  #16  
Old 12/16/11, 1:08 AM
An HI An HI is offline
Active Poster
 
Join Date: Oct 2011
Location: cyberspace
Posts: 286
Please Note: An HI is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Advice on bath exhaust vent termination.

Quote:
Originally Posted by wwalmsley View Post
Just an observation but the last few ft. of the pipe should be wrapped with insulation condensation will occur.Warm pipe cold attic air..
If the total length of exhaust pipe is in the cold attic above the insulation, it should be insulated for its length to prevent interior condensation. I have seen a water filled droop in a flexible plastic pipe that blocked all ventilation. There was about 3/4 quart of water.

If the pipe is run in a heated space, then the last 3 feet at the exterior wall should be insulated with an airtight vapour barrier over it to prevent condensation on the exterior of the duct and consequent dripping. Small amounts of cold air bypass the damper into the duct or the air in the duct become cold (not an insulted damper) and condensation on its exteior occurs.
Reply With Quote
Need a home inspection in South Carolina? Check out InterNACHI's listing of South Carolina certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #17  
Old 12/16/11, 9:18 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
Certified Professional Inspector (CPI)
 
Join Date: Apr 2004
Location: North Central Okla
Posts: 10,712
Default Re: Advice on bath exhaust vent termination.

I be darned if I would of went 15 ft to a side wall with a roof within 3 feet $350.00 for a roofer to do what cut a hole in the roof and install a rain cap duh I would have taken the roofer on the roof and pushed him off and screamed $350.00 just as he hit the ground.
Roof vents of some nature are installed on every roof out there what is the big deal about another one. Sometimes you guys advice is off the wall pun intended



http://www.oklahomathermalinfraredimaging.com/
http://www.freedomexpressinspections.com/
Master HVAC Mechanic Retired
Level III Thermographer # 8486 Infraspection Institute
CMI Certified Master Inspector
Residential/Commercial Inspections
Moisture Intrusion Expert Witness
55 years in the Trades
Okla State License # 130
580-268-3340
Reply With Quote
  #18  
Old 12/16/11, 9:37 AM
An HI An HI is offline
Active Poster
 
Join Date: Oct 2011
Location: cyberspace
Posts: 286
Please Note: An HI is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Advice on bath exhaust vent termination.

Quote:
Originally Posted by cbottger View Post
I be darned if I would of went 15 ft to a side wall with a roof within 3 feet $350.00 for a roofer to do what cut a hole in the roof and install a rain cap duh I would have taken the roofer on the roof and pushed him off and screamed $350.00 just as he hit the ground.
Roof vents of some nature are installed on every roof out there what is the big deal about another one. Sometimes you guys advice is off the wall pun intended
Well said. On Monday I inspected a house with a decent quality range hood installed. It ends there.

The installer went against the manufacturer's instructions of 6" diameter (28.3 sq in) or 3 1/4 X 10 (32.5 sq in) ducting. He installed 4" diameter (12.6 sq in) spiral wound aluminized ducting, essentially dryer ducting. It was about 20' to a side wall while a roof vent would have about 3-4' of duct.

Spiral wound duct acts like ducting of 1 size smaller, so this 4" duct is performing like 3" (7.1 sq in) straight smooth duct! So this is essentially a working condition that is 75% smaller than recommended.

It was uninsulated through a cold attic on top of the insulation batts.

Like I said, a decent medium quality range hood only. Wonder how well that will work?

Last edited by An HI; 12/19/11 at 1:40 AM..
Reply With Quote
  #19  
Old 12/16/11, 9:48 AM
David C. Macy, CMI's Avatar
David C. Macy, CMI David C. Macy, CMI is offline
Certified Master Inspector
 
Join Date: Jan 2004
Location: Home Safe Home
Posts: 4,881
Default Re: Advice on bath exhaust vent termination.

Quote:
Originally Posted by wwalmsley View Post
Just an observation but the last few ft. of the pipe should be wrapped with insulation condensation will occur.Warm pipe cold attic air..
I have the insulation and plan on insulating the last few feet of exposed pipe. I did the other pipe about a week ago.
Reply With Quote
  #20  
Old 12/16/11, 9:49 AM
David C. Macy, CMI's Avatar
David C. Macy, CMI David C. Macy, CMI is offline
Certified Master Inspector
 
Join Date: Jan 2004
Location: Home Safe Home
Posts: 4,881
Default Re: Advice on bath exhaust vent termination.

Quote:
Originally Posted by mgratton View Post
https://www.nachi.org/bathroom-ventil...ducts-fans.htm

And the best practice is to slant horizontal runs of duct down toward the exterior outlet to drain any condensation outside, just saying!
Yes, I could of done a better job with that, so I guess it is not the best practice.
Reply With Quote
  #21  
Old 12/16/11, 9:53 AM
David C. Macy, CMI's Avatar
David C. Macy, CMI David C. Macy, CMI is offline
Certified Master Inspector
 
Join Date: Jan 2004
Location: Home Safe Home
Posts: 4,881
Default Re: Advice on bath exhaust vent termination.

