Here is an 80 AMP breaker on 6 AWG conductor feeding a furnace/heat pump condenser. The Furnace/heat pump condenser has a 60 AMP breaker. Therefore the load should not pull more than 60 AMPS? Right??

PICT0136 (Small).JPG

PICT0136 (Small).JPG

PICT0101 (Small).JPG

I don’t see any problems here Mark.

This is where the dataplate on the equipment need to be consulted for the proper Minimum Circuit Ampacity and the Maximum Overcurrent Size.