Can an AFCI offer GFCI protection

Hi to all,

I was asked this question by a member this morning, here is the sutuation:

  • Newley nemodeled basement including a bathroom
  • Bathroom is served by a dedicated 20 amp AFCI breaker
  • Electrician states that AFCI will offer GFCI protection
    I believe I know the answer to this issue but think it is worth some discussion.

Paul, Joe T where are you? (please keep it simple :mrgreen:)

Regards

Gerry

I can keep that one simple - NO.

A ground fault and an arc fault are uniquely different and one can occur without the other.

Sorry, I’m not Paul or Joe, but I couldn’t help myself :smiley:

I agree with Jeff. Two totally different functions.

lol…Dang JEFF and you dont want to LOOK like me either so atleast you have THAT going for ya…:slight_smile:

Their are some models on the table out their that will do both GFCI and AFCI in a combination and do function as some protection…more ideas are on the table I know of…but CutlerHammer has had an AFCI/GFCI breaker out for a few years now…

“The standard AFCIs have GFP and not GFCI protection built in. The term GFCI should be reserved for “people protective eqquipment”. A GFCI has a ground fault trip level of 4 to 6 mA, but the GFP in an AFCI has a trip level of 30 to 50 mA.” from Mike Holt Forum.

Translation…while the AFCI/GFCI combo offers a level of Protection…in order to TRULY make it for personal protection you would still need a TRADITIONAL GFCI in a form of a receptacle at the first box…the ARC FAULT would still function and some level of GFI protection…

This from Cutler Hammers Website " FIRE-GUARD AFCI can also be equipped with 5 mA ground fault protection to protect from personal shock hazards. Now, there is a residential circuit breaker that provides protection from arcing faults, conductor damage due to thermal overloads and short circuits, as well as 5 mA ground fault protection in one integrated design. "

“The FIRE-GUARD™ Arc Fault Circuit Interrupter (AFCI) is a residential circuit breaker with an integrated processor which recognizes the unique current and/or voltage signatures associated with arcing faults, and acts to interrupt the circuit to reduce the likelihood of an electrical fire. With the Cutler-Hammer FIRE-GUARD AFCI, protection from arcing faults is combined with conventional thermal and magnetic overloads as found in standard residential circuit breakers protecting wiring from excessive heat or damage due to overloading or short circuits. FIRE-GUARD AFCI can also be equipped with 5 mA ground fault protection to protect from personal shock hazards. Now, there is a residential circuit breaker that provides protection from arcing faults, conductor damage due to thermal overloads and short circuits, as well as 5 mA ground fault protection in one integrated design.”

Some may not realize that a GFCI only gives protection from the hot leg to Ground .
You get between the hot and Neutral and the power does not know it is not a regular load.
The results could be surprising.
The GFCI on knows to shut down if you get between the Hot and Ground.
With a regular AFCI it could care less if you get between hot and ground or hot and neutral you are the load and it will not shut down.
Roy Sr

Roy,

Here is a nice article by Mike Holt that I think explains the GFCI rather well so all can understand those fears as well…GFCI’s are great but far from perfect…:slight_smile:

You may know what a GFCI is, but do you really know how it works? A basic understanding of the device can prevent safety problems.
You may know in what situations the NEC requires you to install a ground-fault circuit interrupter (GFCI), but do you know how a it works? A GFCI is specifically designed to protect people against electric shock from an electrical system, and it monitors the imbalance of current between the ungrounded (hot) and grounded (neutral) conductor of a given circuit. Don’t let the name confuse you — these devices will operate on a circuit that does not have an equipment-grounding conductor.

http://www.ecmweb.com/images/archive/203ecm18fig1.gif

With the exception of small amounts of leak-age, the current returning to the power supply in a typical 2-wire circuit will be equal to the current leaving the power supply. If the difference between the current leaving and returning through the current transformer of the GFCI exceeds 5 mA, the solid-state circuitry opens the switching contacts and de-energizes the circuit.
However, a GFCI doesn’t give you a license to be careless. Severe electric shock or death can occur if you touch the hot and neutral conductors in a GFCI-protected circuit at the same time because the current transformer within the protection device won’t sense an imbalance between the departing and returning current and the switching contacts will remain closed.
In addition, GFCI protection devices fail at times, leaving the switching contacts closed and allowing the device to continue to provide power without protection. According to a 1999 study by ( One of our Association Competitors ), 21% of GFCI circuit breakers and 19% of GFCI receptacles inspected didn’t provide protection, leaving the energized circuit unprotected. In most cases, damage to the internal transient voltage surge protectors (metal-oxide varistors) that protect the GFCI sensing circuit were responsible for the failures of the protection devices. In areas of high lightning activity, such as southwest Florida, the failure rate for GFCI circuit breakers and receptacles was over 50%!
GFCIs will also fail if you wire them improperly. The most important thing to remember when wiring them is to connect the wire originating at the breaker to the line side of the GFCI and the wire connecting downstream to the load side of the device. The GFCI terminals are clearly marked “Line” and “Load.” As an added safety improvement, one manufacturer markets a 15A, 125V receptacle with a built-in line-load reversal feature that prevents the GFCI from resetting if the installer mistakenly reverses the load and line connections.
One final thought on GFCI protection: Press the test button of the protection device to ensure it turns off the power to the connected load. You should do this whenever you install one, but also before relying on it to protect you when using it. Do not assume a GFCI protection device is operational unless you properly test it!