Quote:
Originally Posted by cbottger View Post
I be darned if I would of went 15 ft to a side wall with a roof within 3 feet $350.00 for a roofer to do what cut a hole in the roof and install a rain cap duh I would have taken the roofer on the roof and pushed him off and screamed $350.00 just as he hit the ground.
Roof vents of some nature are installed on every roof out there what is the big deal about another one. Sometimes you guys advice is off the wall pun intended
Lets see, I have a 5 year roof that was professionally done and both chimneys leak, the plumbing vent leaks.

I was able to install through the sidewall myself and did not want to extend through the roof.

I thought the advice that was given was excellent and I appreciated the time others took to help me out.

I will need someone next spring to redo the chimneys and plumbing vent flashing's. The chimneys have leaked since day 1 of the roof install as it seams it penetrates between the flashing and bricks and mortar as no one wants to bend the flashing into the mortar joint and then seal.There are also numerous fractures in the brick and mortar. If anybody in the area wants the job I will pay a proper fee.
Reply With Quote
  #22  
Old 12/16/11, 4:28 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
Certified Professional Inspector (CPI)
 
Join Date: Apr 2004
Location: North Central Okla
Posts: 10,712
Default Re: Advice on bath exhaust vent termination.

Quote:
Originally Posted by dmacy View Post
Lets see, I have a 5 year roof that was professionally done and both chimneys leak, the plumbing vent leaks.

I was able to install through the sidewall myself and did not want to extend through the roof.

I thought the advice that was given was excellent and I appreciated the time others took to help me out.

I will need someone next spring to redo the chimneys and plumbing vent flashing's. The chimneys have leaked since day 1 of the roof install as it seams it penetrates between the flashing and bricks and mortar as no one wants to bend the flashing into the mortar joint and then seal.There are also numerous fractures in the brick and mortar. If anybody in the area wants the job I will pay a proper fee.
David we install vents through brand new roofs that are a week old all the time I don't suppose there is anything special about your roof if your roof is already leaking what's another leak between friends. Just kidding Sounds like ya need to find a different roofing contractor



http://www.oklahomathermalinfraredimaging.com/
http://www.freedomexpressinspections.com/
Master HVAC Mechanic Retired
Level III Thermographer # 8486 Infraspection Institute
CMI Certified Master Inspector
Residential/Commercial Inspections
Moisture Intrusion Expert Witness
55 years in the Trades
Okla State License # 130
580-268-3340
Reply With Quote
  #23  
Old 12/16/11, 6:32 PM
James F. McKee's Avatar
James F. McKee James F. McKee is offline
Certified Professional Inspector (CPI)
 
Join Date: Feb 2007
Location: Lorain Ohio
Posts: 7,369
Default Re: Advice on bath exhaust vent termination.

Quote:
Originally Posted by cbottger View Post
I be darned if I would of went 15 ft to a side wall with a roof within 3 feet $350.00 for a roofer to do what cut a hole in the roof and install a rain cap duh I would have taken the roofer on the roof and pushed him off and screamed $350.00 just as he hit the ground.
Roof vents of some nature are installed on every roof out there what is the big deal about another one. Sometimes you guys advice is off the wall pun intended


Looks like Charley wore his cranky pants today ...



Jim McKee
Lorain, Ohio
440 225 8688
www.classicinspector.com
Reply With Quote
  #24  
Old 12/16/11, 8:05 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
Certified Professional Inspector (CPI)
 
Join Date: Apr 2004
Location: North Central Okla
Posts: 10,712
Default Re: Advice on bath exhaust vent termination.

Quote:
Originally Posted by jmckee View Post
Looks like Charley wore his cranky pants today ...
Nah just wanted to rip your shorts knew you would be back, Buddy
Have a Merry Xmas Jim



http://www.oklahomathermalinfraredimaging.com/
http://www.freedomexpressinspections.com/
Master HVAC Mechanic Retired
Level III Thermographer # 8486 Infraspection Institute
CMI Certified Master Inspector
Residential/Commercial Inspections
Moisture Intrusion Expert Witness
55 years in the Trades
Okla State License # 130
580-268-3340
Reply With Quote
  #25  
Old 12/16/11, 8:34 PM
Marcel R. Cyr, CMI's Avatar
Marcel R. Cyr, CMI Marcel R. Cyr, CMI is offline
Certified Master Inspector ®
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 31,182
Default Re: Advice on bath exhaust vent termination.

