A local AHJ said that One supply duct opening at living room, (opposite wall from gas furnace) is adequate at supplying sufficient heat to All habitable rooms, including three bedrooms; Even with doors closed.
Attached Thumbnails
heat-source-every-room-p1010089.jpg   heat-source-every-room-p1010101.jpg  
Reply With Quote
  #2  
Old 1/25/13, 9:11 PM
Bob Elliott, 450.0002662's Avatar
Bob Elliott, 450.0002662 Bob Elliott, 450.0002662 is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 36,509
Default Re: Heat Source in Every Room?

Obviously you know more than him.
Thought the door was sinking in the first shot for a second .
Reply With Quote
  #3  
Old 1/25/13, 9:18 PM
Christopher Currins, CMI Christopher Currins, CMI is offline
Certified Professional Inspector (CPI)
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 15,834
Default Re: Heat Source in Every Room?

Quote:
Originally Posted by belliott View Post
Obviously you know more than him. I try.
Thought the door was sinking in the first shot for a second .
Also no thermostat, The knob at bottom right controls the heat.

I turned it up a little and within a few minutes 3 smoke alarms went off.
Reply With Quote
  #4  
Old 1/25/13, 9:21 PM
Bob Elliott, 450.0002662's Avatar
Bob Elliott, 450.0002662 Bob Elliott, 450.0002662 is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 36,509
Default Re: Heat Source in Every Room?

Quote:
Originally Posted by ccurrins View Post
Also no thermostat, The knob at bottom right controls the heat.

I turned it up a little and within a few minutes 3 smoke alarms went off.
Yikes...how old is that thing?
Time to update.
Reply With Quote
  #5  
Old 1/25/13, 9:30 PM
Christopher Currins, CMI Christopher Currins, CMI is offline
Certified Professional Inspector (CPI)
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 15,834
Default Re: Heat Source in Every Room?

Quote:
Originally Posted by belliott View Post
Yikes...how old is that thing?
Time to update.
Old, probably original, house built in the mid-40's. Manufacturer is "Winkler", Lebanon Indiana, serial # 2239.
Reply With Quote
  #6  
Old 1/25/13, 11:28 PM
Cameron Anderson's Avatar
Cameron Anderson Cameron Anderson is offline
InterNACHI Member
 
Join Date: Nov 2011
Location: Peoria, IL
Posts: 6,988
Please Note: canderson5 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Heat Source in Every Room?

Quote:
Originally Posted by ccurrins View Post
A local AHJ said that One supply duct opening at living room, (opposite wall from gas furnace) is adequate at supplying sufficient heat to All habitable rooms, including three bedrooms; Even with doors closed.
When did he say it, 1940?
Reply With Quote
  #7  
Old 1/25/13, 11:47 PM
Juan C. Jimenez Juan C. Jimenez is offline
Certified Professional Inspector (CPI)
 
Join Date: Jan 2012
Location: central va
Posts: 7,375
Default Re: Heat Source in Every Room?

Were you writing up lack of heat sources in the rooms?



Juan Jimenez
A House on a Rock Home Inspections LLC
God. Family. Home.
804-269-4321
Richmond Home Inspector
Richmond Chimney Sweep
Richmond Radon Testing


Reply With Quote
  #8  
Old 1/26/13, 12:19 AM
Jeffrey R. Pope, CMI's Avatar
Jeffrey R. Pope, CMI Jeffrey R. Pope, CMI is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 13,391
Default Re: Heat Source in Every Room?

The AHJ is correct. The requirement for heat does not say that it has be be distributed via duct to each room. The heater has to be capable of heating every room to a minimum of 70 degrees, measured 36" above the base board. Simple as that.

Even if it's 90 degrees in the room where the heater is located, if the habitable spaces reach 70 degrees, it's compliant.

Smoke detectors will often sound when a unit is fired-up for the first time of the season. The dust that has accumulated on the burner chambers will smoke.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #9  
Old 1/26/13, 12:30 AM
Christopher Currins, CMI Christopher Currins, CMI is offline
Certified Professional Inspector (CPI)
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 15,834
Default Re: Heat Source in Every Room?

Quote:
Originally Posted by jpope View Post
The AHJ is correct. The requirement for heat does not say that it has be be distributed via duct to each room. The heater has to be capable of heating every room to a minimum of 70 degrees, measured 36" above the base board. Simple as that.

Even if it's 90 degrees in the room where the heater is located, if the habitable spaces reach 70 degrees, it's compliant.

Smoke detectors will often sound when a unit is fired-up for the first time of the season. The dust that has accumulated on the burner chambers will smoke.
if the habitable spaces reach 70 degrees, that's the if; when doors are closed preventing heat to enter. The furnace has been running all winter. It wasn't fired-up today.
Reply With Quote
  #10  
Old 1/26/13, 12:36 AM
Bob Elliott, 450.0002662's Avatar
Bob Elliott, 450.0002662 Bob Elliott, 450.0002662 is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 36,509
Default Re: Heat Source in Every Room?