Great article thanks . Just did a condo really perfect . Pushed GFCI test buton heard the snap but the power did not go of .
Used my tester no response.
This was 12 years old and for 12 years they have had no GFCI protection.
For this the person was very glad he had a home inspector .
You just never know .
No idea what was wrong this was for the condo to fix.
Roy sr

**I agree:
**

Two different devices used for two different functions:

[/FONT]

www.nfpa.org

PS: Finishing up my seminar in Buffalo, NY. I will add more information when I get home, also I will discuss this at the NACHI Seminar in Fredrick, Maryland on June 24, 2006.

[/FONT]
How FIRE-GUARD AFCI Works

http://www.cutler-hammer.eaton.com/images/spacer.gif

A detailed grahpical representation of how the technology of the FIRE-GUARD AFCI works.

http://www.cutler-hammer.eaton.com/images/spacer.gif

HOW_AFCI_WORKS.PDF | PDF - 9 KB4. Safer Homes … For Dimes a Day

http://www.cutler-hammer.eaton.com/images/spacer.gif

Homeowners highly value safe houses, and are willing to invest more for the peace of mind such houses offer. Builders benefit by clearly and powerfully differentiating themselves as building a safer home. They benefit further with the comfort of knowing that their customers’ lives and properties are protected as much as possible by such enhanced technologies as arc fault circuit interrupters (AFCIs).

http://www.cutler-hammer.eaton.com/images/spacer.gif

RE00402003E.PDF | PDF - 1 KB5. AFCI Headline News, September 2001

http://www.cutler-hammer.eaton.com/images/spacer.gif

AFCI Headline News is a service of the National Association of State Fire Marshals. This newsletter is focused on the importance of Arc Fault Circuit Interrupter technology and its role in improving home electrical safety.

http://www.cutler-hammer.eaton.com/images/spacer.gif

AFCI_HEADLINE_NEWS.PDF | PDF - 19 KB6. Arc Fault Circuit Interrupters — The Next Step in Circuit Protection

http://www.cutler-hammer.eaton.com/images/spacer.gif

In 1997, Eaton Corporation’s Cutler-Hammer business launched the next wave of circuit protection with the first commercially available Arc Fault Circuit Interrupter (AFCI). This article addresses the hazards in residential wiring systems that develop from either high-energy parallel arcing, or high resistance series faults.

http://www.cutler-hammer.eaton.com/images/spacer.gif

RE00402006E.PDF | PDF - 136 KB7. AFCI Headline News February 2002

http://www.cutler-hammer.eaton.com/images/spacer.gif

AFCI Headline News is a service of the National Association of State Fire Marshals. This newsletter is focused on the importance of Arc Fault Circuit Interrupter technology and its role in improving home electrical safety.

http://www.cutler-hammer.eaton.com/images/spacer.gif

AFCIHEADLINENEWSFEB02.PDF | PDF - 18 KB8. Arc Fault Circuit Interrupters: Bringing a New Level of Electrical Protection to the Home

http://www.cutler-hammer.eaton.com/images/spacer.gif

An article by Dr. Joseph Engle on AFCI technology. “The challenge to improve circuit protection by identifying the presence of arcing faults and responding to them fast enough to prevent fire. AFCIs, devices that recognize the unique current signatures associated with arcing faults and act to interrupt the circuit before the temperature of combustibles can rise to hazardous levels.”

http://www.cutler-hammer.eaton.com/images/spacer.gif

RE00402001E.PDF | PDF - 167 KB9. Don’t Let This Happen To Your Home

http://www.cutler-hammer.eaton.com/images/spacer.gif

This homeowner-focused pocket brochure helps to explain the problem of electrical fires, and how AFCI works in layman’s terms. It should be used by contractors and builders to encourage home owners to have AFCI’s installed in all 15 and 20 amp circuits in the home.

http://www.cutler-hammer.eaton.com/images/spacer.gif

SA00402002E.PDF | PDF - 344 KB10. Structure Fires in One - and Two-Family Dwellings

http://www.cutler-hammer.eaton.com/images/spacer.gif

Structure fires in one - and two-family dwellings in which the form of heat of ignition was the heat from electrical equipment arcing. Including unclassified or unknown-type arcing or overload. By area of origin. 1994-1998 annual averages.

http://www.cutler-hammer.eaton.com/images/spacer.gif

DWELLINGAFCIFIRES.PDF | PDF - 25 KB11. Installation Instructions AFCI Circuit Breakers

http://www.cutler-hammer.eaton.com/images/spacer.gif

Installation instructions for Cutler-Hammer type CH or BR Arc Fault circuit breaker. The detailed step-by-step instructions include a wiring diagram and are presented in English and Spanish.

