Condo panel...

My brain isn’t functioning properly after a long week, so would love some input. Inspected a condo today with grounds and neutrals terminating on the same bus bar. My question: is any panel downstream from the main disconnect a distribution panel, and thus subject to the separated grounds and neutrals rule?

There were a host of other serious problems with this panel and the wiring in the unit so am recommending further evaluation by a QEC, but want to be sure I’m not wrong in pointing out the grounds/neutrals issue.

You did good. Those are obviously added branch circuits with grounds on the neutral bar…should be on a ground bar bonded to the enclosure. The original grounding is through the emt conduit.

Thanks, Brad. Much appreciated.