Default Ice Gaurd membrane

The home was built in 1974. A 2nd layer of architectural shingles were installed over the original roof.

I would assume there was no membrane installed for ice gaurd protection.

Would you report on this missing as I would believe it is required on a 4 year old roof.
Reply With Quote
  #2  
Old 5/9/07, 7:37 PM
Andrew J. Frost Andrew J. Frost is offline
Active Poster
 
Join Date: Jan 2007
Location: Conway, NH
Posts: 354
Please Note: afrost is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Ice Gaurd membrane

Quote:
Originally Posted by dmacy
The home was built in 1974. A 2nd layer of architectural shingles were installed over the original roof.

I would assume there was no membrane installed for ice gaurd protection.

Would you report on this missing as I would believe it is required on a 4 year old roof.
i would either ask grace (mnfct of ice & water shield) for their recommended practice or a shingle manufacturer
Reply With Quote
  #3  
Old 5/9/07, 8:58 PM
Marcel R. Cyr, CMI's Avatar
Marcel R. Cyr, CMI Marcel R. Cyr, CMI is offline
Certified Master Inspector ®
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 31,282
Default Re: Ice Gaurd membrane

David, If the new roofing was installed over the old roofing, the probability that ice and water shield was installed is close to none.

Most Roofing Manufacturers will knock off 5 years on their Warranty for doing it.
Since there are no Manufactures instructions for installing a double layer of roof shingle on the packages, I would have to note that it was double layered and does not comply to a new Manufacturers installation procedure.

Marcel
</IMG></IMG>



CMI 2004-2017 Retired

Awards Committee Member
U.S. Member of the Year Winner 2009
45 Years Residential/Commercial Builder
Submit your AWARDS NOMINATIONS here
The InterNACHI Awards Committee is the final authority of issuance of any award the committee offers and any rules updates.
Reply With Quote
  #4  
Old 5/9/07, 11:38 PM
homebild homebild is offline
Active Poster
 
Join Date: Nov 2006
Location: Pennsylvania
Posts: 195
Please Note: homebild is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Ice Gaurd membrane

Quote:
Originally Posted by mcyr
David, If the new roofing was installed over the old roofing, the probability that ice and water shield was installed is close to none.

Most Roofing Manufacturers will knock off 5 years on their Warranty for doing it.
Since there are no Manufactures instructions for installing a double layer of roof shingle on the packages, I would have to note that it was double layered and does not comply to a new Manufacturers installation procedure.

Marcel
</IMG></IMG>
Shingle Manufacturers and Building Codes recognize "re-roofing", defined as, adding a second layer of shingles over 1 previous existing layer, as a legitimate and warrantee-able installation technique and manufacturers indeed DO illustrate application instructions for doing just that on their product packages and product installation data sheets.

You can see Tamko's re-roofing practices here, for example (see docment page 3 item 8 're-roofing'):

http://www.tamko.com/Portals/0/docum...30AR%20F_T.pdf

Ice and water shield, on the other hand, is only effective and required for new roofing applications.
Reply With Quote
  #5  
Old 5/10/07, 8:15 AM
Marcel R. Cyr, CMI's Avatar
Marcel R. Cyr, CMI Marcel R. Cyr, CMI is offline
Certified Master Inspector ®
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 31,282
Default Re: Ice Gaurd membrane

Quote:
Originally Posted by homebild
Shingle Manufacturers and Building Codes recognize "re-roofing", defined as, adding a second layer of shingles over 1 previous existing layer, as a legitimate and warrantee-able installation technique and manufacturers indeed DO illustrate application instructions for doing just that on their product packages and product installation data sheets.

You can see Tamko's re-roofing practices here, for example (see docment page 3 item 8 're-roofing'):

http://www.tamko.com/Portals/0/docum...30AR%20F_T.pdf

Ice and water shield, on the other hand, is only effective and required for new roofing applications.

It might be all swell and dandy to be able to recognize that Code will allow two layers of roof shingles,
But, not all Manufactures will Warranty their products in this install.
They might allow the installation, but what they don't tell you are the ramifications of the double layered roof.

Including "Tamko", If you read the Warranty, you will find that any defect in or failure of materials used as a roof base over which the Shingles are applied, or for damage by , will not be Warrantied.

So, it is your choice of accepting the fact that Code will allow it or face the music when the shingles don't last the 300 months the Manufacture says it is Warrantied for.

I for one as a Contractor, would never condone installing New Shingles over another layer, whether or not allowed by Code.

