Default Deck Rail Cable Opinions Please

Came across this today and would appreciate some opinions.

The top portion has 2 cables running horizontally to meet the 4" gap requirment.

Near the center of the run it's easy to spread the cables to beyond 4"

I would like to hear some opinions on this Rail #1 construction.
Attached Thumbnails
deck-rail-cable-opinions-please-deck-rail.jpg  

Last edited by mlarson; 6/18/07 at 3:56 PM..
Reply With Quote
  #2  
Old 6/18/07, 3:49 PM
Bruce M. Graham's Avatar
Bruce M. Graham Bruce M. Graham is offline
Certified Professional Inspector (CPI)
 
Join Date: Sep 2005
Location: Gainesville, FL
Posts: 2,510
Default Re: Deck Rail Cable Opinions Please

In some areas they do not allow the horizontal details as it lends itself to the ladder affect. Check with your local ahj.






Bungalows to Mansions
Professional Inspection Services, LLC

Bruce M. Graham III, CMI

Gainesville, FL 32608
352 871 8989

Florida Licensed Home Inspector #HI10
CERTIFIED MASTER INSPECTOR
Certified Level II Infrared Thermographer
Radon Measurment Technician # R2279
NACHI05091592
ICC 5268478
www.BungalowstoMansions.com
Reply With Quote
  #3  
Old 6/18/07, 3:51 PM
Michael Larson's Avatar
Michael Larson Michael Larson is online now
Certified Professional Inspector (CPI)
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 70,065
Default Re: Deck Rail Cable Opinions Please

Bruce, Thanks for chiming in. I didn't consider that a problem as it was on the top 10" or so.

How about this rail example #2 ?
Attached Thumbnails
deck-rail-cable-opinions-please-rail-1146-.jpg  

Last edited by mlarson; 6/18/07 at 3:55 PM..
Reply With Quote
  #4  
Old 6/18/07, 3:57 PM
Bruce M. Graham's Avatar
Bruce M. Graham Bruce M. Graham is offline
Certified Professional Inspector (CPI)
 
Join Date: Sep 2005
Location: Gainesville, FL
Posts: 2,510
Default Re: Deck Rail Cable Opinions Please

Ya but I see all these custom decks with the pretty cable railings and wonder how they get away with it.

Yours may still be a ahj issue, I have known some that would look at that and say the railing is not tall enough because they will not take the top section into account.

I still get this http://deckmagazine.com/ from my remodeling days, lots of good info.






Bungalows to Mansions
Professional Inspection Services, LLC

Bruce M. Graham III, CMI

Gainesville, FL 32608
352 871 8989

Florida Licensed Home Inspector #HI10
CERTIFIED MASTER INSPECTOR
Certified Level II Infrared Thermographer
Radon Measurment Technician # R2279
NACHI05091592
ICC 5268478
www.BungalowstoMansions.com

Last edited by bgraham; 6/18/07 at 4:01 PM..
Reply With Quote
  #5  
Old 6/19/07, 8:35 PM
jkogel jkogel is offline
Active Poster
 
Join Date: Jan 2007
Location: Sooke, BC
Posts: 694
Please Note: jkogel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Deck Rail Cable Opinions Please

an Electric fence unit is all that's missing for rail #1.
Reply With Quote
  #6  
Old 8/19/12, 4:51 PM
Cameron Anderson's Avatar
Cameron Anderson Cameron Anderson is offline
Certified Professional Inspector (CPI)
 
Join Date: Nov 2011
Location: Peoria, IL
Posts: 6,989
Please Note: canderson5 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Deck Rail Cable Opinions Please

Quote:
Originally Posted by mlarson View Post
Bruce, Thanks for chiming in. I didn't consider that a problem as it was on the top 10" or so.
Perhaps that answers the original inquiry. I was thinking the same thing regarding the spread you mentioned which was easily greater than 4". Assuming it is okay with the local AHJ, I don't think a kid can fall through it and they definitely won't get their head stuck.

