Default Garage door inspection procedure

You probably have already read something like this, but I've been writing another course for InterNACHI and I came across this inspection procedure.

It's 10 things to do when inspecting a garage door. I don't think I wrote this originally. I believe I simply paraphrased a garage door association's list.

Just wanted to share...


Garage Door Opener Inspection
Caution: The garage door is the largest moving object in the house. Its parts are under high tension. All repairs and adjustments should be performed by a trained garage door systems technician. To refer to a technician, send you clients to http://www.doors.org. If the garage door appears inoperable, do not attempt to operate the garage door opener.

Manual Release Handle
Begin inside the garage, with the garage door fully closed. Check for a manual release handle or the means of manually detaching the door from the garage door opener. The handle should be colored red and easy to see. The handle should be accessible and no more than six feet above the garage floor.

Garage Door Panels
From inside the garage, with the door fully closed, check the condition of the door panels. There shouldn’t be any cracks, loose pieces, separations or damage.

Warning Labels
From inside the garage, with the door fully closed, look for the following warning labels: (1) A spring warning label attached to the spring assembly, (2) A general warning label attached to the back of a door panel, (3) A warning label attached to the wall in the vicinity of the wall control button and (4) Two warning labels attached to the door in the vicinity of the bottom corner brackets. (Aside note: Some newer doors have tamper-resistant bottom corner brackets that will not require these warning labels.)

Spring and Hardware
With the door still in the closed position, look at the springs for damage. Don’t operate the door if a spring is broken. Operating the door with a damage component can cause serious injury or death. Recommend that the door be not used until the damaged spring is replaced by a trained door systems technician. Visually check the door’s hinges, brackets and fasteners. If the door has an opener, the door must have an opener reinforcement bracket that is securely attached to the door’s top section. The header bracket of the opener rail must be securely attached to the wall or header, using lag bolts or concrete anchors.

Door Operation
Close the door fully. If the door has an opener, pull the manual release to disconnect the door from the opener. Without straining yourself, manually lift and operate the door by grasping the door in a safe place where your fingers cannot be pinched or injured. If the door is hard to lift, then it is out of balance. This is a hazardous condition, and correction by a technician should be recommended.

Raise the door to the fully open position. Then close the door. The door should move freely without difficulty. But it should not open or close more quickly than the force applied. If the door is difficult to open or close, the door should be inspected by a trained door systems technician.

The rollers should stay in the track. If any rollers fall out of the track, the door system should be repaired by a trained door systems technician.

After conducting this check, reconnect the door to the opener, if present. This is generally done by activating the opener until is reconnects itself to the door.

Spring Containment
The counterbalance system is usually comprised of torsion springs, mounted above the door header, or extension springs, which are usually found next to the horizontal track. When springs break, containment helps to prevent broken parts from flying dangerously in the garage. Torsion springs are already mounted on a shaft, which inherently provides containment. If the door has extension springs, verify that spring containment is present. Extension springs should be contained by a secure cable that runs through the center of the springs.

Wall Push Button
Locate the push-button on the wall. Measure the vertical distance between the button and the floor. The button should be at least five feet above the standing surface and high enough to be out of reach of small children. Press the push button to see if it successfully operates the door.

Photoelectric Eyes
Federal law states that residential garage door openers manufactured after 1992 must be equipped with photoelectric eyes or some other safety-reverse feature. If the garage door has an opener, then check to see if photoelectric eyes are installed. They should be near the floor, mounted to the left and right sides of the bottom door panel. The beam of the photoelectric eyes should not be greater than six inches above the floor.

Non-Contact Reversal Test
This check applies to door systems that are equipped with photoelectric eyes. Standing inside the garage and safely away from the path of the door, use the remote control or wall button to close the door. As the door is closing, wave an object in the path of the photoelectric eye beam. The door should immediately reverse and return to the fully open position.

Contact Reversal Test
In some rare instances, a contact reversal test could damage the door system when the opener’s force-setting has been improperly set or when the opener reinforcement bracket is not securely or appropriately attached to the top section. If you have any concerns that a contact reversal test may cause damage, don’t conduct the test. This check applies to doors with openers.

Begin this test with the door fully open. Under the center of the door, place a 2x4 piece of wood flat on the floor, in the path of the door. Standing inside the garage, but safely away from the path of the door, use the wall push button to close the door. When the door contacts the wood, the door should automatically reverse direction and return to the fully open position.



