for proper ventilation evaluation, which you know is beyond the SOP. Just sayin'. Jeffrey R. Jonas Critical Eye Property Inspections JRJ Consultants Owatonna, Minnesota Chapter President InterNachi Awards Portal: http://co.nachi.org/inachiawards/
|
|
#7
|
||||
|
||||
|
Gable vents when used with ridge vents interfere with the air flow form the soffit to the ridge and can lead to mold on the roof sheeting.
You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell |
|
#8
|
||||
|
||||
|
I have closed My roof vents and My Gable vents hope to Close of my Soffit vents soon .
I will be recording my attic and the out side temp regularly . I will also be checking my attic constantly . Will try and post info regularly . I am a constant reader and my feeling at this time is stop allowing my home heat get to the out side . http://www.buildingscience.com/docum...ic-ventilation http://jobsite.buildiq.com/articles/...ted-attic.aspx http://www.energy.wsu.edu/documents/...ented%20attics[1].pdf http://www.greenbuildingadvisor.com/...unvented-attic http://www.greenhorizon.com/files/JL...ray%20Foam.pdf Need help on inspection call my cell 613-827-2011 I like email Roycooke@hotmail.com Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun. |
|
#9
|
||||
|
||||
|
I will initially concede that living on the border or in Canada will have different building practices.
I am from New England (just a few miles from Peter) and I will be the first one to say that regardless of standards or codes, different parts of the country require different practices whether they are adopted by the AHJ . Considering the laws of psychometrics and fluid dynamics, proper attic ventilation requires upper and lower openings to allow convection to occur. The IRC and UBC both recognize that less ventilation is required per square foot of the attic space if more ventilation is located on the upper level of the roof than the lower eve. If you suck air out, you must allow it to come back in somewhere. The attic produces a significant stack effect and if there are not soffit ventilators, this air must be drawn in from ceiling openings on the upper floor of the building. This causes a major efficiency issue. I realize that increasing airflow and making a cold roof causes ice damning and water damage issues so I am not arguing the point. However, people that have a ridge vent and a gable vent are providing a greater source of air ventilation to the exterior at the upper portions of the attic space as required to reduce the necessary ventilation of the attic. So where have we evolved into saying that if you have a ridge vent and a gable vent that you should close one of them up? The more ventilation on the upper part of the roof the greater convection that occurs and except for our friends in the North that have to deal with ice damning, the more up high the better. In the South, we like to stick HVAC equipment in the attic without increasing the attic ventilation. This is stupid on top of stupid. So for anybody in the South that takes on the substantiated practices of the North, you are probably wrong. I am open to suggestions and clarification and I specifically request clarification of perspective from my friend Peter Russell who obviously has a real good reason for controlling ventilation at the soffit. My point is, just because Peter does it, does not mean you need to worry about it if you're in Houston Texas. "Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein Clarksville - Nashville Home Inspector Lic#40 http://www.midtninspections.com ITC Level III Thermographer Cert#1958 Building Science Thermographer Cert#33784 http://www.thermalimagingscan.com HVAC Certification EPA Cert#2046620 Link to my Website at: http://www.midtninspections.com/link-submission |
|
#10
|
||||
|
||||
|
Do I have to close off my gable vents when I use a ridge vent?
Yes, the gable vents (a type of exhaust vent) should be closed off whenever a ridge vent (which is also a type of exhaust vent) is installed because vents installed at the roof’s edge or in the overhang should supply the intake air needed by the ridge vents. Air should flow in through the intake vents evenly along the roofline and exhaust out the peak. Any vents in place between the ridge vents and the intake vents may interrupt or short-circuit that flow of air along the roofline. The gable vents will end up becoming intake for the ridge vent — an undesirable situation that could lead to weather infiltration through the gable vents and also could prevent the attic from being properly ventilated. The same is true with mixing wind turbines or roof louvers with ridge vents. http://www.airvent.com/professional/...shooting.shtml You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell |
|
#11
|
||||
|
||||
|
The gable vent is at the roof line.
Who cares if the air is coming out of the gable vent or a ridge (which was most likely improperly placed)? Air out = air in. It doesn't matter how much air goes where, it's where it happens. That is the point. "Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein Clarksville - Nashville Home Inspector Lic#40 http://www.midtninspections.com ITC Level III Thermographer Cert#1958 Building Science Thermographer Cert#33784 http://www.thermalimagingscan.com HVAC Certification EPA Cert#2046620 Link to my Website at: http://www.midtninspections.com/link-submission |
|
#12
|
||||
|
||||
|
Quote:
This means that less air is drawn in from the soffit vents especially near the center. That interferes with moisture removal due to lack of sufficient air flow. Reduced air flow mens warmer sheeting and increases the possibility of ice damns. You are certainly entitled to your opinion but it would be nice if you would explain it. You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell |
|
#13
|
||||
|
||||
|
Quote:
Russell Inspection Services New Hampshire state license # 57 Level I Thermographer, ITC Certified Building Science Thermographer, ITC Certified Building Analyst, BPI Certified Commercial Inspector, ITA Certified Septic Evaluator, GSDI #148 www.newenglandthermalimaging.com www.russellinspectionservices.com www.nhsepticinspection.com |
| Need a home inspection in New Mexico? Check out InterNACHI's listing of New Mexico certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#14
|
||||
|
||||
|
I must agree with Michael even though I hate too! LOL
THE RIGHT TRAK CIAQP, IAC2 Certified Master Inspector kwoodinspections@hotmail.com www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ www.linkedin.com/in/kevinwoodiaq OOVOO account kwoodinspections Cell: 705-971-2096 Ph : 705-946-2676 |
|
#15
|
||||
|
||||
|
Missing?
Sorry, but I don't think so. I used to think that way when I was a young guy, but now that I'm old and cranky I've come to realize the basics of physics. There are a few things required for air to flow from the interior to the exterior of a building. #1 there must be an opening. #2 there must be a pressure differential from one side of the opening to the other. #3 resistance of air flow regulates the direction of flow. Have you checked the coefficient of friction between a gable vent and a ridge vent? Air flows through the path of least resistance. Air is rising and wants to get out of the attic. Is it going to try to go through the ridge vent with a higher resistance or the gable vent with practically none? If air is going to be drawn through the gable ventilator backwards with very little restriction, through a ridge vent which has a huge restriction coefficient, must we not be able to pass more air through the ridge vent than the gable vent? Check out the "net free area" of a gable vent versus a ridge vent. Air pressure is regulated by temperature differential and elevation. What's the temperature differential and height elevation between a ridge vent and a gable vent? Is it possible to generate the condition that you mentioned? Yes. Does this exist under normal construction techniques? You tell me. I don't live where you do. "Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein Clarksville - Nashville Home Inspector Lic#40 http://www.midtninspections.com ITC Level III Thermographer Cert#1958 Building Science Thermographer Cert#33784 http://www.thermalimagingscan.com HVAC Certification EPA Cert#2046620 Link to my Website at: http://www.midtninspections.com/link-submission |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Roof deck question | wdecker | Exterior Inspections | 3 | 11/17/08 10:17 PM |
| Is inadequate roof or attic ventilation a defect? | gliebig | Exterior Inspections | 85 | 1/16/08 6:56 PM |
| Chimney flashing photo's needed: brick and stone done correctly | kshepard | Exterior Inspections | 6 | 10/13/07 8:10 AM |
| Ice Gaurd membrane | dmacy | Exterior Inspections | 36 | 6/14/07 12:21 AM |
| Moss growing on roof | ecox1 | Exterior Inspections | 45 | 1/19/06 9:57 PM |