Home Service Grounding Electrodes
by Nick Gromicko, Rob London and Kenton Shepard
Electrical grounding systems divert potentially dangerous electrical currents by providing a path between a building’s service boxGrounding Rod and the earth. Lightning and static electricity are the most common sources of dangerous or damaging charges that can be dissipated through a grounding system. Grounding electrodes are connected to the building’s electrical system through grounding electrode conductors, also known as ground wires. A number of different metal alloys can function as grounding electrodes, the most common of which are the focus of this article.
Requirements for electrodes and ground wires:
  • Aluminum has a tendency to corrode and should not be used in ground wires unless they are insulated. Moisture and mineral salts from masonry are common causes of corrosion to uninsulated aluminum. It is also a poorer conductor than copper. Aluminum wires in grounding systems are not permitted in Canada.
  • Since grounding electrodes are not insulated, they can never be made of aluminum.
  • If more than one electrode is present, they must be connected to each other with a bonding jumper.
Common Types of Grounding Electrodes Grounding Rods
The most common form of grounding electrode is a metal rod that is hammered into the ground so that its entire length is submerged. InterNACHI recommends that the rod be inserted vertically and in one piece, but this is not always possible in rocky areas. If the rod is hammered into sub-surface rocks it might become scratched and lose its cladding. Rust can accumulate on exposed iron or steel and degrade the conductive capacity of the rod. Unfortunately, this rust will rarely be visible to an inspector.
Electricians have been known to cut the rod when they have difficulty inserting its entire length beneath the ground. This practice violates code and can be a safety hazard. Inspectors should look for the following signs that indicate that a grounding rod has been shortened:
  • Rust at the rod’s top. Grounding rods have a corrosion-resistant coating but are usually made of steel or iron and are vulnerable to rusting at any location that the rod is cut.
  • Most rods have an etched label on their top. If this label is missing it is likely that the rod has been cut.
Inspectors should bear in mind that utility companies sometimes allow ground rods to be shortened. A qualified electrician can test whether a shortened rod is an adequate grounding electrode.
If accessible, inspectors should check the condition of the clamp that connects the grounding rod to the ground wire. Clamps should be made of bronze or copper and be tightly fastened. Requirements for rod length, thickness, and protective coating are addressed in the 2006 International Residential Code (IRC) as follows:
Rod and pipe electrodes not less than 8 feet (2438 mm) in length and consisting of the following materials shall be considered as a grounding electrode:
  1. Electrodes of pipe or conduit shall be not smaller than trade size ¾ (metric designator 21) and, where of iron or steel, shall have the outer surface galvanized or otherwise metal-coated for corrosion protection.
  2. Electrodes of rods of iron or steel shall be at least 5/8 inch (15.9 mm) in diameter. Stainless steel rods less than 5/8 inch (15.9mm) in diameter, nonferrous rods or their equivalent shall be listed and shall be not less than 1⁄2 inch (12.7mm) in diameter.
Notes
  • Although the 2006 IRC does not mention whether the rod may be driven at an angle, the 1998 California Electrical Code allows for a maximum oblique angle of 45 degrees from the vertical.
  • An electrician can install two grounding rods if necessary. They should be at least 6 feet apart from one another.
  • In Canada, grounding rods should be 10 feet long and two are required.
Concrete-Encased Electrodes (Ufer Grounds)
This electrical grounding technique was invented during World War II in Arizona, and is commonly called “Ufer” after its creator, Herbert G. Ufer. The United States Army was concerned that lightning or static electricity could cause the accidental detonation of explosives that were stored in igloo-shaped vaults. The desert climate restricted the usefulness of grounding rods, which would have to be driven hundreds of feet into the dry earth in order to be effective. Ufer advised the military to connect ground wires into the concrete-encased steel reinforcement bars (re-bar) of the bomb vaults in order to dissipate electricity effectively into the ground. Testing confirmed his theory that the relatively high conductivity of concrete would allow electric current to dissipate into a large surface area of earth. The Ufer method is more common in newer residential construction and requires a metal frame. It might be difficult for an inspector to detect this type of electrode. The 2006 IRC details Ufer grounds as follows:
An electrode encased by at least 2 inches (51 mm) of concrete, located within and near the bottom of a concrete foundation or footing that is in direct contact with the earth, consisting of at least 20 feet (6096 mm) of one or more bare or zinc-galvanized or three electrically conductive coated steel reinforcing bars or rods of not less than 1/2 inch (12.77 mm) diameter or consisting of at least 20 (6096 mm) feet of bare copper conductor not smaller than 4 AWG shall be considered as a grounding electrode. Reinforcing bars shall be permitted to be bonded together by the usual tie wires or other effective means.
Metal Underground Water Pipes
A building’s plumbing system can be connected to the ground wire and function as a grounding electrode. For some time, this was the only mandatory grounding electrode type and it was generally preferred over other methods. As of 1987, however, this method became the only one that must be supplemented with another type of electrode. This transition is due to the increased popularity of nonconductive dielectric unions and plastic pipes. When plumbing has been replaced with plastic pipes a notice is required to be placed at the electrical service panel that states that there is a non-metallic water service. Inspectors will not be able to tell if outdoor water pipes that run to street water mains have been replaced with plastic components.
Inspectors should check for the following:
  • Ground wires should be firmly attached to water pipes close to the point of entry to the building. A ground wire that is loosely tied around a pipe is inadequate.
  • Gas pipes should never be used as grounding conductors. They usually are made of plastic at the exterior of the home and carry flammable gases that may ignite if exposed to electrical current.
The 2006 IRC states the following about water pipe electrodes:
A metal underground water pipe that is in direct contact with the earth for 10 feet (3048 mm) or more, including any well casing effectively bonded to the pipe and that is electrically continuous by bonding around insulating joints or insulating pipe to the points of connection of the grounding electrode conductor and the bonding conductors, shall be considered as a grounding electrode. Interior metal water piping located more than 5 feet (1524 mm) from the entrance to the building shall not be used as part of the grounding electrode system or as a conductor to interconnect electrodes that are part of the grounding electrode system.
Less Common Grounding Electrodes
The previously mentioned grounding electrodes constitute the vast majority of grounding systems that inspectors will encounter. The two electrodes described below are far less common, although they are recognized by the IRC. Inspectors might not be able to verify their presence. The 2006 IRC explains them as follows:
Plate Electrodes
A plate electrode that exposes no less than 2 square feet (0.186 m2) of surface to exterior soil shall be considered as a grounding electrode. Electrodes of iron or steel plates shall be at least 1⁄4 inch (6.4mm) in thickness. Electrodes of nonferrous metal shall be at least 0.06 inch (1.5mm) in thickness. Plate electrodes shall be installed not less than 30 inches (762 mm) below the surface of the earth.
Ground Ring Electrodes
A ground ring encircling the building or structure, in direct contact with the earth at a depth below the earth’s surface of not less than 2.5 feet, consisting of at least 20 feet of bare copper conductor not smaller than No. 2 shall be considered as a grounding electrode.
In summary, a variety of home service grounding electrodes can be used to safely route unexpected electrical charges away from places that they can cause harm. Inspectors should be aware of how they differ from one another and be prepared to spot defects.