I have personally experienced roofing failures 10 years below the projected life expectancy of shingles too many times.

Marcel



CMI 2004-2017 Retired

Awards Committee Member
U.S. Member of the Year Winner 2009
45 Years Residential/Commercial Builder
Submit your AWARDS NOMINATIONS here
The InterNACHI Awards Committee is the final authority of issuance of any award the committee offers and any rules updates.
Reply With Quote
  #6  
Old 5/10/07, 9:00 AM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,587
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Ice Gaurd membrane

Marcel:
"I have personally experienced roofing failures 10 years below the projected life expectancy of shingles too many times. "


Have the roof failures been from "roofing over existing" or from poor shingle product. I've seen much of the the latter since 1993-5 and it has been written about a few times. When I was roofing in the 1980's, a light (frost white, light gray) coloured shingle (Domtar 3-in-1 Truseal brand) with a 10 year warranty would last 23-25+ years if installed correctly. Just last spring I saw failure on a 13 year old bungalow!!! As well, saw similar failure on a 15 year old $500,000 home with a light brown roof the year before.

Note: We are building inspectors and, as such, should call items by their proper names. In Canada, the membrane applied to the lower section of the roof (only roofs with up to 8/12 pitch or slope require it here) for protection from water backup from ice dams is called "eave protection". What term is used in the US?

http://www.iko.com/misc/CasmaPdf/10-IceDams.PDF
Reply With Quote
  #7  
Old 5/10/07, 2:16 PM
Marcel R. Cyr, CMI's Avatar
Marcel R. Cyr, CMI Marcel R. Cyr, CMI is offline
Certified Master Inspector ®
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 31,282
Default Re: Ice Gaurd membrane

Quote:
Originally Posted by Brian A. MacNeish
Marcel:
"I have personally experienced roofing failures 10 years below the projected life expectancy of shingles too many times. "


Have the roof failures been from "roofing over existing" or from poor shingle product.A combination of both. The original roofing on my own house were 32 years old when I re-did it.
The house next door to me was re-roofed 11 years ago and installed as a second layer. The roofing was white and was redone again this year.
The second layer was all curled down and wide gaps and the granules were half gone.
This time the roof was stripped and Ice and WaterShield was added at the valleys and roof edges.
I will have to assume that the second shingles were at least a 20 year warranty.
Ventilation plays a big role on the life of a roofing shingle, because it overheats and basically cooks and you loose a lot of life.

I've seen much of the the latter since 1993-5 and it has been written about a few times. When I was roofing in the 1980's, a light (frost white, light gray) coloured shingle (Domtar 3-in-1 Truseal brand) with a 10 year warranty would last 23-25+ years if installed correctly. Just last spring I saw failure on a 13 year old bungalow!!! As well, saw similar failure on a 15 year old $500,000 home with a light brown roof the year before.

Note: We are building inspectors and, as such, should call items by their proper names. In Canada, the membrane applied to the lower section of the roof (only roofs with up to 8/12 pitch or slope require it here) for protection from water backup from ice dams is called "eave protection". What term is used in the US? Ice and WaterShield.

The composition of and the Matrix of today's shingles has changed a lot over the years and each Manufacturers Products have pros and cons and act different under different circumstances.

http://www.iko.com/misc/CasmaPdf/10-IceDams.PDF
Hope this helps.

Marcel
</IMG>



CMI 2004-2017 Retired

Awards Committee Member
U.S. Member of the Year Winner 2009
45 Years Residential/Commercial Builder
Submit your AWARDS NOMINATIONS here
The InterNACHI Awards Committee is the final authority of issuance of any award the committee offers and any rules updates.
Reply With Quote
  #8  
Old 5/10/07, 8:11 PM
homebild homebild is offline
Active Poster
 
Join Date: Nov 2006
Location: Pennsylvania
Posts: 195
Please Note: homebild is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Ice Gaurd membrane

Sorry to disagree with Marcel, but the manufacturers of shingles offer FULL warranties to second layers installed over existing roofs just as fully as they warrant the shingles if placed on a new roof deck.

A proper installation is required for BOTH practices to be warranted.

I would also disagree completely with Marcel's anecdotal evidence that new shingles placed over existing shingles fail at a greater rate than those placed on new decking.

Such allegations are broadly bandied about, yet is there ever any solid verifiable evidence to back such claims.

I have been installing shingles over existing roofs for 30+ years and have NEVER seen premature failure of the 2nd layer based on the fact that they were installed over an existing layer.