Quote:
Originally Posted by jpope View Post
The AHJ is correct. The requirement for heat does not say that it has be be distributed via duct to each room. The heater has to be capable of heating every room to a minimum of 70 degrees, measured 36" above the base board. Simple as that.

Even if it's 90 degrees in the room where the heater is located, if the habitable spaces reach 70 degrees, it's compliant.

Smoke detectors will often sound when a unit is fired-up for the first time of the season. The dust that has accumulated on the burner chambers will smoke.
A bedroom is no longer a bedroom if the door must stay open.
You crazy cal guys do not need heat and in some cases no need for privacy. Lol
Reply With Quote
  #11  
Old 1/26/13, 12:46 AM
Paul Pendley Paul Pendley is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: CA
Posts: 1,541
Default Re: Heat Source in Every Room?

Quote:
Originally Posted by jpope View Post
The AHJ is correct. The requirement for heat does not say that it has be be distributed via duct to each room. The heater has to be capable of heating every room to a minimum of 70 degrees, measured 36" above the base board. Simple as that.

Even if it's 90 degrees in the room where the heater is located, if the habitable spaces reach 70 degrees, it's compliant.

Smoke detectors will often sound when a unit is fired-up for the first time of the season. The dust that has accumulated on the burner chambers will smoke.
You are right but wait til the appraiser comes around!!! Funny how they are now calling out things out now!!!



Premier Property Inspections
916-361-1021
Reply With Quote
  #12  
Old 1/26/13, 1:49 AM
Bob Elliott, 450.0002662's Avatar
Bob Elliott, 450.0002662 Bob Elliott, 450.0002662 is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 36,509
Default Re: Heat Source in Every Room?

Hi Paul
Please explain why you agree with Jeff besides you both being in a warm weather state.

Chris and I live in Illinois so do you think you can please explain for all of us the exact amount of air space required under a closed door for that 1940 furnace to push heated air into into a closed bedroom space and heat it to a required 70 degree temperature.

First explain how return vents work and why they are used then tell us if it is OK to open a window in in -50 degree weather as we sometimes get that in Illinois ,how about you ?

Back to subject bedrooms are required to have privacy so if the door must be open to heat the room is that OK ?

Thanks and glad you see it my way now .

P.S we do not surf here either .LOL
Reply With Quote
  #13  
Old 1/26/13, 5:51 AM
Cameron Anderson's Avatar
Cameron Anderson Cameron Anderson is offline
InterNACHI Member
 
Join Date: Nov 2011
Location: Peoria, IL
Posts: 6,988
Please Note: canderson5 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Heat Source in Every Room?

Bob's exaggerating, but only a little. The coldest day ever recorded in Illinois was -38F and it happened in 2009. So much for global warming in that location.

I really don't care what the construction standards might say, if a decent sized room(especially a bedroom) has no heat source, I call it out as a defect. It's too cold in this state to report it otherwise.
Reply With Quote
  #14  
Old 1/26/13, 6:15 AM
Joshua L. Frederick Joshua L. Frederick is online now
InterNACHI Member
 
Join Date: Jan 2007
Location: Defiance, OH
Posts: 3,467
Send a message via AIM to jfrederick
Default Re: Heat Source in Every Room?

Who cares about any requirements, codes, or whatever? Common sense to me and that's how I'd inform my clients. Like Cameron stated, that's how I'd report it - No/minminal heat at such and such areas - improve/correct as needed. If they are good with it (living with a central furnace), then so be it. I won't be living there and don't care. Maybe they'll leave the doors open at night so they can hear each other saying, "Goodnight, John Boy, Goodnight Mary Ellen"......
Reply With Quote
  #15  
Old 1/26/13, 9:39 AM
Jeffrey R. Pope, CMI's Avatar
Jeffrey R. Pope, CMI Jeffrey R. Pope, CMI is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 13,391
Default Re: Heat Source in Every Room?

Well, since the OP was inferring that the AHJ was "wrong" by stating that this is a compliant heat source, the thread was not about a "common sense" issue. The AHJ is correct according to construction standards and model codes.
Quote:
Originally Posted by belliott View Post
Back to subject bedrooms are required to have privacy so if the door must be open to heat the room is that OK ?
According to building standards, yes it is.

That certainly doesn't stop us from making recommendations for "upgrades," but to call this a defect is wrong.

Having the ability to heat a residence is a life/safety concern. Privacy is not.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
No heat source ragaian Miscellaneous Discussion for Inspectors 3 8/10/11 10:53 PM
Radiant heating in ceilings bleibgott Ancillary Inspection Services 13 4/26/10 9:27 PM
More Moisture Discoveries jpope Interior Inspections 30 8/16/07 1:54 AM
Heat source required in bathrooms menser Inspecting HVAC Systems 7 7/13/06 12:57 PM

All times are GMT -4. The time now is 9:09 AM.
no new posts