If the ladder affect isn't a concern due to it's height then the spread really wouldn't be a concern either. The ones I have come across with cables are all under much greater tension and the runs between posts are shorter. Wouldn't an extra post be required anyway?
Reply With Quote
  #7  
Old 8/19/12, 5:13 PM
Christopher Currins, CMI Christopher Currins, CMI is offline
Certified Master Inspector ®
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 16,843
Default Re: Deck Rail Cable Opinions Please

Quote:
Originally Posted by mlarson View Post

Near the center of the run it's easy to spread the cables to beyond 4"
I would mention exactly that in the report.
Reply With Quote
  #8  
Old 8/19/12, 5:39 PM
Marcel R. Cyr, CMI's Avatar
Marcel R. Cyr, CMI Marcel R. Cyr, CMI is offline
Certified Master Inspector ®
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 29,059
Default Re: Deck Rail Cable Opinions Please

http://en.wikipedia.org/wiki/Cable_railings
Cable flexibility is an important consideration in designing a cable railing. The old UBC (Uniform Building Code) and newer ICC (IBC and IRC) codes state that a 4” sphere shall not pass through any portion of a barrier on a guardrail rail. In a horizontal or vertical cable rail, the cables, once tensioned must be rigid enough to prevent deflecting enough for a 4 inch ball to pass. Factors influencing this rigidity are: the tension of the cable, intermediate posts (or cable spacers)spacing, the diameter of the cable, top rail cap material and the cable to cable spacing.
Cable Tension: An incredible amount of tension is generated on the end posts when ten or more cables, each tensioned at 200-400 Ibs. over a height of 36" to 42” exists. Many people do not understand the amount of the tension applied to the posts. Poorly designed end posts will result in a railing where the cables cannot be properly tensioned without an unacceptable amount of cable deflection. End posts to which the tensioning hardware attaches must be constructed so that they will not deflect perceptively as the cables are tensioned.
Post Spacing: Intermediate posts are posts which provide mounting for the top rail and have a vertical row of holes to support the cable as it passes through them. Since the post to post spacing is a primary driver of cable rigidity, the post to post spacing is very important (typically between 36" and 42").
Cable Diameter: The next variable is the diameter of the cable. Cables can be 1/8, 3/16 or 1/4 inch diameter. The larger the diameter, the more rigid (and costly) the cable.
Top rail: Top rail material must be strong as it is being compressed by the combined cable forces. Common top cap materials are the stronger species of wood or metal. Composite lumber is not suitable.
Cable to cable spacing: Spacing of the cables vertically is critical to minimize deflection of the cables. Most manufacturers recommended maximum vertical spacing of 3-inch free opening between cables when they are installed.
All of the above factors work together to minimize the deflection of the cable to prevent a 4” sphere from passing between the cables when they are properly tensioned in a well-designed frame.



Used this type of railing system on a Commercial Project, (no photos) before, and the above description is accurate.
You can not spread the cables inbetween supports.



CMI 2004-2017 Retired

Awards Committee Member
Inachi Award Winner 2009
45 Years Residential/Commercial Builder
Submit your AWARDS NOMINATIONS here
The InterNACHI Awards Committee is the final authority of issuance of any award the committee offers.
Reply With Quote
  #9  
Old 8/19/12, 5:57 PM
Cameron Anderson's Avatar
Cameron Anderson Cameron Anderson is offline
Certified Professional Inspector (CPI)
 
Join Date: Nov 2011
Location: Peoria, IL
Posts: 6,989
Please Note: canderson5 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Deck Rail Cable Opinions Please

Quote:
Originally Posted by mcyr View Post
Post Spacing: Intermediate posts are posts which provide mounting for the top rail and have a vertical row of holes to support the cable as it passes through them. Since the post to post spacing is a primary driver of cable rigidity, the post to post spacing is very important (typically between 36" and 42" ).
That right there seems to be the most important design point. You can tighten them to the point of being mostly immobile, but if they are shorter it takes a lot less tension.
Reply With Quote
  #10  
Old 8/19/12, 6:09 PM
kwood kwood is offline
Banned
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 11,820
Please Note: kwood is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Deck Rail Cable Opinions Please

There is a course on this at www.aecdaily.com and it explains all what Marcel has pointed out and even the cable being next to impossible for a child to climb.
They use them in High end buildings everywhere.
Reply With Quote
  #11  
Old 8/19/12, 6:34 PM
Marcel R. Cyr, CMI's Avatar
Marcel R. Cyr, CMI Marcel R. Cyr, CMI is offline
Certified Master Inspector ®
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 29,059
Default Re: Deck Rail Cable Opinions Please

Quote:
Originally Posted by mlarson View Post
Came across this today and would appreciate some opinions.

