Default Turbine roof vents

In an effort to explain to a client why turbine roof vents are not a good thing I produced the attached graph.

turbine-roof-vents-wind-turbines.jpg

It shows graphically that there is an inverse relationship between when the attic space needs the most venting and when the wind is blowing the most. So the turbine is;
  • working its hardest when its needed the least
  • working the least when its needed the most
The second point then brings up the question - When its working the least is it still working enough? I would suppose that would vary greatly on individual instalations.

The velocity of a spinning turbine can be attributed mainly to the force of exterior wind. The spinning from the force of air rising from the attic through the turbine is minimal in comparison.

Certainly there are also other issue regarding turbines such as noise and depressurization which in themselves may be reason enough not to use turnbinbes but I mainly wanted to illustrate the basic venting effects.

The actual data used to plot the graph is from weather data from my local area but I suspect most northern non-coastal locations are similar.
Reply With Quote
  #2  
Old 5/8/06, 11:03 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
Certified Master Inspector
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 10,143
Send a message via Yahoo to jfunderburk
Default Re: Turbine roof vents

I'm not sure I concur that a couple of strategically placed turbines are less effective than, say, a ridge vent (provided that an air intake is available). I appreciate your efforts, but I don't understand the graph at all (the way you've scaled it, it appears to me that wind increases in correlation to a rise in temperature).



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CBO, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
Angie's List Super Award Winner 2016, 2015, 2014, 2013, 2012, 2011, 2010.
Ph: 704-351-1776
www.aohomeinspection.com

Reply With Quote
  #3  
Old 5/8/06, 11:56 PM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
Certified Professional Inspector (CPI)
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 25,989
Default Re: Turbine roof vents

Quote:
Originally Posted by jfunderburk
I'm not sure I concur that a couple of strategically placed turbines are less effective than, say, a ridge vent (provided that an air intake is available). I appreciate your efforts, but I don't understand the graph at all (the way you've scaled it, it appears to me that wind increases in correlation to a rise in temperature).
If for no other reason then that they always become noisy this is enough for me to not have one.
They in high wind pull air from the home ,not a good thing .
I have seen insulation missing from the attic and saw it on the ground , not a good thing.
I have seen snow in the attic under the turbine ,not a good thing .
I have not talked to an experienced home inspector in Canada who feels Turbines are any good .
Roy sr
Reply With Quote
  #4  
Old 5/9/06, 1:41 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
Certified Master Inspector
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 10,143
Send a message via Yahoo to jfunderburk
Default Re: Turbine roof vents

We don't get much snow down here. My mother's house has 2 turbines that have been working perfectly for about 15 years now. I don't know which is "best" but I know power vents have their problems too (including adding to the power bill).



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CBO, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
Angie's List Super Award Winner 2016, 2015, 2014, 2013, 2012, 2011, 2010.
Ph: 704-351-1776
www.aohomeinspection.com

Reply With Quote
  #5  
Old 5/9/06, 3:55 AM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
Certified Professional Inspector (CPI)
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 19,216
Default Re: Turbine roof vents

I'm a big fan of turbine vents.

What many seem to misunderstand is that they work with or without wind. They do not depend on wind alone in order to function.

Remember that hot air rises, so the placement of turbine vents can be critical. They should be up as high as possible, and they will work best if there are some soffit vents or static vents below them, as low as possible.

As the air in the attic heats up, the heat will rise, going through the turbine vents. The hotter the air, the faster it rises, and as it goes through the turbine vents, the turbines will spin. As they spin, they pull more air out. The hot air, the vents, and the resulting wind (or with external wind) work off of each other to create a very nice ventilation system.

If you have snow or rain in the attic, then the vent has not been installed properly.

If your turbine vents are noisy, they either have not been installed properly, you don't have enough insulation in the attic, and/or you need to upgrade from the 40-year-old turbine vent to a modern one.

