Service Drop Run Over Balcony?

Originally Posted By: jtedesco
This post was automatically imported from our archived forum.







![icon_question.gif](upload://t2zemjDOQRADd4xSC3xOot86t0m.gif) __________________


--
Joe Tedesco, NEC Consultant

www.nachi.org/tedescobook.htm

Originally Posted By: Randy Flockton
This post was automatically imported from our archived forum.



Personally, I think it’s hella ugly to have right over the kinda place I’d be relaxing if that was my home, but as long as it’s >10’AFF of the balcony, it’ll meet utility specs here…BTW what’s the box around the top of the risers for? a planter? icon_biggrin.gif the riser on the leftmost service looks like its bowed out for some reason, how’s the support there looking?


-Randy


--
"Prices subject to change with customers additude"

Originally Posted By: jpeck
This post was automatically imported from our archived forum.



Can’t be there like that for several reasons. I will let others add those reasons.



Jerry Peck


South Florida

Originally Posted By: tallen
This post was automatically imported from our archived forum.



1. To close to the window.


2. Doesn’t meet height requirements 10’ min. above a walking surface.


3. I doubt there is an adequate drip loop.


Next


--
I have put the past behind me,
where , however, it now sits, making rude remarks.

www.whiteglovehomeinspections.net

30 Oct 2003-- 29 Nov2005

Originally Posted By: tallen
This post was automatically imported from our archived forum.



Hello icon_lol.gif where did Joe Tedesco go.



I have put the past behind me,


where , however, it now sits, making rude remarks.


www.whiteglovehomeinspections.net

30 Oct 2003-- 29 Nov2005

Originally Posted By: jtedesco
This post was automatically imported from our archived forum.



Great Todd: eusa_clap.gif


I am here. These are additional items we can add to your list:

Quote:
Clearance from Windows.

Service conductors installed as open conductors, or multiconductor cable without an overall outer jacket require a clearance of not less than 3 feet from windows that are designed to be opened, doors, porches, balconies, ladders, stairs, fire escapes, or similar locations.

This does not apply when the conductors run above the top level of a window and can be installed at less then 3 feet.



--
Joe Tedesco, NEC Consultant

www.nachi.org/tedescobook.htm

Originally Posted By: Mike Parks
This post was automatically imported from our archived forum.



Joe


For your info.

If the utitlty co. installed this, the State of Ohio will not allow me to apply the NEC.

If the contractor installed this I can fail 'refuse' this installation.

???

Mike P.


Originally Posted By: Ryan Jackson
This post was automatically imported from our archived forum.



Mike Parks wrote:
Joe

For your info.

If the utitlty co. installed this, the State of Ohio will not allow me to apply the NEC.
Mike P.


Mike: See 90.2 (5) Installations under the exclusive control of an electric utility where such installations
a. Consist of service drops or service laterals, and associated metering.


--
Ryan Jackson, Salt Lake City

Originally Posted By: Mike Parks
This post was automatically imported from our archived forum.



Ryan


My point is that it is OK for the utility but not the contractor.

Mike P.


Originally Posted By: Ryan Jackson
This post was automatically imported from our archived forum.



Mike: When I saw the ??? in your posts I figured you were asking a question as to why you can’t use the NEC for a utility’s installation. I didn’t realize you were just saying an answer in the form of a question ???



Ryan Jackson, Salt Lake City

Originally Posted By: Mike Parks
This post was automatically imported from our archived forum.



OK


We are on the same page!

Mike P.


Originally Posted By: Ryan Jackson
This post was automatically imported from our archived forum.



You should go on Jeopordy! LOL icon_smile.gif



Ryan Jackson, Salt Lake City

Originally Posted By: tallen
This post was automatically imported from our archived forum.



I really do not think 3’ is adequate. icon_eek.gif I know I would not like a service drop 3’ outside my window. Would you?



I have put the past behind me,


where , however, it now sits, making rude remarks.


www.whiteglovehomeinspections.net

30 Oct 2003-- 29 Nov2005

Originally Posted By: ltrower
This post was automatically imported from our archived forum.



How wonderful it must be to wake up on your day off and watch the birds poop on your deck.


Lee Trower


Originally Posted By: jedwards
This post was automatically imported from our archived forum.



The REALLY fun thing about stuff like this is hearing why it may be OK as per the NEC (or the AHJ, or whoever).


Frankly? SCREW THE CODE. IT'S A SAFETY HAZARD.

Children could die here.

Maybe I should find a new line of work?


--
John Edwards
Assurance South, LLC home page
Pre-Paid Legal Services

Originally Posted By: joetedesco
This post was automatically imported from our archived forum.



icon_lol.gif


Originally Posted By: kdolin
This post was automatically imported from our archived forum.



Yeah but boy do those clothes dry fast on that line!


Originally Posted By: Jay Moge
This post was automatically imported from our archived forum.



how about a ladder truck trying to rescue Jr. from his burning bedroom? graphic i know, but some time people “see” what your saying a little better if you put guilt in there minds. icon_cool.gif


Originally Posted By: Monte Lunde
This post was automatically imported from our archived forum.



This installation could not have been permitted. The utility company was there first, a AHJ would never approved this deck installation as installed so don’t blame the Utility Company or the AHJ. Other people have listed the electrical problems that are now created by this deck.



Monte Lunde CCI, CCPM, CRI


Viking Construction Services Inc.

Originally Posted By: darnold1
This post was automatically imported from our archived forum.



That wire looks like it crosses the upper edge of that window. It’s not above the window! From the picture angle. That does not look safe at all. I would write it up as a safety hazard, then contact the electric company in that area. Someone trying to escape a fire by going out that window adds more to the “it does not look safe to me”.