Default Weird framing for a Truss system, thoughts?

I attached the photos of the truss system I inspected this morning. No ridge board? The Trusses are also 24 inches on center for the most part. There is an area where they are less than 16 inches on center.

Not sure what to recommend here. Anyone have any recommendations?

Last edited by pmurphy5; 6/30/18 at 10:58 PM..
Reply With Quote
Need a home inspection in Maine? Check out InterNACHI's listing of Maine certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 6/29/18, 9:15 PM
Patrick Murphy Patrick Murphy is offline
Certified Professional Inspector (CPI) ®
 
Join Date: Jun 2017
Posts: 30
Default Re: Weird framing for a Truss system, thoughts?

Built in 88.
Reply With Quote
  #3  
Old 6/29/18, 9:32 PM
Larry Kage, CMI's Avatar
Larry Kage, CMI Larry Kage, CMI is offline
Certified Master Inspector ®
 
Join Date: Jul 2004
Location: NW, MI
Posts: 18,523
Default Re: Weird framing for a Truss system, thoughts?

What makes you think it is a
Quote:
Weird framing for a Truss system,...?
I don't believe I have ever seen a truss system with a ridge board and 24" on center is normal...16" o.c. is stronger, no?

The center struts do look a little out of alignment, though, and I can't tell if there is any diagonal bracing needed from the pictures.




Awards Committee Officer
SUBMIT YOUR AWARD NOMINATIONS HERE:
http://co.nachi.org/inachiawards/

The InterNACHI Awards Committee is the final authority of the issuance of any award the committee offers and any rules interpretation updates.
____________________________________________

Larry Kage, CMI Lifetime Member
State Licensed Builder since 1973
InterNACHI Lifetime Member
~retired~

The above post represents my personal opinion.
Reply With Quote
  #4  
Old 6/29/18, 9:36 PM
Larry Kage, CMI's Avatar
Larry Kage, CMI Larry Kage, CMI is offline
Certified Master Inspector ®
 
Join Date: Jul 2004
Location: NW, MI
Posts: 18,523
Default Re: Weird framing for a Truss system, thoughts?

Quote:
Originally Posted by pmurphy5 View Post
I attached the photos of the truss system I inspected this morning. No ridge board? The Trusses are also 24 inches on center for the most part. There is an area where they are less than 16 inches on center.

Not sure what to recommend here. Anyone have any recommendations?


Were the center struts loose anywhere, especially on the bottom?




Awards Committee Officer
SUBMIT YOUR AWARD NOMINATIONS HERE:
http://co.nachi.org/inachiawards/

The InterNACHI Awards Committee is the final authority of the issuance of any award the committee offers and any rules interpretation updates.
____________________________________________

Larry Kage, CMI Lifetime Member
State Licensed Builder since 1973
InterNACHI Lifetime Member
~retired~

The above post represents my personal opinion.
Reply With Quote
  #5  
Old 6/29/18, 9:37 PM
Dave Fetty, CMI's Avatar
Dave Fetty, CMI Dave Fetty, CMI is online now
Certified Master Inspector ®
 
Join Date: Feb 2014
Location: Naples all SWFL
Posts: 12,064
Default Re: Weird framing for a Truss system, thoughts?

24" OC is fine, as with anything less. Typically truss members over 5' have some type of bracing, stiff/strong back and/or horizontal bracing across the trusses is common practice. Blueprints should be reviewed to make a definitive recommendation.




Dave Fetty Certified Master Inspector
Florida Home Inspection And Property Services LLC
www.FHIAPS.COM
www.NaplesBestInspector.com
www.FortMyersInspector.com
Naples, Marco Island, Ft. Myers, Bonita Springs, Estero, Cape Coral
Dfetty@FHIAPS.COM
http://https://www.facebook.com/pages/Flori...2450912?ref=hl
Florida Radon Measurement Technician R2547
(239)339-7380
Reply With Quote
  #6  
Old 6/29/18, 9:43 PM
Larry Kage, CMI's Avatar
Larry Kage, CMI Larry Kage, CMI is offline
Certified Master Inspector ®
 
Join Date: Jul 2004
Location: NW, MI
Posts: 18,523
Default Re: Weird framing for a Truss system, thoughts?

Quote:
Originally Posted by sfetty View Post
24" OC is fine, as with anything less. Typically truss members over 5' have some type of bracing, stiff/strong back and/or horizontal bracing across the trusses is common practice. Blueprints should be reviewed to make a definitive recommendation.
That's coming back to me now, Dave...10' max spacing on lateral bracing (or, less distance on long spans for temporary),and as prints show for permanent.

https://prairietruss.com/wp-content/...cing-Guide.pdf




Awards Committee Officer
SUBMIT YOUR AWARD NOMINATIONS HERE:
http://co.nachi.org/inachiawards/

The InterNACHI Awards Committee is the final authority of the issuance of any award the committee offers and any rules interpretation updates.
____________________________________________

Larry Kage, CMI Lifetime Member
State Licensed Builder since 1973
InterNACHI Lifetime Member
~retired~

The above post represents my personal opinion.

