Default Open vent in attic

Anyone know what I am seeing in the pic? It is two metal ducks about 5" diameter vented into a new townhouse attic. But from what?
Attached Thumbnails
Open vent in attic-inspns-031006-036-jpg  
Reply With Quote
  #2  
Old 3/10/06, 2:52 PM
Gerry Beaumont's Avatar
Gerry Beaumont Gerry Beaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,155
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: Open vent in attic

Quote:
Originally Posted by hvanderbeek
Anyone know what I am seeing in the pic? It is two metal ducks about 5" diameter vented into a new townhouse attic. But from what?
Hi Hank,

are they bathroon vents?

Regards

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #3  
Old 3/10/06, 2:57 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is online now
Certified Master Inspector
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 10,946
Send a message via Yahoo to jfunderburk
Default Re: Open vent in attic

My guess would be to provide combustion air, high and low, for a water heater or furnace in a closet.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
T. Roosevelt


Joe Funderburk, CBO, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
Angie's List Super Award Winner 2018, 2017, 2016, 2015, 2014, 2013, 2012, 2011, 2010.
Ph: 704-351-1776
www.aohomeinspection.com

Reply With Quote
  #4  
Old 3/10/06, 3:03 PM
tneumann's Avatar
tneumann tneumann is offline
Active Poster
 
Join Date: Jan 2006
Location: Woodland Park, co
Posts: 2,053
Please Note: tneumann is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Open vent in attic

Quack Quack
Reply With Quote
  #5  
Old 3/10/06, 7:26 PM
Jeff Merritt Jeff Merritt is online now
Certified Professional Inspector (CPI)
 
Join Date: Mar 2005
Location: Chicago, IL
Posts: 1,785
Default Re: Open vent in attic

If they are for combustion air most likley, they should be a little higher than the inslation,
Reply With Quote
  #6  
Old 3/10/06, 8:35 PM
Tim K. Brown Tim K. Brown is offline
New User
 
Join Date: Feb 2005
Location: Omaha, NE
Posts: 12
Please Note: tbrown1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Open vent in attic

Hank:
Looks like back to back exhaust vents for bathrooms. Any chance your master and guest bathrooms share the same wall run' like in some split entry homes? That would be logical, except they should have run flexible ducts to near the roof vents to prevent moisture condensation issues in the insulation,, if that's what we're looking at here. My 2 cents

Tim Brown,
AAHI Inc.
Reply With Quote
  #7  
Old 3/10/06, 8:43 PM
Larry Kage, CMI's Avatar
Larry Kage, CMI Larry Kage, CMI is offline
Certified Master Inspector ®
 
Join Date: Jul 2004
Location: NW, MI
Posts: 18,643
Default Re: Open vent in attic

Quote:
Originally Posted by tbrown1
Hank:
Looks like back to back exhaust vents for bathrooms. Any chance your master and guest bathrooms share the same wall run' like in some split entry homes? That would be logical, except they should have run flexible ducts to near the roof vents to prevent moisture condensation issues in the insulation,, if that's what we're looking at here. My 2 cents

Tim Brown,
AAHI Inc.
If that's what they are, I recommend they are run to the exterior.

Experience has taught me to run them under the insulation to the gable if possible to minimize condensing.

Might be different in NE.
Reply With Quote
  #8  
Old 3/11/06, 8:59 AM
Hank Vanderbeek, MPA, CMI Hank Vanderbeek, MPA, CMI is offline
Certified Master Inspector
 
Join Date: Feb 2004
Location: Bedford, NH
Posts: 59
Default Re: Open vent in attic

Thanks for the feedback. I am going to recommend it be evaluated by a specialist. My training is nothing should be terminated into the attic. Wouldn't a combustion air vent in the attic draw moist air into the furnace? Wouldn't it better to run the combustion air vent to the outside as is normally done?
Reply With Quote
  #9  
Old 3/11/06, 10:49 AM
Hank R. Spinnler's Avatar
Hank R. Spinnler Hank R. Spinnler is offline
Community Guest
 
Join Date: Apr 2005
Location: Hoschton, GA
Posts: 193
Please Note: hspinnler is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Open vent in attic

Hi Hank, these can be one of two things, one would be bathroom exhaust vent fans terminating directly into the attic instead of to the outdoors. Here in Georgia, you will see that alot on home built before the early 1990's.