Neither, apparantly, have shingle manufacturers, nor the Codes, or they would not wholly approve of the practice....despite Marcel's false claims to the contrary.

Adding a second layer of shingles over and existing layer remains a manufacturer and Code approved method of installation...even in Marcel's state.
Reply With Quote
  #9  
Old 5/10/07, 8:53 PM
Marcel R. Cyr, CMI's Avatar
Marcel R. Cyr, CMI Marcel R. Cyr, CMI is offline
Certified Master Inspector ®
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 31,282
Default Re: Ice Gaurd membrane

Quote:
Originally Posted by homebild
Sorry to disagree with Marcel, but the manufacturers of shingles offer FULL warranties to second layers installed over existing roofs just as fully as they warrant the shingles if placed on a new roof deck.
Read your own Warranty of the Product you posted.

A proper installation is required for BOTH practices to be warranted.
Was the second layer installed with six nails.?

I would also disagree completely with Marcel's anecdotal evidence that new shingles placed over existing shingles fail at a greater rate than those placed on new decking.
Well, this person seems to agree with me.


However, be aware that you may encounter the following problems:

If there's any curling of the old shingles, the new asphalt shingles will not lay flat.
Moisture can get trapped under the heavy layers and cause premature rotting of the wood.
You do add excess weight to the roof framing, which can cause the decking and/or roof joists to bow and cause a ripple effect in the roof.
Overlay will not work well at all with dimensional asphalt shingles, only three tab.
If you do overlay, you have to cut off the tab of the first course which will give you a "bump" about 6" up the roof all the way around the roof.
You must pull off both layers before you roof the next time. Many times the cost for a double tear-off is more than doing it two separate times.
Tear-off will give you the opportunity to examine the decking for any rot and make repairs now before it gets worse (and more costly).
If you do remove the old asphalt shingles, you will end up with a nice fresh layer of felt on the roof deck.

David Radcliff, Certified Remodeler


Such allegations are broadly bandied about, yet is there ever any solid verifiable evidence to back such claims.
Clearly exampled in my previous post.

I have been installing shingles over existing roofs for 30+ years and have NEVER seen premature failure of the 2nd layer based on the fact that they were installed over an existing layer.
Maybe that is because you never paid attention or gone back to look.
I have been in the Building Industry since 1965, do the Math.

Neither, apparantly, have shingle manufacturers, nor the Codes, or they would not wholly approve of the practice....despite Marcel's false claims to the contrary.
My claims are not false as you say, because the only thing you seem to be able to realize and see is what you see in the Code. I do not build by the Code. I am one step above it at the very least.

Adding a second layer of shingles over and existing layer remains a manufacturer and Code approved method of installation...even in Marcel's state.
And that means to you that is the right way of doing things in the Building Industry? I feel sorry for you.
Marcel
</IMG>



CMI 2004-2017 Retired

Awards Committee Member
U.S. Member of the Year Winner 2009
45 Years Residential/Commercial Builder
Submit your AWARDS NOMINATIONS here
The InterNACHI Awards Committee is the final authority of issuance of any award the committee offers and any rules updates.
Reply With Quote
  #10  
Old 5/10/07, 9:04 PM
Marcel R. Cyr, CMI's Avatar
Marcel R. Cyr, CMI Marcel R. Cyr, CMI is offline
Certified Master Inspector ®
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 31,282
Default Re: Ice Gaurd membrane

I thought this addittional information might help you understand the facts.

The ROOF-OVER Professional consulting available.


"ROOF-OVER", type roofing: the poor man's roof. "Roofing-Over" is the practice of installing, nailing or placing new roofing directly over old roofing material, to avoid the rip-off and the disposal of the old roofing.

For the customer willing to trade approximately a 10% cost savings for a roof with rough appearance, a potentially short roof life, the cost of additional venting and a doubly difficult tear off and disposal in the future; "roofing-over" is a manufacturer approved practice. This applies to "soft" roofing only, (asphalt shingles, roll roofing, bitumen, and modified bitumen "flat" type roofing). This process is most often done on sloped (shingle) roofs, but it is also common on "flat" type roofing. An increasingly common practice, this procedure became popular in the early 1970's in the USA. With many such "roof-over" applications in place, there is now a growing body of experience and information centered on this abbreviated approach to "re-roofing".


