Default Re: hydronic radiant floor heat on hot water tanks

Mark,

No matter the heat source ,you still have a closed system as long as the water in it is not used for teh potable water system.

The pressure relief at 15-20 psi is right for a dedicated system depending on the elevation of the highest radiator.