View Single Post
 
Old 12/13/18, 10:14 AM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 3,297
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Grounding not verified

Quote:
Originally Posted by eklugmann View Post
I'm sure this has been addressed before but still unclear what to say. 1969 build, single family. Appears to be an upgraded panel in 2012. I know there should be two grounding methods; I see two grounds exiting the panel, but thats it. Couldn't see any grounding rods. The top bare neutral went into an BX type armored cable. So do I mention that I couldn't see any actual grounds? "Actual grounding method couldn't be verified"?
Thank you
Some constructive criticism, you should work on your terminology. The conductors in question are Grounding Electrode Conductors (GEC's) not "grounds". The bare conductor in the cable armor is a GEC not a neutral conductor. If there is a metal water pipe that would be a grounding electrode, same for ground rods. Connection to ground rods are not require to be accessible so it's possible that they're buried.