An increasingly common practice, this procedure became popular in the early 1970's in the USA.
It is generally assumed that only an aging roof in sound condition should be "roofed-over". As long as the old roof is not literally disintegrating, some consider it a candidate. Extreme curling and cupping of the shingles in the case of "flat" roofing, deep material or very uneven materials makes "roofing-over" difficult but not impossible. The first step in "roofing-over" is to remove excess damaged parts, so as to "level" the roof. On sloped roofs, the top peaks or ridges have their "cap" shingles removed, as do any hip ridges (the top of the downward sloping intersection of adjacent "sloped" roof planes). Areas that are not severely damaged may require some simple patching with roofing material and roof cement. At this point, the installation may begin.

On sloped roofs, the actual installation of shingles begins with trimming. A starter shingle cut lengthwise down the middle leaving a 5 inch wide strip which is nailed through and over the bottommost row of shingles; followed by a full shingle with its top edge butted against the lower edge of the old row of shingles above it. After this, the shingles are nailed over the rest of the roof in the same manner until the old roof is covered. At the top, or the ridge, again new shingles are cut, or trimmed, lengthwise to run even with the ridge and a new set of "cap" shingles are cut and installed to cover the peak.

The finished "roof-over" more often than not, will have a rough appearance. This is a reflection of the physical condition of the underlying deteriorated roofing.

Of the many factors that affect the service life and durability of a "roof-over", is the length of the nail, or other type fastener, which is used. Depending on the quality, weight and type of shingles, or roofing material, used on the original roof, the mechanical fasteners for the "roof- over" (nails or screws for some "flat" roofs) should be one half of an inch to three-fourths of an inch longer than the fasteners in the original roof. This means a one and one half of an inch to two inch roofing fastener is generally used on a "roof-over". Since, in the case of sloped roofs, the original shingle provides little support for the portion of the nail passing through it, these longer new nails can suffer lateral, downward "pull". "Nail-pops" caused by expansion and contraction of the underlying material can pull a nail head through the new material thereby loosening it, or push a nail head through the material above causing a hole in the shingle (a guaranteed leak).

Another factor is the continuing deterioration of the original roof. Three basic and interacting multi-factor processes are introduced to the new combination old roof/new roof lamination termed collectively as the "roof-over".

Asphalt shingles, asphalt "flat" roofing, and modified bitumen products are manufactured from an amalgamation (a mix) of petroleum products ranging from tar-like solids and semisolids to liquids (oil-like) and volatiles (solvent-like). These substances diminish over time by evaporation, solidification (embritlement) and by a photochemical process whereby direct exposure to sun breaks down the asphaltic compounds into carbon gas (carbon dioxide, carbon monoxide, methane, etc.) and carbon solids (black, dirty stuff). Once covered, the old shingles, or "flat" roofing material continues to break down by solidification (congealing) and evaporation of the volatiles.


When the roof (of the "roof-over") needs to be replaced, all layers of roofing must be removed and hauled to a dump.
Trapped between the new shingles, or "flat" roofing material, and the underlying roof felt and/or roof deck (usually wood or plywood), the old shingles gather and hold moisture. During the hottest days with direct sunlight, this moisture steams off cooking the new shingles, or asphaltic "flat" roofing. In freezing weather the moisture turns to ice, swelling and tearing or breaking up the old underlying material. These combinations of actions caused by gathering and releasing moisture also involve expansion and contraction of the old roofing.

So, with the continued deterioration of the underlying the old roofing material by 1) material breakdown 2) steaming, and 3) expansion-contraction; the new roofing experiences added stress from heat, mechanical movement (dimensional change from expansion-contraction) and loss of support by deterioration/degradation of the decaying roofing material.

In the unusual case where the new asphalt shingles are installed over a slate, wood shingle, asbestos- cement shingle, or synthetic shingle, life expectancy, performance and secondary affects (side effects) are unpredictable. Such installation and their related problems are beyond the scope of this article, however, needless to say, such practices are not recommended and are rife with negative considerations.

An odd variation on the "roof-over" is the installation of plywood directly over the old shingles followed by roofing over the plywood. There is too little experience with this approach to provide knowledgeable information. It is known that moisture is trapped in the old shingles. This suggests the possibility that some of the types of moisture related problems, mentioned earlier, are likely to occur.

If you are buying a building that has a "roof-over", the primary consideration is that when the roof (of the "roof-over") is worn out and needs to be replaced, all layers of roofing must be removed and hauled to a dump site or disposal point. The expense saved on the "roof- over" is more than exceeded. In other words a "roof-over" transfers the cost of trash disposal to the next "re-roofing" operation. "Three-roofing" or roofing over the "roof-over" has been done and even appears in some literature; however, such practice should be relegated to cartoons and comic books. The results of actual triple roofing practice range from deceptively acceptable to obviously and immediately defective.

