Default Double Tapped Breaker clarifiction

Good Evening Gentlemen
First time posting on this thread.
I did a 4 Point today and found a Cutler-Hammer breaker with a double-tap. The breaker is labeled a "1 Pole Unit". I think I am correct in calling out this as a deficiency, however the last Inspector that did a 4 Point here (2005) labeled it as a legitimate breaker rated for two conductors, in other words...he passed it. Please advise if you have a moment

Thanks so much Matt
Attached Thumbnails
Double Tapped Breaker clarifiction-p1090436-jpg  
Reply With Quote
Need a home inspection in Georgia? Check out InterNACHI's listing of Georgia certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 12/18/18, 7:22 PM
Bradley K. Toye, CMI's Avatar
Bradley K. Toye, CMI Bradley K. Toye, CMI is online now
Certified Master Inspector
 
Join Date: Sep 2010
Location: Clearwater, FL
Posts: 5,437
Default Re: Double Tapped Breaker clarifiction

That particular CH breaker is not listed for two conductors. It has nothing to do with being a 1-pole breaker.



Brad K Toye
ITC/FLIR Level I Building Investigation Thermographer
FL Certified Building Contractor CBC034303
FL Certified Home Inspector HI 391
FL Certified Mold Assessor MRSA 589

727-403-5029
Lecsi2@gmail.com
Reply With Quote
  #3  
Old 12/18/18, 7:44 PM
Dave Fetty, CMI's Avatar
Dave Fetty, CMI Dave Fetty, CMI is online now
Certified Master Inspector ®
 
Join Date: Feb 2014
Location: Naples all SWFL
Posts: 12,118
Default Re: Double Tapped Breaker clarifiction

Brad is spot on... as usual




Dave Fetty Certified Master Inspector
Florida Home Inspection And Property Services LLC
www.FHIAPS.COM
www.NaplesBestInspector.com
www.FortMyersInspector.com
Naples, Marco Island, Ft. Myers, Bonita Springs, Estero, Cape Coral
Dfetty@FHIAPS.COM
http://https://www.facebook.com/pages/Flori...2450912?ref=hl
Florida Radon Measurement Technician R2547
(239)339-7380
Reply With Quote
  #4  
Old 12/18/18, 8:17 PM
Jim Port Jim Port is online now
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 2,690
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Double Tapped Breaker clarifiction

Sorry, I agree with the other inspector. CH breakers are listed for two conductors.
Reply With Quote
  #5  
Old 12/18/18, 8:31 PM
Marc A. Goldenberg's Avatar
Marc A. Goldenberg Marc A. Goldenberg is offline
Certified Professional Inspector (CPI) ®
 
Join Date: Feb 2004
Location: Boca Raton, FL
Posts: 7,185
Default Re: Double Tapped Breaker clarifiction

Quote:
Originally Posted by Jim Port View Post
Sorry, I agree with the other inspector. CH breakers are listed for two conductors.
Jim, as far as I concerned, you're the expert electrician here who freely helps out.
All CH are OK, or you can determine by the pic presented?
<<MG>>



http://www.alltropic.com


~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Awards Committee Member
SUBMIT YOUR AWARD NOMINATIONS HERE

The InterNACHI Awards Committee is the final
authority of issuance of any award the committee offers.
Reply With Quote
  #6  
Old 12/18/18, 9:13 PM
Jim Port Jim Port is online now
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 2,690
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Double Tapped Breaker clarifiction

I am seeing the conductors on each side of the screw head under a clamp plate. The side of the breaker should also be marked.
Reply With Quote
  #7  
Old 12/18/18, 9:18 PM
Michael S. Gleeson, 16000070526 Michael S. Gleeson, 16000070526 is online now
Certified Professional Inspector (CPI) ®
 
Join Date: Feb 2016
Location: Lancaster, NY
Posts: 629
Default Re: Double Tapped Breaker clarifiction

It is a type CH. It is rated for two conductors under the plate. See specifications tab here:
CH120 Eaton Cutler-Hammer 1P 20A 120V Breaker




Michael Gleeson, CPI
InFocus Inspection
NY License: 16000070526
716-548-0610
Serving Western NY including Erie, Niagara, Wyoming and Genesee Counties
http://www.infocusinspection.com
http://www.inspectwny.com
Reply With Quote
  #8  
Old 12/18/18, 9:23 PM
Jim Port Jim Port is online now
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 2,690
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Double Tapped Breaker clarifiction

Quote:
Originally Posted by mgleeson View Post
It is a type CH. It is rated for two conductors under the plate. See specifications tab here:
CH120 Eaton Cutler-Hammer 1P 20A 120V Breaker
Thanks for posting the documentation.
Reply With Quote
  #9  
Old 12/18/18, 10:02 PM
Marc A. Goldenberg's Avatar
Marc A. Goldenberg Marc A. Goldenberg is offline
Certified Professional Inspector (CPI) ®
 
Join Date: Feb 2004
Location: Boca Raton, FL
Posts: 7,185
Default Re: Double Tapped Breaker clarifiction

Quote:
Originally Posted by Jim Port View Post
I am seeing the conductors on each side of the screw head under a clamp plate. The side of the breaker should also be marked.
Thanks Jim.
Pic too dark for me to see the clamp.



http://www.alltropic.com


~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Awards Committee Member
SUBMIT YOUR AWARD NOMINATIONS HERE

The InterNACHI Awards Committee is the final
authority of issuance of any award the committee offers.
Reply With Quote
  #10  
Old 12/19/18, 9:47 AM
Chuck Evans's Avatar
Chuck Evans Chuck Evans is online now
Certified Master Inspector ®
 
Join Date: Sep 2006
Location: Stagecoach, TX
Posts: 10,886
Default Re: Double Tapped Breaker clarifiction

Quote:
Originally Posted by mgoldenberg View Post
Thanks Jim.
Pic too dark for me to see the clamp.
You don't see the clamp plate because there is no clamp plate. The conductors are secured directly under the screw head.