http://www.cutler-hammer.eaton.com/images/spacer.gif

PUB49216REV5.PDF | PDF - 235 KB12. Troubleshooting AFCI Breaker Trips - Instruction

http://www.cutler-hammer.eaton.com/images/spacer.gif

Technical Data Molded Case Circuit Breakers

http://www.cutler-hammer.eaton.com/images/spacer.gif

TD01201038E.PDF | PDF - 77 KB13. AFCIs and Heat Rise - Application Data

http://www.cutler-hammer.eaton.com/images/spacer.gif

Arc Fault Circuit Interrupter (AFCI) breakers are listed to UL 489 and UL 1699. UL 489 covers overload, endurance and short circuit (including temperature). UL 1699 covers arc fault test requirements.

http://www.cutler-hammer.eaton.com/images/spacer.gif

AD00402001E.PDF | PDF - 1808 KB14. Arc Fault Circuit Interrupters

http://www.cutler-hammer.eaton.com/images/spacer.gif

The FIRE-GUARD™ Arc Fault Circuit Interrupter (AFCI) is a residential circuit breaker with an integrated processor which recognizes the unique current and/or voltage signatures associated with arcing faults, and acts to interrupt the circuit.15. Installation Instructions

http://www.cutler-hammer.eaton.com/images/spacer.gif

Installation instructions for Cutler-Hammer type CH or BR Arc Fault and Ground Fault circuit breaker. The detailed step-by-step instructions include a wiring diagram.

You know Roy they just sometimes go bad…and with the new GFCI’s coming out which I think JOE would probably know more about than anyone since he is on the board I think…they will constantly TEST themselves which is GREAT news to the industry…

I wanted to also add in case someone did not know the different in the TYPES of AFCI and GFCI and GFI breakers and their level of protection…just for a FYI guys…just some additional education…

1.) GFCI circuit breakers are designed to protect against ground faults of 4 to 6 mA or more, short-circuits, and overloads.

2.) Dual listed AFCI/GFCI circuit breakers are designed to protect against ground faults of 5 mA or more, short circuits, overloads, and arcing line-to-neutral faults.

3.) Dual listed AFCI/GFI circuit breakers are designed to protect against ground faults of 30 mA or more, short circuits, overloads and arcing line-to-neutral faults.

Important Note : A GFCI does not offer protection against arching line-to-neutral faults.

so you ask…

**Does an AFCI/GFI provide the same level of ground fault protection as a GFCI device?
**No, AFCI/GFI circuit breakers will de-energize the circuit when the ground fault exceeds 30 mA, whereas an AFCI/GFCI circuit breaker opens at 5 mA.

They have TWO different functions…but NO ONE can deny they are MERGING as we speak…if the standards is SIMPLY the function…then yes they do TWO different things…but one device CAN do both…

Just remember and this is important…if someone has a AFCI breaker…DO NOT let them assume it also has GFCI protection…chances are VERY high it does not…and IF it did the breaker would say so…very important…read my COMPARE of the different models above…

If I again HAD to tell someone to have AFCI and GFCI protection in a panel that does NOT have a dual AFCI/GFCI listing breaker available…they should use a STANDARD AFCI for the panel and replace the FIRST receptacle in the branch with a GFCI receptacle…and they will effectivly have the protection…

P.S. remember AFCI’s only protect against ONE type of ARC…anyone KNOW what that is…:)…A good TEST question for ya…:slight_smile:

See this attachment from the UL Book related to the 2005 NEC.

hmmm;)…anyway…most AFCI’s cant deal well with Series Arcs…but they are getting more technical everyday…:slight_smile:

The “electrician” was wrong. An AFCI does not offer ground fault protection.

As stated…

However keep in mind the newer models of AFCI/GFCI combination do provide both…as previously posted…but in basic terms…again a standard AFCI does not offer any level of GFCI " Personal Protection "

APPOLOGIES to Gerry…We did not keep it simple…sorry!

You need to verify which one is installed but there are combo AFCI/GFCIs

Agreed…

“The FIRE-GUARD™ Arc Fault Circuit Interrupter (AFCI) is a residential circuit breaker with an integrated processor which recognizes the unique current and/or voltage signatures associated with arcing faults, and acts to interrupt the circuit to reduce the likelihood of an electrical fire. With the Cutler-Hammer FIRE-GUARD AFCI, protection from arcing faults is combined with conventional thermal and magnetic overloads as found in standard residential circuit breakers protecting wiring from excessive heat or damage due to overloading or short circuits. FIRE-GUARD AFCI can also be equipped with 5 mA ground fault protection to protect from personal shock hazards. Now, there is a residential circuit breaker that provides protection from arcing faults, conductor damage due to thermal overloads and short circuits, as well as 5 mA ground fault protection in one integrated design.”

Roy, I encounter this problem very frequently. It’s been my experience to learn that the LINE and LOAD wires are switched. Some installers just don’t read the instructions on the back.