There are a number of special considerations when doing or taking possession of a "roof-over" roof. Because of the moisture trapped in the old roofing, and the additional heat trapped in the extra mass, a "roof-over" roof requires additional ventilation --an added expense-- to help reduce accelerated and premature aging of the new roofing. (Which includes bubbles, and lumping in "flat" type roofs.)

Another consideration is the added load (weight) of the combination of the old and new roofing. The added weight may necessitate additional structural roof bracing. (In one instance of the author's experience involving a one-story cottage, the added weight actually snapped the horizontal cross-ties, and ceiling joists, "flattened" out the roof, bowed the front and rear exterior walls literally ripping the exterior walls away from the interior partitions -- virtually destroying the cottage. In another case an 1880 vintage sloped roof (114 years old at the time) suffered lengthwise splits in its (unsupported and unbraced with no cross ties, which were not needed in the original construction) rafters. One more heavy snow load on this roof, and collapse was likely.

With "flat" type roofing, an older roof generally provides a poor surface for the new installation, especially if the newer roof requires total adhesion. Usually when roofing over a "flat" roof, a non-adhesive mechanically fastened (nails of screws) approach is far more likely to provide adequate performance.

With both "flat" roofing and sloped, shingled roofs, "roofing-over" works best with considerable additional venting of the roof cavity and/or membrane type vents for "flat" roofs. This additional venting, when done, often offsets the shortsighted financial savings in forgoing the rip-off and dump costs.

There is only one incentive for doing a "roof-over", to save money, in the short run.

Is that what your Codes are for?





CMI 2004-2017 Retired

Awards Committee Member
U.S. Member of the Year Winner 2009
45 Years Residential/Commercial Builder
Submit your AWARDS NOMINATIONS here
The InterNACHI Awards Committee is the final authority of issuance of any award the committee offers and any rules updates.
Reply With Quote
  #11  
Old 5/10/07, 9:07 PM
Peter C. Russell's Avatar
Peter C. Russell Peter C. Russell is offline
Certified Professional Inspector (CPI)
 
Join Date: Jul 2004
Location: Alton Bay NH
Posts: 5,316
Default Re: Ice Gaurd membrane

Marcel, I agree with you and after 22 years as a contractor I will very rarely put a second layer of shingle on a roof. The roofs I sell would be a complete strip job so the proper installation of ice and water shield can be achieved as well as a good roof installation.

Beside, I don't care what the MFG puts on the package for a warranty or their installation instruction, listen to what they tell you when there is a problem, they have a list a mile long of excuses of why they won't warranty the shingles..... been there, done that!!!!
Reply With Quote
  #12  
Old 5/10/07, 11:56 PM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,587
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Ice Gaurd membrane

Marcel:

"Ventilation plays a big role on the life of a roofing shingle, because it overheats and basically cooks and you loose a lot of life."

Research has shown over the last 20 years or more that ventilation has less and less (almost nothing) to do about shingle life. Shingle colour, shingle quality or shingle orientation are the big items!!! See research by Bill Rose , research Architect at University of Illinois.

Also adding ventilation to solve attic condensation problems is the last thing you should do!! Believe it or not???

See http://www.cmhc.ca/en/co/maho/gemare/gemare_001.cfm This is from Canada's National Housing Agency. Don't be too ed at what is said. It fills in where the old building science ln roof ventilation left gaps. I know! When I gave a 1 night seminar to the local architect's association, (I was teaching building science at the local architectural college then) more than a few came up to mention how their understanding was much better now. To my surprise, I was asked to do another night within 2 weeks, (usually they have monthly meetings only and none in December) just before Xmas.
Reply With Quote
  #13  
Old 5/11/07, 1:12 AM
Robert R. Cramer's Avatar
Robert R. Cramer Robert R. Cramer is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Belleville, IL
Posts: 128
Default Re: Ice Gaurd membrane