The top portion has 2 cables running horizontally to meet the 4" gap requirment.

Near the center of the run it's easy to spread the cables to beyond 4"

I would like to hear some opinions on this Rail #1 construction.
Mike, if you click on the oaconstruction link in my signature, go to Project Gallery and click on the Industrial link and then George & Barbara Bush Center/UNE and the pictures will show you a cable railing.

Look how close the rail posts are.

That is all that is needed in the photo you supplied.
Intermediate cable guide.



CMI 2004-2017 Retired

Awards Committee Member
Inachi Award Winner 2009
45 Years Residential/Commercial Builder
Submit your AWARDS NOMINATIONS here
The InterNACHI Awards Committee is the final authority of issuance of any award the committee offers.
Reply With Quote
  #12  
Old 8/19/12, 6:34 PM
Steven C. Waskewicz, CMI's Avatar
Steven C. Waskewicz, CMI Steven C. Waskewicz, CMI is offline
Certified Master Inspector
 
Join Date: Apr 2006
Location: Elbert, CO
Posts: 2,390
Default Re: Deck Rail Cable Opinions Please

Great link, thanks Kevin...Continuing Education courses...





Steven Waskewicz

Rest Assured Inspection Services, LLC.


719-510-7703 mobile all the time

Ask me about The Home Energy Score





Reply With Quote
  #13  
Old 8/19/12, 7:19 PM
Greg W. Mathias, CCHI, CMI's Avatar
Greg W. Mathias, CCHI, CMI Greg W. Mathias, CCHI, CMI is offline
Certified Master Inspector ®
 
Join Date: May 2010
Location: Lloydminster,Ab
Posts: 3,266
Default Re: Deck Rail Cable Opinions Please

In the NBC It say that the top 32" of the rail cannot be climbable. Not sure of the IRC but most of the time they are parallel



Greg Mathias, CCHI
Journeyman Carpenter
Level I Thermographer
Certified Master Inspector
Global Property Inspections
(780)205-9912
Reply With Quote
Need a home inspection in Oregon? Check out InterNACHI's listing of Oregon certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 8/20/12, 1:20 AM
Nick Gromicko, CMI's Avatar
Nick Gromicko, CMI Nick Gromicko, CMI is online now
Active Poster
 
Join Date: Aug 2002
Location: Nederland, Colorado
Posts: 60,120
Default Re: Deck Rail Cable Opinions Please

I don't like it at all for many reasons:
  • Ladder effect (I count 5 rungs on less than a 3' high rail... that's more rungs/foot than the ladder I use).
  • Child spacing (I'm sure the cables spread in the middle).
  • Tension will bow the top rail (and if it bows the top rail down, the middle may no longer meet rail height requirement).
  • Two cables running parallel (as you tighten one, the other is going to loosen).
  • Style (too eclectic).

Last edited by gromicko; 8/20/12 at 1:47 AM..
Reply With Quote
  #15  
Old 8/20/12, 5:15 AM
kwood kwood is offline
Banned
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 11,820
Please Note: kwood is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Deck Rail Cable Opinions Please

Nick even though you dont like them does not mean they have not been accepted. Reason is they cannot find any documentation of kids trying to climb them successfully I guess.
The cables are not easy to hang onto and it takes allot of effort just to hang on with your hands to climb not to mention coordinating that with stepping on the cable.
The cables are placed at 3 inches not 4 on some manufacturers so there is no way for a kid to get his head stuck.
But since this is BS go take the course and see.

Last edited by kwood; 8/20/12 at 5:20 AM..
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Short circuit failures with 12/3 NM-B cable and NM clamp connectors pabernathy Electrical Inspections 10 4/17/11 1:43 PM
Did you KNOW this about NM Cable? pabernathy Electrical Inspections 0 12/19/06 8:46 AM
Hey Joe Tedesco pbolliger Electrical Inspections 7 4/11/06 12:17 AM
Ceilings falling with wires in it. jsmith3 Interior Inspections 9 3/16/06 7:24 PM

All times are GMT -4. The time now is 8:42 AM.
no new posts