Otherwise, it is attic combustion air for one or more gas fired appliances including water heater or furnace. Section M1703.3 of the 2003 IRC states "attic ventilation shall be sufficient to provide the required volume of combustion air" and "The combustion air opening shall be provided with a metal sleeve extending from the appliance enclosure to at least 6 inches above the top of the ceiling joists and ceiling insulation."

There are sizing requirements based on Btu/h input rating of appliances. Two openings inside the closet should be both within 12" of the top and 12" within the bottom of the enclosure. Common violations here.

Hope this helps.
Reply With Quote
  #10  
Old 3/11/06, 11:40 AM
Michael W. Gault's Avatar
Michael W. Gault Michael W. Gault is offline
Certified Master Inspector ®
 
Join Date: Apr 2005
Location: Mount Pleasant, SC
Posts: 1,093
Default Re: Open vent in attic

Quote:
Originally Posted by hvanderbeek
Thanks for the feedback. I am going to recommend it be evaluated by a specialist. My training is nothing should be terminated into the attic. Wouldn't a combustion air vent in the attic draw moist air into the furnace? Wouldn't it better to run the combustion air vent to the outside as is normally done?
Most (nearing 90%) of New Construction in SC terminates the bathroom vents in the attic space. Most via the white flexible ducting tied off to a truss member 36 inches or so above the blown in insulation...

Those that don't terminate in the attic run to a soffit to vent (and we all know the laws of thermodynamics apply to this setup )



- Mike

Michael W. Gault, SC RBI 1728
A to Z Home Inspections
Charleston, Dorchester & Berkeley Counties in S.C.
NACHI05040682
www.atozinspector.com

(843) 442-9755
Charleston Home Inspector
Reply With Quote
  #11  
Old 3/11/06, 12:29 PM
Hank Vanderbeek, MPA, CMI Hank Vanderbeek, MPA, CMI is offline
Certified Master Inspector
 
Join Date: Feb 2004
Location: Bedford, NH
Posts: 59
Default Re: Open vent in attic

Fantastic Hank. Thanks much!! This was an issue in another unit by the same builder and the duck was > 12" above insulation. Thanks all for your responses. What a great way to communicate.

Hank V.
Reply With Quote
  #12  
Old 3/12/06, 1:04 AM
Will Handley's Avatar
Will Handley Will Handley is offline
Active Poster
 
Join Date: Sep 2004
Location: Laguna Niguel, CA
Posts: 2,090
Please Note: whandley is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Open vent in attic

Do combustion air vents require screen mesh to prevent rodents and or vermin from entering the interior structure?
Reply With Quote
  #13  
Old 3/12/06, 9:08 AM
jbromwell jbromwell is offline
New User
 
Join Date: Jan 2006
Location: CUMMING, GA
Posts: 2
Please Note: jbromwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Open vent in attic

If there is a clothes dryer in the same area as a gas water heater and the area can be closed off by a door then the dryer has the potential to draw the air away from the heater and cause the flame to go out. The vent into the space above will prevent this from happening. It does not have to be high or low, it just has to be able to draw air into the area.
Reply With Quote
  #14  
Old 3/20/06, 7:44 PM
Denny a. Proulx Denny a. Proulx is offline
InterNACHI Member
 
Join Date: Feb 2006
Location: edmonton alberta canada
Posts: 8
Send a message via MSN to dproulx
Default Re: Open vent in attic

Did I take it that running bath exhaust to a soffit vent is a bad idea? And I'm glad to clear up that there are indeed "Metal Ducks". I expend a lot of ammunition on these stealthy waterfowl each fall, and just KNEW they had to be armor plated...Den
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
vent pipe in attic brepanshek Inspecting HVAC Systems 2 3/6/07 2:32 PM
Gas and oil hot water tank and Boiler Share Vents hvanderbeek Miscellaneous Discussion for Inspectors 8 1/25/07 5:22 PM
Open attic access from garage jveivia Interior Inspections 13 7/26/06 12:01 PM

All times are GMT -4. The time now is 7:32 PM.
no new posts