Last edited by lkage; 6/29/18 at 9:50 PM..
Reply With Quote
  #7  
Old 6/29/18, 10:42 PM
Christopher Currins, CMI Christopher Currins, CMI is offline
Certified Master Inspector ®
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 17,686
Default Re: Weird framing for a Truss system, thoughts?

What you have is a typical truss system. No visible issues. Trusses do Not have a ridge board. 24 inch on center is common.

You should consider brushing up on the Basic fundamentals of residential construction.
Reply With Quote
  #8  
Old 6/29/18, 10:48 PM
Bradley K. Toye, CMI's Avatar
Bradley K. Toye, CMI Bradley K. Toye, CMI is online now
Certified Master Inspector
 
Join Date: Sep 2010
Location: Clearwater, FL
Posts: 5,414
Default Re: Weird framing for a Truss system, thoughts?

Truss systems don't have ridge boards, and they are 99% of the time 24" OC. Is this the new norm now? Are we not getting the proper training anymore?



Brad K Toye
ITC/FLIR Level I Building Investigation Thermographer
FL Certified Building Contractor CBC034303
FL Certified Home Inspector HI 391
FL Certified Mold Assessor MRSA 589

727-403-5029
Lecsi2@gmail.com
Reply With Quote
  #9  
Old 6/29/18, 10:58 PM
Larry Kage, CMI's Avatar
Larry Kage, CMI Larry Kage, CMI is offline
Certified Master Inspector ®
 
Join Date: Jul 2004
Location: NW, MI
Posts: 18,523
Default Re: Weird framing for a Truss system, thoughts?

Quote:
Originally Posted by ccurrins View Post
What you have is a typical truss system. No visible issues. Trusses do Not have a ridge board. 24 inch on center is common.

You should consider brushing up on the Basic fundamentals of residential construction.
It would help immensely.


Quote:
Originally Posted by btoye View Post
Truss systems don't have ridge boards, and they are 99% of the time 24" OC. Is this the new norm now? Are we not getting the proper training anymore?
It appears so...CMI, too?




Awards Committee Officer
SUBMIT YOUR AWARD NOMINATIONS HERE:
http://co.nachi.org/inachiawards/

The InterNACHI Awards Committee is the final authority of the issuance of any award the committee offers and any rules interpretation updates.
____________________________________________

Larry Kage, CMI Lifetime Member
State Licensed Builder since 1973
InterNACHI Lifetime Member
~retired~

The above post represents my personal opinion.

Last edited by lkage; 6/30/18 at 4:58 PM..
Reply With Quote
  #10  
Old 6/30/18, 12:55 PM
Dave Fetty, CMI's Avatar
Dave Fetty, CMI Dave Fetty, CMI is online now
Certified Master Inspector ®
 
Join Date: Feb 2014
Location: Naples all SWFL
Posts: 12,064
Default Re: Weird framing for a Truss system, thoughts?

Quote:
Originally Posted by lkage View Post
That's coming back to me now, Dave...10' max spacing on lateral bracing (or, less distance on long spans for temporary),and as prints show for permanent.

https://prairietruss.com/wp-content/...cing-Guide.pdf
I am thinking of concrete tile roof systems I see here almost daily to
lighter materials would have different requirements .




Dave Fetty Certified Master Inspector
Florida Home Inspection And Property Services LLC
www.FHIAPS.COM
www.NaplesBestInspector.com
www.FortMyersInspector.com
Naples, Marco Island, Ft. Myers, Bonita Springs, Estero, Cape Coral
Dfetty@FHIAPS.COM
http://https://www.facebook.com/pages/Flori...2450912?ref=hl
Florida Radon Measurement Technician R2547
(239)339-7380
Reply With Quote
  #11  
Old 6/30/18, 1:09 PM
Marcel R. Cyr, CMI's Avatar
Marcel R. Cyr, CMI Marcel R. Cyr, CMI is offline
Certified Master Inspector ®
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 31,164
Default Re: Weird framing for a Truss system, thoughts?

Quote:
Originally Posted by pmurphy5 View Post
I attached the photos of the truss system I inspected this morning. No ridge board? The Trusses are also 24 inches on center for the most part. There is an area where they are less than 16 inches on center.