BEN GROMICKO
View Profile
Chief Operating Officer
Chief Academic Officer
NACHI.TV Producer
Certified Master Inspector®
Certified Professional Inspector®
Author Home Inspection Standards of Practice
Author IAC2 Mold Standards of Practice
Author Radon Mitigation System Standards of Practice
Author 12 Home Inspection Textbooks
Author 2 Home Maintenance Books
Author of 78 Online Education Courses
Producer of 400+ Training Videos
Instructor of 30,000+ Students in Live Online Classes
Reply With Quote
Find an InterNACHI certified Utah Home Inspector (and anywhere else in North America)
  #2  
Old 8/6/09, 11:50 PM
Scott Gilligan, CMI's Avatar
Scott Gilligan, CMI Scott Gilligan, CMI is offline
Certified Master Inspector ®
 
Join Date: May 2007
Location: Philadelphia, PA
Posts: 1,866
Send a message via AIM to sgilligan1 Send a message via MSN to sgilligan1 Send a message via Yahoo to sgilligan1
Default Re: Garage door inspection procedure

Quote:
Contact Reversal Test
In some rare instances, a contact reversal test could damage the door system when the opener’s force-setting has been improperly set or when the opener reinforcement bracket is not securely or appropriately attached to the top section. If you have any concerns that a contact reversal test may cause damage, don’t conduct the test. This check applies to doors with openers.

Begin this test with the door fully open. Under the center of the door, place a 2x4 piece of wood flat on the floor, in the path of the door. Standing inside the garage, but safely away from the path of the door, use the wall push button to close the door. When the door contacts the wood, the door should automatically reverse direction and return to the fully open position.
I never perform this test anymore the way it is described because of the potential damage that can result from a door not reversing. I use my forearm with my palm facing down to put under the door when it is several feet off the ground. Pay close attention to the bracket at the top of the door and the tension in the drive chain. If it is the screw type track, keep your eyes open for any resistance and listen for any noises indicating the hardware is not functioning properly. It doesn't take but a fraction of a second for a garage door to start to self destruct doing this test. I have seen it happen in the past and it isn't pretty. BTW...It wasn't me or my client who did it...It was the seller!
Reply With Quote
  #3  
Old 8/7/09, 12:18 AM
Keith Runquist Keith Runquist is offline
Certified Professional Inspector (CPI)
 
Join Date: Dec 2008
Location: Rapid City, SD
Posts: 636
Send a message via AIM to krunquist
Default Re: Garage door inspection procedure

I had a garage door self destruct last year. The builder did it on a new house. It buckled and actually fell to the ground. Fourtunatly no one was under it. The buyer, a young girl, almost broke down in tears. Builder blamed the sub. I laughed all the way back to the office.



Keith Runquist, CMI
Reply With Quote
  #4  
Old 8/7/09, 12:24 AM
Ben J. Gromicko's Avatar
Ben J. Gromicko Ben J. Gromicko is offline
InterNACHI Staff
 
Join Date: Nov 2003
Location: Boulder, CO
Posts: 5,725
Default Re: Garage door inspection procedure

I once had a two Harley Davidson sitting in a garage. I had to refuse to test the garage door. I didn't even open the door. Inspection restriction.

The use of a 2x4 comes from a test listed in/by UL. I think UL 325.

I just use my hand. I put my back to the closing door and grab the bottom of the door with my fingers while looking at the opener to check for deflection and bending that would indicate a possible problem prior to causing damage to the opener or door.



BEN GROMICKO
View Profile
Chief Operating Officer
Chief Academic Officer
NACHI.TV Producer
Certified Master Inspector®
Certified Professional Inspector®
Author Home Inspection Standards of Practice
Author IAC2 Mold Standards of Practice
Author Radon Mitigation System Standards of Practice
Author 12 Home Inspection Textbooks
Author 2 Home Maintenance Books
Author of 78 Online Education Courses
Producer of 400+ Training Videos
Instructor of 30,000+ Students in Live Online Classes
Reply With Quote
  #5  
Old 8/7/09, 1:38 AM
Frank Magdefrau's Avatar
Frank Magdefrau Frank Magdefrau is offline
Certified Professional Inspector (CPI) ®
 