My neighbor, at my recommendation, had two turbine vents installed when he re-roofed his house last summer. He reports that the attic is about 30° cooler post-turbine as opposed to pre-turbine. They are constantly in their attic since they store stuff up there. And in our daily sunshine here that lasts for about 11 months, his turbine vents are always spinning, with or without wind.



House Key News
Getting your past Clients to work as hard for you as you worked for them.
Sign up at http://www.housekeynews.com

NACHI 2005 U.S. Member of the Year

Reply With Quote
  #6  
Old 5/9/06, 4:50 AM
Steve Boozer Steve Boozer is offline
New User
 
Join Date: Mar 2006
Location: Suwanee Georgia
Posts: 55
Please Note: Steve Boozer is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Turbine roof vents

Ventilation is an issue you'll get 100 different opinions on. I don't like the turbines and they can make some bad squealing noises at times and are prone to damage from tree limbs. We usually put ridge vent everywhere we can where it is applicable except for the main attic. You get alot of square inches of opening. I guess at least 96 inches of opening for only a 4 foot section. I usually go with power roof vents in the main attic here in GA since the HVAC units are generally located there. I'm told the cooler the units stay, the better they work. PRVS can make some noise and do need replacing, but anything with a motor and a fan has to be the best at making air flow. Lomanco has a nice design. Metal screen, aluminum hood and base, rain shield and even a test button on the thermostat. I especially like the fact that they are the only one I've seen that does not have a seem only 1 inch up from the roofline.

IM000382.JPG (63.5 KB)
Attached Thumbnails
turbine-roof-vents-im000382.jpg  
Reply With Quote
  #7  
Old 5/9/06, 4:58 AM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
Certified Professional Inspector (CPI)
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 19,216
Default Re: Turbine roof vents

Quote:
Originally Posted by Steve Boozer
Ventilation is an issue you'll get 100 different opinions on.
And that's only if you ask 50 people.


Quote:
Originally Posted by Steve Boozer
....turbines ... can make some bad squealing noises at times
Upgrade to modern turbines or increase the insulation in your attic.


Quote:
Originally Posted by Steve Boozer
....turbines ... are prone to damage from tree limbs.
Hmmmmmmmm. Me thinks that if the tree limbs are that close to your roof, you've got other issues to deal with as well. Those tree limbs should be trimmed away from the roof. There's such a thing as trees providing shade, but they should never be that close too your roof.



House Key News
Getting your past Clients to work as hard for you as you worked for them.
Sign up at http://www.housekeynews.com

NACHI 2005 U.S. Member of the Year

Reply With Quote
  #8  
Old 5/9/06, 7:43 AM
Paul Hinsperger, CMI's Avatar
Paul Hinsperger, CMI Paul Hinsperger, CMI is offline
InterNACHI Member
 
Join Date: Dec 2003
Location: Orangeville, ON
Posts: 1,848
Please Note: phinsperger is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Turbine roof vents

Quote:
Originally Posted by jfunderburk
I'm not sure I concur that a couple of strategically placed turbines are less effective than, say, a ridge vent (provided that an air intake is available). I appreciate your efforts, but I don't understand the graph at all (the way you've scaled it, it appears to me that wind increases in correlation to a rise in temperature).
Hi Joe,

I don't know about the weather patterns or venting dynamics in South Carolina so maybe they work well in your area. I only know that in my climate they do not work as well as people think. More venting in the winter and less venting in the summer.

The aqua colored line is the wind speed. During the summer months when the temp and humidity are the highest there is less wind speed then during the winter months.

I think that people purchase them because they can see something spin - ergo it must something must be happening. Unfortunately something is happening, just not the way they think.

I also see that when a long attic space is vented with a turbine placed even in the middle of the run that there is more ice damming than usual near the ends of the roof. I have seen this on more that one occasion. The problem is that the turbine technically may have enough the exhaust output for the upper venting requirements but as it pulls the warm air from the living space near the ends of the attic, the heat from that air has been transfered to the snow on the roof before it can get all the way down the attic and exhausted through the turbine. More evenly spaced static vents or a full length ridge vent would work alot better.