Not sure what to recommend here. Anyone have any recommendations?
Mr. Murphy, I am sorry but if you have been doing 20 years of Inspections and a CMI as you claim on your Website, and don't recognize a standard roof truss system, you are definitely doing the public an injustice and falsifying your credentials to make an unethical charge for your services.

I would highly recommend another line of work to fit your capabilities.




CMI 2004-2017 Retired

Awards Committee Member
U.S. Member of the Year Winner 2009
45 Years Residential/Commercial Builder
Submit your AWARDS NOMINATIONS here
The InterNACHI Awards Committee is the final authority of issuance of any award the committee offers and any rules updates.
Reply With Quote
  #12  
Old 6/30/18, 1:24 PM
Patrick Murphy Patrick Murphy is offline
Certified Professional Inspector (CPI) ®
 
Join Date: Jun 2017
Posts: 30
Default Re: Weird framing for a Truss system, thoughts?

Quote:
Originally Posted by mcyr View Post
Mr. Murphy, I am sorry but if you have been doing 20 years of Inspections and a CMI as you claim on your Website, and don't recognize a standard roof truss system, you are definitely doing the public an injustice and falsifying your credentials to make an unethical charge for your services.

I would highly recommend another line of work to fit your capabilities.

First, I am not a CMI, nor have I ever said I am. I would recommend you read the entire page (instead of the header) before you assume, and go out of your way to insult them.

In this photo you can see a ridge beam.
Ridge board must not be the right terminology for this system. I know it's not required but the truss webbing is at an angle I have never seen before. Not to mention an improperly supported package unit on the roof. I was asking for thoughts not insults. Thanks for the advice...
Attached Thumbnails
Weird framing for a Truss system, thoughts?-p6290056-jpg  

Last edited by pmurphy5; 6/30/18 at 1:37 PM..
Reply With Quote
  #13  
Old 6/30/18, 2:04 PM
Bradley K. Toye, CMI's Avatar
Bradley K. Toye, CMI Bradley K. Toye, CMI is online now
Certified Master Inspector
 
Join Date: Sep 2010
Location: Clearwater, FL
Posts: 5,414
Default Re: Weird framing for a Truss system, thoughts?

Quote:
Originally Posted by pmurphy5 View Post
First, I am not a CMI, nor have I ever said I am. I would recommend you read the entire page (instead of the header) before you assume, and go out of your way to insult them.

In this photo you can see a ridge beam.
Ridge board must not be the right terminology for this system. I know it's not required but the truss webbing is at an angle I have never seen before. Not to mention an improperly supported package unit on the roof. I was asking for thoughts not insults. Thanks for the advice...
That's not a ridge board. It's part of gable end bracing, and not adequate for high wind loading. There is plenty of information out there on truss systems to research.



Brad K Toye
ITC/FLIR Level I Building Investigation Thermographer
FL Certified Building Contractor CBC034303
FL Certified Home Inspector HI 391
FL Certified Mold Assessor MRSA 589

727-403-5029
Lecsi2@gmail.com
Reply With Quote
Need a home inspection in Maine? Check out InterNACHI's listing of Maine certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 6/30/18, 3:30 PM
Patrick Murphy Patrick Murphy is offline
Certified Professional Inspector (CPI) ®
 
Join Date: Jun 2017
Posts: 30
Default Re: Weird framing for a Truss system, thoughts?

Quote:
Originally Posted by lkage View Post
What makes you think it is a

I don't believe I have ever seen a truss system with a ridge board and 24" on center is normal...16" o.c. is stronger, no?

The center struts do look a little out of alignment, though, and I can't tell if there is any diagonal bracing needed from the pictures.
The center struts were twisted. And they look out of allignment to me. Ive seen 24 and 16 OC obviously. I just don't normally see both used in one house.
Reply With Quote
  #15  
Old 6/30/18, 5:01 PM
Larry Kage, CMI's Avatar
Larry Kage, CMI Larry Kage, CMI is offline
Certified Master Inspector ®
 
Join Date: Jul 2004
Location: NW, MI
Posts: 18,523
Default Re: Weird framing for a Truss system, thoughts?

Quote:
Originally Posted by sfetty View Post
I am thinking of concrete tile roof systems I see here almost daily to
lighter materials would have different requirements .
Yes, we don't see much of that up here.




Awards Committee Officer
SUBMIT YOUR AWARD NOMINATIONS HERE:
http://co.nachi.org/inachiawards/

The InterNACHI Awards Committee is the final authority of the issuance of any award the committee offers and any rules interpretation updates.
____________________________________________

Larry Kage, CMI Lifetime Member
State Licensed Builder since 1973
InterNACHI Lifetime Member
~retired~

The above post represents my personal opinion.