Join Date: Nov 2003
Location: Hernando, MS
Posts: 4,342
Default Re: Garage door inspection procedure

Quote:
Originally Posted by sgilligan1 View Post
I never perform this test anymore the way it is described because of the potential damage that can result from a door not reversing. I use my forearm with my palm facing down to put under the door when it is several feet off the ground. Pay close attention to the bracket at the top of the door and the tension in the drive chain. If it is the screw type track, keep your eyes open for any resistance and listen for any noises indicating the hardware is not functioning properly. It doesn't take but a fraction of a second for a garage door to start to self destruct doing this test. I have seen it happen in the past and it isn't pretty. BTW...It wasn't me or my client who did it...It was the seller!
Sooner or later you will cause damage to a garage door by conducting a Contact Reversal Test of any kind.



Frank Magdefrau
Certified Master Inspector
DeSoto Home Inspection Services, LLC
3152 Big Ben S
Hernando, MS 38632
(901) 486-0421

InterNACHI Member since 2002
InterNACHI message board member since 2003
InterNACHI ESOP member from 2004 to 2010
Reply With Quote
  #6  
Old 8/7/09, 1:47 PM
Mark A. Timpani, CMI's Avatar
Mark A. Timpani, CMI Mark A. Timpani, CMI is online now
Certified Master Inspector
 
Join Date: May 2004
Location: Tucson, AZ
Posts: 3,281
Default Re: Garage door inspection procedure

Ben, I do the same with my hand... Never use a 2x anything!!




"Be Proud of Your Home, Go With Pride!"
'Not just a Home Inspection, but an Education'

Pride Property Inspections provides professional Home Inspections throughout Tucson and Southern Arizona including Pima, Cochise, Pinal, Santa Cruz, Graham counties.

Reply With Quote
  #7  
Old 9/17/17, 2:59 PM
Nick Gromicko, CMI's Avatar
Nick Gromicko, CMI Nick Gromicko, CMI is online now
Active Poster
 
Join Date: Aug 2002
Location: Nederland, Colorado
Posts: 63,842
Default Re: Garage door inspection procedure

Use your hand.
Reply With Quote
  #8  
Old 9/17/17, 3:17 PM
Mark E. Glowczynski's Avatar
Mark E. Glowczynski Mark E. Glowczynski is online now
Certified Professional Inspector (CPI)
 
Join Date: Apr 2010
Location: Will County Il
Posts: 573
Send a message via ICQ to mglowczynski
Default Re: Garage door inspection procedure

First and foremost...
Check for locks and bolts through the tracks prevent the door from opening.



Mark Glowczynski C.P.I.
Illinois Licensed Home Inspections
Certified Mold Inspections
Water Quality Assessments
http://righthomeinspect.com
http://www.facebook.com/joliethomeinspection
https://www.facebook.com/rightathome...nsandsolutions
Reply With Quote
  #9  
Old 9/17/17, 4:21 PM
Chuck Evans's Avatar
Chuck Evans Chuck Evans is online now
Certified Master Inspector ®
 
Join Date: Sep 2006
Location: Stagecoach, TX
Posts: 10,558
Default Re: Garage door inspection procedure

Quote:
Originally Posted by gromicko View Post
Use your hand.
All the door breakage is done by hand



Chuck Evans (TREC #7657)
Level III Infraspection Institute Certified Infrared Thermographer (#8402)
HomeCert Houston Home Inspections & Thermal Inspections Find us on Facebook
The Woodlands Home Inspections
Magnolia TX Home Inspections & Thermography


Houston, TX
_______________________
Awards Committee Member

SUBMIT YOUR AWARD NOMINATIONS HERE

The InterNACHI Awards Committee is the final authority of issuance of any award the committee offers.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Installing GFCI in garage with no ground cyezza Electrical Inspections 53 11/30/07 6:05 PM
Evaporative cooler in garage chellickson Inspecting HVAC Systems 9 7/23/07 1:08 AM
Garage ceiling & door header Al Barb Interior Inspections 7 3/27/07 1:07 PM
Garage Door Safety...No Reverse...Advice Please gliebig Exterior Inspections 33 3/17/07 8:28 PM
Garage fire rated wall jlybolt Interior Inspections 3 6/18/06 7:21 PM

All times are GMT -4. The time now is 12:54 AM.
no new posts