Again let me say that I am talking about northern non-coastal climates here. In other climates they be fine.
Reply With Quote
  #9  
Old 5/9/06, 8:11 AM
Raymond E. Wand Raymond E. Wand is offline
Active Poster
 
Join Date: Sep 2005
Location: Caledon, ON
Posts: 7,804
Please Note: rwand1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Turbine roof vents

The bearings sieze up on cheap models. They can allow rain and snow entry regardless how installed.

They can depressurize the attic, if there are not enough soffit vents. This depressurization can cause further problems particularly during winter months when moisture laiden air can enter the attic from attic penetrations. Particularly important consideration in winter months in cold climates, like Canada.

I would not install them, nor do I recommend them.

Thanks Paul.
Reply With Quote
  #10  
Old 5/9/06, 9:50 AM
Dale Duffy's Avatar
Dale Duffy Dale Duffy is offline
Certified Professional Inspector (CPI)
 
Join Date: Oct 2005
Location: Scottsdale, Arizona, Cuenca, Ecuador
Posts: 9,119
Default Re: Turbine roof vents

Their a "Hot" item in Arizona. I generally see them still operating fine after 15 years plus. One can tell if they were installed on all the homes in a subdivision originally, they are located in the same portion of all the roofs.

Great source of ventilation in the desert.
Reply With Quote
  #11  
Old 5/10/06, 6:33 AM
Charles R. N. Crooker, CMI's Avatar
Charles R. N. Crooker, CMI Charles R. N. Crooker, CMI is offline
InterNACHI Member
 
Join Date: Jun 2004
Location: Brantford, ON
Posts: 841
Default Re: Turbine roof vents

Maximum for a better vent. Have a look at www.ventilation-maximum.com ,no moving parts and different sizes , to each his or her own!!



Chuck Crooker I.M.M., Canadian Home Inspectorhttp://www.crookerhancox.com "Not just an inspection, an Education!!!"

Last edited by ccrooker; 5/10/06 at 6:57 AM..
Reply With Quote
  #12  
Old 5/10/06, 6:46 AM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
Certified Professional Inspector (CPI)
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 19,216
Default Re: Turbine roof vents

Quote:
Originally Posted by ccrooker
Maximum for a better vent. Have a look at www.ventilatin-maximum.com ,no moving parts and different sizes , to each his or her own!!
T'was a little typo there.

Try this one:

www.ventilation-maximum.com



House Key News
Getting your past Clients to work as hard for you as you worked for them.
Sign up at http://www.housekeynews.com

NACHI 2005 U.S. Member of the Year

Reply With Quote
  #13  
Old 5/10/06, 6:57 AM
Charles R. N. Crooker, CMI's Avatar
Charles R. N. Crooker, CMI Charles R. N. Crooker, CMI is offline
InterNACHI Member
 
Join Date: Jun 2004
Location: Brantford, ON
Posts: 841
Default Re: Turbine roof vents

thanx RR T'is early, but still a good vent!



Chuck Crooker I.M.M., Canadian Home Inspectorhttp://www.crookerhancox.com "Not just an inspection, an Education!!!"
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
A little on the Commercial side of things. mcyr General Inspection Discussion 457 8/1/09 10:50 AM
Cracked shingles pwigle Exterior Inspections 54 4/23/09 11:52 PM
Chimney flashing photo's needed: brick and stone done correctly kshepard Exterior Inspections 6 10/13/07 8:10 AM
Ice Gaurd membrane dmacy Exterior Inspections 36 6/14/07 12:21 AM
Roof Repair? Maybe NO jhagarty Exterior Inspections 9 2/15/07 1:19 AM

All times are GMT -4. The time now is 9:48 PM.
no new posts