Inside a clothes closet, an incandescent luminaire mounted on the surface should have at least _____ inches of clearance from the nearest point of storage space.
Take a guess. (try to refrain from looking up the answer)
Bob…I thought I read 42 inches from lite to clothing, paper goods etc. I could not remember for sure so went with 24.
12 as Robert says is what code chek shows in diagram. Thats sounds way too close to flammables as you say.
The answer is 12" from bare incadescent bulb, but I note any bare bulb in report because you do not know what new owner will be placing in closet. It is a dangerous condition in my opinion.
Porcelain or plastic lampholders of the key less or pull chain types are not, and never were allowed in a clothes closet, because they are not considered as a fixture. See 410.8 in the NEC.
(B) Luminaire (Fixture) Types Permitted. Listed luminaires (fixtures) of the following types shall be permitted to be installed in a closet:
(1) A surface-mounted or recessed incandescent luminaire (fixture) with a completely enclosed lamp
(2) A surface-mounted or recessed fluorescent luminaire (fixture)
(D) Location. Luminaires (fixtures) in clothes closets shall be permitted to be installed as follows:
(1) Surface-mounted incandescent luminaires (fixtures) installed on the wall above the door or on the ceiling, provided there is a minimum clearance of 300 mm (12 in.) between the luminaire (fixture) and the nearest point of a storage space
(2) Surface-mounted fluorescent luminaires (fixtures) installed on the wall above the door or on the ceiling, provided there is a minimum clearance of 150 mm (6 in.) between the luminaire (fixture) and the nearest point of a storage space
(3) Recessed incandescent luminaires (fixtures) with a completely enclosed lamp installed in the wall or the ceiling, provided there is a minimum clearance of 150 mm (6 in.) between the luminaire (fixture) and the nearest point of a storage space
(4) Recessed fluorescent luminaires (fixtures) installed in the wall or the ceiling, provided there is a minimum clearance of 150 mm (6 in.) between the luminaire (fixture) and the nearest point of a storage space