Default Electrical Panel Clearance

The seller of this house is debating the fact that the house was built in the 1980's and that his "electrician friend" told him that there were no electrical panel clearance requirements in the code back then.

I found in the NEC 110.26 that there were requirements for workspace clearances all the way back to 1965, the dimensions have changes, but the requirement has been there for decades.

Look at the picture and please let me know your thoughts. The tub platform extends to the wall the the panel is on. I had to stand on it to remove the panel cover.

electrical-panel-clearance-panel-workspace.jpg




Andrew Constantine
InspectPro Home Inspections
Serving NC and SC
Charlotte NC Home Inspections
Reply With Quote
Need a home inspection in Vermont? Check out InterNACHI's listing of Vermont certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 11/29/12, 3:24 PM
Thomas Witt's Avatar
Thomas Witt Thomas Witt is offline
InterNACHI Member
 
Join Date: Aug 2010
Location: Paris, New York, Baltimore
Posts: 4,174
Default Re: Electrical Panel Clearance

As you already know the sparkys feelings about this matter don't matter here. The code does and even more so common sense rules over this situation. Panel or tub have to be moved! Problem is that unless they can turn it around in the wall cavity they'll have to run a new SEC for the new location.
Reply With Quote
  #3  
Old 11/29/12, 4:27 PM
David A. Andersen, TN HI# 40's Avatar
David A. Andersen, TN HI# 40 David A. Andersen, TN HI# 40 is offline
Certified Professional Inspector (CPI)
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 9,306
Default Re: Electrical Panel Clearance

Clearance !?

WTF? It's a bathroom isn't it?!

Don't need no clearance in a bathroom...


...it can't be there in the first place.



"working together to get-IR-done" Chris Walsh
Bracebridge, Ontario:


David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #4  
Old 3/18/16, 2:52 PM
Jason L. Middleton Jason L. Middleton is offline
InterNACHI Student
 
Join Date: Mar 2016
Posts: 3
Default Re: Electrical Panel Clearance

Wow, long story short, this panel installation was in no way permitted and is not up to code past or present. Electrical codes surrounding distance from water/conductible sources have been around in Illinois since 1960!

Also viewing the panel there is other considerations such as the breaker height which is not met (main breaker is too high). The 30" clearance from the center of the panel is not met and the 36" clearance from the front is not met.

All the way around, even if the tub was removed; this load center would not pass code.
Reply With Quote
  #5  
Old 3/19/16, 12:12 AM
Dan Bowers, CMI's Avatar
Dan Bowers, CMI Dan Bowers, CMI is online now
Certified Professional Inspector (CPI)
 
Join Date: Oct 2003
Location: Shawnee Mission, KS
Posts: 7,757
Default Re: Electrical Panel Clearance

Andrew ..........................

You're wasting your time. Anytime I have SELLER tell me **************

I sweetly say, "Wow, thats good to know". To authenticate that, have your licensed, competent &%$#@* send me the reference in the code book that says thats OK".

NEVER let them make you prove your opinion ..... IF they question MY opinion, THEY need to send ME written proof. I got WAY to many things to do for me to be running around trying to give them proof I'm right.

Let them PROVE you're wrong.

The Home Inspection Expert

PS ........... Screw the clearances .... Listen to David A. regarding the bathroom location



Dan Bowers, CMI
Licensed Contractor / Builder
Certified IAQ2 Mold Inspector
Licensed HVAC Service Technician
EDI Certified Stucco / EIFS Inspector
Certified Commercial Building Inspector
iNACHI US Member of the Year 2010
ITC / FLIR - Level I Infrared Thermographer
FHA - 203k Inspector / Compliance Inspector
ICC Code Inspector (Plmbg, Elec, Mech, Bldg)
Reply With Quote
  #6  
Old 3/19/16, 12:48 AM
Nick Gromicko's Avatar
Nick Gromicko Nick Gromicko is online now
InterNACHI Staff
 
Join Date: Aug 2002
Location: Nederland, Colorado
Posts: 55,694
Default Re: Electrical Panel Clearance

https://www.nachi.org/gallery/electr...pace-depth.jpg



Nick Gromicko, Certified Master Inspector
President, Contractors Association
Author, How to Run a Successful Home Inspection Business
Founder, InterNACHI
Owner,Nick Gromicko General Contractor
Author, STACKS: A Home Inspector's Guide to Increasing Gross Revenue


"Just as iron sharpens iron, one man sharpens another."- Proverbs 27:17
Planet InterNACHI.... resistance is futile.
Reply With Quote
  #7  
Old 3/19/16, 5:58 AM
Joshua L. Frederick Joshua L. Frederick is online now
Certified Professional Inspector (CPI)
 
Join Date: Jan 2007
Location: Defiance, OH
Posts: 3,545
Send a message via AIM to jfrederick
Default Re: Electrical Panel Clearance

Quote:
Originally Posted by gromicko View Post
I like this graphic, but I don't use it because I thought the wording "service equipment" implies main service disconnects/panels only. Not accurate when using the graphic for a remote distribution (sub) panel.

Am I wrong in my thinking?

Thanks in advance.




http://northwestohiohomeinspector.com

Defiance home inspector
Northwest Ohio home inspector
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Help proof the safety section on inspecting electrical panels: read here kshepard Electrical Inspections 58 6/8/14 4:52 PM
Electrical panel rating question lking Electrical Inspections 6 2/10/12 9:51 PM
Electrical Safety Foundation International Links jtedesco1 Electrical Inspections 5 12/8/07 3:10 PM
Bad electrical problem Pest Guy Electrical Inspections 4 1/20/06 9:26 PM

All times are GMT -4. The time now is 3:00 AM.
no new posts