Default Deck joist hangers

Deck joist hangers are supposed to be full height, is that correct?
But how would you word it?
"Deck joist hangers should be full height, further evaluation by a licensed contractor is recommended".?
Attached Thumbnails
Deck joist hangers-img_1731-jpg  
Reply With Quote
Need a home inspection in Alaska? Check out InterNACHI's listing of Alaska certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 5/9/18, 12:15 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is online now
Certified Professional Inspector (CPI) ®
 
Join Date: Feb 2007
Location: Minnesota & Northern Iowa
Posts: 30,272
Default Re: Deck joist hangers

Hangars are rated by load capacity and function, not size. Recommend that you peruse the Simpson Strong-Tie website, especially their FREE education offerings!



Jeffrey R. Jonas
Owatonna, Minnesota



"I am not a teacher, but an awakener."
- Robert Frost, American poet (1874-1963).

"We Respect Our Clients Right to Privacy"

Reply With Quote
  #3  
Old 5/9/18, 12:21 PM
Marcel R. Cyr, CMI's Avatar
Marcel R. Cyr, CMI Marcel R. Cyr, CMI is offline
Certified Master Inspector ®
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 30,082
Default Re: Deck joist hangers

You need to check the markings to see if they are marked for Some hangers are good for 2x8 and 2x10.
What size framing are we looking at?

I would be more concerned in noting how the ledger board was fastened and if flashing was installed at the wall attachment.



CMI 2004-2017 Retired

Awards Committee Member
U.S. Member of the Year Winner 2009
45 Years Residential/Commercial Builder
Submit your AWARDS NOMINATIONS here
The InterNACHI Awards Committee is the final authority of issuance of any award the committee offers.
Reply With Quote
  #4  
Old 5/9/18, 5:27 PM
John Olson John Olson is offline
Certified Professional Inspector (CPI)
 
Join Date: Aug 2014
Location: De Pere Wisconsin
Posts: 1,136
Default Re: Deck joist hangers

"I would be more concerned in noting how the ledger board was fastened and if flashing was installed at the wall attachment"
Speaking of that is there a place or a diagram that would tell me the correct amount of the new screws being used, that need to be installed on the ledger board.?
Reply With Quote
  #5  
Old 5/9/18, 5:35 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is online now
Certified Professional Inspector (CPI) ®
 
Join Date: Feb 2007
Location: Minnesota & Northern Iowa
Posts: 30,272
Default Re: Deck joist hangers

Quote:
Originally Posted by jolson8 View Post
"I would be more concerned in noting how the ledger board was fastened and if flashing was installed at the wall attachment"
Speaking of that is there a place or a diagram that would tell me the correct amount of the new screws being used, that need to be installed on the ledger board.?
The DCA-2 2015 is considered the "Bible" for decks, and the document that is used to create the codes for decks.


DCA 6 - Prescriptive Residential Wood Deck Construction Guide



Jeffrey R. Jonas
Owatonna, Minnesota



"I am not a teacher, but an awakener."
- Robert Frost, American poet (1874-1963).

"We Respect Our Clients Right to Privacy"

Reply With Quote
  #6  
Old 5/9/18, 5:55 PM
John Olson John Olson is offline
Certified Professional Inspector (CPI)
 
Join Date: Aug 2014
Location: De Pere Wisconsin
Posts: 1,136
Default Re: Deck joist hangers

I have that. It is the ledgerlok screws that I have concerns about, the distance between them on the ledger is it the same as lag screws or do they need more. The pattern is a W
Reply With Quote
  #7  
Old 5/9/18, 8:24 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is online now
Certified Professional Inspector (CPI) ®
 
Join Date: Feb 2007
Location: Minnesota & Northern Iowa
Posts: 30,272
Default Re: Deck joist hangers

Quote:
Originally Posted by jolson8 View Post
I have that. It is the ledgerlok screws that I have concerns about, the distance between them on the ledger is it the same as lag screws or do they need more. The pattern is a W
You need to go the the actual Manufacturer of the screws for specific details as all manufaturers are NOT equal. If you do as I suggested in my first post above, you will be able to view Strong-Ties product information on their product(s). You may not get so lucky with other manufacturers and will need to call them. DO NOT assume others are equal to SST, because they're not.



Jeffrey R. Jonas
Owatonna, Minnesota



"I am not a teacher, but an awakener."
- Robert Frost, American poet (1874-1963).

"We Respect Our Clients Right to Privacy"

Reply With Quote
  #8  
Old 5/10/18, 7:05 AM
Marcel R. Cyr, CMI's Avatar
Marcel R. Cyr, CMI Marcel R. Cyr, CMI is offline
Certified Master Inspector ®
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 30,082
Default Re: Deck joist hangers

Quote:
Originally Posted by jolson8 View Post
I have that. It is the ledgerlok screws that I have concerns about, the distance between them on the ledger is it the same as lag screws or do they need more. The pattern is a W
Check here John.