Marcel,
I totally agree with you. And so does the largest manufacture in North AmericaÖ.GAF. As part of a Master Elite Roofing Contractor our company never once put a second layer of roofing on. While the manufacture says it will warrant the shingle, they will find a way to dismiss the warranty, easily. GAFís official position with its contractor program was it would not issue the contractor a warranty for the practice of roof overís for its contractor program, but would offer an extended warranty if the roof was striped, and was totally looked upon as a big no no. Companies that practiced roof overís were simply not invited back into the program and would lose the status of Master Elite Contractor. While GAF says they will warrant a roof over on the package they strongly discourage the practice. Why, because GAF knows that for a contractor to maintain a great reputation within the community, they cannot practice the poor manís tactics. They know that a roof will not last as long as a roof that has been striped.
I ask about this same subject at a GAF seminar and was told in laymanís terms: When a roof is installed directly over another roof of decaying nature, the old brittle shingles draw the oils out of the asphalt of the new shingles laid above them, thus drastically reducing the life of the new shingles. Not to mention the old layer has to be totally nailed flat for the new shingles to lie flat or they will void the warranty on this point alone. The old shingles need to have sealant installed under all of the tabs of the old shingles were the sealant is no longer properly sealing the shingle tab or the warranty is void. The old shingles need to be totally dry before any application of the new shingles or this will also void the warranty. Furthermore, most roofing systems are not designed to handle the additional weight of two layers of roofing and can cause structural failure, especially if it is in an area with high annual snow falls or if the roof sheeting and framing do not meet the manufactures recommend requirements.
As far as roof ventilation is concerned, again GAFís official position is they will void the roof warranty of a roof system that does not have adequate ventilation. A balanced ventilation system is absolutely critical to the life of the roofing system, both for winter and summer. I read the article that Brian was referring to and it didnít say that ventilation wasnít necessary. It simply stated that adding additional ventilation could be bad and I think they were referring to an unbalance system, which is true for extreme winter only.
Personally I have inspected thousands of roofs and one thing always remained constant with roofs that had two layers or more and a crappy ventilation system. They simply wore out prematurely.



Robert Cramer
Five Star Property Inspections
Your Best & Safest Choice
www.fivestarpi.com
1-877-378-2774
Reply With Quote
  #14  
Old 5/11/07, 5:53 AM
Marcel R. Cyr, CMI's Avatar
Marcel R. Cyr, CMI Marcel R. Cyr, CMI is offline
Certified Master Inspector ®
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 31,282
Default Re: Ice Gaurd membrane

Peter, Brian, and Robert, Thank you for reinforceing my point, I totally agree.

Marcel



CMI 2004-2017 Retired

Awards Committee Member
U.S. Member of the Year Winner 2009
45 Years Residential/Commercial Builder
Submit your AWARDS NOMINATIONS here
The InterNACHI Awards Committee is the final authority of issuance of any award the committee offers and any rules updates.
Reply With Quote
  #15  
Old 5/11/07, 7:00 AM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,587
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Ice Gaurd membrane

Robert Cramer:

"I read the article that Brian was referring to....."

This is just the beginning of articles I will supply on these issues that I have been fighting since 1983. The first partial one was to Roy Cooke about a weeek ago concerning the origins of the 1:300 attic venting rule.......it has no scientifically proven basis yet it is in codes everywhere. It was derived from a single lab experiment in 1947-8 at Penn State University on vapour barriers in flat roof assemblies. They weren't even testing for attic venting but derived a number due to having an incomplete understanding of how these systems truly worked back then.

If we really knew the building science of moisture movement in houses then (98-99% is air movement; the rest is vapour diffusion), vapour barriers would not be installed in homes but they would be built more airtight (as is happening now). If you put in a loose, unsealed vapour barrier, you are attacking 1-2% of the problem and the other 98% defeats you at every receptacle/switch box and unsealed joint!! Make the drywall airtight and leave out the vapour barrier and now you have hit the real problem- air leakage. Same as with attic moisture from condensation- have an airtight ceiling so that house moisture does not migrate by upward air leakage and the need for venting goes way down to about what's naturally left in the attic anyways.

Joe Lstiburek (Phd., P. Eng.) of Building Science Corporation (www.buildingscience.com) promotes a basement wall system that has no vapour barrier on the warm side of the wall behind the drywall.

Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Ripples in Rubber Roofing? jberthiaume Exterior Inspections 15 6/23/08 10:34 PM
Who is smart enough to know the perfect way of doing this? Bill Featherstone Interior Inspections 7 11/15/07 1:00 AM
Reverse Osmosis phinsperger Plumbing Inspections 3 10/30/07 6:28 PM
Fibertite roofing Membrane mcyr Exterior Inspections 5 5/28/07 3:14 AM

All times are GMT -4. The time now is 12:44 PM.
no new posts