I put my vent through the roof 4 years ago which is about 3' above the ceiling and never had a problem.
And anyone charging $350 should be thrown off the roof as Charley said. Took me two hours to install the fan and roof vent.


Mine is not insulated and my roof that I installed 16 years ago and flashing does not leak. Seems like roofers in your area are a little steep in price and don't know what they are doing, just call themselves roofers.



CMI 2004-2017 Retired

Awards Committee Member
U.S. Member of the Year Winner 2009
45 Years Residential/Commercial Builder
Submit your AWARDS NOMINATIONS here
The InterNACHI Awards Committee is the final authority of issuance of any award the committee offers and any rules updates.
Reply With Quote
  #26  
Old 12/16/11, 9:26 PM
James F. McKee's Avatar
James F. McKee James F. McKee is offline
Certified Professional Inspector (CPI)
 
Join Date: Feb 2007
Location: Lorain Ohio
Posts: 7,369
Default Re: Advice on bath exhaust vent termination.

Quote:
Originally Posted by cbottger View Post
Nah just wanted to rip your shorts knew you would be back, Buddy
Have a Merry Xmas Jim

You too Partner ...will be thinking about You guys on Monday...



Jim McKee
Lorain, Ohio
440 225 8688
www.classicinspector.com
Reply With Quote
  #27  
Old 12/17/11, 1:25 AM
An HI An HI is offline
Active Poster
 
Join Date: Oct 2011
Location: cyberspace
Posts: 286
Please Note: An HI is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Advice on bath exhaust vent termination.

Quote:
Originally Posted by mcyr View Post
I put my vent through the roof 4 years ago which is about 3' above the ceiling and never had a problem.
And anyone charging $350 should be thrown off the roof as Charley said. Took me two hours to install the fan and roof vent.


Mine is not insulated and my roof that I installed 16 years ago and flashing does not leak. Seems like roofers in your area are a little steep in price and don't know what they are doing, just call themselves roofers.
I have seen 2 small (1"+) icicles hanging from a interior fan cover a few years ago. It was a new package home from a major modular home company.

The bathroom was on the north corner of the house with the exterior vent outlet facing north. Got a call from the owner ( my life insurance guy) after a very cold February night.
Reply With Quote
  #28  
Old 4/11/18, 11:00 AM
Richard J. Triggs Richard J. Triggs is offline
InterNACHI Applicant
 
Join Date: Mar 2018
Posts: 11
Default Re: Advice on bath exhaust vent termination.

I have a question about a bathroom vent that terminates at a foundation vent in the crawl space, but does not extend through the vent to the exterior. Is this an acceptable installation? Thanks
Reply With Quote
Need a home inspection in South Carolina? Check out InterNACHI's listing of South Carolina certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #29  
Old 4/11/18, 11:04 AM
Roy Lewis, CMI's Avatar
Roy Lewis, CMI Roy Lewis, CMI is online now
Certified Master Inspector ®
 
Join Date: Nov 2012
Location: North Florida
Posts: 13,565
Default Re: Advice on bath exhaust vent termination.

No! It should went through the exterior wall.




InterNACHI Lifetime Member.
www.1stproinspection.com
roy@1stproinspection.com
Serving Gainesville Florida and surrounding areas.
Florida Certified Contractor #CRC1328001
Florida Certified Home Inspector #HI7019
Deus solus me iudicare potest
#1st Pro Inspection
Well! They may have degrees, but that is not an indicator of common sense or right thinking...M. Larson circa 9-27-2018.
Reply With Quote
  #30  
Old 4/12/18, 5:13 AM
Joshua L. Frederick Joshua L. Frederick is online now
Certified Professional Inspector (CPI) ®
 
Join Date: Jan 2007
Location: Defiance, OH
Posts: 4,903
Send a message via AIM to jfrederick
Default Re: Advice on bath exhaust vent termination.

Quote:
Originally Posted by rtriggs View Post
I have a question about a bathroom vent that terminates at a foundation vent in the crawl space, but does not extend through the vent to the exterior. Is this an acceptable installation? Thanks
How would a bath vent terminate at a crawlspace, was it a basement bathroom?




http://aspecresidential.com

Defiance home inspector
Northwest Ohio home inspector
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Sidewall vent termination code update vmitchinson Inspecting HVAC Systems 0 9/16/10 11:14 PM
Is a bath vent fan ok over the stove? rwashington Inspecting HVAC Systems 5 7/23/09 6:08 PM
Question on vent termination gwilcox Inspecting HVAC Systems 4 6/23/09 11:26 PM
Gas and oil hot water tank and Boiler Share Vents hvanderbeek Miscellaneous Discussion for Inspectors 8 1/25/07 6:22 PM

All times are GMT -4. The time now is 7:28 PM.
no new posts