ICC-ES ESR 1078 – Technical Evaluation Reports – Technical Bulletins – CAD Drawings















CMI 2004-2017 Retired

Awards Committee Member
U.S. Member of the Year Winner 2009
45 Years Residential/Commercial Builder
Submit your AWARDS NOMINATIONS here
The InterNACHI Awards Committee is the final authority of issuance of any award the committee offers.
Reply With Quote
  #9  
Old 5/10/18, 7:37 PM
John Olson John Olson is offline
Certified Professional Inspector (CPI)
 
Join Date: Aug 2014
Location: De Pere Wisconsin
Posts: 1,136
Default Re: Deck joist hangers

Thanks Marcel
Reply With Quote
  #10  
Old 5/13/18, 11:31 PM
Eli Klugmann Eli Klugmann is online now
InterNACHI Applicant
 
Join Date: Jan 2018
Location: Clifton, NJ
Posts: 24
Default Re: Deck joist hangers

Thank you, and the ledger was nailed only! No lag bolts...
Reply With Quote
  #11  
Old 5/19/18, 3:14 PM
Kenton Shepard, CMI's Avatar
Kenton Shepard, CMI Kenton Shepard, CMI is offline
Certified Master Inspector
 
Join Date: Aug 2004
Location: Lyons, CO
Posts: 6,349
Send a message via ICQ to kshepard
Default Re: Deck joist hangers

Joist hangers typically don't have to be full height, they can be one size under; 2x8 hanger for 2x10 joists, for example.

DCA 6 - Prescriptive Residential Wood Deck Construction Guide is for new decks.

Some decks are built to some version of the IRC standards, the UBC standards, or to best practice, or they are just built. Unless you are performing a code inspection you might not want to call out things just because they don't comply with a standard, but instead, call out defective components (won't perform as designed) or safety issues, which is our mandate.

For example, those hangers were not hot-dipped galvanized or stainless steel as recommended by most standards. They were electro-coated galvanized steel hangers, which the manufacturer (Simpson StrongTie) says won't last as long as hot-dipped galvanized or stainless steel hangers, and that's all they say.

You could mention that in your report, but don't make a big deal out of it because most decks in the US are built using electro-coated galvanized steel hangers because they are what suppliers stock. Hot-dipped galvanized and stainless steel are special order and more expensive.

Those hangers looked like they were nailed with roofing nails, which if that's the case, is a more important defect and they should be replaced with 10d hanger nails if that's the case. And... of course recommend installation of lags or bolts at the ledger.

The thing about nailed ledgers is that when they're relatively new, if adequately nailed, that connection is fine. There have been hundreds of thousands of decks built with nailed ledgers. They eventually fail, but all decks eventually fail.

The big difference between nailed and lagged/bolted connections is that over time, due to moisture and thermal cycling, the nail holes will get bigger, nails will corrode and the nailed ledger connection will weaken at a faster rate than a lagged or bolted connection that doesn't depend on withdrawal of a smooth-shank fastener or shear failure of a relatively small-diameter fastener to prevent ledger separation.



Kenton Shepard, CMI Inspector/Instructor

InterNACHI Director of International Development
Director of Green Building
Builder: House of Horrors 1&2
Author: InterNACHI Narrative Library


Last edited by kshepard; 5/19/18 at 3:55 PM..
Reply With Quote
  #12  
Old 5/19/18, 4:02 PM
Kenton Shepard, CMI's Avatar
Kenton Shepard, CMI Kenton Shepard, CMI is offline
Certified Master Inspector
 
Join Date: Aug 2004
Location: Lyons, CO
Posts: 6,349
Send a message via ICQ to kshepard
Default Re: Deck joist hangers

Quote:
Originally Posted by jolson8 View Post
"I would be more concerned in noting how the ledger board was fastened and if flashing was installed at the wall attachment"
Speaking of that is there a place or a diagram that would tell me the correct amount of the new screws being used, that need to be installed on the ledger board.?
For years, best practice was one ½" lag every 2', staggered up and down, with two lags at the ends of each ledger board. Less is worse, more is better. The trick is deciding when it's inadequate, and the answer is to pass on the liability by recommending evaluation by a qualified contractor... or structural engineer, if the only contractor around is the guy who built the deck.



Kenton Shepard, CMI Inspector/Instructor

InterNACHI Director of International Development
Director of Green Building
Builder: House of Horrors 1&2
Author: InterNACHI Narrative Library

Reply With Quote
  #13  
Old 5/20/18, 7:04 AM
Marcel R. Cyr, CMI's Avatar
Marcel R. Cyr, CMI Marcel R. Cyr, CMI is offline
Certified Master Inspector ®
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 30,082
Default Re: Deck joist hangers

Should show you all you need here Kenton.

ICC-ES ESR 1078 – Technical Evaluation Reports – Technical Bulletins – CAD Drawings

and here; http://www.icc-es.org/reports/pdf_files//ESR-2442.pdf
https://www.grkfasteners.com/Portals...vs%203_new.pdf
Tech Bulletins









CMI 2004-2017 Retired

Awards Committee Member
U.S. Member of the Year Winner 2009
45 Years Residential/Commercial Builder
Submit your AWARDS NOMINATIONS here
The InterNACHI Awards Committee is the final authority of issuance of any award the committee offers.

Last edited by mcyr; 5/20/18 at 7:11 AM..
Reply With Quote
Need a home inspection in Alaska? Check out InterNACHI's listing of Alaska certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 5/20/18, 8:23 PM
Russell G. Cloyd's Avatar
Russell G. Cloyd Russell G. Cloyd is offline
Certified Professional Inspector (CPI)
 
Join Date: Nov 2003
Location: Greater Cincinnati
Posts: 416
Default Re: Deck joist hangers

The hanger should be stamped for the size of member it can handle. I would also be concerned about the lack of a visible flashing where the deck ledger board penetrates the siding.



Russell G. Cloyd
House 2 Home Inspections, LLC
859-739-7858

Certified Home Inspector
KY License #166164
Certified Radon Measurement Specialist
Certified IAC2 Mold Inspector
KY Fire Prevention Inspector
www.house2homeinspectionsllc.com
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off


All times are GMT -4. The time now is 12:54 AM.
no new posts