I think I would want to see the breaker label before I decided it's OK as is.

Double Tapped Breaker clarifiction-untitled-1-jpg
Attached Thumbnails
Double Tapped Breaker clarifiction-untitled-1-jpg  



Chuck Evans (TREC #7657)
Level III Infraspection Institute Certified Infrared Thermographer (#8402)
HomeCert Houston Home Inspections & Thermal Inspections Find us on Facebook
The Woodlands Home Inspections
Magnolia TX Home Inspections & Thermography


Houston, TX
_______________________
Awards Committee Member

SUBMIT YOUR AWARD NOMINATIONS HERE

The InterNACHI Awards Committee is the final authority of issuance of any award the committee offers.
Reply With Quote
  #11  
Old 12/19/18, 10:15 AM
Matt Durst Matt Durst is offline
Certified Professional Inspector (CPI) ®
 
Join Date: Feb 2018
Location: Boca Raton FL
Posts: 44
Default Re: Double Tapped Breaker clarifiction

I guess I will eat a little crow on this inspection. But at the end of the day, its my (our) #1 job to "get it right". I appreciate the documentation you supplied Michael, I amended my original report and re-sent. This forum is amazing in the ability to get experienced perspectives on tricky stuff like this. Thank you all for responding
Matt
Reply With Quote
  #12  
Old 12/19/18, 10:18 AM
Bradley K. Toye, CMI's Avatar
Bradley K. Toye, CMI Bradley K. Toye, CMI is online now
Certified Master Inspector
 
Join Date: Sep 2010
Location: Clearwater, FL
Posts: 5,437
Default Re: Double Tapped Breaker clarifiction

Sorry guys. This has been discussed many times. The older CH breakers with metal claw feet are not listed for two conductors. These have the conductor terminate under the screw head. The CH breaker that IS listed for two conductors has a plastic claw foot and the conductors terminate under a compression clamp well below the screw.



Brad K Toye
ITC/FLIR Level I Building Investigation Thermographer
FL Certified Building Contractor CBC034303
FL Certified Home Inspector HI 391
FL Certified Mold Assessor MRSA 589

727-403-5029
Lecsi2@gmail.com
Reply With Quote
  #13  
Old 12/19/18, 10:18 AM
Michael Larson's Avatar
Michael Larson Michael Larson is online now
Certified Professional Inspector (CPI)
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 75,337
Default Re: Double Tapped Breaker clarifiction

Quote:
Originally Posted by mdurst View Post
I guess I will eat a little crow on this inspection. But at the end of the day, its my (our) #1 job to "get it right". I appreciate the documentation you supplied Michael, I amended my original report and re-sent. This forum is amazing in the ability to get experienced perspectives on tricky stuff like this. Thank you all for responding
Matt
You were right. Why eat crow?



As a Professional Home Inspector, I support the privacy of my clients.

You own your private information. I won't sell or give away yours, others do


www.InspectraPro.com
www.MinnesotaHomeInspector.biz

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Call me


Reply With Quote
Need a home inspection in Georgia? Check out InterNACHI's listing of Georgia certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 12/19/18, 10:35 AM
Bradley K. Toye, CMI's Avatar
Bradley K. Toye, CMI Bradley K. Toye, CMI is online now
Certified Master Inspector
 
Join Date: Sep 2010
Location: Clearwater, FL
Posts: 5,437
Default Re: Double Tapped Breaker clarifiction

This is the termination point of a CH listed for two conductors.
Attached Thumbnails
Double Tapped Breaker clarifiction-elec-ch-conductor-jpg  



Brad K Toye
ITC/FLIR Level I Building Investigation Thermographer
FL Certified Building Contractor CBC034303
FL Certified Home Inspector HI 391
FL Certified Mold Assessor MRSA 589

727-403-5029
Lecsi2@gmail.com
Reply With Quote
  #15  
Old 12/19/18, 11:09 AM
Chuck Evans's Avatar
Chuck Evans Chuck Evans is online now
Certified Master Inspector ®
 
Join Date: Sep 2006
Location: Stagecoach, TX
Posts: 10,886
Default Re: Double Tapped Breaker clarifiction

Quote:
Originally Posted by mdurst View Post
I guess I will eat a little crow on this inspection. But at the end of the day, its my (our) #1 job to "get it right". I appreciate the documentation you supplied Michael, I amended my original report and re-sent. This forum is amazing in the ability to get experienced perspectives on tricky stuff like this. Thank you all for responding
Matt
Now you need to change it back to what you started with



Chuck Evans (TREC #7657)
Level III Infraspection Institute Certified Infrared Thermographer (#8402)
HomeCert Houston Home Inspections & Thermal Inspections Find us on Facebook
The Woodlands Home Inspections
Magnolia TX Home Inspections & Thermography


Houston, TX
_______________________
Awards Committee Member

SUBMIT YOUR AWARD NOMINATIONS HERE

The InterNACHI Awards Committee is the final authority of issuance of any award the committee offers.
Reply With Quote