My observation is that this should be a 4 wire feed to the sub panel and the bond screw be removed from the sub panel. Please let me know if this could be refuted and if this set up is acceptable.
Thanks
3 wire feed to sub panel new construction-dscn5259-jpg
3 wire feed to sub panel new construction-dscn5261-jpg
Need a home inspection in Maryland? Check out InterNACHI's listing of Maryland certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
Old 2/4/19, 5:31 PM
Robert Meier's Avatar
Default Re: 3 wire feed to sub panel new construction
Yes the bonding screw should be removed. Is that a metal raceway between the panel and the disconnect? If so that is the "4th wire' which is actually the EGC. If it's PVC then you're correct an additional conductor is required to serve as the EGC.
Old 2/4/19, 6:26 PM
Thanks
Old 2/5/19, 6:39 PM
Michael PARKS Michael PARKS is online now
Community Guest
Please Note: mparks2 is a non-member guest and is in no way affiliated with InterNACHI or its members.
DO NOT removed the bonding screw!